Re: [RE-wrenches] Enphase M190 source?

2011-09-29 Thread Howie Michaelson
Hey Dave,

We have 4 of these left over from a job earlier in the year.  Do you still
have need for these?  Sorry for the delayed response.

Hope you are well,
Howie
-- 
Howie Michaelson
NABCEP Certified Solar PV Installer™

Catamount Solar, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric & Hot Water Incentive Partner
http://www.CatamountSolar.com
802-272-0004


On Mon, September 12, 2011 8:54 am, Dave Palumbo wrote:
> I'm looking for 18 enphase M-190's for an installation here in Vermont. 72
> cell modules 185 Watts. Anybody know of a source?
>
>
>
> David Palumbo
>
> Independent Power LLC
>
> 462 Solar Way Drive
>
> Hyde Park, VT 05655
>
> www.independentpowerllc.com
>
> NABCEP Certified PV Installer
>
> Vermont Solar Partner
>
> 23 Years Experience, (802) 888-7194
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GNB Battery Contact

2011-09-29 Thread Philip Boutelle
Mac,
Try Paul Mattaliano , paul.mattali...@exide.com. When I asked him about
using two parallel strings of that same 100A33 battery configuration at 48V,
he told me this: "C100 rating of 100G33 is 2100 so 2 parallel strings is
4200.  5%=210A.
Since their 300A charging current exceeds 5%, recommend 2.35 VPC bulk/absorb
and 2.25 VPC float with monthly equalization charges.  Depending on system
performance/operating parameters, these values may have to be tweaked."

If you can't get Paul, try Erica or Paula; neither are in tech support but
could direct you.

Erica Binnewies

*GNB** **I**NDUSTRIAL** P**OWER*

(510) 843-9433

(510) 843-9434 Fax

erica.binnew...@exide.com

or

Paula Robison

Exide Technologies - Industrial Energy

(V) 510-581-6464

(F) 510-247-1165


On Thu, Sep 29, 2011 at 8:04 PM, mac Lewis  wrote:

> Hello wrenches,
>
> Does anyone have a good technical contact at GNB?  Specifically, I am
> looking for good charging setpoints for the Absolyte IIP Type 100A33.
>  Oddly, on all the spec sheets I've found they call this a 6V battery,
> however these are 2V batteries.
>
> Thanks
>
> --
>
>
>
> Mac Lewis
>
> *
>
> "Yo solo sé que no sé nada." -Sócrates
> *
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] GNB Battery Contact

2011-09-29 Thread mac Lewis
Hello wrenches,

Does anyone have a good technical contact at GNB?  Specifically, I am
looking for good charging setpoints for the Absolyte IIP Type 100A33.
 Oddly, on all the spec sheets I've found they call this a 6V battery,
however these are 2V batteries.

Thanks

-- 



Mac Lewis

*

"Yo solo sé que no sé nada." -Sócrates
*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Home Depot solar?

2011-09-29 Thread Jesse Dahl
I just bid against them here in Northern MN. I saw BP modules, I had heard BP 
was leaving the residential market.

Jesse

Sent from my iPhone

On Sep 29, 2011, at 10:48 AM, Andrew Truitt  wrote:

> HD hires local contractors to install their systems.  I've worked for a 
> couple of quality-oriented  companies that have explored this relationship 
> but both determined that the margins were just too thin.  
> 
> Andrew Truitt MSc, LEED GA
> Truitt Renewable Energy Consulting
> 202 486-7507
> http://www.linkedin.com/pub/andrew-truitt/8/622/713
> 
> Please excuse brevity and typos - this message was typed on tiny keys.
> 
> On Sep 29, 2011 9:17 AM, "Jason Szumlanski"  wrote:
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] ground

2011-09-29 Thread dan
Seems to me you're in 250.52(A)3 land. I'd guess not likely.Dan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message 
Subject: [RE-wrenches] ground
From: toddc...@finestplanet.com
Date: Thu, September 29, 2011 4:10 pm
To: "RE-wrenches" 

Does anyone know if it is ok to use the rebar in a pole mount foundation as a ufer ground? I need to ask the inspector too, but thought I'd ask here first.   Todd Sent from Finest Planet WebMail.___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding on to existing PV System

2011-09-29 Thread David Brearley
Agreed. The intent of the change to 690.64(B) in NEC 2008 was not to
restrict the use of a dedicated inverter aggregation subpanel for
amp-shaving purposed (meaning the panel is being used to reduce the PV CB
size ultimately used for 120% rule calculations). The intent was to clarify
the that there is no need to apply the 120% rule to progressively larger
upstream breakers when the interconnection happens in a subpanel.

A reasonable inspector or jurisdiction will interpret the Code consistent
with its intent, not according to an unintended consequence. However, you
may have to educate them about the distinction between the two possible
interpretations.

