Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Jason Szumlanski
I agree that it just ain't worth it to do work twice. The bottom line is
that if you insist on using the Enphase WEEB solution, ask your
inspector it if it will pass before you do it. Once you develop a
rapport, most are willing to discuss these issues in advance of the
inspection. It doesn't hurt to clearly indicate your intentions on your
plans. I also agree that a bare #6 to each microinverter is not that
difficult to accomplish, and not much more expensive if at all. It's a
little more painful when using a microinverter mounted to a Zep Solar
rail-less system, but there is no approved WEEB for that anyway.

I wonder what Enphase has to say about industry experts disagreeing with
their assessment of the WEEB. Hopefully they understand that I as an
installer am not trying to just make things a) cheap and b) easy. I am
trying to make things a) right, and b) clear.

Jason Szumlanski
Fafco Solar


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill
Brooks
Sent: Friday, March 04, 2011 1:48 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

All,

While there is ambiguity in the 2008 NEC in 690.47(C) on the
requirements
for system grounding of PV systems, the 2011 NEC in 690.47(C) clarifies
the
intent. 

While an application note from Enphase may state that WEEBs can be used
as
part of the grounding electrode system, I disagree with this concept and
do
not believe it meets the requirements or intent of the NEC as clarified
in
the 2011 NEC. The problem with a grounded PV inverter is that it
requires a
grounding electrode conductor (GEC) from the grounding point (on the
inverter) to the grounding electrode. The 2008 and 2011 NEC allows for
that
connection to be terminated at the grounding bar in the service panel
supplying the micro-inverters.

There is no problem with using the WEEB to bond the rails to the modules
and
then to the Enphase Micro-inverter. From the micro-inverter, a bare 6AWG
could be run to pick up each micro-inveter in each row of
micro-inverters
with splices made to a single bare 6AWG made with irreversible splices.
At
the rooftop junction box, the GEC could be irreversibly spliced to an
8AWG
green insulated conductor to run unbroken to the grounding busbar in the
service equipment.

While this may not be in agreement with the Enphase application note, I
believe it meets the intent and letter of the NEC as clarified in the
2011
NEC 690.47(C). While using the WEEBs in the GEC circuit may not cause a
life
or death issue, it is absolutely open to being questioned by the
electrical
inspector. If the electrical inspector decides it is wrong--it is wrong.
If
you or the field inspector appeals to me or an expert like John Wiles,
we
will state what I have stated above. Then you would have to remove all
the
modules, throw away the WEEBs, put in new WEEBs with the new bare copper
6AWG and reinstall the modules--it just ain't worth it.

690.47(D) was removed from the 2011 NEC because it was primarily for
lightning protection (not a safety issue according to the NEC) and was
ambiguously worded with respect to residential rooftop PV systems. If
the
local jurisdiction requires the additional electrode, install a j-box at
the
point near ground-level where the conduit transitions from vertical to
horizontal and install an irreversibly spliced bare 6AWG to run from the
j-box to a ground rod below the j-box--mildly painful, but very doable.

Bill.

Bill Brooks, PE
Principal
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
707-332-0761 (office and mobile)
707-451-7739 (fax)
b...@brooksolar.com (email)
www.brooksolar.com (web)



-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, March 03, 2011 12:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] grounding the Enphase inverter

I don't see it in your comments. At least that wasn't clear. Anyway, in
that case there is absolutely no reason to use the inverter ground clip.
The whole purpose of the inverter- rail WEEB is to eliminate the ground
wire.

Take a look at the Enphase App Note here:
http://www.enphaseenergy.com/downloads/EnphaseAppNote_WEEB_Installation.
pdf

It starts out, As an alternative to installing a continuous grounding
electrode conductor connected to each microinverter chassis, a grounding
washer may be used to ground the microinverter to grounded racking. It
couldn't be more clear for an inspector, but I understand that sometimes
it's hard to convince them. Hope this helps!

Jason Szumlanski
Fafco Solar

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk
Herander, VSE
Sent: Thursday, March 03, 2011 8:46 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

As an aside, why didn't you 

Re: [RE-wrenches] York furnace

2011-03-04 Thread Bill Loesch
William,

Reportedly this is the same issue that Staber (the top loading, horizontal axis 
clothes washer manufacturer) has made their quest to solve. Reportedly 
configuring their washer with different caps. for different inverter models. 
You might want to touch base with them for suggestions.

Good luck,

Bill
  - Original Message - 
  From: William Miller 
  To: RE-wrenches 
  Sent: Friday, March 04, 2011 12:25 AM
  Subject: Re: [RE-wrenches] York furnace


  Dave:

  What value was the capacitor?

  Wm



  At 06:58 PM 3/3/2011, you wrote:

Content-Type: multipart/alternative;
boundary==_NextPart_000_0028_01CBD9EE.292D4E70
Content-Language: en-us

William,
 
It's been yrs since I dealt with this issue, and it wasn't a York 
specifically.. But I had an issue with a furnace and an old black Trace mod 
sine. A capacitor in the feed to the furnace did the trick.
 
Dave
 
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Thursday, March 03, 2011 7:42 PM
To: RE-wrenches
Subject: [RE-wrenches] York furnace
 
Friends:

Have any of you ever had problems with a York furnace on a modified sine 
wave inverter?  What steps did you take to resolve the issues?

