Wrenches,

When the inverter charger charges the battery bank and runs loads this can
affect the harmonics of the generator output.

Not much you can do about it other than putting in a larger generator to
handle the inverter/charging load along with the loads of the system, and
even in some of those cases depending on the generator dosn't even fix
that.

I have seen some successful with filter caps on the output / Input of the
inverter, but that is pretty hit an miss..




<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020  m +1.206.790.5840
f +1.902.597.8447  e st...@surrette.com
<#SignatureSanitizer_SafeHtmlFilter_> <http://www.facebook.com/RollsBattery>
<http://www.facebook.com/RollsBattery> <http://www.twitter.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>

------------------------------
*Become a Certified PV Professional. Register for* *NABCEP CEC 2020*
<http://rollsbattery.com/nabcep2020> *using promo code* *20RBE*
<http://rollsbattery.com/nabcep2020>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------


On Mon, Aug 17, 2020 at 10:42 AM Will White <w...@solarenergy.org> wrote:

> I've seen that same issue too. I assumed that the battery charging, house
> base loads, and the microwave were too much power for the small generator.
> The voltage drops big time which I assume is what was causing the issue
> with the microwave and most likely with the dryer too.
>
> On Sat, Aug 15, 2020 at 11:51 AM Dan Fink <danbo...@gmail.com> wrote:
>
>> I have the same problem at my place, and a couple client's systems, with
>> Magnum inverter/chargers and small ~2-3kw generators (not just Honda). But
>> the problem appliance is microwave ovens, doesn't matter which microwave
>> brand. They run fine straight from the generator, and fine from the
>> inverter with no generator running, but make a strange, loud hum, dim
>> internal light, and food doesn't heat if the generator is also charging the
>> battery bank. I'll try to figure out how to capture a waveform photo with
>> my scopemeter and post it.
>> Dan Fink
>> Executive Director, Buckville Energy Consulting
>> NABCEP PV Associate
>> NABCEP Certified PV System Inspector
>> IREC Certified Instructor™ for:
>> ~ PV Installation Professional
>> ~ Small Wind Installer
>> NABCEP Registered Continuing Education Providers
>> d <dan.f...@greendustrialtraining.com>anbo...@gmail.com
>> 970-672-4342
>>
>>
>>
>>
>> On Sat, Aug 15, 2020 at 9:37 AM Kent Osterberg <k...@coveoregon.com>
>> wrote:
>>
>>> Matt,
>>>
>>> I haven't looked at what the FXR does to the waveform of a 3000-watt
>>> Honda, but I have used an oscilloscope to look at the waveform of a small
>>> generator while an FX inverter is charging batteries -- it pretty much
>>> makes an ugly mess of the voltage waveform. Not surprised to hear that some
>>> loads don't like to operate when the FXR is charging batteries from a small
>>> generator. The FX charger has a poor power factor and little filtering of
>>> the current waveform, it is a tough load on a small generator. The
>>> generator responds with lots of harmonic voltages and high frequency noise.
>>>
>>> Kent Osterberg
>>> Blue Mountain Solar
>>>
>>>
>>> On 8/15/2020 8:06 AM, Matt Sherald wrote:
>>>
>>> Hello All,
>>>
>>> My curiosity was piqued by a recent customer complaint.  I'm hoping
>>> someone has bumped up against this issue before.
>>>
>>> The customer has a OB FXR2812 and a 3,000W Honda gen.
>>> Her gas clothes dryer runs just fine off the OB inverter.
>>> It runs properly on the Honda gen (when the inverter is bypassed)
>>> It will not run when the gen is on and battery charging is taking place.
>>>
>>> All the other AC loads (including the washing machine) run properly
>>> during battery charging with the gen.
>>> The OB inverter replaced an old Trace unit.  The dryer worked as it
>>> should with the Trace during battery charging.
>>>
>>> Any thoughts are greatly appreciated.  Thanks in advance!
>>>
>>> --
>>> Matt Sherald
>>> PIMBY Energy, LLC
>>> NABCEP Certified Solar PV Installer®
>>> 304-704-5943
>>>
>>> www.getpimby.blogspot.com
>>> www.getpimby.com
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & 
>>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:www.members.re-wrenches.org
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
> *Will White*
> Curriculum Developer
>
>
> e: w...@solarenergy.org
> w: www.solarenergy.org
> p: 802-272-3092
>
> NABCEP Certified PV Installation Professional
> # 093006-34
> Do you envision a world powered by renewable energy? Be the change
> <http://solarenergy.org/donate>.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to