David Brearley, Senior Technical Editor
SolarPro magazine 

On 9/29/11 1:50 PM, "Mark Frye"  wrote:

> OK, this subject has come up before and this is a gray area in the Code. What
> is the definition of "the output of the inverters."
>  
> I have sucessfully argued that the output of the inverters is the last point
> in the circuit where the circuit is free of premise load circuits. In this
> case it would be the 40A breaker connecting the dedicated PV load center to
> the busbar of the main panel.
>  
> So...it is between you and you inspector. Tell him you are going to put a
> label on the subpanel that says something to the effect of "Dedicated inverter
> output accumulation subpanel. Add no additional circuits."
>  
> I think this is a much better interpretation and method that preserves a clean
> and functional load side connection topology. I think most reasonable
> inspectors would agree as well.
>  
> Good Luck.
>  
> Mark Frye 
> Berkeley Solar Electric Systems
> 303 Redbud Way 
> Nevada City,  CA 95959
> (530) 401-8024 
> www.berkeleysolar.com 
>  
> 
> 
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
> Szumlanski
> Sent: Thursday, September 29, 2011 1:33 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Adding on to existing PV System
> 
> I understand what you are saying about the 40A breaker, but according to
> 690.64(B)(2), ³Šwith panelboards connected in series, the rating of the
> *first* overcurrent device connected *directly* to the output of the inverters
> shall be used in the calculations for *all* busbars and conductors.² The way I
> have seen that interpreted is that the main distribution panel needs to be
> rated to support 120% of the two inverter circuits plus the main breaker,
> regardless of the fact that there is a 40A backfeed breaker in the main panel.
>  
> 200+30+15 > 200 x 1.2
>  
> I know it doesn¹t make much sense, but that¹s the way it¹s been interpreted
> around here. It stands to reason that this applies only to the PV subpanel
> busbar and the conductors between the panels, and that the calculation for
> those should be:
>  
> (30 + 15 + 40) / 1.2 = 70.83A required ampacity
>  
> Šand the calculation for the main distribution panel should be:
>  
> (200 + 40) / 1.2 = 200A required ampacity
>  
> Š but that¹s not what I am being told.
>  
> 
> Jason Szumlanski
> Fafco Solar
>  
>  
> 
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
> Sent: Thursday, September 29, 2011 4:19 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] Adding on to existing PV System
>  
> Jason:
>  
> SB 5000 = 21A @ 240V, 21A x 1.25 = 26.3A needs 30A breaker
> M215 = 0.9 A @ 240V, 0.9A x 9 = 8.1 A, 8.1 x 1.25 = 10.1A needs 15A breaker.
> (Or that rounded to 10A and use a 10A breaker)?
>  
> 26.3A + 10.1A = 36.4 A needs 40A breaker
>  
> So, get a new 100A main lug subpanel. Connect it to a 40A breaker in the
> existing main panel. Move the existing 30A breaker into the new subpanel and
> install the new 15A breaker into the same.
> 
> Mark Frye 
> Berkeley Solar Electric Systems
> 303 Redbud Way 
> Nevada City,  CA 95959
> (530) 401-8024 
> www.berkeleysolar.com 
> 
>  
>  
> 
> 
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
> Szumlanski
> Sent: Thursday, September 29, 2011 12:55 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Adding on to existing PV System
> That¹s not a bad idea, except that 690.64(B)(2) requires that the breaker
> directly connected to each inverter(s) must be used for the calculation.
>  
> I have an existing SB5000 with a 30A breaker and a new string of nine Enphase
> M215¹s requiring a 15A breaker. If you combine these in a 100A or higher rated
> subpanel with a 40A main breaker, you still calculate the total current
> supplying the busbar in the main distribution panel based on 200A + 30A + 15A
> = 245A (with 30A and 15A being the overcurrent protection directly connected
> to the inverters). This exceeds the 120% rule by 5A. It also requires that the
> ampacity of the conductors between the two panels be 85A / 1.2 = 70.83A
> (assum

Re: [RE-wrenches] Adding on to existing PV System

2011-09-29 Thread Mark Frye
OK, this subject has come up before and this is a gray area in the Code.
What is the definition of "the output of the inverters."
 
I have sucessfully argued that the output of the inverters is the last point
in the circuit where the circuit is free of premise load circuits. In this
case it would be the 40A breaker connecting the dedicated PV load center to
the busbar of the main panel.
 
So...it is between you and you inspector. Tell him you are going to put a
label on the subpanel that says something to the effect of "Dedicated
inverter output accumulation subpanel. Add no additional circuits."
 
I think this is a much better interpretation and method that preserves a
clean and functional load side connection topology. I think most reasonable
inspectors would agree as well.
 
