HI August,

I guess my question is.  
Are they asking for a lockout AC disconnect on a AC circuit IE from the AC 
panel?
or
are they asking for a lockout from the inverter AC at the inverter?

thanks
jay

peltz power


> On Apr 28, 2016, at 3:11 PM, August Goers <aug...@luminalt.com> wrote:
> 
> Hi Wrenches,
>  
> We have a particular plan checker who wants us to provide a lockable AC 
> disconnect for our inverter output circuit. His particular issue is that he 
> wants the locking mechanism to be installed and on site. Here is a little NEC 
> background info:
>  
> 2014 NEC 705.22 Disconnect Device
> The disconnecting means for ungrounded conductors shall consist of a manually 
> or power operable switch(es) or circuit breaker(s) with the following 
> features:
> (1)    Located where readily accessible
> (2)    Externally operable without exposing the operator to contact with live 
> parts and, if power operable, of a type that could be opened by hand in the 
> event of a power-supply failure
> (3)    Plainly indicating whether in the open (off) or closed (on) position
> (4)    Having ratings not less than the load to be carried and the fault 
> current to be interrupted. For disconnect equipment energized from both 
> sides, a marking shall be provided to indicate that all contacts of the 
> disconnect equipment might be energized.
> Informational Note to (4): In parallel generation systems, some equipment, 
> including knife blade switches and fuses, is likely to be energized from both 
> directions. See 240.40.
> (5)    Simultaneous disconnect of all ungrounded conductors of the circuit
> (6)    Capable of being locked in the open (off) position
>  
> NEC 110.25 Lockable Disconnecting Means:
> Where a disconnecting means is required to be lockable open elsewhere in this 
> Code, it shall be capable of being locked in the open position. The 
> provisions for locking shall remain in place with or without the lock 
> installed. 
>  
> Many times we are using a standard back-fed circuit breaker to comply with 
> 705.22. Then we can supply a handle padlock attachment such as the one shown 
> for Square D:
>  
> http://static.schneider-electric.us/assets/pdf/retail/QO-and-Homeline-Accessories.pdf
>  
> <http://static.schneider-electric.us/assets/pdf/retail/QO-and-Homeline-Accessories.pdf>
>  
> Does anyone else have experience installing these breaker handle padlock 
> attachments? My concern is whether we can find them for all of the old types 
> of breakers that we have to deal with. Also, our plan checker is requiring 
> that this handle padlock attachment accessory is installed at the time of our 
> inspection. Is anyone else dealing with similar issues?
>  
> Best,
>  
> August
> Luminalt
>  
>  
>  
>  
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to