Thanks in advance,

William Miller


Please note new e-mail address and domain:

William Miller 
Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1204 / Virus Database: 1435/3480 - Release Date: 03/03/11
  Please note new e-mail address and domain:

  William Miller 
  Miller Solar
  Voice :805-438-5600
  email: will...@millersolar.com
  http://millersolar.com
  License No. C-10-773985




--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] York furnace

2011-03-04 Thread dave
William,

I do not recall. Presently I'm away from my office. I could check tomorrow on 
that.

Dave
Sent via BlackBerry by ATT

-Original Message-
From: William Miller will...@millersolar.com
Sender: re-wrenches-boun...@lists.re-wrenches.orgDate: Thu, 03 Mar 2011 
22:25:29 
To: RE-wrenchesre-wrenches@lists.re-wrenches.org
Reply-To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] York furnace

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread August Goers
Hi Bill -

I see that you recommend that the GEC  between the micro inverters be run
in 6AWG before it enters the conduit and transitions to 8AWG. I assume
this is to meet the intent of 250.64(B) - Securing and Protection Against
Physical Damage?

Switching over to equipment grounding, it is very common in the industry
to run bare 10AWG between the modules and racks. Does this still seem
acceptable to you?

Best,

August


August Goers

Luminalt Energy Corporation
1320 Potrero Avenue
San Francisco, CA 94110
m: 415.559.1525
o: 415.641.4000
aug...@luminalt.com

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill
Brooks
Sent: Thursday, March 03, 2011 10:48 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

All,

While there is ambiguity in the 2008 NEC in 690.47(C) on the requirements
for system grounding of PV systems, the 2011 NEC in 690.47(C) clarifies
the intent.

While an application note from Enphase may state that WEEBs can be used as
part of the grounding electrode system, I disagree with this concept and
do not believe it meets the requirements or intent of the NEC as clarified
in the 2011 NEC. The problem with a grounded PV inverter is that it
requires a grounding electrode conductor (GEC) from the grounding point
(on the
inverter) to the grounding electrode. The 2008 and 2011 NEC allows for
that connection to be terminated at the grounding bar in the service panel
supplying the micro-inverters.

There is no problem with using the WEEB to bond the rails to the modules
and then to the Enphase Micro-inverter. From the micro-inverter, a bare
6AWG could be run to pick up each micro-inveter in each row of
micro-inverters with splices made to a single bare 6AWG made with
irreversible splices. At the rooftop junction box, the GEC could be
irreversibly spliced to an 8AWG green insulated conductor to run unbroken
to the grounding busbar in the service equipment.

While this may not be in agreement with the Enphase application note, I
believe it meets the intent and letter of the NEC as clarified in the 2011
NEC 690.47(C). While using the WEEBs in the GEC circuit may not cause a
life or death issue, it is absolutely open to being questioned by the
electrical inspector. If the electrical inspector decides it is wrong--it
is wrong. If you or the field inspector appeals to me or an expert like
John Wiles, we will state what I have stated above. Then you would have to
remove all the modules, throw away the WEEBs, put in new WEEBs with the
new bare copper 6AWG and reinstall the modules--it just ain't worth it.

690.47(D) was removed from the 2011 NEC because it was primarily for
lightning protection (not a safety issue according to the NEC) and was
ambiguously worded with respect to residential rooftop PV systems. If the
local jurisdiction requires the additional electrode, install a j-box at
the point near ground-level where the conduit transitions from vertical to
horizontal and install an irreversibly spliced bare 6AWG to run from the
j-box to a ground rod below the j-box--mildly painful, but very doable.

Bill.

Bill Brooks, PE
Principal
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
707-332-0761 (office and mobile)
707-451-7739 (fax)
b...@brooksolar.com (email)
www.brooksolar.com (web)



-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, March 03, 2011 12:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] grounding the Enphase inverter

I don't see it in your comments. At least that wasn't clear. Anyway, in
that case there is absolutely no reason to use the inverter ground clip.
The whole purpose of the inverter- rail WEEB is to eliminate the ground
wire.

Take a look at the Enphase App Note here:
http://www.enphaseenergy.com/downloads/EnphaseAppNote_WEEB_Installation.
pdf

It starts out, As an alternative to installing a continuous grounding
electrode conductor connected to each microinverter chassis, a grounding
washer may be used to ground the microinverter to grounded racking. It
couldn't be more clear for an inspector, but I understand that sometimes
it's hard to convince them. Hope this helps!

Jason Szumlanski
Fafco Solar

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk
Herander, VSE
Sent: Thursday, March 03, 2011 8:46 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

As an aside, why didn't you use approved WEEB's to bond the inverters to
the rails? This eliminates the ground wire to each inverter. Simpler
IMHO.

I did. It is in my comments.

Kirk Herander
Vermont Solar Engineering
802.863.1202
NABCEP(tm) Certified Solar Installer
NYSERDA-eligible Installer
VT Solar Incentive Program Partner


Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Mark Frye
The interesting thing to me is the underlying assumption in the Code that a
GEC is requried for grid-tied inverters at all. Why isn't EG sufficient for
function and safety. 

Which of the following common electrical equipment has the same requirement:

UPS
Motors with regenerative energy disipators
DC power supplies
Standby generators

??
 
