I too would like to know the make and model of batteries that are loosing 
capacity. In the past 5 years we have experienced abnormally high failures from 
2 brands. 

Larry

On Jan 15, 2018, at 2:00 PM, Jay <jay.pe...@gmail.com> wrote:

Can you tell us:

Battery make,model and size?

Jay
Peltz power. 

On Jan 15, 2018, at 12:32 PM, Daniel Young <dyo...@dovetailsolar.com 
<mailto:dyo...@dovetailsolar.com>> wrote:

> Hello Wrenches,
>  
> I have a client that is running into an issue with his off grid system. The 
> system is 3yrs old and they are starting to notice their AGM battery bank is 
> loosing capacity, in reality they are noticing the generator is triggering 
> more often. They want to try to lower the frequency of the generator 
> triggering if possible.
>  
> The system is not occupied during much of the winter (unconditioned, which 
> further hurts the battery bank capacity), but the client has a security 
> system with a cell modem installed and always on. This fortunately allows 
> Optics-RE access, but unfortunately based on the FNDC shunt readings, is 
> pulling a consistent 150w from the battery bank. Currently the network and 
> security equipment is powered from standard wall-warts running on AC.
>  
> I’d like to help the client extend the time between generator cycles by 
> taking the network loads and powering them directly from the battery bank 
> (the loads are all 12Vdc). Does anyone have any recommendations for a decent 
> quality DC_DC converter that would be applicable? Given inverter losses and 
> the efficiency of the typical wall-wart, I’d expect the running loads to be 
> closer to 80-100w rather than the 150w we see now. The intent is to then take 
> the inverter into search mode, or even switch it off, to remove the tare 
> losses there, and also to take all the wasted power from the standard 
> wall-warts and go to a single, more efficient dc power supply.
>  
> Any recommendations on a good DC_DC converter are appreciated.
>  
> With Regards,
>  
> Daniel Young, 
> NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
> Dovetail Solar and Wind
>  
> __________________________
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to