This is interesting, since the definition of high voltage was changed to
>1000V a few code cycles ago and it is somewhat consistently applied
throughout the NEC at that voltage (except for workspace clearances...er).
It seems this 392.18 label requirement could cause confusion and should be
changed to apply to >1000V circuits.  However, the definition of high
voltage only applies with Article 490 , Equipment >1000V so the Article 392
Cable Tray folks can do what they want in terms of where they require high
voltage labeling. I haven't done any research on the history of this
labeling requirement.


Corey maybe you would be willing to make a public input to change where the
label is required to >1000V circuits, thus there would be no conflict with
690 since PV DC circuits in or on buildings cannot be >1000V. Due Sept 10!

490.2 Definition.

The definition in this section shall apply only within this article.
High Voltage.

A potential difference of more than 1000 volts, nominal.

Thanks for bringing this up Corey!


On Thu, Sep 3, 2020 at 12:36 AM Ray <r...@solarray.com> wrote:

> This is interesting, because we were considering cable trays, too.  My
> guess is that both requirements would apply.  Picky, but I don't see that
> 690 exempts the requirements of 392. One is for PV, one is for over 600 v.
> Some code iteration in the future might have combined language for PV over
> 600 v " Danger - High Voltage Photovoltaic Source - Keep Away"  and of
> course that's so verbose that the average Joe is just going to stick his
> paws in there anyway.....
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 9/2/20 7:54 PM, Corey Shalanski wrote:
>
> Wrenches,
>
> I am curious about the marking requirements for cable trays containing PV
> source/output circuits rated over 600 volts, installed on a building:
>
>
> NEC 392.18(H) requires a permanent, legible warning notice carrying the
> wording “DANGER — HIGH VOLTAGE — KEEP AWAY” at least once every 10 ft.
>
> NEC 690.31(G)(3) requires a label or marking with the wording "WARNING:
> PHOTOVOLTAIC POWER SOURCE" at least once every 10 ft.
>
> Does the 690.31 label take precedence? Are there any situations where both
> labels would be required (or recommended)?
>
> --
> Corey Shalanski
> Jah Light Solar
> Portland, Jamaica
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to