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Thursday, March 03, 2011 10:48 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

All,

While there is ambiguity in the 2008 NEC in 690.47(C) on the requirements
for system grounding of PV systems, the 2011 NEC in 690.47(C) clarifies the
intent. 

While an application note from Enphase may state that WEEBs can be used as
part of the grounding electrode system, I disagree with this concept and do
not believe it meets the requirements or intent of the NEC as clarified in
the 2011 NEC. The problem with a grounded PV inverter is that it requires a
grounding electrode conductor (GEC) from the grounding point (on the
inverter) to the grounding electrode. The 2008 and 2011 NEC allows for that
connection to be terminated at the grounding bar in the service panel
supplying the micro-inverters.

There is no problem with using the WEEB to bond the rails to the modules and
then to the Enphase Micro-inverter. From the micro-inverter, a bare 6AWG
could be run to pick up each micro-inveter in each row of micro-inverters
with splices made to a single bare 6AWG made with irreversible splices. At
the rooftop junction box, the GEC could be irreversibly spliced to an 8AWG
green insulated conductor to run unbroken to the grounding busbar in the
service equipment.

While this may not be in agreement with the Enphase application note, I
believe it meets the intent and letter of the NEC as clarified in the 2011
NEC 690.47(C). While using the WEEBs in the GEC circuit may not cause a life
or death issue, it is absolutely open to being questioned by the electrical
inspector. If the electrical inspector decides it is wrong--it is wrong. If
you or the field inspector appeals to me or an expert like John Wiles, we
will state what I have stated above. Then you would have to remove all the
modules, throw away the WEEBs, put in new WEEBs with the new bare copper
6AWG and reinstall the modules--it just ain't worth it.

690.47(D) was removed from the 2011 NEC because it was primarily for
lightning protection (not a safety issue according to the NEC) and was
ambiguously worded with respect to residential rooftop PV systems. If the
local jurisdiction requires the additional electrode, install a j-box at the
point near ground-level where the conduit transitions from vertical to
horizontal and install an irreversibly spliced bare 6AWG to run from the
j-box to a ground rod below the j-box--mildly painful, but very doable.

Bill.

Bill Brooks, PE
Principal
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
707-332-0761 (office and mobile)
707-451-7739 (fax)
b...@brooksolar.com (email)
www.brooksolar.com (web)

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Mage NABCEP Training

2011-03-04 Thread Dean T. Newberry

Hello Wrenches,
Does anyone have experience with Mage NABCEP course prep?

Thanks in advance,
Dean

--
Dean T. Newberry
Talbott Solar  Radiant Homes Inc.
397 B Street
Davis, CA 95616

T: 530 753-1900
F: 530 758-2050
E: de...@talbottsolar.com
W: http://www.TalbottSolar.com/


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Mage NABCEP Training

2011-03-04 Thread wirewiz
Dean,

No experience with Mage but the two prep courses I took were a waist of time
and money (IMHO). Find yourself a one day John Wiles seminar for $100, that
is well worth it. Study, study, study. I would set aside 3-4 hours a day
until test time. Become quick and sure at referencing the NEC, they supply
you with one at the test. Buy the Casio FX260 calculator, again supplied at
the test, and become familiar with it. Use the NABCEP study guide. Get your
PV math down pat. Read Dunlop's book. I failed it because I did not study
hard enough. It's really not that difficult a test to pass (70 grade) if you
know the material. I will send you my prep material if you want to use it as
a guideline. Good luck.

I'm the guy who whined about the NABCEP ad and kind of regret doing so. My
apologies to all who studied hard and passed the test.

Larry Liesner
System Design
Elektron Solar, LLC
16 Ketchum St.
Westport, CT 06880
203-557-3127 (office)
203-644-2404 (cell)
203-549-0977 (fax)
wire...@gmail.com


On Fri, Mar 4, 2011 at 11:27 AM, Dean T. Newberry de...@dcn.org wrote:

 Hello Wrenches,
 Does anyone have experience with Mage NABCEP course prep?

 Thanks in advance,
 Dean

 --
 Dean T. Newberry
 Talbott Solar  Radiant Homes Inc.
 397 B Street
 Davis, CA 95616

 T: 530 753-1900
 F: 530 758-2050
 E: de...@talbottsolar.com
 W: http://www.TalbottSolar.com/


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




--
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Bill Brooks
System grounding requirements.

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Friday, March 04, 2011 7:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

The interesting thing to me is the underlying assumption in the Code that a
GEC is requried for grid-tied inverters at all. Why isn't EG sufficient for
function and safety. 

Which of the following common electrical equipment has the same requirement:

UPS
Motors with regenerative energy disipators
DC power supplies
Standby generators

??
 
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Thursday, March 03, 2011 10:48 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

All,

While there is ambiguity in the 2008 NEC in 690.47(C) on the requirements
for system grounding of PV systems, the 2011 NEC in 690.47(C) clarifies the
intent. 

While an application note from Enphase may state that WEEBs can be used as
part of the grounding electrode system, I disagree with this concept and do
not believe it meets the requirements or intent of the NEC as clarified in
the 2011 NEC. The problem with a grounded PV inverter is that it requires a
grounding electrode conductor (GEC) from the grounding point (on the
inverter) to the grounding electrode. The 2008 and 2011 NEC allows for that
connection to be terminated at the grounding bar in the service panel
supplying the micro-inverters.

