Be carefull about modifying inverters or any cabinets with long term
warranties because modifying may result in sending your unit for repair and
not getting exchange units in the event of a warranty issue. Outback is
served in parts so that may not be an issue, solark is too soon to tell.
Fronius refused to warranty inverters because they say the shell was
modified.
But hey thats my luck

On Sun, May 8, 2022, 11:04 AM Michael Morningstar via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> We cut out the bottom plate entirely with a die grinder/cut off wheel and
> then wrap the raw edge with vinyl "edge wrap" and set the inverters on top
> of 10 x 10 x whatever gutters. The layout and sizes of Sol-Arks knock-outs
> is screwy. Just need a bonding jumper between both enclosures. This is
> common practice in the industrial world when dealing with large VFDs and
> such.
>
>
> On Sun, May 8, 2022 at 6:47 AM Jay via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi Chris,
>>
>> Can’t you increase the size of the KO’s?
>>
>> Jay
>>
>> On May 7, 2022, at 7:17 PM, Chris Sparadeo via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>> 
>> Jason,
>>
>> I think I agree with your interpretation of the wiring diagram. My
>> hesitation is, with a 1-1/4” KO for AC inputs, only choice seems to be a
>> >24” stub conduit for 2/0 conductores to a fused disconnect. Not a fun pipe
>> to bend…and extra BOS seems like a less than ideal solution.
>>
>> Is this your conclusion as well?
>>
>> On Sun, Apr 17, 2022 at 10:38 PM Darryl Thayer via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> Yes and no, I think this is a tap, "a tap shall be permitted anywhere
>>> along a feeder"  ' as long as it is less than a 10-foot rule or 25-foot
>>> rule ending in a listed OCPD with a rating sufficient to handle the maximum
>>> overcurrent'.  Service equipment residential is rated for fault currents of
>>> up to 10,000 amps withstand.    Refer to 240.4.B and 240.21 (B) (1 & 2)
>>>
>>> On Sun, Apr 17, 2022 at 10:39 AM Jason Szumlanski via RE-wrenches <
>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>
>>>> But this isn't a tap. It's a feeder conductor connected to an OCPD.
>>>>
>>>> I guess if you don't have a grid in or generator in or AC Coupled PV,
>>>> you could just call it an inverter output circuit and it could be sized
>>>> accordingly. But it would still need to be protected at it's source by an
>>>> appropriately rated OCPD. Don't get me wrong... I don't think there is a
>>>> real safety issue here, but I also don't see how the NEC allows the
>>>> conductor to be sized for anything less than 200A.
>>>>
>>>> Jason
>>>>
>>>>
>>>> On Sun, Apr 17, 2022, 11:29 AM Darryl Thayer via RE-wrenches <
>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>
>>>>> The tap rule says you can reduce to 10% of the nominal size for 10
>>>>> feet and protect at the downstream OCPD or 25% for 25 feet for solar with
>>>>> multiple sources see 705
>>>>>
>>>>> On Sat, Apr 16, 2022 at 9:16 PM Jason Szumlanski via RE-wrenches <
>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>
>>>>>> That's what I'm thinking. You would need to use a 200A conductor to a
>>>>>> separate load out OCPD before downsizing the wire. I guess there are pros
>>>>>> and cons, but it seems this is geared toward whole house backup for 200A
>>>>>> services. I'm eager to get an opportunity to use it in that scenario.
>>>>>>
>>>>>> Jason
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> On Sat, Apr 16, 2022, 10:06 PM Chris Sparadeo via RE-wrenches <
>>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>
>>>>>>> Jason,
>>>>>>>
>>>>>>> Any additional OCPD downstream of the 200A load output breaker could
>>>>>>> allow for a smaller wire size to be used at these terminals. For 
>>>>>>> example,
>>>>>>> load output conductors run to a 100A main breaker panel board.  
>>>>>>> Obviously
>>>>>>> depending on circumstances, a #4 copper could fit the bill.
