Steve,
Are you suggesting that even for like batteries in closed loop, that you
would add 20 minutes per paralleled battery of absorb time? This is much
longer than what I have understood various manufacturers to state. Thanks
for your input.
Howie Michaelson


On Mon, Jul 14, 2025 at 10:33 AM Steve Higgins via RE-wrenches <
[email protected]> wrote:

> Each battery has its own internal resistance. The higher the resistance,
> the longer it takes to charge. The issue is that chargers are
> voltage-based, and when charging multiple batteries in parallel, the
> lower-resistance batteries reach the target voltage sooner than the
> higher-resistance batteries.  These lower resistance batteries cause the
> voltage-based chargers to bypass the absorb stage, and this prevents the
> batteries that are a bit low and out of balance from achieving that voltage
> target.
>
> If your charger isn't a 2-stage charger, or you aren't holding the
> absorb timer long enough, or the charger is a "Smart Charger" and it can be
> made to think that the batteries are fully charged when they are not.
>
> The best way to avoid this:
>
> Wire parallel connections using positive/negative bus bars with
> equal-sized cabling. Do not parallel LFP batteries with only cables, and do
> not use the connections on the battery as a parallel connection.
>
> Use a charger that can be programmed for 2-stage charging.  Unfortunately,
> there aren't many of these out there...
>
> If you can't use a charger that operates in 2 Stage, you need to extend
> the absorb timers so the charger is supplying voltage to the BMSs of the
> parallel batteries, so all batteries have time to get to full balance.   We
> typically suggest 20-30 minutes of absorption time per parallel-connected
> battery up to about 3 to 4 hours.   For that bank with 10 batteries, I
> would set the absorb timers to at least four, if not five, hours.
>
> You should also disable any end amp/return amp settings, as these are
> often not programmed with a time delay and will result in the charger
> bypassing the absorption timer.
>
> In general, the more the customer works with the bank, the more often
> they'll have to balance.
>
> I would start by checking SOCs and Voltages every 90 days. If you notice a
> difference of more than 0.3 volts or a spread of more than 4-5% points, I
> would separate each parallel battery and boost each battery at Bulk/Abs
> Voltage for at least one hour of abs time.   Suppose the bank is way out of
> balance. In that case, it may take a few cycles(6-10) to achieve that
> balance, even so if it's been out of balance for a long time, you may never
> again achieve full balacne, in those cases I would manually balance more
> often every 1-2 months instead of 6-12 months.
>
>
>
> *Steve Higgins* *⋅* *Technical Services Manager*
> *t* +1.902.597.4020   *m* +1.206.790.5840
> *f* +1.902.597.8447   *e* [email protected]
> ------------------------------
> CONFIDENTIALITY: The information transmitted herein is intended only for
> the addressee and may contain confidential, proprietary and/or privileged
> material. Any unauthorized review, distribution or other use of or the
> taking of any action in reliance upon this information is prohibited. If
> you receive this email in error, please contact the sender and delete or
> destroy this message and all copies.
> ------------------------------
>
>
>
>
> On Mon, Jul 14, 2025 at 6:54 AM jay via RE-wrenches <
> [email protected]> wrote:
>
>> Hi Steve,
>>
>> Maybe you can elaborate as to how this could happen.
>>
>> Let’s say all the batteries are designed for a 57.4 usual charge voltage
>> with an acceptance range of around 56-58.4v.
>>
>> If you’re charging 10 batteries to 57.4v, the most that any one battery
>> gets to is 57.4.  If one gets full before others then it stops accepting
>> charge, but at no point in the system does any battery see more than 57.4.
>>
>> Iv’e seen this with same 10 batteries all from one OEM all in one system,
>> all new.  They get off just a little and some take longer or shorter to
>> charge fully to 100% but the voltage never rises above what the inverter or
>> CC is set to. I don’t understand how this would cause damage or issue.
>>
>>
>>
>> thanks
>>
>> jay
>>
>>
>>
>> On Jul 14, 2025, at 7:46 AM, Steve Higgins via RE-wrenches <
>> [email protected]> wrote:
>>
>> I wouldn't do it... By doing so, you'll likely void any manufacturer's
>> warranty.
>>
>> If you must do it, I would manually balance the old/new banks every 60-90
>> days. This involves separating the parallel strings of batteries and
>> charging each string independently to achieve a full charge. If you don't
>> do this, the different ages can cause imbalances, which will lead to
>> problems with the BMS, regardless of whether it is in open-loop or
>> closed-loop configuration.
>>
>>
>>
>> *Steve Higgins* *⋅* *Technical Services Manager*
>> *t* +1.902.597.4020   *m* +1.206.790.5840
>> *f* +1.902.597.8447   *e* [email protected]
>> ------------------------------
>> CONFIDENTIALITY: The information transmitted herein is intended only for
>> the addressee and may contain confidential, proprietary and/or privileged
>> material. Any unauthorized review, distribution or other use of or the
>> taking of any action in reliance upon this information is prohibited. If
>> you receive this email in error, please contact the sender and delete or
>> destroy this message and all copies.
>> ------------------------------
>>
>>
>>
>> On Mon, Jul 14, 2025 at 4:09 AM Jason Szumlanski via RE-wrenches <
>> [email protected]> wrote:
>>
>>> There are never-ending videos on YouTube showing different brands and
>>> capacities of LFP batteries working in parallel. I have never tried it
>>> myself, and every instinct says don't do it, but I have a situation where
>>> it would be very helpful.
>>>
>>> I have a client with an older 60 kWh battery that is discontinued and
>>> incompatible with any other battery from the same manufacturer. It has a
>>> BMS with a 51.2 volt nominal rating. They need another 20 kWh of capacity.
>>> It is too costly to scrap the existing battery and start over, and the
>>> existing battery has been tested and confirmed to hold very close to its
>>> rated capacity.
>>>
>>> What is the real deal on mixing and matching? Is anyone doing this
>>> safely and successfully? I wonder what the battery manufacturers say about
>>> it.
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to