There is no problem with using the WEEB to bond the rails to the modules and
then to the Enphase Micro-inverter. From the micro-inverter, a bare 6AWG
could be run to pick up each micro-inveter in each row of micro-inverters
with splices made to a single bare 6AWG made with irreversible splices. At
the rooftop junction box, the GEC could be irreversibly spliced to an 8AWG
green insulated conductor to run unbroken to the grounding busbar in the
service equipment.

While this may not be in agreement with the Enphase application note, I
believe it meets the intent and letter of the NEC as clarified in the 2011
NEC 690.47(C). While using the WEEBs in the GEC circuit may not cause a life
or death issue, it is absolutely open to being questioned by the electrical
inspector. If the electrical inspector decides it is wrong--it is wrong. If
you or the field inspector appeals to me or an expert like John Wiles, we
will state what I have stated above. Then you would have to remove all the
modules, throw away the WEEBs, put in new WEEBs with the new bare copper
6AWG and reinstall the modules--it just ain't worth it.

690.47(D) was removed from the 2011 NEC because it was primarily for
lightning protection (not a safety issue according to the NEC) and was
ambiguously worded with respect to residential rooftop PV systems. If the
local jurisdiction requires the additional electrode, install a j-box at the
point near ground-level where the conduit transitions from vertical to
horizontal and install an irreversibly spliced bare 6AWG to run from the
j-box to a ground rod below the j-box--mildly painful, but very doable.

Bill.

Bill Brooks, PE
Principal
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
707-332-0761 (office and mobile)
707-451-7739 (fax)
b...@brooksolar.com (email)
www.brooksolar.com (web)

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread William Miller

Bill:

Other than  complying just because this is a rule that has to be followed, 
is there any logical foundation to the requirement to provide a #8 ground 
to a circuit with OC protection at 20 amps?


If there is a valid safety reason, then let's all get behind it and become 
adept at providing this GEC.


If the rule makes no sense, let's advocate that it be changed.

What is the reason for providing this GEC to an inverter?

Thanks in advance.

William Miller




At 09:51 AM 3/4/2011, you wrote:

System grounding requirements.

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Friday, March 04, 2011 7:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

The interesting thing to me is the underlying assumption in the Code that a
GEC is requried for grid-tied inverters at all. Why isn't EG sufficient for
function and safety.

Which of the following common electrical equipment has the same requirement:

UPS
Motors with regenerative energy disipators
DC power supplies
Standby generators

??

Mark Frye
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Jason Szumlanski
To bring the discussion back around to Enphase, at least in the case of
the D380, there is a green wire in the AC Interconnect. This is
irreversibly crimped to a GEC in the rooftop J-Box.  The same question
applies: why a GEC to each microinverter case, and/or why require an
inverter-rail WEEB at all?

 

Jason Szumlanski

Fafco Solar

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Friday, March 04, 2011 12:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] grounding the Enphase inverter

 

Bill:

Other than  complying just because this is a rule that has to be
followed, is there any logical foundation to the requirement to provide
a #8 ground to a circuit with OC protection at 20 amps?

If there is a valid safety reason, then let's all get behind it and
become adept at providing this GEC.

If the rule makes no sense, let's advocate that it be changed.

What is the reason for providing this GEC to an inverter?

Thanks in advance.

William Miller




At 09:51 AM 3/4/2011, you wrote:



System grounding requirements.

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Friday, March 04, 2011 7:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

The interesting thing to me is the underlying assumption in the Code
that a
GEC is requried for grid-tied inverters at all. Why isn't EG sufficient
for
function and safety. 

Which of the following common electrical equipment has the same
requirement:

UPS
Motors with regenerative energy disipators
DC power supplies
Standby generators

??
 
Mark Frye

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Mark Frye
Yes, but that comes from the assumption that the inverter constitutes a
seperately derived system.

But if the only purpose or use of the DC power derived from the DC system is
to drive the AC side of the inverter, how closely does it realy resemble a
classic seperately derived system. As opposed to having the DC power source
actually run DC utilization equipment such as motors and appliances.

It is interesting that the very language in the code descibes the inverter
as utility interactive. Is it really correct to describe a UL174 inverter
operating only in parrallel with the utility as a seperately derived system?

To what degree has the Code failed to reflect the evolution of technology?
Yes, battery-based inverter systems capable of powering a facility in the
absense of a utility power souce do in fact become a seperately derived
system which need to have a GEC. But to impose the same requirement on an
inverter which cannot possibly deliver power to anything other than a system
that already has a GEC seems to me to be a crude cookie cutter response to a
far more complex situation.

We have put the complexity into the inverters. Recogonizing this we see that
we don't need the complexity in wiring?
 
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Friday, March 04, 2011 9:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

System grounding requirements.

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Friday, March 04, 2011 7:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

The interesting thing to me is the underlying assumption in the Code that a
GEC is requried for grid-tied inverters at all. Why isn't EG sufficient for
function and safety. 

Which of the following common electrical equipment has the same requirement:

UPS
Motors with regenerative energy disipators DC power supplies Standby
generators

??
 
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Thursday, March 03, 2011 10:48 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

All,

While there is ambiguity in the 2008 NEC in 690.47(C) on the requirements
for system grounding of PV systems, the 2011 NEC in 690.47(C) clarifies the
intent. 

