Wrenches
There is a guy that has parts and boards for the SW4048 Inverters, l may
have got the name from this list, l will post it if there is any interest
Jerry


On Tue, Dec 24, 2019, 5:09 PM <d...@energysolarnow.com> wrote:

> Hi Dave
> Your experience here closely resembles mine on at least two jobs with
> these inverters.
> When the AC1in light blinks the inverter is no longer connected to the
> grid. The loads are running off battery power, but this will be short term
> in winter weather. I have a VFXR3648A in my truck now to replace an SW4048
> that has lost the ability to connect to the grid.  It killed the batteries
> in rainy weather, so they are being replaced as well.
>
> If you set the terminals of your meter from the AC1 input to the Load
> output you will see the voltage phase difference. If they are in phase the
> voltage difference is zero. In my case this voltage drifts from 0 to 240
> over a period of 15 secs or so, indicating the lack of sync.  I have not
> found anyone who repairs these old modified square wave inverters. The old
> SW4048 should still be good for off grid use.
> If anyone wants it let me know. Located in Bolinas, CA.
> At least I can go surfing after service calls there....
>
> Don Barch
> Energy Solar
>
>
> -------- Original Message --------
> Subject: RE-wrenches Digest, Vol 12, Issue 362
> From: re-wrenches-requ...@lists.re-wrenches.org
> Date: Tue, December 24, 2019 2:34 pm
> To: re-wrenches@lists.re-wrenches.org
>
> Send RE-wrenches mailing list submissions to
> re-wrenches@lists.re-wrenches.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
> or, via email, send a message with subject or body 'help' to
> re-wrenches-requ...@lists.re-wrenches.org
>
> You can reach the person managing the list at
> re-wrenches-ow...@lists.re-wrenches.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of RE-wrenches digest..."
>
>
> When responding to posts within the Digest, be sure to restore the
> Subject: line to the original, and please edit out any extraneous lines
> from the quoted message.
>
>
> Today's Topics:
>
> 1. Re: Xantrex SW 4048 grid tie mystery (Dave Tedeyan)
>
>
> ----------------------------------------------------------------------
>
> Message: 1
> Date: Tue, 24 Dec 2019 15:14:18 -0500
> From: Dave Tedeyan <dtede...@taitem.com>
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Xantrex SW 4048 grid tie mystery
> Message-ID:
> <ca+cq0bvfmczx5vakqo-1vhztqadvsob42hkg1--7no9emrr...@mail.gmail.com>
> Content-Type: text/plain; charset="utf-8"
>
> Hi All,
> So I went back today and updated all the programming. There was actually
> lots of sun too (a rare event in upstate NY this time of year)!
>
> The inverters have not yet had any issues with powering the backed up loads
> so far. But there have been issues with selling back to the grid. One
> inverter was selling just fine, with the sell current right around the max
> sell setting. The other inverter would very quickly ramp up its sell and go
> way past the setting (set at 30A) and start selling at up to about 60A, and
> then would stop selling (but continue to power the backed up loads. When
> selling, the AC1 in good light would stay on green solid. Then when the one
> inverter would stop selling, that light would flash. Then 5 minutes or so
> later, it would click a bunch of times, start selling, and within about 10
> seconds overshoot the setting again and kick off.
>
> I tried Tumps suggestion of removing the black jumper. When I did that in
> each inverter, neither one would sell, but they would continue to power the
> backed up loads.
>
> I also tried bypassing the GTI on the inverter that was having selling
> issues. When I did that, the AC1 in good light never came on at all, even
> though I verified AC voltage on the input. It never started selling, but it
> would at least continue to power the backed up loads. I only had it like
> this for about 15 minutes before I had to leave the site, so will be
> checking in on the system in the coming days. Last time I was there and
> fired it up, it worked fine to begin with and it was not until many hours
> later that the issues with powering the backed up loads started appearing.
