Hi All,
I upgraded an old clients' off-grid system about five years ago to a
Schneider XW6848+ and 2 Blue Ion 2.0 cabinets (32kWh). When the batteries
were moving toward full, if the charge rate was on the higher side via
generator or solar (AC coupled w/SolarEdge 6kW and DC coupled with an FM
80), they would start to get pulsating lights similar to symptoms of other
older inverters when using a generator for charging. The solution for this
pulsation has usually been to kick back the AC charge amperage just enough
so the pulsating calmed down to a tolerable inconsequential level.  And
that worked in this case as well.
However, a few weeks ago, the pulsating became more noticeable and has now
become fairly intolerable.  To my knowledge, no settings changes we made
within the previous year, and these clients would be loath to make any
changes, so I doubt there were any. More puzzling is the pulsating has
started to happen at seemingly random times not related to charging.  It
happens at night or pre-dawn mornings without the generator, or during the
afternoons with solar charging.  And it is getting progressively worse.
Anyone have any thoughts on why that would start getting worse now?
Howie
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to