Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread boB Gudgel

On 7/19/2011 2:34 PM, David Brearley wrote:
Presumably the latter---added as part of the cycle of revisions 
initiated in 1987.



The array shorting requirement must have gone away near 1993 or 1994 as
I designed an opening and  shorting of the array style GFPD version in
1994 while at Trace Engineering.

It  would have been expensive.

boB










On 7/19/11 3:29 PM, "Hans Frederickson"  wrote:

David,
Thanks for the interesting history on GFPDs. My copy of the 1987
NEC does not have 690-5, and it's not missing any pages. Either my
code book is an incomplete printing or perhaps John Wiles was
referring to a 1987 proposal that didn't make it into the code
until the 1990 NEC.

Regards,
-Hans


*From:* re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*David Brearley
*Sent:* Tuesday, July 19, 2011 12:57 PM
*To:* RE-wrenches
    *Subject:* Re: [RE-wrenches] 1987 NEC

Hans,

John Wiles described the evolution of this standard for a Home
Power article that we referenced later in a SolarPro on PV System
Ground Faults:

http://solarprofessional.com/article/?file=SP2_5_pg60_Mync

"As described by John Wiles, program manager for the Institute for
the Energy and the Environment, in the February/ March 2008 Home
Power article "Ground-Fault Protection Is Expanding," Article
690.5 was added to the /NEC/ in 1987. One of Wiles' first projects
in the PV industry was to develop "prototype hardware" to meet the
new /Code/ requirement. "The basic concept (of the original GFPD
prototype)," writes Wiles, "was to insert a 0.5- or 1-amp circuit
breaker in the dc system-bonding conductor." This small circuit
breaker senses any current between the grounded current-carrying
conductor and the grounding system, tripping if current exceeds
the 0.5 A or 1 A rating. By mechanically linking this smaller
breaker to larger capacity breakers that are installed inline with
the ungrounded current-carrying array conductors, it is possible
to detect, interrupt and indicate that a ground fault has
occurred, and to disconnect the fault.

These early GFPDs were manufactured for 48 V or lower PV systems.
According to Wiles, "As higher voltage, utility-interactive PV
inverters became available in the late 1990s, using a 0.5- or
1-amp fuse as the sensing element and the inverter's control
electronics to monitor the fuse was more cost effective." While
the sensing equipment may have changed, in general the role of the
modern GFPD remains the same as it was in 1987:

1. Detect ground faults in PV arrays.
2. Interrupt the fault current.
3. Indicate that a ground fault has occurred.
4. Disconnect the faulted part of the array.

These four GFPD requirements for grounded PV arrays are spelled
out in /NEC/ 690.5(A) and 690.5(B). The former requires
ground-fault detection and interruption (GFDI), which includes the
provision to indicate the presence of a ground fault. The latter
requires that faulted circuits be isolated either by disconnecting
the ungrounded conductors of the faulted circuit or by shutting
down power to the output power circuits of the inverter or charge
controller.

A final GFPD requirement is found in Article 960.5(C), which calls
for a visible warning in the proximity of the ground-fault
indicator. The warning could be an LED, an LCD or both. In
general, the manufacturer provides this electric shock hazard
warning as part of the listed grid-tied inverter or charge
controller. However, where a PV system includes batteries, the
installer must apply a duplicate warning label near the batteries,
stating:

WARNING
ELECTRIC SHOCK HAZARD
IF A GROUND FAULT IS INDICATED, NORMALLY
GROUNDED CONDUCTORS MAY BE UNGROUNDED
AND ENERGIZED


One change in the GFPD requirements introduced in 1987 is that it
is no longer necessary to short-circuit, or "crowbar," the PV
array in the event of a ground fault. This added step had the
effect of reducing the PV array voltage to zero, minimizing shock
hazard. The requirement was dropped in a subsequent /Code/ cycle,
as leaving the array in a short-circuited condition created
several other issues."


If you're a Home Power subscriber, you can access the original
article in the HP archives. If not, it is summarized above.

