Yes, I meant the stack BMS on top. It's pretty crazy that I can connect a cable to it and see all of the individual battery units below, and the stack appears to be operating normally, but the stack BMS will not operate in parallel and does not display anything but zeroes on the display. I would think it could be recovered remotely or with software on my laptop, but apparently not. Why they are pushing back on the warranty is a mystery to me.
Jason Szumlanski Principal Solar Designer | Florida Solar Design Group NABCEP Certified Solar Professional (PVIP) Florida State Certified Solar Contractor CVC56956 Florida Certified Electrical Contractor EC13013208 On Tue, Sep 23, 2025 at 5:51 PM Maverick Brown via RE-wrenches < [email protected]> wrote: > By BMS, you mean the Main BMS, the top of the stack. I thought you meant > BMS that is inside of each battery. Oh Boy! That’s a pain and is a whole > other level! > > > Maverick Brown > Off-Grid Solar Commander since 2006 > *Maverick Solar Enterprises, Inc.* > * • Solar Commander Remote Power* > > * • SunFlow Systems Cathodic Protection *[email protected] > 512-460-9825 > > On Sep 23, 2025, at 1:38 PM, Jason Szumlanski < > [email protected]> wrote: > > You can purchase the BMS and base unit combination for each stack, but it > costs nearly $1,500. I'm not sure if you can purchase the BMS separately > from the base unit, but that probably wouldn't significantly impact the > price. At this point, it's the principle of the matter. Not warranting > something like this is bad business. It can't cost much to fix, and it > would be important to understand what happened for future reference and > quality assurance purposes. I guess they don't care to understand what > happened. > > I'm going to run this up the chain before I give up and tell the customer > they're out of luck. > > > Jason Szumlanski > Principal Solar Designer | Florida Solar Design Group > NABCEP Certified Solar Professional (PVIP) > Florida State Certified Solar Contractor CVC56956 > Florida Certified Electrical Contractor EC13013208 > > > On Tue, Sep 23, 2025 at 11:21 AM Maverick Brown via RE-wrenches < > [email protected]> wrote: > >> Will they sell just the BMS instead of having to buy a whole other >> battery? >> >> I know it should be covered under warranty, but buying a BMS is better >> than buying a battery. >> >> I do have a home grid battery that’s behaved in the same way. I went >> around in circles with tech-support. I even bought $200 worth of cables so >> I can figure out what happened. But I never figured out what happened. And >> I don’t think it’s necessary for a tech-support to take control of my >> computer in order to do something that written instructions should be >> adequate. >> >> >> Thank you, >> >> Maverick >> >> Maverick Brown >> Off-Grid Solar Commander since 2006 >> Maverick Solar Enterprises, Inc. >> • Solar Commander Remote Power >> • SunFlow Systems Cathodic Protection >> [email protected] >> 512-460-9825 >> >> >> >> On Sep 23, 2025, at 9:48 AM, Jason Szumlanski via RE-wrenches < >> [email protected]> wrote: >> >> >> It was only a matter of time. HomeGrid is denying warranty on a BMS that >> I did not install. I can't prove when it was purchased or installed, but >> the original installer never registered it or connected it to the Internet. >> It was likely installed just over a year ago, perhaps 18 months. There was >> no Internet on site at the initial time of installation. What a garbage >> warranty policy. >> >> In this case, the BMS seems to be working behind the scenes. The battery >> modules are charging and discharging (confirmed with EMS Tools). The >> problem is that the LCD display shows all zeroes, and the unit will not >> work in parallel with the three other stacks. It is causing a parallel >> error and shutting down the whole house. >> >> I did exhaustive diagnostics on it with HomeGrid support, and they sent >> me a "CANalyst-II" tool to try to unbrick or update the faulty unit. All >> attempts to recover the unit failed, but I can "see" the whole stack of >> battery modules through the BMS's RS232 port. >> >> So they're going to further alienate a customer over a clearly faulty BMS >> unit that should be replaced under warranty. Not smart. >> >> >> I will reiterate my recommendation against this brand for off-grid use. >> It's simply not resilient enough and too hard to service/maintain. >> >> >> Jason Szumlanski >> Principal Solar Designer | Florida Solar Design Group >> NABCEP Certified Solar Professional (PVIP) >> Florida State Certified Solar Contractor CVC56956 >> Florida Certified Electrical Contractor EC13013208 >> >> >> On Tue, Feb 11, 2025 at 9:17 PM Jason Szumlanski < >> [email protected]> wrote: >> >>> For what it's worth, they haven't said anything about internet >>> connectivity on these two systems I'm dealing with right now, and they are >>> both Gen 3. >>> >>> One site has a bunch of firmware discrepancies, and this is the site >>> with one module that has all cells low voltage. Not sure if it's even >>> recoverable. It's sitting at 39V. >>> >>> The other site has all the same firmware. This is the one I went to >>> today. One of 16 modules (2 full stacks) has one of 15 cells internally >>> that is low voltage. To me, that's a clear warranty swap situation, but >>> customer service wasn't having it. Disassemble the battery and charge it? >>> That's not a solution. It has been escalated. We will see what happens. >>> >>> Clearly we should be able to take these back to the shop for diagnostics >>> at a minimum and get them