While an application note from Enphase may state that WEEBs can be used as
part of the grounding electrode system, I disagree with this concept and do
not believe it meets the requirements or intent of the NEC as clarified in
the 2011 NEC. The problem with a grounded PV inverter is that it requires a
grounding electrode conductor (GEC) from the grounding point (on the
inverter) to the grounding electrode. The 2008 and 2011 NEC allows for that
connection to be terminated at the grounding bar in the service panel
supplying the micro-inverters.

There is no problem with using the WEEB to bond the rails to the modules and
then to the Enphase Micro-inverter. From the micro-inverter, a bare 6AWG
could be run to pick up each micro-inveter in each row of micro-inverters
with splices made to a single bare 6AWG made with irreversible splices. At
the rooftop junction box, the GEC could be irreversibly spliced to an 8AWG
green insulated conductor to run unbroken to the grounding busbar in the
service equipment.

While this may not be in agreement with the Enphase application note, I
believe it meets the intent and letter of the NEC as clarified in the 2011
NEC 690.47(C). While using the WEEBs in the GEC circuit may not cause a life
or death issue, it is absolutely open to being questioned by the electrical
inspector. If the electrical inspector decides it is wrong--it is wrong. If
you or the field inspector appeals to me or an expert like John Wiles, we
will state what I have stated above. Then you would have to remove all the
modules, throw away the WEEBs, put in new WEEBs with the new bare copper
6AWG and reinstall the modules--it just ain't worth it.

690.47(D) was removed from the 2011 NEC because it was primarily for
lightning protection (not a safety issue according to the NEC) and was
ambiguously worded with respect to residential rooftop PV systems. If the
local jurisdiction requires the additional electrode, install a j-box at the
point near ground-level where the conduit transitions from vertical to
horizontal and install an irreversibly spliced bare 6AWG to run from the
j-box to a ground rod below the j-box--mildly painful, but very doable.

Bill.

Bill Brooks, PE

[RE-wrenches] Spot welding PV's to rails for theft prevention: bad idea?

2011-03-04 Thread Mick Abraham
Hello, we mounted some PV onesy modules as high as we could reach without a
man-lift, but an enterprising thief could reach just as high. The side of
pole mounts hold the bolt heads captive so I bought some aluminum
breakaway nuts. However the nuts have a big diameter which would not fit
inside the Kyocera PV frames.

Has anyone tried spot welding the PV frames direct to the aluminum rails to
which they are mounted? Would this over stress the glass laminate or cause
other problems? I realize this would void the Kyo warranty but nothing voids
system performance like a stolen PV module.

Happy Friday,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Spot welding PV's to rails for theft prevention: bad idea?

2011-03-04 Thread Bill Hoffer
Mick

Solar World welds their frame corners, but use a laser with high precision
and very low heat.  I have seen racks in Haiti welded instead of bolted to
keep people from walking off with the entire rack.  I would not recommend
welding a module frame, Too risky and would probably void warranty.  Of
course you can not warranty a stolen module either!  However welding a cross
bar to the racking that locks the module in place may be a reasonable
alternative because you could weld away from the frame.  Use asbestos
protection to keep harmful heat away from the module.  That just might work,
would be harder to replace, but harder to steal also...although some
thief would still find a way around it!  Now all we need is a way to protect
against drunk hunters shooting holes in the modules for target practice!

Bill

On Fri, Mar 4, 2011 at 11:22 AM, Mick Abraham m...@abrahamsolar.com wrote:

 Hello, we mounted some PV onesy modules as high as we could reach without a
 man-lift, but an enterprising thief could reach just as high. The side of
 pole mounts hold the bolt heads captive so I bought some aluminum
 breakaway nuts. However the nuts have a big diameter which would not fit
 inside the Kyocera PV frames.

 Has anyone tried spot welding the PV frames direct to the aluminum rails to
 which they are mounted? Would this over stress the glass laminate or cause
 other problems? I realize this would void the Kyo warranty but nothing voids
 system performance like a stolen PV module.

 Happy Friday,

 Mick Abraham, Proprietor
 www.abrahamsolar.com

 Voice: 970-731-4675

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Bill Hoffer PE
NABCEP Certified Solar PV Installerâ„¢
Sunergy Engineering Services PLLC
2504 Columbia Ave NW
East Wenatchee WA 98802-3941
suneng...@gmail.com (509)470-7762
Cell(509)679-6165
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread R Ray Walters
Excellent post Mark. We spend way too much time as an industry worrying about 
these mundane grounding (and over grounding) issues, when there are very little 
actual safety issues involved.
Meanwhile, we're missing the real safety problems. (recent commercial system 
fires??)
I can't wait for our industry to mature to the point that we treat grounding as 
other industries do. I don't see any technical reason (besides onerous NEC 
language) that would prevent us from safely grounding the Enphase inverters 
like any other permanently mounted AC appliance (#12 EGC on a 20A circuit, run 
with the conductors, forget about all the irreversible splices, ad nauseum)

I respect BIll's points, too, as he is laying down the actual law as currently 
written to keep us out of trouble with the AHJs. (Thanks BIll)
But, as with numerous other code issues over the years, the code needs to 
change to catch up with technology and the actual safety issues. 
(remember when we had to ground battery based inverters with a 4/0 cable? ugh!)