Best,

David Brearley, Senior Technical Editor
/SolarPro/ magazine
NABCEP Certified PV Installer ^(TM)
david.brear...@solarprofessional.com
Direct: 541.261.6545


On 7/19/11 2:19 PM, "Hans Frederickson"  wrote:

Kent

Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread David Brearley
Presumably the latter‹added as part of the cycle of revisions initiated in
1987. 


On 7/19/11 3:29 PM, "Hans Frederickson"  wrote:

> David,
> Thanks for the interesting history on GFPDs. My copy of the 1987 NEC does not
> have 690-5, and it's not missing any pages. Either my code book is an
> incomplete printing or perhaps John Wiles was referring to a 1987 proposal
> that didn't make it into the code until the 1990 NEC.
>  
> Regards,
> -Hans 
> 
> 
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Brearley
> Sent: Tuesday, July 19, 2011 12:57 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] 1987 NEC
> 
> Hans,
> 
> John Wiles described the evolution of this standard for a Home Power article
> that we referenced later in a SolarPro on PV System Ground Faults:
> 
> http://solarprofessional.com/article/?file=SP2_5_pg60_Mync
> 
> ³As described by John Wiles, program manager for the Institute for the Energy
> and the Environment, in the February/ March 2008 Home Power article
> "Ground-Fault Protection Is Expanding," Article 690.5 was added to the NEC in
> 1987. One of Wiles¹ first projects in the PV industry was to develop
> ³prototype hardware² to meet the new Code requirement. "The basic concept (of
> the original GFPD prototype)," writes Wiles, "was to insert a 0.5- or 1-amp
> circuit breaker in the dc system-bonding conductor." This small circuit
> breaker senses any current between the grounded current-carrying conductor and
> the grounding system, tripping if current exceeds the 0.5 A or 1 A rating. By
> mechanically linking this smaller breaker to larger capacity breakers that are
> installed inline with the ungrounded current-carrying array conductors, it is
> possible to detect, interrupt and indicate that a ground fault has occurred,
> and to disconnect the fault.
> 
> These early GFPDs were manufactured for 48 V or lower PV systems. According to
> Wiles, ³As higher voltage, utility-interactive PV inverters became available
> in the late 1990s, using a 0.5- or 1-amp fuse as the sensing element and the
> inverter¹s control electronics to monitor the fuse was more cost effective.²
> While the sensing equipment may have changed, in general the role of the
> modern GFPD remains the same as it was in 1987:
> 
> 1. Detect ground faults in PV arrays.
> 2. Interrupt the fault current.
> 3. Indicate that a ground fault has occurred.
> 4. Disconnect the faulted part of the array.
> 
> These four GFPD requirements for grounded PV arrays are spelled out in NEC
> 690.5(A) and 690.5(B). The former requires ground-fault detection and
> interruption (GFDI), which includes the provision to indicate the presence of
> a ground fault. The latter requires that faulted circuits be isolated either
> by disconnecting the ungrounded conductors of the faulted circuit or by
> shutting down power to the output power circuits of the inverter or charge
> controller.
> 
> A final GFPD requirement is found in Article 960.5(C), which calls for a
> visible warning in the proximity of the ground-fault indicator. The warning
> could be an LED, an LCD or both. In general, the manufacturer provides this
> electric shock hazard warning as part of the listed grid-tied inverter or
> charge controller. However, where a PV system includes batteries, the
> installer must apply a duplicate warning label near the batteries, stating:
> 
> WARNING 
> ELECTRIC SHOCK HAZARD
> IF A GROUND FAULT IS INDICATED, NORMALLY
> GROUNDED CONDUCTORS MAY BE UNGROUNDED
> AND ENERGIZED 
> 
> One change in the GFPD requirements introduced in 1987 is that it is no longer
> necessary to short-circuit, or ³crowbar,² the PV array in the event of a
> ground fault. This added step had the effect of reducing the PV array voltage
> to zero, minimizing shock hazard. The requirement was dropped in a subsequent
> Code cycle, as leaving the array in a short-circuited condition created
> several other issues.²
> 
> 
> If you¹re a Home Power subscriber, you can access the original article in the
> HP archives. If not, it is summarized above.
> 
> Best,
> 
> David Brearley, Senior Technical Editor
> SolarPro magazine
> NABCEP Certified PV Installer 
> david.brear...@solarprofessional.com
> Direct: 541.261.6545
> 
> 
> On 7/19/11 2:19 PM, "Hans Frederickson"  wrote:
> 
>> Kent,
>> I'm not a geezer yet, but thanks to my dad I do have a  copy of the 1987 NEC.
>> 690-5 (Ground Fault Detection and Interruption) was  added in the 1990 NEC.
>> There is no 690-5 or mention of ground fault  detection/interruption in the
>> 1987 NEC.
>> 
>

Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread R Ray Walters
We had an early 90s system with a DCGFP(complete with 4/0 GEC:)). A ground 
fault on a DC load circuit caused the  GFP to lift the ground, shut the array 
off, but the short was still being fed by the battery and wouldn't trip the DC 
breaker, since negative was disconnected from ground. I thought it was fairly 
backwards and dangerous from what you would want to see in this situation.
I still think this requirement causes more trouble than it fixes, especially on 
battery based off grid systems with DC loads.
I'm looking forward to trying some of the "smart" combiner boxes to move us 
forward on this issue to real safety.
Since we've had DCGFP for almost 20 years, has anyone seen these actually stop 
a dangerous situation? My experience is that the danger continues after the 
DCGFP trips, but at least you know something is wrong because after a week or 
so, the customer calls to complain that his array isn't charging. It's a rather 
complicated and less than fool proof idiot light. As Kent just pointed out: the 
situation is actually getting more dangerous with the higher voltages being 
used on off grid projects.

R. Walters
r...@solarray.com
Solar Engineer




> 
>  Not openning the PV array grounded conductor means that not only is the 
> normally grounded conductor in the PV array possibly energized (that can't be 
> avoided), but everything else it is attached to is possibly energized. For 
> battery based systems that includes: the battery negative terminal, battery 
> vent fan wiring, and all dc loads. The fact that all dc loads may be 
> energized to the potential of the PV array is troubling. Especially with the 
> possibility now of a 600-volt PV array charging a battery system.
> 
> Kent Osterberg
> Blue Mountain Solar
> 
> 
> 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread Kent Osterberg




Thanks, Hans. 

The part about shorting the array was abandoned, I'm not sure but it
may be have been removed for the 1993 code. 

It's item two on this list that I've been trying to backtrack to. It is
pretty much the same as in the current code: "open the grounded
conductor". It is also not the way things are actually done. The GFP
fuse, circuit breaker, or PTC (Positive Temperature Coefficient) in
inverters and now in some charge controllers opens the system bond (As
described by John Wiles) not the grounded PV array conductor. Not
openning the PV array grounded conductor means that not only is the
normally grounded conductor in the PV array possibly energized (that
can't be avoided), but everything else it is attached to is possibly
energized. For battery based systems that includes: the battery
negative terminal, battery vent fan wiring, and all dc loads. The fact
that all dc loads may be energized to the potential of the PV array is
troubling. Especially with the possibility now of a 600-volt PV array
charging a battery system.

Kent Osterberg
Blue Mountain Solar




Hans Frederickson wrote:

  
  
  
  Kent,
  I'm not a geezer yet, but thanks
to my dad I do have a copy of the 1987 NEC. 690-5 (Ground Fault
Detection and Interruption) was added in the 1990 NEC. There is
no 690-5 or mention of ground fault detection/interruption in the 1987
NEC.
   
  In the 1990 NEC, section 690-5
is very small compared to 690.5 in the 2011 NEC. Here's the complete
text from 1990:
   
  "690-5. Ground Fault Detection
and Interruption.  Roof-mounted photovoltaic arrays located on
dwellings shall be provided with ground-fault protection to reduce fire
hazard. The ground-fault protection circuit shall be capable of
detecting a ground fault, interrupting the fault path, and disabling
the array."
   
