Run the system without the branch that tripped. Sorry if I missed that
you have done this. I appreciate you reminding me why I keep all of the
electronics inside. I get tempted  

Dave Angelini Offgrid Solar
"we go
where powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail
offgridso...@sti.net [2]
text 209 813 0060

On Mon, 1 Jun 2020 10:23:35
-0400, Jason Szumlanski  wrote:  Well, that didn't resolve it. The main
breaker and a branch circuit breaker tripped again a few days ago. It was
the same branch this time.   As my next diagnostic step I swapped two
circuits (on which breaker they are landed). If history is a guide, it will
work for about two weeks and then trip again.   I'm dumbfounded. I really
don't want to have to tear this whole system apart. At this point, if I
have to remove all the modules, I feel that I need to replace all of the
trunk cable which is an expensive proposition. I really don't know what
else to do at this point.   Jason    
  On Mon, May 25, 2020, 10:43 AM
Jason Szumlanski  wrote:    I strongly suspect the CH240 combined breaker
was compromised (we will see). Since it happened that two different strings
tripped, I doubt I have two microinverters with internal faults. It has to
be the combined breaker. I was just surprised that branch circuit breakers
were tripping simultaneously with the combined output breaker.   Of all the
supply side connected systems I have installed, I have never seen a
combined output fusible disconnect fuse blow, but I have seen many combined
output breakers tripped. I was worried early on that I would be replacing
fuses constantly, but that has not been an issue whatsoever.             


On Thu, May 21, 2020 at 11:15 AM  wrote:    

Actually, we had a IQ7
string loaded up to its max panel size and max string length and in the
spring on cool, clear day, it tripped the string's associated breaker in
the Enphase combiner. 

We reset but of course that breaker was impaired
and it tripped again. We replaced and never had an issue going forward. We
suspect the breaker was less than perfect from the start as we've add
equally nice days since. 

This almost reminds me of loading up Outback
FM80. It says 4,000 watts but in reality, 3,600 is the max when amps spike.
I will be extra careful going forward on IQ7 string length when going to
the max published... 

My story. 

Scot 

FROM: RE-wrenches  ON BEHALF OF
Jason Szumlanski
SENT: Thursday, May 21, 2020 8:57 AM
TO: RE-wrenches

SUBJECT: [RE-wrenches] Enphase intermittent breaker trippjng  

I'm trying
to resolve an intermittent frustrating problem with and Enphase IQ system.
There are three AC Branch circuits of 9 microinverters each coming into an
Enphase AC combiner.   

What has been happening is one of the BR220 branch
circuit breakers and the combine CH240 breaker in the main backfed load
center have been tripping simultaneously. It has happened about four times
in the last 6 months. It was always the same branch circuit breaker, so we
kept investigating that string, checking the junction box, trunk cable, and
cap, etc. Finally we swapped out the BR220 breaker.    

Fast forward 4
weeks, and we got another call. This time a different branch circuit
breaker and the main breaker tripped simultaneously. We checked that branch
circuit and could not find any fault. It seems unlikely that two branch
circuit breakers would be faulty, so we have now switched out the CH240
main breaker in hopes that it is the culprit.    

I'm not totally
confident in this resolution and I have my fingers crossed. If that doesn't
work, does anyone have any suggestions on another diagnostic step? These
intermittent problems are a major hassle. One thought I had was to switch
to a supply side interconnection with a fusible disconnect. Maybe the
intermittent fault would blow one of the two line fuses so at least I could
narrow it down to which line the fault is on if there is in fact a fault.  


I have experienced two other tripping breaker issues with Enphase systems
in the past. Neither of them were systems I installed. One turned out to be
branch circuits that were not properly paired up and landed on different
breakers. Another time we had an inverter with an internal fault which
eventually"blew up" with a loud popping noise and smoke billowing out of
it. That happened after resetting a trip breaker multiple times. This case
seems to be unrelated to those issues. I'm perplexed.    

Jason Szumlanski
 

Florida Solar Design Group   

     
_______________________________________________
 List sponsored by Redwood
Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [7]

 Change
listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [8]


List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[9]

 List rules " alt="" width="0" height="0" />   

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridso...@sti.net
[3]
mailto:ja...@floridasolardesigngroup.com
[4]
mailto:scot.a...@solarcentex.com
[5]
mailto:re-wrenches-boun...@lists.re-wrenches.org
[6]
mailto:re-wrenches@lists.re-wrenches.org
[7]
mailto:RE-wrenches@lists.re-wrenches.org
[8]
https://mailtrack.io/trace/link/796b1796eb4c075a74298513a530f62e4a496cb2?notrack=1&url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c7dea131fd9cb45a
[9]
https://mailtrack.io/trace/link/c06e48af2da3d129a58c08ef2043bd2d8fcbef6f?notrack=1&url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=06899a19621f54d8
[10]
https://mailtrack.io/trace/link/215cb4d0fcfb04e4124aae9b2616249f1eef5542?notrack=1&url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8bc84049c81c183c
[11]
https://mailtrack.io/trace/link/27c3e706e7f2b4836b1669b31c9454db7fee1b52?notrack=1&url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4a75a2d55681f39a
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to