Good Luck.
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
  www.berkeleysolar.com  
 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 1:33 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Adding on to existing PV System



I understand what you are saying about the 40A breaker, but according to
690.64(B)(2), ".with panelboards connected in series, the rating of the
*first* overcurrent device connected *directly* to the output of the
inverters shall be used in the calculations for *all* busbars and
conductors." The way I have seen that interpreted is that the main
distribution panel needs to be rated to support 120% of the two inverter
circuits plus the main breaker, regardless of the fact that there is a 40A
backfeed breaker in the main panel.

 

200+30+15 > 200 x 1.2

 

I know it doesn't make much sense, but that's the way it's been interpreted
around here. It stands to reason that this applies only to the PV subpanel
busbar and the conductors between the panels, and that the calculation for
those should be:

 

(30 + 15 + 40) / 1.2 = 70.83A required ampacity

 

.and the calculation for the main distribution panel should be:

 

(200 + 40) / 1.2 = 200A required ampacity

 

. but that's not what I am being told.

 

Jason Szumlanski

Fafco Solar

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Thursday, September 29, 2011 4:19 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Adding on to existing PV System

 

Jason:

 

SB 5000 = 21A @ 240V, 21A x 1.25 = 26.3A needs 30A breaker

M215 = 0.9 A @ 240V, 0.9A x 9 = 8.1 A, 8.1 x 1.25 = 10.1A needs 15A breaker.
(Or that rounded to 10A and use a 10A breaker)?

 

26.3A + 10.1A = 36.4 A needs 40A breaker

 

So, get a new 100A main lug subpanel. Connect it to a 40A breaker in the
existing main panel. Move the existing 30A breaker into the new subpanel and
install the new 15A breaker into the same.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
  www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 12:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Adding on to existing PV System

That's not a bad idea, except that 690.64(B)(2) requires that the breaker
directly connected to each inverter(s) must be used for the calculation.

 

I have an existing SB5000 with a 30A breaker and a new string of nine
Enphase M215's requiring a 15A breaker. If you combine these in a 100A or
higher rated subpanel with a 40A main breaker, you still calculate the total
current supplying the busbar in the main distribution panel based on 200A +
30A + 15A = 245A (with 30A and 15A being the overcurrent protection directly
connected to the inverters). This exceeds the 120% rule by 5A. It also
requires that the ampacity of the conductors between the two panels be 85A /
1.2 = 70.83A (assuming a 40A backfeed breaker in the main distribution
panel). If your interpretation is different, please let me know!

 

If my interpretation is correct, I like the idea of just adding a fusible
disconnect and using #10 conductors all the way to the tap. That would be
the most cost effective solution I believe, and since there is no
foreseeable further system rating increases, the advantage of a subpanel is
reduced.

 

 

Thanks for all the other suggestions provided. Unfortunately I can't put in
smaller main breaker, and the busbar in the main panel is definitely rated
200A.

 

Jason Szumlanski

Fafco Solar

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Glenn Burt
Sent: Thursday, September 29, 2011 2:40 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Adding on to existing PV System

 

How about feeding both systems into an AC combining

Re: [RE-wrenches] ground

2011-09-29 Thread Kent Osterberg




See NEC 250.52.

If there is 10 feet of pipe in the ground, that qualifies as a
grounding electrode. The foundation rebar qualifies as a grounding
electrode too, but it must have a length of at least 20 feet. If using
multiple pieces to get 20 feet they must be bonded (or simply wired)
together. 

Kent Osterberg
Blue Mountain Solar, Inc.


toddc...@finestplanet.com wrote:

  Does anyone know if it is
ok to use the rebar in a pole mount foundation as a ufer ground? I need
to ask the inspector too, but thought I'd ask
here first.
   
  Todd
   
  
  
  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding on to existing PV System

2011-09-29 Thread Jason Szumlanski
I understand what you are saying about the 40A breaker, but according to
690.64(B)(2), "...with panelboards connected in series, the rating of
the *first* overcurrent device connected *directly* to the output of the
inverters shall be used in the calculations for *all* busbars and
conductors." The way I have seen that interpreted is that the main
distribution panel needs to be rated to support 120% of the two inverter
circuits plus the main breaker, regardless of the fact that there is a
40A backfeed breaker in the main panel.

 

200+30+15 > 200 x 1.2

 

I know it doesn't make much sense, but that's the way it's been
interpreted around here. It stands to reason that this applies only to
the PV subpanel busbar and the conductors between the panels, and that
the calculation for those should be:

 

(30 + 15 + 40) / 1.2 = 70.83A required ampacity

 

...and the calculation for the main distribution panel should be:

 

(200 + 40) / 1.2 = 200A required ampacity

 

... but that's not what I am being told.