Let's all work together to make micro-inverter grounding more sensible too.

R. Walters
r...@solarray.com
Solar Engineer




On Mar 4, 2011, at 11:53 AM, Mark Frye wrote:

 Yes, but that comes from the assumption that the inverter constitutes a
 seperately derived system.
 
 But if the only purpose or use of the DC power derived from the DC system is
 to drive the AC side of the inverter, how closely does it realy resemble a
 classic seperately derived system. As opposed to having the DC power source
 actually run DC utilization equipment such as motors and appliances.
 
 It is interesting that the very language in the code descibes the inverter
 as utility interactive. Is it really correct to describe a UL174 inverter
 operating only in parrallel with the utility as a seperately derived system?
 
 To what degree has the Code failed to reflect the evolution of technology?
 Yes, battery-based inverter systems capable of powering a facility in the
 absense of a utility power souce do in fact become a seperately derived
 system which need to have a GEC. But to impose the same requirement on an
 inverter which cannot possibly deliver power to anything other than a system
 that already has a GEC seems to me to be a crude cookie cutter response to a
 far more complex situation.
 
 We have put the complexity into the inverters. Recogonizing this we see that
 we don't need the complexity in wiring?
 
 Mark Frye
 Berkeley Solar Electric Systems
 303 Redbud Way
 Nevada City,  CA 95959
 (530) 401-8024
 www.berkeleysolar.com 
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
 Sent: Friday, March 04, 2011 9:51 AM
 To: 'RE-wrenches'
 Subject: Re: [RE-wrenches] grounding the Enphase inverter
 
 System grounding requirements.
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
 Sent: Friday, March 04, 2011 7:51 AM
 To: 'RE-wrenches'
 Subject: Re: [RE-wrenches] grounding the Enphase inverter
 
 The interesting thing to me is the underlying assumption in the Code that a
 GEC is requried for grid-tied inverters at all. Why isn't EG sufficient for
 function and safety. 
 
 Which of the following common electrical equipment has the same requirement:
 
 UPS
 Motors with regenerative energy disipators DC power supplies Standby
 generators
 
 ??
 
 Mark Frye
 Berkeley Solar Electric Systems
 303 Redbud Way
 Nevada City,  CA 95959
 (530) 401-8024
 www.berkeleysolar.com 
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
 Sent: Thursday, March 03, 2011 10:48 PM
 To: 'RE-wrenches'
 Subject: Re: [RE-wrenches] grounding the Enphase inverter
 
 All,
 
 While there is ambiguity in the 2008 NEC in 690.47(C) on the requirements
 for system grounding of PV systems, the 2011 NEC in 690.47(C) clarifies the
 intent. 
 
 While an application note from Enphase may state that WEEBs can be used as
 part of the grounding electrode system, I disagree with this concept and do
 not believe it meets the requirements or intent of the NEC as clarified in
 the 2011 NEC. The problem with a grounded PV inverter is that it requires a
 grounding electrode conductor (GEC) from the grounding point (on the
 inverter) to the grounding electrode. The 2008 and 2011 NEC allows for that
 connection to be terminated at the grounding bar in the service panel
 supplying the micro-inverters.
 
 There is no problem with using the WEEB to bond the rails to the modules and
 then to the Enphase Micro-inverter. From the micro-inverter, a bare 6AWG
 could be run to pick up each micro-inveter in each row of micro-inverters
 with splices made to a single bare 6AWG made with irreversible splices. At
 the rooftop junction box, the GEC could be irreversibly 

Re: [RE-wrenches] Spot welding PV's to rails for theft prevention: bad idea?

2011-03-04 Thread R Ray Walters
From the bit of aluminum welding I've done (MIG not the preferred TIG) I'd say 
it would be pretty hard to do without damaging the laminate.
I actually successfully welded attachments to salvage modules back in the 90s.
Also the alloys are probably different between the module and rail, so even if 
you welded it without damage, the weld probably would just pop off when the 
industrious thief started twisting and pulling on it.

I'd look at using a frame of angle iron over the module edges that captures the 
module. I've seen racks built this way, and then the 2 frames (upper and lower) 
can be welded together, or locked with a hasp and padlock)
No warranty voided either.
The breakaway nuts are a waste, we used them for a while, broke the special 
tool on a job where we needed to remove a module, and within seconds my very 
trusty old assistant Russ had the expensive security hardware off with a 
Leatherman, and a vice grips.

R. Walters
r...@solarray.com
Solar Engineer




On Mar 4, 2011, at 12:22 PM, Mick Abraham wrote:

 Hello, we mounted some PV onesy modules as high as we could reach without a 
 man-lift, but an enterprising thief could reach just as high. The side of 
 pole mounts hold the bolt heads captive so I bought some aluminum 
 breakaway nuts. However the nuts have a big diameter which would not fit 
 inside the Kyocera PV frames. 
 
 Has anyone tried spot welding the PV frames direct to the aluminum rails to 
 which they are mounted? Would this over stress the glass laminate or cause 
 other problems? I realize this would void the Kyo warranty but nothing voids 
 system performance like a stolen PV module. 
 
