I was wiling away the time perusing a Radian (GS4048/GS8048) quick-start guide that came with a recently acquired set of Radians. I was quite surprised to see the AC inputs, outputs and throughputs are shown in the quick-start guide as rated at 60 Amp AC. The guide also indicates a minimum wire size of #6AWG (does not specify CU or AL, will assume CU). I always remembered that rating to be 50 Amps AC. I checked old and new installation manuals and they all say 50 Amps AC. Am I missing something? The guide also says: “Only one AC source can be wired at a time; use an external selector switch if more than one source is available.” It really sounds like this section was cut and pasted from an FX/FXR manual by mistake. Anyone catch this? Lones, you out there? William Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 Quote of the month: “As they age, batteries transition from energy storage devices to energy consuming devices.“ W. Miller
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org