Hi Maverick
That is a unique to me charging parameters. Did you figure this out on your own or did you get this from a OEM?
Is the long absorb time for making sure the internal passive balancing has time to work?
I don’t understand the very low charge voltage. Can you explain please? Thanks Jay
On Jul 14, 2025, at 11:12 AM, Maverick Brown via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:
Jason
It looks like you are in great shape to do what you’re trying to do.
For legacy inverter systems, I have set the absorb quite long: 4 to 6 hours depending on the quantity of individual batteries.
Here at my own house, I have 8 eFlex batteries and 8 Pytes batteries. All in parallel on an outback radian. I have 55.2v absorb set for six hours with zero end amps. For the E flex batteries I have the fortress guardian and I can see the battery state of charge remotely individually. When the individual battery state of charge variation gets too large, I run an equalize session getting the battery voltage up to 56 V.
I have other customers with various mixes of batteries. They are all 16 S lithium iron phosphate and as long as somebody is paying attention so far it’s been working fine.
For this customer, I would select Pytes as the brand of battery to add to the system because in the future, you can still add more batteries to that rack. And you can get the individual battery state of charge using solar assistant. Thank you,
Maverick
Maverick Brown Off-Grid Solar Commander since 2006 Maverick Solar Enterprises, Inc. • Solar Commander Remote Power • SunFlow Systems Cathodic Protection maver...@mavericksolar.com 512-460-9825
On Jul 14, 2025, at 10:56 AM, Jason Szumlanski via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:
This client has been advised that it's not a good idea, and any failures might result in a complete battery replacement. If he goes forward, it will be at his own risk.
They have a full-time homewatch person who is quite capable. He could monitor SOC and also isolate banks for balancing efforts if necessary. We have a nice Midnite 2000A battery combiner there with breakers for each battery, so it would be pretty convenient.
Self-insured. I don't think any of my off-grid barrier island clients have insurance. The mainland insurance market is messed up in Florida. Forget about the islands. Jason Szumlanski Principal Solar Designer | Florida Solar Design Group NABCEP Certified Solar Professional (PVIP) Florida State Certified Solar Contractor CVC56956 Florida Certified Electrical Contractor EC13013208
_______________________________________________List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org
_______________________________________________List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org
|