Mike,
Jay's suggestion to turn off string three, the low one, is good. Plus I can guide the homeowner by phone, thus avoiding the cost of another site visit, so that adds appeal.

I just spoke with him. While he lacks the DMM and DC amp clamp, he is going to record V and I in and out for each string, using the MX60 display as his data source. I'll post any noteworthy results here. We're in monsoon season (afternoon cloud buildup and thunderstorms) so it may not be for a few days.

Re Jerry's comments: I think that you mean an I/V curve tracer test, rather than Solmetric, right? That's not a tool I have or will get for my current work, but it's a good idea, thanks. The client and I are pretty much in agreement that we're dealing with serious browning - indeed, more than I have ever seen with BP 75W modules of this vintage (my own home's 18 BP590 modules of similar age show very little browning and about 15% degradation, rather than 50%) and aren't worth the cost of a whole bunch of testing. Mostly, we're looking for any specific and correctable cause, as we have one spare matching module in storage, and I also simply posted to seek answers as to why the Vmp was so low.

Jerry, it was selling, so the voltage would be held around the sell level of 26.4V. The inverter is set to the default sell AC amps, 35A as I recall and the MX60 is defaulted to 60A output, so they aren't causing any restrictions. The batteries are known to be used up - indeed, we want to better understand the array issue in order to help determine whether to replace the SunXtender AGMs for backup power or just leave the system in a state of benign neglect. The client is considering our suggestion to install a separate grid-tied batteryless system once he has lived in the home for a year or so to determine consumption. This legacy system would pretty much just be backup, as with hardware that old a new array as well as batteries is hard to justify.

Thank you to all. More to come later if we learn anything worth sharing.
Allan

*Allan Sindelar*
al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

**

On 8/26/2016 10:14 AM, Mike Kocsmiersky wrote:

Your measurements of the Isc for the four stings seems to be odd in string 3 with only 2.4A. However, when you measure the circuit under load, you are getting 14.6A from all 4 strings, which averages 3.65A. I’d say check that string again, perhaps the current clamp wasn’t zeroed or something.

First I would try reading the MPPT voltage and current for each string individually connected to the load. If one of the strings had a bad diode, I’m not sure it would show up in a Voc test. Perhaps a bad bypass diode could give the MPPT algorithm a difficult time finding the MPPT of the array, and it gets stuck on curve of the one string that has a bad diode.

Also, it could be more of an issue with the MPPT controller thinking the array is a 24V Array, or some other controller failure. I would look there.

Mike Kocsmiersky

Principal

Phone: 413 883-3144

*Spirit Solar*


Can you do a solmetric type test, when you performed the amp test the volts were at near "0" so the test does not show an accurate value, you said the modules are brown this is not good but are they checked because if so you are done needs new modules. I would suggest doing some additional testing, is it selling, and at what amount, whats going into or out of the batteries at that time, what inverter is it, trace 24 I would assume, if it is selling is the inverter capable of selling more than it is or is at the limit, I need more numbers to get a better understanding if there is even a problem. You can adjust "Sell" down to perform a test and see if the DC climbs, also you can set the MX amp down too.
Jerry
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to