I consulted our Code expert on this question, and this is his explanation:

In 2020 NEC and previous code cycles, the N-G bond requirement in the Solar 
OCPD for supply side taps was a grey area.  In the 2023 NEC, it is clear the 
Solar OCPD for supply side taps requires the N-G bond.  This mimics the 
requirement where a building has multiple service OCPD enclosures.
 
If the N-G bond, supply side tap conductors (phase and neutral, no EGC), and 
GEC are all sized and installed correctly (as if it is a separate service), 
there should not be any issues.

I’m not familiar with Midnite inverters, but “CA-DC link Overvoltage error“ 
sounds like a DC issue, so I don’t see how the AC voltage would matter.  If 
this error is related to AC voltage, maybe the real issue is a faulty neutral 
connection between the service and utility transformer?
 

Tom McCalmont, P.E.
CEO, Paired Power
pairedpower.com <http://pairedpower.com/> | LinkedIn 
<https://www.linkedin.com/company/paired-power/>
Direct: (669) 877-2931



> On Oct 23, 2025, at 8:01 AM, Tyrone Houck via RE-wrenches 
> <[email protected]> wrote:
> 
> My interpretation, and the way it was explained to me by both Ryan Mayfield 
> and Kyle Bolger(several years ago at this point, popular opinion may have 
> changed since). Is that it is not a seperate service.
>  It is however required to have a ground-neutral bond( though in my opinion 
> pointless and redundant as there is a bond in the enclosure where the tap is 
> made). If it gives you any issue, ensure as close to equal potential to the 
> grounding electrode as possible(and make sure your neutral is appropriately 
> sized). I personally don't see the point but it is an NEC requirement 
> 
> 
>    
> 
> On Thu, Oct 23, 2025, 6:08 AM Dave Tedeyan via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
>> Hi All, 
>> 
>> For years I have understood that when doing a supply side connection, you 
>> are supposed to bond the neutral to ground in the solar service disconnect. 
>> I have a Midnite AIO system with two inverters (set up as a supply side 
>> connection) that recently was getting a CA-DC link Overvoltage error. When 
>> talking to Midnite, their first response was to make sure that there was 
>> only one N-G bond in the whole system. When I mentioned that the solar is a 
>> separate service and thus there is a N-G bond in both the main panel and the 
>> inverter distribution panel, they said to remove it from the inverter 
>> distribution panel. I want to make the system work right, but I also am 
>> hesitant to do something against how I have understood the NEC to be for a 
>> long time. I am curious if you all have thoughts on this or run into a 
>> similar situation.
>> 
>> Cheers, 
>> Dave
>> 
>> --
>> 
>>  <https://www.sungineersolar.com/>   
>> Dave Tedeyan, P.E.
>> Owner | Sungineer Solar
>> p: he | him | his
>> a: 1653 Slaterville Rd. 
>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>   
>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>|
>>  Ithaca, NY 14850 
>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>> c: (607) 270-0370
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to