Hey Wrenches,

So the upshot from this soft start thread is it turns out that with today's electronics just about any motor can be soft start BUT Sewage Macerator pumps can't!  They will most likely clog if started up at anything but full RPM and torque.

So be aware if a customer you have has a sewage macerator pump - especially with high head - if they do and you are designing an off-grid system - suggest you take a Fluke 350 meter or oscilloscope - start the pump if already installed on a beefy generator and test the inrush and voltage lag etc.

If not installed you probably need to plan for the full Locked Rotor Amps (LRA) and get an inverter with a rating that can withstand that for 5 secs.

Thanks to all for your input,

Best,

Jeff Clearwater
Village Power Design




Jeff Clearwater wrote on 7/29/19 9:59 AM:

Hey Chris and Wrenches,

So I talked to Steve at Gen Pro and he says that his soft starts are intended to be used for LRA conditions where there is a load against the shaft on start-up - although they do do some well pumps.  See below - still searching!

Thanks though cause he is going to have his engineers look at it.

From their website FAQ:


How do I verify SureStart is performing as stated?

To verify LRA reduction in a field installation, technicians will require a device that can capture inrush current and display this LRA value in a digital readout.  FLUKE® 375 Clamp Meter is one such tool that is available for field use.  Although not as accurate as an oscilloscope (which is required to test and rate LRA for compressors), this device should allow field technicians to verify SureStart performance when used properly.

The LED portal on the front cover of SureStart can also be used to verify operation.  A steady, non-flashing light indicates SureStart is wired and operating properly.  If the LED light is flashing, this indicates a "fault" condition.  Please review Installation Instructions, Specification Catalog, or Submittal Sets to determine the fault codes.

Can I apply SureStart to well pumps or other applications?

Although no significant testing has been done, well pump applications have had SureStart applied successfully. Please review the requirements for reciprocating/rotary compressors as they pertain to starting "under a load."  SureStart is designed to start direct, across-the-line motor starts that have ZERO load applied on the motor shaft.  If there is a load on the compressor or pump motor at startup, SureStart should not be applied.


Compressor motor RLA considerations are also necessary to verify potential operation.

SureStart should not be applied to "squirrel-cage" or other types of fans.

SureStart is an electrical device and should be mounted in a protected compartment.

In the future, we hope to publish Specifications for well pump



Best,

Jeff Clearwater
Village Power Design



Chris Schaefer wrote on 7/29/19 8:39 AM:

I've been following this post with great interest. I was looking at an off-grid project a couple years back that was being run entirely by large diesel generators and had two massive AC units where the LRA was 104 Amps. I found a company that makes what amounts to a soft start. I don't recall the engineer/owners name but he was very knowledgeable. His number is 813-601-0947 and web site is gen-pro.biz <http://gen-pro.biz>. To finish the client never made the switch from generator to solar so I can't say if these units work. Hope this provides another option.

Sincerely,
Christopher

/229-2083 or Cell 585-748-1870
//5115 South Hill Road ~ Canandaigua New York 14424
//www.solarandwindfx.com <http://www.solarandwindfx.com/> ~ E-mail: ch...@solarandwindfx.com <mailto:ch...@solarandwindfx.com>/

/
/

Thomas Jefferson, the author of our great Constitution, once said, "democracy" will cease to exist when you take away from those who are willing to work and give to those who would not."


On Fri, Jul 26, 2019 at 4:15 PM Jeff Clearwater <je...@villagepowerdesign.com <mailto:je...@villagepowerdesign.com>> wrote:

    Hey Jerry,

    I think the issue is capacitor start motors can't handle VFDs. 
    but there are other approaches to soft start - still learning. 
    Thanks for the reference!

    Best,

    Jeff

    Jerry Shafer wrote on 7/26/19 12:59 PM:

    Wrenches
    I have quite a few freq drives on single phase, the controller
    came from ABB, the pic attached is reference only, it was for a
    AC chiller grid connected not off grid but the controller works
    either way
    Jerry

    On Fri, Jul 26, 2019, 12:47 PM Jeff Clearwater
    <je...@villagepowerdesign.com
    <mailto:je...@villagepowerdesign.com>> wrote:

        Thanks Chris!