 

Jason Szumlanski

Fafco Solar

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Thursday, September 29, 2011 4:19 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Adding on to existing PV System

 

Jason:

 

SB 5000 = 21A @ 240V, 21A x 1.25 = 26.3A needs 30A breaker

M215 = 0.9 A @ 240V, 0.9A x 9 = 8.1 A, 8.1 x 1.25 = 10.1A needs 15A
breaker. (Or that rounded to 10A and use a 10A breaker)?

 

26.3A + 10.1A = 36.4 A needs 40A breaker

 

So, get a new 100A main lug subpanel. Connect it to a 40A breaker in the
existing main panel. Move the existing 30A breaker into the new subpanel
and install the new 15A breaker into the same.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com    

 

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 12:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Adding on to existing PV System

That's not a bad idea, except that 690.64(B)(2) requires that the
breaker directly connected to each inverter(s) must be used for the
calculation.

 

I have an existing SB5000 with a 30A breaker and a new string of nine
Enphase M215's requiring a 15A breaker. If you combine these in a 100A
or higher rated subpanel with a 40A main breaker, you still calculate
the total current supplying the busbar in the main distribution panel
based on 200A + 30A + 15A = 245A (with 30A and 15A being the overcurrent
protection directly connected to the inverters). This exceeds the 120%
rule by 5A. It also requires that the ampacity of the conductors between
the two panels be 85A / 1.2 = 70.83A (assuming a 40A backfeed breaker in
the main distribution panel). If your interpretation is different,
please let me know!

 

If my interpretation is correct, I like the idea of just adding a
fusible disconnect and using #10 conductors all the way to the tap. That
would be the most cost effective solution I believe, and since there is
no foreseeable further system rating increases, the advantage of a
subpanel is reduced.

 

 

Thanks for all the other suggestions provided. Unfortunately I can't put
in smaller main breaker, and the busbar in the main panel is definitely
rated 200A.

 

Jason Szumlanski

Fafco Solar

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Glenn
Burt
Sent: Thursday, September 29, 2011 2:40 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Adding on to existing PV System

 

How about feeding both systems into an AC combining subpanel before
feeding the main load center?

Often the calculations required will allow you to do more backfeeding
than the simple backfeeding a load center with individual breakers.

 

-Glenn

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 11:49 AM
To: RE-wrenches
Subject: [RE-wrenches] Adding on to existing PV System

 

We've been contracted to add on to an existing PV system in a residence.
The existing system has a 30A 2P Breaker on a 200A rated panel with a
200A main breaker. The new system would require a 15A breaker, which
would exceed the limit in NEC 690.64(B)(2).

 

The existing system has a fusible AC disconnect mounted next to the
meter. This was originally intended as the utility external disconnect.
The utility no longer requires a disconnect, but if we do a supply side
connection, we would need a fusible AC disconnect anyway for the new
system. I would collocate the new disconnect with the old.

 

Does anyone see any problem with doing a supply size connection for the
new system? Any labeling snags that I might need to consider?

 

Jas

Re: [RE-wrenches] Adding on to existing PV System

2011-09-29 Thread Mark Frye
Jason:
 
SB 5000 = 21A @ 240V, 21A x 1.25 = 26.3A needs 30A breaker
M215 = 0.9 A @ 240V, 0.9A x 9 = 8.1 A, 8.1 x 1.25 = 10.1A needs 15A breaker.
(Or that rounded to 10A and use a 10A breaker)?
 
26.3A + 10.1A = 36.4 A needs 40A breaker
 
So, get a new 100A main lug subpanel. Connect it to a 40A breaker in the
existing main panel. Move the existing 30A breaker into the new subpanel and
install the new 15A breaker into the same.

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
  www.berkeleysolar.com  
 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 12:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Adding on to existing PV System



That's not a bad idea, except that 690.64(B)(2) requires that the breaker
directly connected to each inverter(s) must be used for the calculation.

 

I have an existing SB5000 with a 30A breaker and a new string of nine
Enphase M215's requiring a 15A breaker. If you combine these in a 100A or
higher rated subpanel with a 40A main breaker, you still calculate the total
current supplying the busbar in the main distribution panel based on 200A +
30A + 15A = 245A (with 30A and 15A being the overcurrent protection directly
connected to the inverters). This exceeds the 120% rule by 5A. It also
requires that the ampacity of the conductors between the two panels be 85A /
1.2 = 70.83A (assuming a 40A backfeed breaker in the main distribution
panel). If your interpretation is different, please let me know!

 

If my interpretation is correct, I like the idea of just adding a fusible
disconnect and using #10 conductors all the way to the tap. That would be
the most cost effective solution I believe, and since there is no
foreseeable further system rating increases, the advantage of a subpanel is
reduced.

