I told them that SolArk says not to use the 12VDC RS output terminals for connecting the transmitter. I gave them the attached drawing which they ask for, which shows the transmitter connected to a 120VAC/12VDC breaker which they supply. They told me to wire the 120VAC source to the main service panel so the array would shut down on loss of power. I told them that is exactly NOTwhat I wanted to happen as that would stop the battery charging when there is a loss of utility power. I said I wanted the 120VAC source to be the back up loads panel. After about a week of calls and emails, I got an email back saying to use the SolArk 12VDC terminals for RS. I just emailed them a screen shot of the SolArk manual that says not to do that.
At this point, I am asking anyone on the list to let me know how they wired the transmitter successfully. Thank you for any guidance, Chris Warfel
-- Christopher Warfel ENTECH Engineering, Inc. PO Box 871, Block Island, RI 02807 401-466-8978 <http://entech-engineering.com>
Tigo Transmitter Powering.pdf
Description: Adobe PDF document
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org