A possible fix.

You could run a DC relay on the SB PV input that would be voltage triggered to 
prevent the battery volts from getting higher than you want.

The SI has 2 aux relays I think?  Or could do a tristar with RD-1 relay that 
has 4 channels.

Just a thought

jay

> On May 7, 2024, at 11:11 PM, William Miller via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> Friends:
>  
> I am still wrestling with problems integrating a Sunny Island / Sunny Boy AC 
> coupled system to a set of 5 E-vault Max battery cabinets.  
>  
> As a refresher, with closed loop comms, the Frequency Shift Power Control 
> system is not working, or not working quickly enough, and when nearing full 
> charge, the voltage can spike up to 66 volts and the SI system shuts down.  
> Fortress has told me in a roundabout way that they agree this is a real 
> problem and they are working on a solution.
>  
> Another problem has reared its head:  If the E-Vaults do not get charged 
> fully every 5 to 7 days, the BMS units SOC value becomes radically out of 
> calibration.  The E-vault will report a higher SOC than is realistic.  The SI 
> system starts the generator based on SOC and if the SOC is reported as high 
> the generator don’t start.  Sooner rather than later the battery voltage gets 
> too low and the system shuts down.
>  
> I have been tweaking on the settings like days-since-full-charge to attempt 
> to get this cycle to stop.  No definitive answer yet.
>  
> Here is the reason I am writing:  Yesterday I could not get the Sunny Islands 
> to start.  The battery voltage was 46 which should have been enough but for 
> some reason they just would not start.  Because of this I could not charge 
> the batteries from generator or from AC coupled solar.  I called SMA but they 
> told me they could not advise because of the non-compatible batteries.  I 
> asked about the emergency charging procedure in the manual but I was told 
> this does not work with lithium batteries.  The process is pretty scary 
> anyway so I was not inclined to try.
>  
> SMA told me I may need an external 48 volt charging system.  I have heard of 
> this being required in certain scenarios by wrenches.  This would be a huge 
> pain in the ass: ordering one, waiting for it, hooking it up, etc.
>  
> Here is what I did:  I initiated the Quick Start Configuration mode and told 
> the SI system there was a new battery bank.  I told it the bank was a very 
> small VRLA battery.   The SI system accepted the 46 volts, started up and 
> allowed a generator charge.  After an hour or so we reprogrammed the system 
> for lithium and problem resolved, at least for now.
>  
> Hopefully this trick may help one of you some day.  If it does, it was worth 
> my time typing it out.
>  
> William
>  
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com <http://www.millersolar.com/>
> CA Lic. 773985
>  
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to