 

 

Thanks for all the other suggestions provided. Unfortunately I can't put in
smaller main breaker, and the busbar in the main panel is definitely rated
200A.

 

Jason Szumlanski

Fafco Solar

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Glenn Burt
Sent: Thursday, September 29, 2011 2:40 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Adding on to existing PV System

 

How about feeding both systems into an AC combining subpanel before feeding
the main load center?

Often the calculations required will allow you to do more backfeeding than
the simple backfeeding a load center with individual breakers.

 

-Glenn

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 11:49 AM
To: RE-wrenches
Subject: [RE-wrenches] Adding on to existing PV System

 

We've been contracted to add on to an existing PV system in a residence. The
existing system has a 30A 2P Breaker on a 200A rated panel with a 200A main
breaker. The new system would require a 15A breaker, which would exceed the
limit in NEC 690.64(B)(2).

 

The existing system has a fusible AC disconnect mounted next to the meter.
This was originally intended as the utility external disconnect. The utility
no longer requires a disconnect, but if we do a supply side connection, we
would need a fusible AC disconnect anyway for the new system. I would
collocate the new disconnect with the old.

 

Does anyone see any problem with doing a supply size connection for the new
system? Any labeling snags that I might need to consider?

 

Jason Szumlanski

Fafco Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] ground

2011-09-29 Thread toddcory

Does anyone know if it is ok to use the rebar in a pole mount foundation as a 
ufer ground? I need to ask the inspector too, but thought I'd ask here first.
 
Todd
 
 



Sent from Finest Planet WebMail.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding on to existing PV System

2011-09-29 Thread Jason Szumlanski
That's not a bad idea, except that 690.64(B)(2) requires that the
breaker directly connected to each inverter(s) must be used for the
calculation.

 

I have an existing SB5000 with a 30A breaker and a new string of nine
Enphase M215's requiring a 15A breaker. If you combine these in a 100A
or higher rated subpanel with a 40A main breaker, you still calculate
the total current supplying the busbar in the main distribution panel
based on 200A + 30A + 15A = 245A (with 30A and 15A being the overcurrent
protection directly connected to the inverters). This exceeds the 120%
rule by 5A. It also requires that the ampacity of the conductors between
the two panels be 85A / 1.2 = 70.83A (assuming a 40A backfeed breaker in
the main distribution panel). If your interpretation is different,
please let me know!

 

If my interpretation is correct, I like the idea of just adding a
fusible disconnect and using #10 conductors all the way to the tap. That
would be the most cost effective solution I believe, and since there is
no foreseeable further system rating increases, the advantage of a
subpanel is reduced.

 

 

Thanks for all the other suggestions provided. Unfortunately I can't put
in smaller main breaker, and the busbar in the main panel is definitely
rated 200A.

 

Jason Szumlanski

Fafco Solar

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Glenn
Burt
Sent: Thursday, September 29, 2011 2:40 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Adding on to existing PV System

 

How about feeding both systems into an AC combining subpanel before
feeding the main load center?

Often the calculations required will allow you to do more backfeeding
than the simple backfeeding a load center with individual breakers.

 

-Glenn

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 11:49 AM
To: RE-wrenches
Subject: [RE-wrenches] Adding on to existing PV System

 

We've been contracted to add on to an existing PV system in a residence.
The existing system has a 30A 2P Breaker on a 200A rated panel with a
200A main breaker. The new system would require a 15A breaker, which
would exceed the limit in NEC 690.64(B)(2).

 

The existing system has a fusible AC disconnect mounted next to the
meter. This was originally intended as the utility external disconnect.
The utility no longer requires a disconnect, but if we do a supply side
connection, we would need a fusible AC disconnect anyway for the new
system. I would collocate the new disconnect with the old.

 

Does anyone see any problem with doing a supply size connection for the
new system? Any labeling snags that I might need to consider?

 

Jason Szumlanski

Fafco Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding on to existing PV System

2011-09-29 Thread Jesse Dahl
Maybe you can put in a smaller main breaker? 