>>>>>>>
>>>>>>> What I’m not extremely  excited about with the new design is that in
>>>>>>> an off-grid scenario with a generator and smart load, we would now need 
>>>>>>> to
>>>>>>> integrate an AC disconnect for generator input (grid)  and either a 
>>>>>>> fused
>>>>>>> disconnect or loads panel for any smart load output. With the 12K unit, 
>>>>>>> the
>>>>>>> integrated breakers help cut down on BOS and install time.
>>>>>>>
>>>>>>> -Chris
>>>>>>>
>>>>>>> On Sat, Apr 16, 2022 at 5:35 PM Darryl Thayer via RE-wrenches <
>>>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>
>>>>>>>> Hello, The overcurrent device is to protect the conductors.  you
>>>>>>>> can put any size wire, but you must protect with the overcurrent 
>>>>>>>> device.
>>>>>>>> REmember in solar equipment; you may have more than one supply source. 
>>>>>>>>  The
>>>>>>>> DC best example is solar modules connected in parallel,      on
>>>>>>>>
>>>>>>>> On Fri, Apr 15, 2022 at 8:26 PM Jerry Shafer via RE-wrenches <
>>>>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>>
>>>>>>>>> You must meet all expected source output potentials within the
>>>>>>>>> design and operating limits, as long as the distribution panel and
>>>>>>>>> connected wiring is rated for the max output of the protected source 
>>>>>>>>> then
>>>>>>>>> you are good. A 200 ATS connected to a 10 kW genny does not require 
>>>>>>>>> 2/0 as
>>>>>>>>> it will never meet that rating. Just remember its whatever the max 
>>>>>>>>> output
>>>>>>>>> can be plus your margin.
>>>>>>>>>
>>>>>>>>> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
>>>>>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>>>
>>>>>>>>>> Hi Jason,
>>>>>>>>>>
>>>>>>>>>> You bring up a valid point….in an off-grid scenario with the 15k
>>>>>>>>>> do you size the conductors to the continuous capacity, surge 
>>>>>>>>>> capacity or
>>>>>>>>>> the OCPD of the unit?
>>>>>>>>>>
>>>>>>>>>> -Chris
>>>>>>>>>>
>>>>>>>>>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
>>>>>>>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>>>>
>>>>>>>>>>> P.S. ICYMI, this inverter has a massive combined AC coupled and
>>>>>>>>>>> DC coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>>>>>>>>>>> ja...@floridasolardesigngroup.com> wrote:
>>>>>>>>>>>
>>>>>>>>>>>> I'm not following the wiring diagrams for this new inverter. It
>>>>>>>>>>>> has 200A pass-through capability with an integrated 200A load 
>>>>>>>>>>>> disconnect.
>>>>>>>>>>>> But then it says the wire gauge for the load out wiring can be #4 
>>>>>>>>>>>> to 2/0.
>>>>>>>>>>>>
>>>>>>>>>>>> In an off-grid scenario where there is no generator, the max
>>>>>>>>>>>> continuous output is 62.5A, so I assume 80A circuit protection 
>>>>>>>>>>>> could be
>>>>>>>>>>>> used with 80A rated wire (#4), but how is that circuit protection
>>>>>>>>>>>> implemented if the 200A breaker is integrated? Do you have to run 
>>>>>>>>>>>> a short
>>>>>>>>>>>> piece of 2/0 to an external 80A rated OCPD and then step down to 
>>>>>>>>>>>> #4?
>>>>>>>>>>>>
>>>>>>>>>>>> Jason Szumlanski
>>>>>>>>>>>>
>>>>>>>>>>>>
>>>>>>>>>>>>
>>>>>>>>>>>>
>>>>>>>>>>>>
>>>>>>>>>>>> _______________________________________________
>>>>>>>>>>>
>>>>>>>>>>
>>>>>>> _______________________________________________
>>>>>>
>>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> --
>> Chris Sparadeo
>>
>>
>> C_802-369-4458
>> H_802-728-3059
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
> Michael Morningstar
>
>
> Morningstar Electric
>
> PO Box 1494
>
> Mount Shasta, CA 96067
>
> 530-921-0560
>
> mjmornings...@gmail.com
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to