 Happy Friday,
 
 Mick Abraham, Proprietor
 www.abrahamsolar.com
 
 Voice: 970-731-4675
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Dana
I would like to remember us all back to 16-20 years ago when
we were required to use a ground cable equal to the
largest conductor in the system. This was typically sized by
the inverter cable at 4/0 copper. I gotta say that was a
really dumb rule. 
At that time we were to not create  ground loops. One
point of ground was the maximum for the DC circuit. 

Today's grounding requirements create ground loops [ in my
opinion]. I wonder where this topic will ground out, 10
years  from now. I am delighted to be done with 4/0 ground
cable though.

Dana Orzel
Great Solar Works, Inc
E - d...@solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com

Responsible Technologies for Responsible People since 1988
Do not ever believe anything, but seriously trust through
action.




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Spot welding PV's to rails for theft prevention: bad idea?

2011-03-04 Thread Dana
Mick,

 

I partially belt sanded off one side of the security  nut
flange on the cone part just enough to make it fit on one
install. They are still there. Be sure to use gloves that
belt sander is rough on the fingers.

I resorted to holding with a Vice grip wrench. Even then
they flew quite a distance if they came loose.

 

Dana Orzel

Great Solar Works, Inc

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

Responsible Technologies for Responsible People since 1988

Do not ever believe anything, but seriously trust through
action.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Mick Abraham
Sent: Friday, March 04, 2011 12:22 PM
To: RE-wrenches
Subject: [RE-wrenches] Spot welding PV's to rails for theft
prevention: bad idea?

 

Hello, we mounted some PV onesy modules as high as we could
reach without a man-lift, but an enterprising thief could
reach just as high. The side of pole mounts hold the bolt
heads captive so I bought some aluminum breakaway nuts.
However the nuts have a big diameter which would not fit
inside the Kyocera PV frames. 

Has anyone tried spot welding the PV frames direct to the
aluminum rails to which they are mounted? Would this over
stress the glass laminate or cause other problems? I realize
this would void the Kyo warranty but nothing voids system
performance like a stolen PV module. 

Happy Friday,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Spot welding PV's to rails for theft prevention: bad idea?

2011-03-04 Thread Allan Sindelar
Mick,
Direct Power did this some years ago on a piece of Interstate roadside art.
I think it worked quite well to discourage theft. You might want to call
DPW for info; I'd talk with Jeff.

Allan at Positive Energy
On Mar 4, 2011 12:22 PM, Mick Abraham m...@abrahamsolar.com wrote:
 Hello, we mounted some PV onesy modules as high as we could reach without
a
 man-lift, but an enterprising thief could reach just as high. The side of
 pole mounts hold the bolt heads captive so I bought some aluminum
 breakaway nuts. However the nuts have a big diameter which would not fit
 inside the Kyocera PV frames.

 Has anyone tried spot welding the PV frames direct to the aluminum rails
to
 which they are mounted? Would this over stress the glass laminate or cause
 other problems? I realize this would void the Kyo warranty but nothing
voids
 system performance like a stolen PV module.

 Happy Friday,

 Mick Abraham, Proprietor
 www.abrahamsolar.com

 Voice: 970-731-4675
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Spot welding PV's to rails for theft prevention: bad idea?

2011-03-04 Thread Nick Soleil
The BP oil company installed a ton of solar arrays for cathodic protection in 
the desert near Bakerfield in the 80s and 90s.  They used Arco and Kyocera 
modules at ~50 watts each.  They had a terrible time with theft, so they began 
welding the modules to the racks and the racks to the steel structures.  
However, the thieves persisted, by cutting the steel substructures with torches 
to get the modules.  

Eventually, BP brought in the utility power.  Too bad.  The good thing was 
that I got to buy the remaining 600 used modules for a good price. 


 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: Allan Sindelar al...@positiveenergysolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Fri, March 4, 2011 4:06:53 PM
Subject: Re: [RE-wrenches] Spot welding PV's to rails for theft prevention: bad 
idea?


Mick,
Direct Power did this some years ago on a piece of Interstate roadside art. I 
think it worked quite well to discourage theft. You might want to call DPW for 
info; I'd talk with Jeff.
Allan at Positive Energy 

On Mar 4, 2011 12:22 PM, Mick Abraham m...@abrahamsolar.com wrote:
 Hello, we mounted some PV onesy modules as high as we could reach without a
 man-lift, but an enterprising thief could reach just as high. The side of
 pole mounts hold the bolt heads captive so I bought some aluminum
 breakaway nuts. However the nuts have a big diameter which would not fit
 inside the Kyocera PV frames.
 
 Has anyone tried spot welding the PV frames direct to the aluminum rails to
 which they are mounted? Would this over stress the glass laminate or cause
 other problems? I realize this would void the Kyo warranty but nothing voids
 system performance like a stolen PV module.
 
 Happy Friday,
 
 Mick Abraham, Proprietor
 www.abrahamsolar.com
 
 Voice: 970-731-4675



  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Nick Soleil
Hi Mark, Ray, and wrenches:
I agree that the grounding requirements can be onerous, but I have to 
interject that most generator manufacturers do specify a dedicated grounding 
electrode conductor.  Also, I do not feel that a #8 ground is too big.  
Probably 
unnecessary 99% of the time, but with all the shorts and arced connections that 
I have found in j-boxes, I feel good about running a larger grounding conductor.
With regard to the Enphase grounded with WEEB; which I have done many 
times, 
I would recommend spelling out the exact grounding method for the 
micro-inverters on the permit package.  We should have this issue resolved 
before installation begins.