Jesse

Sent from my iPhone

On Sep 29, 2011, at 1:39 PM, "Glenn Burt"  wrote:

> How about feeding both systems into an AC combining subpanel before feeding 
> the main load center?
> 
> Often the calculations required will allow you to do more backfeeding than 
> the simple backfeeding a load center with individual breakers.
> 
>  
> 
> -Glenn
> 
>  
> 
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason 
> Szumlanski
> Sent: Thursday, September 29, 2011 11:49 AM
> To: RE-wrenches
> Subject: [RE-wrenches] Adding on to existing PV System
> 
>  
> 
> We’ve been contracted to add on to an existing PV system in a residence. The 
> existing system has a 30A 2P Breaker on a 200A rated panel with a 200A main 
> breaker. The new system would require a 15A breaker, which would exceed the 
> limit in NEC 690.64(B)(2).
> 
>  
> 
> The existing system has a fusible AC disconnect mounted next to the meter. 
> This was originally intended as the utility external disconnect. The utility 
> no longer requires a disconnect, but if we do a supply side connection, we 
> would need a fusible AC disconnect anyway for the new system. I would 
> collocate the new disconnect with the old.
> 
>  
> 
> Does anyone see any problem with doing a supply size connection for the new 
> system? Any labeling snags that I might need to consider?
> 
>  
> 
> Jason Szumlanski
> 
> Fafco Solar
> 
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding on to existing PV System

2011-09-29 Thread Glenn Burt
How about feeding both systems into an AC combining subpanel before feeding
the main load center?

Often the calculations required will allow you to do more backfeeding than
the simple backfeeding a load center with individual breakers.

 

-Glenn

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Thursday, September 29, 2011 11:49 AM
To: RE-wrenches
Subject: [RE-wrenches] Adding on to existing PV System

 

We've been contracted to add on to an existing PV system in a residence. The
existing system has a 30A 2P Breaker on a 200A rated panel with a 200A main
breaker. The new system would require a 15A breaker, which would exceed the
limit in NEC 690.64(B)(2).

 

The existing system has a fusible AC disconnect mounted next to the meter.
This was originally intended as the utility external disconnect. The utility
no longer requires a disconnect, but if we do a supply side connection, we
would need a fusible AC disconnect anyway for the new system. I would
collocate the new disconnect with the old.

 

Does anyone see any problem with doing a supply size connection for the new
system? Any labeling snags that I might need to consider?

 

Jason Szumlanski

Fafco Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Home Depot solar?

2011-09-29 Thread Andrew Truitt
HD hires local contractors to install their systems.  I've worked for a
couple of quality-oriented  companies that have explored this relationship
but both determined that the margins were just too thin.

Andrew Truitt MSc, LEED GA
Truitt Renewable Energy Consulting
202 486-7507
http://www.linkedin.com/pub/andrew-truitt/8/622/713

Please excuse brevity and typos - this message was typed on tiny keys.
On Sep 29, 2011 9:17 AM, "Jason Szumlanski"  wrote:
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding on to existing PV System

2011-09-29 Thread Max Balchowsky
Check the specs on the buss rating for that 200 amp panel. A lot of the 200 amp 
panels actually have a 225 amp rated buss
 
Max Balchowsky
Design Engineer
SEE Systems
1048 Irvine Ave Suite 217
Newport Beach, Ca. 92660
760-403-6810



From: Jason Szumlanski 
To: RE-wrenches 
Sent: Thursday, September 29, 2011 8:48 AM
Subject: [RE-wrenches] Adding on to existing PV System


We’ve been contracted to add on to an existing PV system in a residence. The 
existing system has a 30A 2P Breaker on a 200A rated panel with a 200A main 
breaker. The new system would require a 15A breaker, which would exceed the 
limit in NEC 690.64(B)(2).
 
The existing system has a fusible AC disconnect mounted next to the meter. This 
was originally intended as the utility external disconnect. The utility no 
longer requires a disconnect, but if we do a supply side connection, we would 
need a fusible AC disconnect anyway for the new system. I would collocate the 
new disconnect with the old.
 
Does anyone see any problem with doing a supply size connection for the new 
system? Any labeling snags that I might need to consider?
 
Jason Szumlanski
Fafco Solar
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Home Depot solar?

2011-09-29 Thread Max Balchowsky
We sold for Home Depot (actually through HD for Astropower in 2000- 2001 in the 
Palm Springs area. It lasted about a year before they started shopping install 
labor - then it fell apart with competitors slinging lowball prices to get the 
work.
 
Max Balchowsky
Design Engineer
SEE Systems
1048 Irvine Ave Suite 217
Newport Beach, Ca. 92660
760-403-6810



From: "wire...@gmail.com" 
To: Solar Energy Solutions ; RE-wrenches 

Sent: Thursday, September 29, 2011 9:40 AM
Subject: Re: [RE-wrenches] Home Depot solar?


Andrew,

Koyaanisqatsi is also a great movie by Francis Ford Copolla. You should all see 
it. It's been awhile since I've seen it but if I remember correctly it's a Hopi 
Indian term meaning once we start digging from the earth, we're screwed beyond 
repair.

