I've done 3phase with 6 Schneider Conext XW. It worked well but when you
convert to 3-phase you lose surge capacity because you are turning the
inverters into 120V inverters from 240.


*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*

* <https://viridianenergy.ca/>*


On Tue, 20 Apr 2021 at 17:45, Darryl Thayer <darylsol...@gmail.com> wrote:

> Hello all,  When I have done a small 3-phase I have used Outback GVFX
> 3548  up to 32 kW (120/208) my largest was about 45 kW it worked for 12
> years, then was replaced when the owner wanted to go larger.   I made a
> 3-phase design using Solark but SolArk did not understand 3-phase and could
> not answer in English my questions. (So I did not submit)  However, they
> assumed their equipment could go to about 50 kW when combined into 9
> units.
>
> On Tue, Apr 20, 2021 at 5:15 PM Chris Schaefer <ch...@solarandwindfx.com>
> wrote:
>
>> G'day All,
>>
>> I'm not familiar with any 3 ph 208 to 480vac battery backup inverter
>> manufacturers. So if you could point me in the right direction on who you
>> know and better yet who you've had experience with, good, bad or otherwise,
>> that would be extremely helpful.
>>
>> Happy 420 to all my fellow Solar Bozo's,
>> Christopher-
>>
>> Chris Schaefer’s
>> <http:www.solarandwindfx.com>
>>
>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>> <http://www.solarandwindfx.com> ~ E-mail: ch...@solarandwindfx.com
>> <ch...@solarandwindfx.com>*
>>
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to