        Unfortunately I'm finding that unless you build an
        integrated control - motor combo that can soft start like
        Franklin did - the majority of single phase motors can't use
        soft start.  That is probably a 3-phase motor in that pump
        that they have an inverter for in the controls - or they
        used a shaded pole or spit capacitor single phase motor
        which can use soft start - at least that is what my initial
        research and phone call to the pump control company has thus
        far revealed.

        Apparently you can play with the voltage-amperage tradeoffs
        when you have the 3 magnetic fields interaction - single
        phase doesn't allow you much room to wiggle.

        I do see single phase soft-starts on the market - still
        researching but that's my initial findings.

        Anyone know differently?

        Thanks!

        Jeff



        ch...@oasismontana.com <mailto:ch...@oasismontana.com> wrote
        on 7/26/19 9:27 AM:

        Here at the Oasis home/office, we have a Goulds 3 hp 240VAC
        soft start pump (#18GS30, w/ Franklin motor HS09970 and
        #3AS30 Aquavar Solo controller); it’s been running off of
        my 2011 Radian GS8048 since 2016, when I had to drill a new
        well (the water table is dropping) and pump from about 300
        ft. depth.I have 3500 ft. of drip irrigation, a big garden
        and the usual domestic water loads.It’s worked flawlessly
        since its inception, and I cannot speak more highly of
        Goulds pumps.My first one lasted 23 years (it was a 1.5HP
        model).

        Best,

        Chris Daum

        Oasis Montana Inc.

        406-777-4309 or 4321

        406-777-4309 fax

        www.oasismontana.com <http://www.oasismontana.com>

        *From:*RE-wrenches
        <re-wrenches-boun...@lists.re-wrenches.org>
        <mailto:re-wrenches-boun...@lists.re-wrenches.org> *On
        Behalf Of *Dana
        *Sent:* Friday, July 26, 2019 9:34 AM
        *To:* 'Jeff Clearwater' <je...@villagepowerdesign.com>
        <mailto:je...@villagepowerdesign.com>; 'RE-wrenches'
        <re-wrenches@lists.re-wrenches.org>
        <mailto:re-wrenches@lists.re-wrenches.org>
        *Subject:* Re: [RE-wrenches] Soft Start Modules for Well
        and Sewage Pumps?

        Yes I have used soft starts offgrid with SW & VFX for 15+
        years, in spite of doing load evaluations & others
        installing what ever they normally used. It has been a
        great rescue device. Well pump, 2 dish washers, booster
        pump, etc.

        Dana Orzel                              Great Solar Works,
        Inc.

        *C - 208.721.7003 d...@solarwork.com
        <mailto:d...@solarwork.com>*

        Idaho Contractor - # 028765         Idaho PV # 028374

        NABCEP # 051112-136 www.solarwork.com
        <http://www.solarwork.com>

        _"Responsible Technologies for Responsible People since 1988" _

        *P*Please consider the environment before printing this email.

        *From:*RE-wrenches
        <re-wrenches-boun...@lists.re-wrenches.org
        <mailto:re-wrenches-boun...@lists.re-wrenches.org>> *On
        Behalf Of *Jeff Clearwater
        *Sent:* Friday, July 26, 2019 8:04 AM
        *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org
        <mailto:re-wrenches@lists.re-wrenches.org>>
        *Subject:* [RE-wrenches] Soft Start Modules for Well and
        Sewage Pumps?

        Hey Wrenches,

        Anyone have success using soft-start modules on well and
        sewage pumps to lower the surge for off-grid inverters?

        The baby we are trying to tame is a 2 HP 15 amp, 53 LRA
        Omnivore Grinder Pump - LSG200 series - single phase 230 Vac.

        Thanks!

