Team;

With the move to larger cells, some modules have an Isc that is pushing the 
limits of 12 AWG wire.  If I apply the rule of 156% (or 125% solar derate*125% 
continuous load derate) to an 18 Amp Isc module this will exceed the 25A that a 
12 AWG wire can carry.  I understand that the homeruns will need to be a larger 
AWG (10 ga), but do the solar module cables (from junction box to MC4) also 
need to be larger?  Any guidance or reference material would be greatly 
appreciated.

Thx,

George McClellan | Senior Technical Sales Manager | REC Americas LLC
330 James Way Ste 150 | Pismo Beach, CA 93449 | USA
Cell phone +1 805 704 3226 | Fax +1 805 357 6104
www.recgroup.com<http://www.recgroup.com/> | 
george.mcclel...@recgroup.com<mailto:shannon.k...@recgroup.com>


________________________________

This message is private and confidential and may be privileged. Any 
unauthorized use, dissemination of the information or copying of this message 
is prohibited. If you have received this message in error, please notify us 
immediately and remove it from your system. Thank you.
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to