Thanks Michael,

Thats what I wanted to confirm.  

For some reason the engineer on this project is in way over his head.

OK back to my client

jay

> On Jul 11, 2024, at 11:11 AM, Michael Morningstar via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> I’ve years of experience running vfds on generator power. No issues. 
> Personally, I run numerous old cast iron woodworking machines that all have 5 
> and 10hp 3p motors with VFDs from a 15kw Kubota open frame generator. 15 
> second ramp up time. And my generator is single phase.
> 
> On Thu, Jul 11, 2024 at 10:06 AM jay via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org 
> <mailto:re-wrenches@lists.re-wrenches.org>> wrote:
> HI All,
> 
> I’m being asked to comment about running a 10hp 3 phase well centrifugal pump 
> off of a 30kw single phase generator with a VFD drive.
> This well pump is located in a tank for fire fighting applications, so its 
> not down a deep well meaning almost no head pressure. And the start time can 
> be quite slow as its not supplying a house/pressure tank.
> 
> 
> I”m not an expert on VFD drives, but I figure many of you are.
> 
> My question, based on the question from the engineer is:
> 
> 1. is there any issue with running a VFD off of a good quality 30kw brand new 
> Kohler turbo propane generator?
> The engineer seems to think there is but he won’t say why. 
> 
> i can’t think of any reason at all?
> 
> This generator is only running this one load, the well pump.
> 
> jay
> 
> 
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> -- 
> 
> Michael Morningstar 
> 
> Morningstar Electric Inc
> PO Box 1494
> Mount Shasta, CA 96067
> 530-921-0560
> CSLB 1116835
> mjmornings...@gmail.com <mailto:mjmornings...@gmail.com>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to