Good point Glenn. 
My question is if this system is in its own building. If so it is probably easier to convince the AHJ about not needing a remote battery disco. 

Jay

On Jan 27, 2023, at 12:46 PM, Glenn Burt via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:


Does the AHJ really want the batteries disconnected from conductors, or does he really just want the inverters to stop operating and producing AC within the house?
Obviously there is a big difference here and it may be changing as the code evolves.

-Glenn
Sent from my 'smart'phone, so please excuse typos and spelling errors.

------ Original message------
From: William Miller via RE-wrenches
Date: Fri, Jan 27, 2023 2:26 PM
To: RE-wrenches;
Cc: William Miller;
Subject:[RE-wrenches] Remote battery disconnects

Friends:

 

We have a large-ish residential off-grid system install coming up.  The AHJ has said they will require a remote battery disconnect.  I suspect there will be fire sprinkler controls and a pressure pump that would become inoperable if this system were engaged.  In this case we will apply for a waiver.

 

The last time this was discussed here as far as I can find was October of 2020.  At that time no one suggested any specific battery disconnect equipment. 

 

To further clarify my needs:  There will be 4 or 5 Radian 8048 inverters (5 or 6 4/0 battery circuits, ~350A each) and two 175 amp PV recombiner outputs.  That is 6 poles of high amperage DC disconnects.    

 

The battery array will be either a UnigyII VRLA or a lithium of a brand yet to be determined.  In the case of lithium we will look for a system that can remotely enable a BMS shutdown.  In the case of a VRLA lead-acid, we will not have that luxury.

 

I have done some considerable research and have not found viable, high amperage, remotely activated shutdown equipment.

 

I am wondering what hardware others may be using to achieve remote battery disconnecting in these types of cases..

 

William

 

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985

 

 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to