Jason,

I think I agree with your interpretation of the wiring diagram. My
hesitation is, with a 1-1/4” KO for AC inputs, only choice seems to be a
>24” stub conduit for 2/0 conductores to a fused disconnect. Not a fun pipe
to bend…and extra BOS seems like a less than ideal solution.

Is this your conclusion as well?

On Sun, Apr 17, 2022 at 10:38 PM Darryl Thayer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Yes and no, I think this is a tap, "a tap shall be permitted anywhere
> along a feeder"  ' as long as it is less than a 10-foot rule or 25-foot
> rule ending in a listed OCPD with a rating sufficient to handle the maximum
> overcurrent'.  Service equipment residential is rated for fault currents of
> up to 10,000 amps withstand.    Refer to 240.4.B and 240.21 (B) (1 & 2)
>
> On Sun, Apr 17, 2022 at 10:39 AM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> But this isn't a tap. It's a feeder conductor connected to an OCPD.
>>
>> I guess if you don't have a grid in or generator in or AC Coupled PV, you
>> could just call it an inverter output circuit and it could be sized
>> accordingly. But it would still need to be protected at it's source by an
>> appropriately rated OCPD. Don't get me wrong... I don't think there is a
>> real safety issue here, but I also don't see how the NEC allows the
>> conductor to be sized for anything less than 200A.
>>
>> Jason
>>
>>
>> On Sun, Apr 17, 2022, 11:29 AM Darryl Thayer via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> The tap rule says you can reduce to 10% of the nominal size for 10 feet
>>> and protect at the downstream OCPD or 25% for 25 feet for solar with
>>> multiple sources see 705
>>>
>>> On Sat, Apr 16, 2022 at 9:16 PM Jason Szumlanski via RE-wrenches <
>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>
>>>> That's what I'm thinking. You would need to use a 200A conductor to a
>>>> separate load out OCPD before downsizing the wire. I guess there are pros
>>>> and cons, but it seems this is geared toward whole house backup for 200A
>>>> services. I'm eager to get an opportunity to use it in that scenario.
>>>>
>>>> Jason
>>>>
>>>>
>>>>
>>>>
>>>> On Sat, Apr 16, 2022, 10:06 PM Chris Sparadeo via RE-wrenches <
>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>
>>>>> Jason,
>>>>>
>>>>> Any additional OCPD downstream of the 200A load output breaker could
>>>>> allow for a smaller wire size to be used at these terminals. For example,
>>>>> load output conductors run to a 100A main breaker panel board.  Obviously
>>>>> depending on circumstances, a #4 copper could fit the bill.
>>>>>
>>>>> What I’m not extremely  excited about with the new design is that in
>>>>> an off-grid scenario with a generator and smart load, we would now need to
>>>>> integrate an AC disconnect for generator input (grid)  and either a fused
>>>>> disconnect or loads panel for any smart load output. With the 12K unit, 
>>>>> the
>>>>> integrated breakers help cut down on BOS and install time.
>>>>>
>>>>> -Chris
>>>>>
>>>>> On Sat, Apr 16, 2022 at 5:35 PM Darryl Thayer via RE-wrenches <
>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>
>>>>>> Hello, The overcurrent device is to protect the conductors.  you can
>>>>>> put any size wire, but you must protect with the overcurrent device.
>>>>>> REmember in solar equipment; you may have more than one supply source.  
>>>>>> The
>>>>>> DC best example is solar modules connected in parallel,      on
>>>>>>
>>>>>> On Fri, Apr 15, 2022 at 8:26 PM Jerry Shafer via RE-wrenches <
>>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>
>>>>>>> You must meet all expected source output potentials within the
>>>>>>> design and operating limits, as long as the distribution panel and
>>>>>>> connected wiring is rated for the max output of the protected source 
>>>>>>> then
>>>>>>> you are good. A 200 ATS connected to a 10 kW genny does not require 2/0 
>>>>>>> as
>>>>>>> it will never meet that rating. Just remember its whatever the max 
>>>>>>> output
>>>>>>> can be plus your margin.
>>>>>>>
>>>>>>> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
>>>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>
>>>>>>>> Hi Jason,
>>>>>>>>
>>>>>>>> You bring up a valid point….in an off-grid scenario with the 15k do
>>>>>>>> you size the conductors to the continuous capacity, surge capacity or 
>>>>>>>> the
>>>>>>>> OCPD of the unit?
>>>>>>>>
>>>>>>>> -Chris
>>>>>>>>
>>>>>>>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
>>>>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>>
>>>>>>>>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC
>>>>>>>>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>>
>>>>>>>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>>>>>>>>> ja...@floridasolardesigngroup.com> wrote:
>>>>>>>>>
>>>>>>>>>> I'm not following the wiring diagrams for this new inverter. It
>>>>>>>>>> has 200A pass-through capability with an integrated 200A load 
>>>>>>>>>> disconnect.
>>>>>>>>>> But then it says the wire gauge for the load out wiring can be #4 to 
>>>>>>>>>> 2/0.
>>>>>>>>>>
>>>>>>>>>> In an off-grid scenario where there is no generator, the max
>>>>>>>>>> continuous output is 62.5A, so I assume 80A circuit protection could 
>>>>>>>>>> be
>>>>>>>>>> used with 80A rated wire (#4), but how is that circuit protection
>>>>>>>>>> implemented if the 200A breaker is integrated? Do you have to run a 
>>>>>>>>>> short
>>>>>>>>>> piece of 2/0 to an external 80A rated OCPD and then step down to #4?
>>>>>>>>>>
>>>>>>>>>> Jason Szumlanski
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> _______________________________________________
>>>>>>>>>
>>>>>>>>
>>>>> _______________________________________________
>>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo


C_802-369-4458
H_802-728-3059
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to