Larry Liesner
Design and Installations
Elektron Solar, LLC
49 Richmondville Ave Suite 107
Westport, CT 06880
203-557-3127 (office)
203-644-2404 (cell)
203-549-0977 (fax)
wire...@gmail.com


On Thu, Sep 29, 2011 at 12:31 PM, Solar Energy Solutions 
 wrote:

Home Depot IS selling PV in Portland Oregon through Solar City.  
> 
>Seirrabuton Club is marketing PV to their members in Oregon.  They have chosen 
>a single contractor for the entire state to install all of their member's 
>systems.  Payola is $300.00/system installed.
> 
>  
>Andrew Koyaanisqatsi
>President
>Solar Energy Solutions, Inc.
>Since 1987,
>Moving Portland and Beyond 
>to an Environmentally Sustainable Future.
>503-238-4502
>www.solarenergyoregon.com 
> 
>"Better one's House too little one day
>than too big all the Year after."
>
>
>From: Jason Szumlanski 
>To: RE-wrenches 
>Sent: Thursday, September 29, 2011 8:17 AM
>Subject: Re: [RE-wrenches] Home Depot solar?
>
>We were recently asked to fix a royal mess by a SDHW installer
>contracted via Home Depot. Not fun. 60+ systems with various
>deficiencies. The installer was to blame, not HD.
>
>HD is not selling PV in our market (fortunately).
>
>Jason Szumlanski
>
>
>-Original Message-
>From: re-wrenches-boun...@lists.re-wrenches.org
>[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse
>Dahl
>Sent: Thursday, September 29, 2011 10:39 AM
>To: RE-wrenches
>Subject: [RE-wrenches] Home Depot solar?
>
>Anyone out there have any experience with Home Depot's solar installers?
>
>Jesse
>
>___
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches@lists.re-wrenches.org
>
>Options &
 settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>
>
>___
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches@lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>



NABCEP Certified PV Installer (# 032611-184)


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Home Depot solar?

2011-09-29 Thread Joel Davidson
Solar Electrical Systems (SES) in Westlake Village California was a Home 
Depot installer for BP Solar systems for a few years. SES does excellent 
work. SES no longer installs BP Solar or Home Depot systems but occasionally 
replaces BP modules that fail on the systems that they installed.


Joel Davidson

- Original Message - 
From: "Jesse Dahl" 

To: "RE-wrenches" 
Sent: Thursday, September 29, 2011 7:39 AM
Subject: [RE-wrenches] Home Depot solar?



Anyone out there have any experience with Home Depot's solar installers?

Jesse

Sent from my iPhone
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



re-wrenches@lists.re-wrenches.org

2011-09-29 Thread Ray Walters

We have a few Kohler 20kw, 30 kw, and 40 kw  units on big off grid stuff.
Great machines, get about 5000 hours before they need work. 2 wire 
start, 1800 rpm water cooled.
Ours had 4 to 6 cylinder Ford motors. I don't know what they use now, or 
if they've changed the line recently. I found over the years that 
oversizing them more, helped everything from cleaner waveform, to 
running the chargers at full throttle, to having more pass through 
current, and the fuel efficiency seems to better. This was at 11,000 ft, 
so you would have to take some of my observations with a grain of salt, 
but we replaced a 30 Kw unit feeding 4 SW4048s, with a 40 KW, and the 
customer was happier.
You're burning more fuel while running, but the generator seemed to 
charge the batteries faster, reducing overall run time, and overall fuel 
use.
From looking at many Kohlers on an oscilloscope, they have an excellent 
waveform, (no funny spikes, like most portable units) so I can't imagine 
why a Sunny Island wouldn't work well with it, but I never actually used 
one with a Kohler.


Ray Walters

On 9/29/2011 9:53 AM, Jeff Clearwater wrote:

Fellow Wrenchers,

What's folks favorite Propane Gen line in the 30 KW range for off-grid 
backup?


SMA has limited exposure to larger generators for the SI for approval 
to their list.


Anybody out there know which SI's in the 30 KW range that the SI likes?

Thanks!

jc
--
Jeff Clearwater
Village Power Design

Renewable Energy Consultant
32 Years in all Aspects of Renewables
www.villagepower.com
skype: jclearwater
413-559-9763
~



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options&  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules&  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Home Depot solar?

2011-09-29 Thread wirewiz
Andrew,

Koyaanisqatsi is also a great movie by Francis Ford Copolla. You should all
see it. It's been awhile since I've seen it but if I remember correctly it's
a Hopi Indian term meaning once we start digging from the earth, we're
screwed beyond repair.

