I think you stated the answer, use a frequency drive, your AC source or even DC source can charge the capacitors in the drive. Call your local ABB drive supplier and they will tell you how to set up. If you need 15 kW I find the drive has to be larger than 15 kW, because you are supplying with single phase and not 3 phase.
On Thu, Jul 25, 2024 at 11:46 AM Lou Russo via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Aloha All, > > I have a project that requires powering 6 different pieces of equipment > (mostly small motors) from East Japan that require 200V 3 phase (L-L-L) at > 50Hz (though 60Hz appears to be OK), a unique electrical scheme for sure. > The amp requirement for the various pieces of equipment ranges from 0.75A > to 6A. For a total maximum load of 28 amps. The site is off-grid with > standard 120/240V North American Electrical Scheme using a Sol-Ark 15kW. > > My initial plan was to use Digital Phase Converters from MYUNG YOUN > ELECTRONICS for each device but after seeing the wiring in the control > panel and power distribution box in person there is no room to do this. > Plus the entire panel would need to be rewired. > > Ideally, I would have one device that converts the > electricity appropriately (transformer, VFD, etc). I have reached out to > several EEs and am awaiting responses. > > In the meantime I figured the hive mind of the Wrenches group may have > some ideas or know somebody that would. > > As always, thanks for everyone's time. > > Aloha, > > Lou Russo > Owner > l...@spreesolarsystems.com > Office - 808 345 6762 > Direct Line - 808 731 1907 > Spree Solar Systems LLC > CT-34322 > > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org