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: Mark Frye ma...@berkeleysolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Fri, March 4, 2011 10:53:46 AM
Subject: Re: [RE-wrenches] grounding the Enphase inverter

Yes, but that comes from the assumption that the inverter constitutes a
seperately derived system.

But if the only purpose or use of the DC power derived from the DC system is
to drive the AC side of the inverter, how closely does it realy resemble a
classic seperately derived system. As opposed to having the DC power source
actually run DC utilization equipment such as motors and appliances.

It is interesting that the very language in the code descibes the inverter
as utility interactive. Is it really correct to describe a UL174 inverter
operating only in parrallel with the utility as a seperately derived system?

To what degree has the Code failed to reflect the evolution of technology?
Yes, battery-based inverter systems capable of powering a facility in the
absense of a utility power souce do in fact become a seperately derived
system which need to have a GEC. But to impose the same requirement on an
inverter which cannot possibly deliver power to anything other than a system
that already has a GEC seems to me to be a crude cookie cutter response to a
far more complex situation.

We have put the complexity into the inverters. Recogonizing this we see that
we don't need the complexity in wiring?

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Friday, March 04, 2011 9:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

System grounding requirements.

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Friday, March 04, 2011 7:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

The interesting thing to me is the underlying assumption in the Code that a
GEC is requried for grid-tied inverters at all. Why isn't EG sufficient for
function and safety. 

Which of the following common electrical equipment has the same requirement:

UPS
Motors with regenerative energy disipators DC power supplies Standby
generators

??

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Thursday, March 03, 2011 10:48 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

All,

While there is ambiguity in the 2008 NEC in 690.47(C) on the requirements
for system grounding of PV systems, the 2011 NEC in 690.47(C) clarifies the
intent. 

While an application note from Enphase may state that WEEBs can be used as
part of the grounding electrode system, I disagree with this concept and do
not believe it meets the requirements or intent of the NEC as clarified in
the 2011 NEC. The problem with a grounded PV inverter is that it requires a
grounding electrode conductor (GEC) from the grounding point (on the
inverter) to the grounding electrode. The 2008 and 2011 NEC allows for that
connection to be terminated at the grounding bar in the service panel
supplying the micro-inverters.

There is no problem with using the WEEB to bond the rails to the modules and
then to the Enphase Micro-inverter. From the micro-inverter, a bare 6AWG
could be run to pick up each micro-inveter in each row of micro-inverters
with splices made to a single bare 6AWG made with irreversible splices. At
the rooftop junction box, the GEC could be irreversibly spliced to an 8AWG
green insulated conductor to run unbroken to the grounding busbar in the
service equipment.

While this may not be in agreement with the Enphase application note, I
believe it meets the intent and letter of the 

Re: [RE-wrenches] grounding the Enphase inverter

2011-03-04 Thread Bill Brooks
The better question is why is there a solid ground in the inverter. 

 

As I stated before-we are talking about system grounding-with 100+ years of
electrical history and precedent to back it up.

 

System grounding rules are not open to a lot of discussion. That is why my
recommendation since before they released their first product was to go
ungrounded. Just because it is a pain, and we think there is no technical
reason, does not mean we can ignore the rules. As I said in my post, this is
not really a safety issue, but it is very much a compliance issue. System
grounding is so much a part of our electrical culture, that tiny electrical
supplies like PV microinverters were never really considered. 

 

Any installer can use the don't ask, don't tell method of installation,
but once we start down that path, the ability of the human mind to justify
actions is limitless. We have to go back to why we ground systems in the
first place. It is to prevent the voltage on the system conductors from
wondering too far from ground potential. There are other ways to prevent
this, but in the U.S. we mostly use conductors (not a variety of conductive
materials without clear ratings). The advent of the WEEB, with all its great
benefits, does not fundamentally change system grounding.

 

The sooner we get PV systems ungrounded, or resistively grounded, the better
the whole U.S. PV industry will be. To that end, everyone should move to PV
Cable/Wire and modules with PV Cable/Wire so we are using better products
than USE-2 and we can easily transition to ungrounded inverters as they
become more available. We already have several so now is not a bad time to
start thinking about it.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Friday, March 04, 2011 9:58 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] grounding the Enphase inverter

 

Bill:

Other than  complying just because this is a rule that has to be followed,
is there any logical foundation to the requirement to provide a #8 ground to
a circuit with OC protection at 20 amps?

If there is a valid safety reason, then let's all get behind it and become
adept at providing this GEC.

If the rule makes no sense, let's advocate that it be changed.

What is the reason for providing this GEC to an inverter?

Thanks in advance.

William Miller




At 09:51 AM 3/4/2011, you wrote:



System grounding requirements.

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Friday, March 04, 2011 7:51 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] grounding the Enphase inverter

The interesting thing to me is the underlying assumption in the Code that a
GEC is requried for grid-tied inverters at all. Why isn't EG sufficient for
function and safety. 

Which of the following common electrical equipment has the same requirement:

UPS
Motors with regenerative energy disipators
DC power supplies
Standby generators

??
 
Mark Frye

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org