It could be the LED bulbs. I've had different brands flicker like crazy
on grid and off. Seems to relate to other loads that are on, especially
stuff like washing machines with VFD drives, and well pumps. Add
dimmers and it can get even worse.
IMHO, they really need to improve the quality of the driver circuits on
the LED bulbs. Only gets worse on a less than perfect AC waveform.
Ray Walters
Remote Solar
On 7/3/2023 5:09 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote:
I think I would try eliminating things. Turn off the AC coupling for a
few days and get results. Turn of DC solar and get results. Measure AC
voltage with a scope or just observe voltage during the flicker. Are
all of the lights flickering? Are they on dimmers? Are there any
loads failing that could be the source? Is the output with-in spec?
Rock solid 60 HZ right.
Do an AC bypass of XW with the genset and check for flicker symptoms.
Are they on Insight? They really need it for you to monitor. Are there
any faults, warnings or events ? Check history. There are a few
settings in the old XW+ that could have been glitched by a surge or
nearby lightning strike.
XW+ could have a damaged FET. Open the unit and do a visual.
There would be a smell and transistor fragments on the bottom right
side of the power bridge. 90% of XW failures have visual evidence.
While you have it open, Check the DSP sensing and control board, both
LEDs (light-emitting diodes) D24 and D25 are on.
Last thing is a DC power down of the unit and the DC buss for 5
minutes. If that does not work, then a reset to factory values.
This is off an old list I got from Support many years ago and combined
with my findings over the years. Really rare for this kind of
weirdness and why it would be getting worse without visual evidence.
Good Luck Howie!
*Dave Angelini Offgrid Solar "we go where powerlines don't"
http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text
209 813 0060*
On 2023-07-03 12:42 pm, Howie Michaelson via RE-wrenches wrote:
Hi All,
I upgraded an old clients' off-grid system about five years ago to a
Schneider XW6848+ and 2 Blue Ion 2.0 cabinets (32kWh). When the
batteries were moving toward full, if the charge rate was on the
higher side via generator or solar (AC coupled w/SolarEdge 6kW and DC
coupled with an FM 80), they would start to get pulsating lights
similar to symptoms of other older inverters when using a generator
for charging. The solution for this pulsation has usually been to
kick back the AC charge amperage just enough so the pulsating calmed
down to a tolerable inconsequential level. And that worked in this
case as well.
However, a few weeks ago, the pulsating became more noticeable and
has now become fairly intolerable. To my knowledge, no settings
changes we made within the previous year, and these clients would be
loath to make any changes, so I doubt there were any. More puzzling
is the pulsating has started to happen at seemingly random times not
related to charging. It happens at night or pre-dawn mornings
without the generator, or during the afternoons with solar charging.
And it is getting progressively worse.
Anyone have any thoughts on why that would start getting worse now?
Howie
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org