        Jeff


        ~~~~~~~~~~~

        Jeff Clearwater
        Village Power Design
        linkedin
        <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
        www.villagepowerdesign.com <http://www.villagepowerdesign.com>
        cell - 413-559-9763
        ~~~~~~~~~~~~~~~~~~~~~~~


        Jeff Clearwater wrote on 7/26/19 6:32 AM:

            *Thanks Ray and Jerry,

            Great to hear from you both with your years of combined
            experience :)*

            *So yes looking at the 5 sec has me switching back to a
            trusty Radian - _even then from what you are saying it
            may not work._*

            And you are right Ray -  Outback is careful to rate the
            "overload capability" in KVA rather than KW due most
            likely to voltage sag of course.

            *So this 53 LRA 2 HP motor - if I can only trust the 5
            second (50 A) might not start - especially with other
            loads on the system?*

            *RADIAN SURGE RATINGS:*

            *Maximum Output Current*
            1 ms peak 100 Amps AC at 240 VAC, 200 Amps AC at 120 VAC
            100 ms RMS 70.7 Amps AC at 240 VAC

            *Overload Capability*
            100 ms surge 16.97 kVa
            5 seconds 12 kVa
            30 minute 9 kVa

            *Other's experience with 2 HP sewage pump or well pump
            motors on a Radian?

            Thanks!

            Jeff*


            Ray wrote on 7/25/19 5:48 PM:

                I only look at the 5 sec and 30 sec surge ratings
                to get an idea what an inverter can really do in
                the real world.  All those millisecond ratings/ in
                rush current specs won't get a pump or motor
                started, and will basically just get you into
                trouble. The reason they have those ratings in amps
                and not watts, is that the voltage craters during
                that 100mS surge.

                I can't tell you how many times we tried to start a
                pump, compressor, or large table saw, and the
                inverter just shut off, even though the "in rush
                current" was within the theoretical inverter
                capacity.  Actual Wrench list testimonials are much
                more valuable than those arcane specs.

                Ray Walters

                Remote Solar

                303 505-8760

                On 7/25/19 5:15 PM, Jeff Clearwater wrote:

                    *Hey There Wrenches,*

                    So be advised that after a little research the
                    SW dual stack will NOT double the surge ratings
                    of a single SW.

                    But that brings me to my second question:
                    *
                    What inverter surge rating should one refer to
                    when looking at maximum Inrush or LRA - 1ms? 
                    100ms?  1 sec?*

                    *Your engineering wisdom welcomed!*

                    Thanks,

                    Jeff



                    Jeff Clearwater wrote on 7/23/19 8:27 PM:

                        Thanks for the tip!  I'll check the firmware.

                        Dave Angelini Offgrid Solar wrote on
                        7/22/19 9:11 AM:

                            Hi Jeff,

                            I am not going to guess if this will
                            work, it should.  I use XW's because
                            they start anything I have come across.

                            If you do this, make sure but SW's have
                            the latest and same firmware. There
                            were problems with stacked SW's early
                            on in their development.

                            **Dave Angelini Offgrid Solar**

                            **"we go where powerlines don't"**

                            **http://members.sti.net/offgridsolar/**

                            **e-mail offgridso...@sti.net
                            <mailto:offgridso...@sti.net>**

                            **text 209 813 0060**

                            On Mon, 22 Jul 2019 07:26:07 -0700,
                            Jeff Clearwater
                            <je...@villagepowerdesign.com>
                            <mailto:je...@villagepowerdesign.com>
                            wrote:

                                Hey Esteemed Wrenches,

                                So I recently built a power trailer
                                with a single 4 KW (4048) Schneider
                                SW for a client with a moderate
                                cabin lifestyle.

                                But he lives on a high hill and
                                even though his 2 HP Macerator is
                                only rated at 15 amps continuous
                                that baby starts up with a whopping
                                kick - probably close to or at it's
                                53 Amps Locked Rotor rating.