RMA'd. Requiring the purchase of a Windows laptop >>> and a battery charger is not ideal for sure. >>> >>> The only good thing I can say is customer service took over my PC today >>> remotely and ran diagnostics after installing the required software (which >>> isn't a fast process). I was expecting them to say, "yep it's toast and >>> we're sending you a new one, valued customer." >>> >>> No such luck. >>> >>> Jason >>> >>> >>> On Tue, Feb 11, 2025, 6:48 PM Tyrone Houck via RE-wrenches < >>> [email protected]> wrote: >>> >>>> Yep. And the 10 year warranty is only good if connected to the >>>> internet. Firmware update of every module is crucial or else there will >>>> likely be imbalances. You may be able to address it as 1 and shut of the >>>> others and charge it through the bus but if it's cell voltage is too low it >>>> may be an rma situation. I have had similar issues especially with gen 2. >>>> Zero issues yet with any gen 3 modules but the internet thing really struck >>>> a nerve as they only just recently got their internet monitoring >>>> functional.. having to go back to every site is a serious pain just to >>>> ensure what should be a basic warranty. Best of luck and feel free to >>>> contact me offsite if you have any other questions I might be able to help >>>> with. >>>> Tyrone Houck >>>> Oregon Solarworks LLC >>>> CCB #204937 LRT #076 >>>> 541-787-1366 >>>> [email protected] >>>> >>>> >>>> >>>> On Tue, Feb 11, 2025, 3:36 PM Jason Szumlanski via RE-wrenches < >>>> [email protected]> wrote: >>>> >>>>> Hi Wrenches, >>>>> >>>>> I am regretting some HomeGrid Stack'd off-grid installations right >>>>> now. There is a major flaw in the way these function in an error state. >>>>> For >>>>> those of you that don't know, these 48V batteries are stacked with a >>>>> single >>>>> BMS on top, covering up to 8 batteries below. Each battery module has a >>>>> circuit breaker and dip switches to identify the battery communication >>>>> number and location in the stack. Each BMS can be paralleled to additional >>>>> stacks with communication cabling. >>>>> >>>>> The issue is when one battery module goes into an error state. What >>>>> will happen is that battery stack's BMS will recognize the error, and then >>>>> shut down the whole stack. This cascades to the other stacks and the >>>>> system >>>>> shuts down - fails to deliver 48V at the output terminals on the BMS of >>>>> any >>>>> stack. >>>>> >>>>> That is annoying, but what's even more problematic is you can't just >>>>> shut off the offending battery to bypass it. You need to physically change >>>>> all of the dip switches to bypass it and then reprogram the BMS to >>>>> re-recognize the new module count (after taking it out of parallel). This >>>>> is all very time consuming and requires the inverter system to be shut >>>>> down. Even if a battery is not in an error state, you can't just turn it >>>>> off. The whole system goes haywire. >>>>> >>>>> Once you have it bypassed, you can hook up a RS-232 cable (Mac users >>>>> need not apply) and use their software to gather diagnostics. Customer >>>>> service will then want to do additional diagnostics with the battery in >>>>> the >>>>> stock, but that is not reasonable in and off-grid system where uptime is >>>>> critical. One of the faulty modules I am dealing with was diagnosed as one >>>>> of 15 cells with low voltage. The "solution" is to take it out of the >>>>> stack >>>>> and charge it to 100% with an external charger. >>>>> >>>>> By the time I'm done with all of the diagnostic nonsense, I can almost >>>>> pay for a new battery with the lost labor. Isn't the whole idea for this >>>>> not to happen with balancing done automatically? It was suggested to me >>>>> that it didn't get charged to 100% often enough, and that is why it >>>>> happened. That isn't an acceptable reason for failure in an off-grid >>>>> system. >>>>> >>>>> I hate to say this, but EG4 has a far better 5kWh solution in this >>>>> respect. Each module has it's own BMS. When one fails, you can simply turn >>>>> off the circuit breaker and everything else continues to work. In fact, a >>>>> fault in one BMS doesn't take out the whole stack or stacks of battery >>>>> modules. >>>>> >>>>> Back to HomeGrid. When this happens, in my mind this is an automatic >>>>> RMA. They should be replacing these, no questions asked. Especially at >>>>> almost twice the price of EG4. They actually want me to disassemble the >>>>> case of the battery and charge it with an external charger (which I don't >>>>> have) directly from the terminals that are internal to the battery case. >>>>> Totally unacceptable. Whatever is inside that case is their problem in my >>>>> opinion. >>>>> >>>>> I am not selling anymore HomeGrid until I get satisfactory resolution >>>>> to these issues. EG4 isn't perfect, but I have actually had pretty good >>>>> success installing some that I sold and quite a few that consumers >>>>> purchased directly. And at almost half the price, it's easier to eat the >>>>> cost of a battery here and there for customer satisfaction. >>>>> >>>>> Anyone have similar issues with HomeGrid? >>>>> >>>>> Jason Szumlanski >>>>> Florida Solar Design Group >>>>> _______________________________________________ >>>>> >>>> _______________________________________________ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/[email protected]/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/[email protected]/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> >> > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org

