By BMS, you mean the Main BMS, the top of the stack. I thought you meant BMS 
that is inside of each battery. Oh Boy! That’s a pain and is a whole other 
level! 


Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection 
[email protected]
512-460-9825

> On Sep 23, 2025, at 1:38 PM, Jason Szumlanski 
> <[email protected]> wrote:
> 
> You can purchase the BMS and base unit combination for each stack, but it 
> costs nearly $1,500. I'm not sure if you can purchase the BMS separately from 
> the base unit, but that probably wouldn't significantly impact the price. At 
> this point, it's the principle of the matter. Not warranting something like 
> this is bad business. It can't cost much to fix, and it would be important to 
> understand what happened for future reference and quality assurance purposes. 
> I guess they don't care to understand what happened.
> 
> I'm going to run this up the chain before I give up and tell the customer 
> they're out of luck.
> 
> 
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
> 
> 
> On Tue, Sep 23, 2025 at 11:21 AM Maverick Brown via RE-wrenches 
> <[email protected]> wrote:
>> Will they sell just the BMS instead of having to buy a whole other battery?
>> 
>> I know it should be covered under warranty, but buying a BMS is better than 
>> buying a battery.
>> 
>> I do have a home grid battery that’s behaved in the same way. I went around 
>> in circles with tech-support. I even bought $200 worth of cables so I can 
>> figure out what happened. But I never figured out what happened. And I don’t 
>> think it’s necessary for a tech-support to take control of my computer in 
>> order to do something that written instructions should be adequate.
>> 
>> 
>> Thank you,
>> 
>> Maverick
>> 
>> Maverick Brown
>> Off-Grid Solar Commander since 2006
>> Maverick Solar Enterprises, Inc.
>>  • Solar Commander Remote Power
>>  • SunFlow Systems Cathodic Protection 
>> [email protected] <mailto:[email protected]>
>> 512-460-9825
>> 
>> 
>> 
>>> On Sep 23, 2025, at 9:48 AM, Jason Szumlanski via RE-wrenches 
>>> <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>> 
>>> 
>>> It was only a matter of time. HomeGrid is denying warranty on a BMS that I 
>>> did not install. I can't prove when it was purchased or installed, but the 
>>> original installer never registered it or connected it to the Internet. It 
>>> was likely installed just over a year ago, perhaps 18 months. There was no 
>>> Internet on site at the initial time of installation. What a garbage 
>>> warranty policy.
>>> 
>>> In this case, the BMS seems to be working behind the scenes. The battery 
>>> modules are charging and discharging (confirmed with EMS Tools). The 
>>> problem is that the LCD display shows all zeroes, and the unit will not 
>>> work in parallel with the three other stacks. It is causing a parallel 
>>> error and shutting down the whole house.
>>> 
>>> I did exhaustive diagnostics on it with HomeGrid support, and they sent me 
>>> a "CANalyst-II" tool to try to unbrick or update the faulty unit. All 
>>> attempts to recover the unit failed, but I can "see" the whole stack of 
>>> battery modules through the BMS's RS232 port. 
>>> 
>>> So they're going to further alienate a customer over a clearly faulty BMS 
>>> unit that should be replaced under warranty. Not smart.
>>> 
>>> 
>>> I will reiterate my recommendation against this brand for off-grid use. 
>>> It's simply not resilient enough and too hard to service/maintain.
>>> 
>>> 
>>> Jason Szumlanski
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>> Florida Certified Electrical Contractor EC13013208
>>> 
>>> 
>>> 
>>> On Tue, Feb 11, 2025 at 9:17 PM Jason Szumlanski 
>>> <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>>> For what it's worth, they haven't said anything about internet 
>>>> connectivity on these two systems I'm dealing with right now, and they are 
>>>> both Gen 3.
>>>> 
>>>> One site has a bunch of firmware discrepancies, and this is the site with 
>>>> one module that has all cells low voltage. Not sure if it's even 
>>>> recoverable. It's sitting at 39V.
>>>> 
>>>> The other site has all the same firmware. This is the one I went to today. 
>>>> One of 16 modules (2 full stacks) has one of 15 cells internally that is 
>>>> low voltage. To me, that's a clear warranty swap situation, but customer 
>>>> service wasn't having it. Disassemble the battery and charge it? That's 
>>>> not a solution. It has been escalated. We will see what happens. 
>>>> 
>>>> Clearly we should be able to take these back to the shop for diagnostics 
>>>> at a minimum and get them RMA'd. Requiring the purchase of a Windows 
>>>> laptop and a battery charger is not ideal for sure. 
>>>> 
>>>> The only good thing I can say is customer service took over my PC today 
>>>> remotely and ran diagnostics after installing the required software (which 
>>>> isn't a fast process). I was expecting them to say, "yep it's toast and 
>>>> we're sending you a new one, valued customer."
>>>> 
>>>> No such luck. 
>>>> 
>>>> Jason
>>>> 
>>>> 
>>>> On Tue, Feb 11, 2025, 6:48 PM Tyrone Houck via RE-wrenches 
>>>> <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>>> Yep. And the 10 year warranty is only good if connected to the internet. 