>
> Cheers,
> Dave
>
> *Dave Tedeyan, PE*
> Senior Engineer | Taitem Engineering, PC
>
> 110 South Albany Street | Ithaca, NY 14850
> o. *607.277.1118 x121* f. 607.277.2119
> www.taitem.com
>
> Solar ? Sustainability ? Energy ? Design
> Certified B-Corporation since 2013
>
>
> On Sun, Dec 22, 2019 at 5:11 PM b...@midnitesolar.com <b...@midnitesolar.com
> >
> wrote:
>
> >
> > Forgot to say that if the inverters ARE grid tied, then they will NOT
> > drift around in phase and will
> >
> > be synchronized and therefore will stay in sync and be passing through
> > from grid to output.
> >
> > boB
> >
> >
> >
> > On 12/22/2019 12:57 AM, Jerry Shafer wrote:
> >
> > Well l would start simple and get a sync cable and make sure that they
> are
> > al least staying g in correct phasing, then look closely at the
> > programming, look at the grid voltages and settings, take it out of IEEE
> > for test purposes only, you might find out you have a board that's out of
> > calibration causing the issue but start simple
> > Jerry
> >
> > On Fri, Dec 20, 2019, 9:44 AM Dave Tedeyan <dtede...@taitem.com> wrote:
> >
> >> Hi All,
> >>
> >> I am someone's last ditch effort to get their system working which has
> >> been non-functional since a few months after installation, 13 years
> ago...
> >>
> >> After getting some new batteries in there, I can at least fire it up. It
> >> is a grid tie with battery backup situation with two Xantrex SW4048
> >> inverters. Each inverter is kind of like its own system with two Outback
> >> MX60 CC's per inverter, and each inverter powers its own 120V backed up
> >> loads panel. They do not see each other until their 60A single pole
> >> breakers in the main panel.
> >>
> >> What seems to be happening is that after turning on the inverters the
> AC1
> >> in good light will flash for about 30 seconds, then it syncs up to the
> grid
> >> and the light stays on solid. But then after a little bit, that light
> will
> >> start flashing, indicating that the utility power has been dropped,
> when it
> >> has not actually been dropped. Then at some point the backed up loads
> would
> >> lose power. The customer says that every 1-10 minutes, they would lose
> the
> >> backed up loads for 10-90 seconds. This happened all night long until
> they
> >> bypassed the inverters.
> >>
> >> There are a few other things of note:
> >> 1. There is a Xantrex GTI for each inverter.
> >> 2. I see in the manual there is information about stacking the
> inverters,
> >> but I am guessing in this setup this not necessary or would even be
> counter
> >> productive to stack the inverters. Not sure if the inverters not being
> >> stacked could cause one of them to unsync with the utility?
> >> 3. Neutrals and grounds are bonded in their main panel, but also in each
> >> of the Xantrex DC breaker boxes. I was going to separate them in the DC
> >> breaker boxes, but found that there is no way to isolate the battery
> >> negative bus from the box itself, and figured it would be dodgy to
> unground
> >> the enclosure. So I am also not sure if the multiple N-G bonds could be
> >> causing these issues.
> >>
> >> Does anyone have any ideas?
> >> Cheers,
> >> Dave
> >>
> >> *Dave Tedeyan, PE*
> >> Senior Engineer | Taitem Engineering, PC
> >>
> >> 110 South Albany Street | Ithaca, NY 14850
> >> o. *607.277.1118 x121* f. 607.277.2119
> >> www.taitem.com
> >>
> >> Solar ? Sustainability ? Energy ? Design
> >> Certified B-Corporation since 2013
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >>
> >> List Address: RE-wrenches@lists.re-wrenches.org
> >>
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> List-Archive:
> >>
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >>
> >> List rules & etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out or update participant bios:
> >> www.members.re-wrenches.org
> >>
> >>
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:www.members.re-wrenches.org
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> >
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20191224/4dfa8f2d/attachment-0001.html
> >
>
> ------------------------------
>
> Subject: Digest Footer
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> ------------------------------
>
> End of RE-wrenches Digest, Vol 12, Issue 362
> ********************************************
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to