Larry Liesner
Design and Installations
Elektron Solar, LLC
49 Richmondville Ave Suite 107
Westport, CT 06880
203-557-3127 (office)
203-644-2404 (cell)
203-549-0977 (fax)
wire...@gmail.com

On Thu, Sep 29, 2011 at 12:31 PM, Solar Energy Solutions <
solarenergysoluti...@yahoo.com> wrote:

> Home Depot IS selling PV in Portland Oregon through Solar City.
>
>  Seirrabuton Club is marketing PV to their members in Oregon.  They
> have chosen a single contractor for the entire state to install all of
> their member's systems.  Payola is $300.00/system installed.
>
>
> *Andrew Koyaanisqatsi*
> President
> *Solar Energy Solutions, Inc.*
> Since 1987,
> Moving Portland and Beyond
> to an Environmentally Sustainable Future.
>  *503-238-4502*
> *www.solarenergyoregon.com *
> **
> *"Better one's House too little one day*
> *than too big all the Year after."*
>
>  *From:* Jason Szumlanski 
> *To:* RE-wrenches 
> *Sent:* Thursday, September 29, 2011 8:17 AM
> *Subject:* Re: [RE-wrenches] Home Depot solar?
>
> We were recently asked to fix a royal mess by a SDHW installer
> contracted via Home Depot. Not fun. 60+ systems with various
> deficiencies. The installer was to blame, not HD.
>
> HD is not selling PV in our market (fortunately).
>
> Jason Szumlanski
>
>
> -Original Message-
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse
> Dahl
> Sent: Thursday, September 29, 2011 10:39 AM
> To: RE-wrenches
> Subject: [RE-wrenches] Home Depot solar?
>
> Anyone out there have any experience with Home Depot's solar installers?
>
> Jesse
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>



NABCEP Certified PV Installer (# 032611-184)
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Home Depot solar?

2011-09-29 Thread Solar Energy Solutions
Home Depot IS selling PV in Portland Oregon through Solar City.  
 
Seirrabuton Club is marketing PV to their members in Oregon.  They have chosen 
a single contractor for the entire state to install all of their member's 
systems.  Payola is $300.00/system installed.

  
Andrew Koyaanisqatsi
President
Solar Energy Solutions, Inc.
Since 1987,
Moving Portland and Beyond 
to an Environmentally Sustainable Future.
503-238-4502
www.solarenergyoregon.com 
 
"Better one's House too little one day
than too big all the Year after."

From: Jason Szumlanski 
To: RE-wrenches 
Sent: Thursday, September 29, 2011 8:17 AM
Subject: Re: [RE-wrenches] Home Depot solar?

We were recently asked to fix a royal mess by a SDHW installer
contracted via Home Depot. Not fun. 60+ systems with various
deficiencies. The installer was to blame, not HD.

HD is not selling PV in our market (fortunately).

Jason Szumlanski


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse
Dahl
Sent: Thursday, September 29, 2011 10:39 AM
To: RE-wrenches
Subject: [RE-wrenches] Home Depot solar?

Anyone out there have any experience with Home Depot's solar installers?

Jesse

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



re-wrenches@lists.re-wrenches.org

2011-09-29 Thread Jeff Clearwater

Fellow Wrenchers,

What's folks favorite Propane Gen line in the 30 KW range for off-grid 
backup?


SMA has limited exposure to larger generators for the SI for approval to 
their list.


Anybody out there know which SI's in the 30 KW range that the SI likes?

Thanks!

jc
--
Jeff Clearwater
Village Power Design

Renewable Energy Consultant
32 Years in all Aspects of Renewables
www.villagepower.com
skype: jclearwater
413-559-9763
~

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Adding on to existing PV System

2011-09-29 Thread Jason Szumlanski
We've been contracted to add on to an existing PV system in a residence.
The existing system has a 30A 2P Breaker on a 200A rated panel with a
200A main breaker. The new system would require a 15A breaker, which
would exceed the limit in NEC 690.64(B)(2).

 

The existing system has a fusible AC disconnect mounted next to the
meter. This was originally intended as the utility external disconnect.
The utility no longer requires a disconnect, but if we do a supply side
connection, we would need a fusible AC disconnect anyway for the new
system. I would collocate the new disconnect with the old.

 

Does anyone see any problem with doing a supply size connection for the
new system? Any labeling snags that I might need to consider?

 

Jason Szumlanski

Fafco Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Home Depot solar?

2011-09-29 Thread Jason Szumlanski
We were recently asked to fix a royal mess by a SDHW installer
contracted via Home Depot. Not fun. 60+ systems with various
deficiencies. The installer was to blame, not HD.

HD is not selling PV in our market (fortunately).

Jason Szumlanski


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse
Dahl
Sent: Thursday, September 29, 2011 10:39 AM
To: RE-wrenches
Subject: [RE-wrenches] Home Depot solar?

Anyone out there have any experience with Home Depot's solar installers?

Jesse

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Home Depot solar?

2011-09-29 Thread Jesse Dahl
Anyone out there have any experience with Home Depot's solar installers?

Jesse

Sent from my iPhone
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org