>>>>> Firmware update of every module is crucial or else there will likely be 
>>>>> imbalances. You may be able to address it as 1 and shut of the others and 
>>>>> charge it through the bus but if it's cell voltage is too low it may be 
>>>>> an rma situation. I have had similar issues especially with gen 2. Zero 
>>>>> issues yet with any gen 3 modules but the internet thing really struck a 
>>>>> nerve as they only just recently got their internet monitoring 
>>>>> functional.. having to go back to every site is a serious pain just to 
>>>>> ensure what should be a basic warranty. Best of luck and feel free to 
>>>>> contact me offsite if you have any other questions I might be able to  
>>>>> help with.
>>>>> Tyrone Houck
>>>>> Oregon Solarworks LLC 
>>>>> CCB #204937 LRT #076
>>>>> 541-787-1366 
>>>>> [email protected] <mailto:[email protected]>
>>>>> 
>>>>>    
>>>>> 
>>>>> On Tue, Feb 11, 2025, 3:36 PM Jason Szumlanski via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>>> Hi Wrenches,
>>>>>> 
>>>>>> I am regretting some HomeGrid Stack'd off-grid installations right now. 
>>>>>> There is a major flaw in the way these function in an error state. For 
>>>>>> those of you that don't know, these 48V batteries are stacked with a 
>>>>>> single BMS on top, covering up to 8 batteries below. Each battery module 
>>>>>> has a circuit breaker and dip switches to identify the battery 
>>>>>> communication number and location in the stack. Each BMS can be 
>>>>>> paralleled to additional stacks with communication cabling. 
>>>>>> 
>>>>>> The issue is when one battery module goes into an error state. What will 
>>>>>> happen is that battery stack's BMS will recognize the error, and then 
>>>>>> shut down the whole stack. This cascades to the other stacks and the 
>>>>>> system shuts down - fails to deliver 48V at the output terminals on the 
>>>>>> BMS of any stack.
>>>>>> 
>>>>>> That is annoying, but what's even more problematic is you can't just 
>>>>>> shut off the offending battery to bypass it. You need to physically 
>>>>>> change all of the dip switches to bypass it and then reprogram the BMS 
>>>>>> to re-recognize the new module count (after taking it out of parallel). 
>>>>>> This is all very time consuming and requires the inverter system to be 
>>>>>> shut down. Even if a battery is not in an error state, you can't just 
>>>>>> turn it off. The whole system goes haywire. 
>>>>>>  
>>>>>> Once you have it bypassed, you can hook up a RS-232 cable (Mac users 
>>>>>> need not apply) and use their software to gather diagnostics. Customer 
>>>>>> service will then want to do additional diagnostics with the battery in 
>>>>>> the stock, but that is not reasonable in and off-grid system where 
>>>>>> uptime is critical. One of the faulty modules I am dealing with was 
>>>>>> diagnosed as one of 15 cells with low voltage. The "solution" is to take 
>>>>>> it out of the stack and charge it to 100% with an external charger. 
>>>>>> 
>>>>>> By the time I'm done with all of the diagnostic nonsense, I can almost 
>>>>>> pay for a new battery with the lost labor. Isn't the whole idea for this 
>>>>>> not to happen with balancing done automatically? It was suggested to me 
>>>>>> that it didn't get charged to 100% often enough, and that is why it 
>>>>>> happened. That isn't an acceptable reason for failure in an off-grid 
>>>>>> system. 
>>>>>> 
>>>>>> I hate to say this, but EG4 has a far better 5kWh solution in this 
>>>>>> respect. Each module has it's own BMS. When one fails, you can simply 
>>>>>> turn off the circuit breaker and everything else continues to work. In 
>>>>>> fact, a fault in one BMS doesn't take out the whole stack or stacks of 
>>>>>> battery modules. 
>>>>>> 
>>>>>> Back to HomeGrid. When this happens, in my mind this is an automatic 
>>>>>> RMA. They should be replacing these, no questions asked. Especially at 
>>>>>> almost twice the price of EG4. They actually want me to disassemble the 
>>>>>> case of the battery and charge it with an external charger (which I 
>>>>>> don't have) directly from the terminals that are internal to the battery 
>>>>>> case. Totally unacceptable. Whatever is inside that case is their 
>>>>>> problem in my opinion. 
>>>>>> 
>>>>>> I am not selling anymore HomeGrid until I get satisfactory resolution to 
>>>>>> these issues. EG4 isn't perfect, but I have actually had pretty good 
>>>>>> success installing some that I sold and quite a few that consumers 
>>>>>> purchased directly. And at almost half the price, it's easier to eat the 
>>>>>> cost of a battery here and there for customer satisfaction.
>>>>>> 
>>>>>> Anyone have similar issues with HomeGrid?
>>>>>> 
>>>>>> Jason Szumlanski 
>>>>>> Florida Solar Design Group
>>>>>> _______________________________________________
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to