Seems confusing that the AHJ is requiring a disconnect for AC wiring,
not specific to which or both panel types, and then a dc disconnect with
no code reference. Was trying to convey a reasonable, safe approach. A
lot of bad information from fire department solar consultants making a
lot of money fear mongering, which has led to this type of situation. Chris
On 1/27/2023 3:35 PM, William Miller via RE-wrenches wrote:
Glenn:
As I wrote, a DC disconnect is required. Here is an excerpt from the
Q&A with the building official:
4.Will you be requiring an external disconnect to disconnect the AC
output of the inverter system from premise wiring?
Yes, as required per 230.85
5.Will you be requiring an external disconnect to disconnect batteries
from the inverters?
Yes
If the DC disconnect was not required I would not be wasting
everyone’s time with my post. I try to be careful about that,
researching on my own before posting and trying to make my questions
very clear. I also try not to embarrass myself with dumb questions,
but that does happen occasionally…
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com <http://www.millersolar.com/>
CA Lic. 773985
*From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *Glenn Burt via RE-wrenches
*Sent:* Friday, January 27, 2023 11:46 AM
*To:* William Miller via RE-wrenches
*Cc:* Glenn Burt
*Subject:* Re: [RE-wrenches] Remote battery disconnects
Does the AHJ really want the batteries disconnected from conductors,
or does he really just want the inverters to stop operating and
producing AC within the house?
Obviously there is a big difference here and it may be changing as the
code evolves.
-Glenn
Sent from my 'smart'phone, so please excuse typos and spelling errors.
------ Original message------
*From: *William Miller via RE-wrenches
*Date: *Fri, Jan 27, 2023 2:26 PM
*To: *RE-wrenches;
*Cc: *William Miller;
*Subject:*[RE-wrenches] Remote battery disconnects
Friends:
We have a large-ish residential off-grid system install coming up.
The AHJ has said they will require a remote battery disconnect. I
suspect there will be fire sprinkler controls and a pressure pump that
would become inoperable if this system were engaged. In this case we
will apply for a waiver.
The last time this was discussed here as far as I can find was October
of 2020. At that time no one suggested any specific battery
disconnect equipment.
To further clarify my needs: There will be 4 or 5 Radian 8048
inverters (5 or 6 4/0 battery circuits, ~350A each) and two 175 amp PV
recombiner outputs. That is 6 poles of high amperage DC disconnects.
The battery array will be either a UnigyII VRLA or a lithium of a
brand yet to be determined. In the case of lithium we will look for a
system that can remotely enable a BMS shutdown. In the case of a VRLA
lead-acid, we will not have that luxury.
I have done some considerable research and have not found viable, high
amperage, remotely activated shutdown equipment.
I am wondering what hardware others may be using to achieve remote
battery disconnecting in these types of cases..
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600 <tel:805-438-5600>
www.millersolar.com <http://www.millersolar.com/>
CA Lic. 773985
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
BEGIN:VCARD
VERSION:4.0
N:Warfel;Christopher;;;
TEL;VALUE=TEXT:401-447-5773 (c)
NOTE:Use the cell phone number for all communications. Thank you.
URL:https://www.entech-engineering.com
END:VCARD
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org