                                *The SW has the following surge
                                capability:*

                                *SW 4048 Rated @ 240 Volts:*
                                Continuous - 15.2 Amps 3700 Watts
                                30 Minutes - 18.3 Amps 4400 Watts
                                5 Secs - 29.2 Amps 7000 Watts
                                Max (100ms?) - 41 Amps - 9840 Watts

                                Can I be confidant that 2 stacked
                                SWs will start this baby?

                                *Any experience with similar
                                macerators - or simply educated
                                guesses?
                                *
                                Thanks!

                                Jeff

--
                            **Dave Angelini Offgrid Solar**

                            **"we go where powerlines don't"**

                            **http://members.sti.net/offgridsolar/**

                            **e-mail offgridso...@sti.net
                            <mailto:offgridso...@sti.net>**

                            **text 209 813 0060**




                        _______________________________________________

                        List sponsored by Redwood Alliance

                        List Address:
                        RE-wrenches@lists.re-wrenches.org
                        <mailto:RE-wrenches@lists.re-wrenches.org>

                        Change listserver email address & settings:

                        
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                        List-Archive:
                        
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

                        List rules & etiquette:

                        www.re-wrenches.org/etiquette.htm
                        <http://www.re-wrenches.org/etiquette.htm>

                        Check out or update participant bios:

                        www.members.re-wrenches.org
                        <http://www.members.re-wrenches.org>



                    _______________________________________________

                    List sponsored by Redwood Alliance

                    List Address: RE-wrenches@lists.re-wrenches.org
                    <mailto:RE-wrenches@lists.re-wrenches.org>

                    Change listserver email address & settings:

                    
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                    List-Archive:
                    
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

                    List rules & etiquette:

                    www.re-wrenches.org/etiquette.htm
                    <http://www.re-wrenches.org/etiquette.htm>

                    Check out or update participant bios:

                    www.members.re-wrenches.org
                    <http://www.members.re-wrenches.org>



                _______________________________________________

                List sponsored by Redwood Alliance

                List Address: RE-wrenches@lists.re-wrenches.org
                <mailto:RE-wrenches@lists.re-wrenches.org>

                Change listserver email address & settings:

                
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                List-Archive:
                
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

                List rules & etiquette:

                www.re-wrenches.org/etiquette.htm
                <http://www.re-wrenches.org/etiquette.htm>

                Check out or update participant bios:

                www.members.re-wrenches.org
                <http://www.members.re-wrenches.org>




            _______________________________________________

            List sponsored by Redwood Alliance

            List Address: RE-wrenches@lists.re-wrenches.org
            <mailto:RE-wrenches@lists.re-wrenches.org>

            Change listserver email address & settings:

            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            List-Archive:
            
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

            List rules & etiquette:

            www.re-wrenches.org/etiquette.htm
            <http://www.re-wrenches.org/etiquette.htm>

            Check out or update participant bios:

            www.members.re-wrenches.org
            <http://www.members.re-wrenches.org>

-- ~~~~~~~~~~~

        Jeff Clearwater
        Village Power Design
        linkedin
        <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
        www.villagepowerdesign.com <http://www.villagepowerdesign.com>
        cell - 413-559-9763
        ~~~~~~~~~~~~~~~~~~~~~~~



        _______________________________________________
        List sponsored by Redwood Alliance

        List Address:RE-wrenches@lists.re-wrenches.org
        <mailto:RE-wrenches@lists.re-wrenches.org>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org
        <http://www.members.re-wrenches.org>


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: RE-wrenches@lists.re-wrenches.org
        <mailto:RE-wrenches@lists.re-wrenches.org>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



--

Chris Schaefer’s
<http:www.solarandwindfx.com>
/Tel/Fax 585-229-2083 or Cell 585-748-1870
//5115 South Hill Road ~ Canandaigua New York 14424
//www.solarandwindfx.com <http://www.solarandwindfx.com> ~ E-mail: ch...@solarandwindfx.com <mailto:ch...@solarandwindfx.com>/

/
/

Thomas Jefferson, the author of our great Constitution, once said, "democracy" will cease to exist when you take away from those who are willing to work and give to those who would not."




_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to