Thanks everyone, the person I started with a SolArk asked me to call them, so I've left a message.  I'll let everyone know what the determination is.  Bradley raises a good point about shutting down the back up loads panel. We would like to have an outdoor accessible disconnect switch between the back up loads panel and the inverter so that can happen more easily for first responders.  I have to go back and understand a few more things and will let you know.  Thanks again. Chris

On 11/16/2022 10:14 PM, Bradley Bassett wrote:
The issue as I see it is that the Tigo RSS Transmitter and the APsmart transmitter are both rated to draw up to 800ma. The 12VDC output of the Sol-Ark inverters is limited to 100ma. Since some have used this successfully I suppose that means that either these transmitters don't really use more than 100ma, or the 12VDC output of the Sol-Ark can actually handle more than that, or some combination of both. If I owned a Sol-Ark I'd test this to see what the answer is, but alas I do not. I design systems using a 48VDC to 12VDC power supply (Online Components has a Mean-Well device for a reasonable price, sorry no link from here) and a fairly rare IMO shutdown button (we have that) that has both NO and NC contacts. This is needed because to shut down the Sol-Ark inverter requires a NO contact that closes on initiation which is quite rare in RSD initiators. And you do still need to shut down the inverter as well as the RSD devices so that it does not continue to feed voltage back into the PV circuits (I think). This also shuts down the AC output of the Sol-Ark which tends to make the inspector happy. Since it also shuts down the inverter, that limits the battery to its own circuits, does this count as a battery disconnect also?? I'm seeing some inspectors calling out for battery disconnects which is much more problematic.

Brad Bassett
AEE Solar

On Wed, Nov 16, 2022 at 4:27 PM Jerry Shafer via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

    Wrenches, Christopher
    I have done quite a few and per solark have always connected in
    the inverter with no issues, Now with that connecting to the
    output side it would do much the same work until it did not then
    shut off the modules.
    Fun times

    On Wed, Nov 16, 2022 at 6:33 AM Christopher Warfel via RE-wrenches
    <re-wrenches@lists.re-wrenches.org> wrote:

        Hi, We are doing our first system with these two devices. The
        inverter is SolArk 12P (mutimode) and the Tigo product for RS
        is the TS4F. Tigo has me a little bit walking in circles.

        I told them that SolArk says not to use the 12VDC RS output
        terminals for connecting the transmitter.  I gave them the
        attached drawing which they ask for, which shows the
        transmitter connected to a 120VAC/12VDC breaker which they
        supply.  They told me to wire the 120VAC source to the main
        service panel so the array would shut down on loss of power. I
        told them that is exactly NOTwhat I wanted to happen as that
        would stop the battery charging when there is a loss of
        utility power. I said I wanted the 120VAC source to be the
        back up loads panel. After about a week of calls and emails, I
        got an email back saying to use the SolArk 12VDC terminals for
        RS.  I just emailed them a screen shot of the SolArk manual
        that says not to do that.

        At this point, I am asking anyone on the list to let me know
        how they wired the transmitter successfully. Thank you for any
        guidance, Chris Warfel





--                             Christopher Warfel
             ENTECH Engineering, Inc.
        PO Box 871, Block Island, RI 02807
            401-466-8978
        <http://entech-engineering.com>


        _______________________________________________
        List sponsored by Redwood Alliance

        Pay optional member dues here: http://re-wrenches.org

        List Address: RE-wrenches@lists.re-wrenches.org

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        There are two list archives for searching. When one doesn't
        work, try the other:
        https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        http://www.re-wrenches.org/etiquette.htm

        Check out or update participant bios:
        http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to