Thimbles are easy to install and make fine strand wire OK for use in standard 
connections. 

Jay
Peltz power. 

> On Aug 8, 2016, at 5:39 PM, Glenn Burt <glenn.b...@glbcc.com> wrote:
> 
> Be aware that depending upon the vintage of the Engage cable, up to recently 
> the conductors used in their cables are fine stranded and cannot be used in 
> the terminal blocks provided with the Soladeck. 
> This has been acknowledged by Enphase with a revision to their Engage 
> manufacturing spec, and by Soladeck to me in writing. One fix is to confirm 
> the date of manufacturer of the Engage cable ( much of the fine strand 
> version remains in distribution). Another is to source appropriate ferrules 
> to be crimped onto the fine stranded conductors before using them in the 
> standard Soladeck terminals.
> 
> Also beware of the same issue if you are splicing with these older Engage 
> cables. Most screw terminals like Polaris are also not listed for use with 
> fine stranded conductors. NSI has a special Polaris terminal that is grey 
> that is listed for use with fine stranding, and can safely be used.
> I saw a few incorrect Polaris blocks pulled from an installation recently 
> that had melted...
> From: Michael Morningstar
> Sent: ‎8/‎8/‎2016 15:23
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
> 
> I use DIN rail mount "feed through" terminal blocks. There's all kinds and 
> you will find some constructed such that no live parts exposed.
> Michael
> 
>> On Aug 8, 2016, at 8:49 AM, Jason Szumlanski 
>> <ja...@floridasolardesigngroup.com> wrote:
>> 
>> I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an 
>> enclosure inside the attic where I can transition to Romex. I'd rather use 
>> some kind of rail mounted terminals in an enclosure or something rather than 
>> making splices in a generic j-box. I'm not looking to combine circuits - 
>> just transition from THWN to Romex and keep things neat an organized.
>> 
>> Any suggestions?
>> 
>> Jason Szumlanski
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to