HI Jon,

Can you tell us how long the system has been operational?  Trying to figure out 
if this is a new system or an older.

And what size generator do you have? 

If its an older system and with a big generator/big loads then there is a 
possibility of damaged/sticky relays.

jay

peltz power





> On Dec 14, 2020, at 9:07 AM, Tuss, Lones <lt...@outbackpower.com> wrote:
> 
> Hi Jon
> Not much to go on here the suggestion to look for damaged relays is probably 
> a good idea.
> Look to see if there is signs of arcing or the relay covers have a smokey 
> appearance.
> You stated the system has worked for the last week and the AGS has gone 
> through several start stop sequences and the system error has not repeated.
> It might be interesting to see if there were any warning in the event log 
> perhaps that would give more clues.
> It is difficult to be certain when the system is currently functioning.
> Sorry that is all I have.
> Take Care Sir
>  
>  
> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org 
> <mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Jon 
> Siegenthaler
> Sent: Friday, December 11, 2020 6:01 PM
> To: re-wrenches@lists.re-wrenches.org 
> <mailto:re-wrenches@lists.re-wrenches.org>
> Subject: [RE-wrenches] Outback AC Backfeed Error
>  
> Hey wrenches,
>  
> I have a client who has a couple of the Radian 8048's and has an error code 
> of "AC Backfeed Error GS-1". Looking at the manual it states that "Usually 
> indicates another AC power source (out of phase with the inverter) was 
> connected to the unit’s AC output. Can also occur if an out-of-phase AC 
> source is connected to the inverter’s AC input."
>  
> However when this happened the generator wasn't running and it's an off grid 
> system. Is there a way that the master is looking to the slave as another 
> power source? The system had been running fine this week, auto running the 
> generator early morning and shutting down on its own. 
>  
> Anyone seen something like this before? Thanks,
>  
> Jon Siegenthaler
> 
> 
> This email and any attachments may contain confidential information that is 
> intended only for the recipient(s). If you have received this email in error, 
> please notify the sender and delete it from your system. Any views or 
> opinions presented in this email are solely those of the author and do not 
> necessarily represent those of the company or its affiliates. This email does 
> not constitute an agreement to conduct transactions by electronic means and 
> does not create any legally binding contract or enforceable obligation in the 
> absence of a fully signed written contract. The recipient should check this 
> email and any attachments for viruses. The company accepts no liability for 
> any loss or damage caused by software viruses. If you are the intended 
> recipient and you do not wish to receive similar email(s) from us in the 
> future then please notify the sender. Please consider the environment before 
> printing._______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to