All, thanks for the responses.  I greatly appreciate it.  Yes the 30 amp disco is non-fusible and rated for full load.  True, you have to check the manu's specs.  You _always_ should check the manufacturers specs.
Anyway, 705.22(4) indicates the disco:
/Have ratings sufficient for the maximum circuit current, //
//available short-circuit current, and voltage that is available //
//at the terminals/.
That rules out a 30 amp disco in this case.

Best,
Greg Egan
Remote Power Inc.

On 8/21/2019 3:20 PM, Greg wrote:
All, the engineer came back with 705.22(4) to back up his request.  I think that's the end of it.  Per code he is right but since the inverter is only capable of 25 amps, the only time the 30 amp disco would see more than 30 amps is if the inverter was shorted.  If that's the case opening the 30 amp disco at that time could cause failure.  Pretty unlikely event. Although I think installing a 60 on this circuit is an overabundance of caution but I'll be installing a 60 amp disco on this one.

Best,
Greg Egan
Remote Power Inc.


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to