@DustinDouglas do you mind confirming if the Tigo RSS Transmitter is
compatible with the 12vdc power supply from Sol-Ark, and if not…what should
we be doing to supply power without having to rely on 120VAC output of the
inverter?

Thanks,

-Chris


On Wed, Nov 16, 2022 at 4:22 PM Christopher Warfel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi Nick and List, that was my problem exactly.  Chris
>

On 11/16/2022 12:38 PM, Nick A Lucchese via RE-wrenches wrote:
>
> All, I believe what Chris is referring to is something I was initially
> confused on during a Solark install I was involved with last year.
> Uncertain if the manual has changed but in the Solark 12k manual dated
> April 2, 2021 on page 23 it has a line saying-
>
> Note: Tigo Optimizers are compatible with the Sol-Ark 12k (Do not use the
> built in 12v Power supply in the Sol-Ark user area to power the Tigo
> Optimizer TX transmitter)
>
> I too had to confirm with Sol-Ark to clarify these details. I’ve not
> looked at any of their newer manuals to see if some of these notes have
> changed.
>
> Enjoy your day, Nick
>
>
>
> On Nov 16, 2022, at 8:41 AM, Chris Sparadeo via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Hi Chris,
>
> I echo Ronald’s experience. I wasn’t aware of any memo from Sol Ark
> suggesting pins 15 and 16 should not be used for the Tigo RSS Transmitter.
> The 12K and 15K manuals both refrence a 12vdc RSS transmitter to achieve
> rapid shut down.
>
> Best,
>
> Chris
>
> On Wed, Nov 16, 2022 at 11:21 AM Roland - RES via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Aloha Chris,
>>
>> We have numerous Sol-Ark systems with Tigo TS4Fs where we have the
>> transmitter wired to the 12v supply of the inverter, with no issues to date.
>>
>> Sent from a IPhone, with touch screen keys on the fly. Please excuse
>> shortcuts and typos.
>>
>>
>> Roland Shackelford
>> NABCEP CERTIFIED PV INSTALLER
>> President
>> Renewable Energy Services (RES), Inc.
>> Mobile:  *808-938-9239 <http://808-938-9239/>*
>> www.renewablenergy.com
>>
>> On Nov 16, 2022, at 4:33 AM, Christopher Warfel via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>> 
>>
>> Hi, We are doing our first system with these two devices. The inverter is
>> SolArk 12P (mutimode) and the Tigo product for RS is the TS4F.  Tigo has me
>> a little bit walking in circles.
>>
>> I told them that SolArk says not to use the 12VDC RS output terminals for
>> connecting the transmitter.  I gave them the attached drawing which they
>> ask for, which shows the transmitter connected to a 120VAC/12VDC breaker
>> which they supply.  They told me to wire the 120VAC source to the main
>> service panel so the array would shut down on loss of power. I told them
>> that is exactly NOTwhat I wanted to happen as that would stop the battery
>> charging when there is a loss of utility power. I said I wanted the 120VAC
>> source to be the back up loads panel. After about a week of calls and
>> emails, I got an email back saying to use the SolArk 12VDC terminals for
>> RS.  I just emailed them a screen shot of the SolArk manual that says not
>> to do that.
>>
>> At this point, I am asking anyone on the list to let me know how they
>> wired the transmitter successfully. Thank you for any guidance, Chris Warfel
>>
>>
>>
>>
>>
>> --
>>                                          Christopher Warfel
>>                      ENTECH Engineering, Inc.
>> PO Box 871, Block Island, RI 02807
>>                                                             401-466-8978
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:http://www.members.re-wrenches.org
>
> --
>                                          Christopher Warfel
>                      ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
>                                                             401-466-8978
> <http://entech-engineering.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo


C_802-369-4458
H_802-728-3059
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to