Hi William -

This article is a few years old, but I think describes ground fault
detection issues well:
http://www.solarabcs.org/about/publications/reports/blindspot/pdfs/inverter_groundfault-2013.pdf


I don't have experience (at least since the late 90s) with the type of GFD
breaker you describe on the DC-side PV circuit. We switched to AC coupled
systems with standard grid tied inverters (transformerless non-isolated)
years ago. What kind of setup are you referring to?

Best,

August

Luminalt



On Mon, Jul 22, 2019 at 1:42 PM William Miller <will...@millersolar.com>
wrote:

> Wrenches:
>
>
>
> Here is a question that has bothered me for some time:  If one is using a
> GFD (ground fault detection) breaker on a PV feeder(s) to a battery
> inverter system, the state of the industry is to use a breaker with an
> extra 0.5 or 1 amp pole.  This section of the breaker connects, or bonds
> the DC negative, or grounded conductor, to the grounding system.
>
>
>
> In order for the GFD breaker to work one needs to isolate the grounded bus
> bar (negative).  If there is a ground fault the breaker opens and breaks
> the bond.
>
>
>
> This goes very much against my conceptualization of how a bonding system
> should work.  The bond should never be broken, particularly when there is a
> fault in the system.  When this breaker opens, either manually or by an
> overcurrent condition on any pole, the DC bond is removed for all portions
> of the DC system.
>
>
>
> There is a prominent personality in the industry that often presents
> academic opinions on solar related electrical issues in articles and in
> seminars.  This person claimed to have invented this GFD system, but when
> pressed to comment on the concerns mentioned above, changed the subject.
>
>
>
> I believe ground fault protection is important.  I just don’t believe the
> method the industry has offered is really effective in solving the issues
> presented in a ground fault scenario.
>
>
>
> I believe similar issues present on non-battery PV systems with the simple
> fuse in the ground system found on many inverters.  I know some
> troubleshooting guides warn of energized parts in ground fault conditions.
>
>
>
> Have any of you thought about these concerns?  Are my concerns valid?
> What are your policies on this subject?
>
>
>
> Thanks in advance for any insight.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
> Quote of the month:  “As they age, batteries transition from energy
>
> storage devices to energy consuming devices.“ W. Miller
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to