The lay-in lugs are not listed for use outdoors and will weld up with rust in 
little time.

Best bet is to replace the lug only with one of the several available that are 
listed for direct burial and have been used to bond modules in years past. It 
is a compromise as the bushing itself is not listed for use outdoors either, 
but I think it is the lay-in lug that is the big problem.

I believe this has been discussed here in the past.

 

BTW, it is not being used as a strain relief, just a conduit end protector 
(there is no gripping of conductors) and a conduit bonding point.

 

-Glenn

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of AE Solar
Sent: Tuesday, February 16, 2016 5:51 PM
To: RE-wrenches
Subject: [RE-wrenches] MIGB's

 

Wrenchers,

What are you all using as strain reliefs on the ends of conduit runs that run 
between arrays on roof mounts? We have arrays on two roof sections with a piece 
of rigid conduit connecting the two,  and galvanized MIGB's (ground bushings 
maybe some people call them?) on each end of the pipe. It was just cited on an 
inspection that this was improper use of equipment because the galv MIGB's are 
not rated for outdoor use? Anyone have anything to back up the use of this 
method or have a preferred method for strain relief and bonding for this 
application? Thanks for any thoughts.

Adam




Adam Katzman
Autonomous Energies
PO Box 1245

Kingston, NY 12402
www.autonomousenergies.com
(518) 567-1468

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to