I just had an experience at work with battery problems. I work for a wireless company and we use 105 amp lead acid cells in a series-paralel configuration, 12 volt cells, three 48 volt strings. I was at the site last week and detected the smell (and taste) of overcharging batteries. I learned a trick in my old "Bell Head" days to open my mouth and inhale while in the battery room of central offices. This was taught to me by and old time technician. If a battery is overcharging, you will detect a strange taste on your tongue that you learn to remember, that also warns you of the possibility of explosive gasses in the area.
In the cellsite, I found one of the 48 volt strings very warm and the battery cases of all 4 batteries buckling and swelling. A voltage test showed one battery reading 10.5 volts instead of 13.5 volts. This indicated a shorted cell in that 12 volt battery. I ventilated the room, put on safety glasses, and disconnected the sting from the other two strings. The entire string will have to be replaced. This is an example of what can happen to a series battery. I would discourage you from using parallel batteries on a repeater, one large battery would be a much better and safer choice. We do use parallel batteries at work, but routine maintenance is required to keep them safely operating. 73, Joe, K1ike ---- goodyk3ng <[EMAIL PROTECTED]> wrote: > Greetings, > > I'm curious if anyone has experience paralleling deep cycle batteries > for a repeater backup. Yahoo! Groups Links <*> To visit your group on the web, go to: http://groups.yahoo.com/group/Repeater-Builder/ <*> To unsubscribe from this group, send an email to: [EMAIL PROTECTED] <*> Your use of Yahoo! Groups is subject to: http://docs.yahoo.com/info/terms/