  The handbook for 1990 goes on to
say that the gfp device must:
  1) detect the ground fault
  2) open the grounded conductor
to interrupt the ground fault
  3) open the ungrounded
conductors and short the photoltaic array source to disable it
   
  For some reason, I've never
heard of item #3, specifically the part about shorting the array. Can
anyone shed light on this?
   
  Regards,
  -Hans
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
  Sent: Monday, July 18, 2011 10:07 PM
  To: g...@icarussolarservices.com; RE-wrenches
  Subject: Re: [RE-wrenches] 1987 NEC
  
  
Gary,
  
No one else has come up with a 1987 NEC. If you can get a copy of 1987
section 690.5 (I think it was 690-5 back then), I'd appreciate it.
  
Kent Osterberg
Blue Mountain Solar
  
  
  
Gary Willett wrote:
  Kent:

I am a member of the International Association of Electrical Inspectors
(IAEI), and they're headquartered here in the Dallas area.

If you aren't successful getting the info from a Wrench with the 1987
code book, let me know and I am sure I can request a FAXed copy of 1987
section 690.5.













Regards,

Gary Willett, PE
g...@icarussolarservices.com



On 7/15/2011 4:30 PM, Kent Osterberg wrote:
I'm
looking for the text of 1987 NEC 690.5 to compare with 2011 version. If
any of you geezers have kept copies that old, please contact me off
list. Thanks. 
  
Kent Osterberg 
Blue Mountain Solar 
___ 
List sponsored by Home Power magazine 
  
List Address: RE-wrenches@lists.re-wrenches.org
  
  
Options & settings: 
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
  
List rules & etiquette: 
  www.re-wrenches.org/etiquette.htm
  
  
Check out participant bios: 
  www.members.re-wrenches.org
  
  
  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
  
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  



___
List sponsored by Home Power magazine

List Address:

Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread Kent Osterberg




Thanks, David. I've been looking for a 1987 NEC because of this
reference and others where John Wiles has referred to it. 

David Brearley wrote:

  Re: [RE-wrenches] 1987 NEC
  Hans,
  
John Wiles described the evolution of this standard for a Home Power
article that we referenced later in a SolarPro on PV System Ground
Faults:
  
  http://solarprofessional.com/article/?file=SP2_5_pg60_Mync
  
“As described by John Wiles, program manager
for the Institute for the Energy and the Environment, in the February/
March 2008 Home Power article "Ground-Fault Protection Is Expanding,"
Article 690.5 was added to the NEC in 1987. One of Wiles’ first
projects in the PV industry was to develop “prototype hardware” to meet
the new Code requirement. "The basic concept (of the original
GFPD prototype)," writes Wiles, "was to insert a 0.5- or 1-amp circuit
breaker in the dc system-bonding conductor." This small circuit breaker
senses any current between the grounded current-carrying conductor and
the grounding system, tripping if current exceeds the 0.5 A or 1 A
rating. By mechanically linking this smaller breaker to larger capacity
breakers that are installed inline with the ungrounded current-carrying
array conductors, it is possible to detect, interrupt and indicate that
a ground fault has occurred, and to disconnect the fault.
  
These early GFPDs were manufactured for 48 V or lower PV systems.
According to Wiles, “As higher voltage, utility-interactive PV
inverters became available in the late 1990s, using a 0.5- or 1-amp
fuse as the sensing element and the inverter’s control electronics to
monitor the fuse was more cost effective.” While the sensing equipment
may have changed, in general the role of the modern GFPD remains the
same as it was in 1987:
  
1. Detect ground faults in PV arrays. 
2. Interrupt the fault current. 
3. Indicate that a ground fault has occurred. 
4. Disconnect the faulted part of the array.
  
These four GFPD requirements for grounded PV arrays are spelled out in NEC 690.5(A)
and 690.5(B). The former requires ground-fault detection and
interruption (GFDI), which includes the provision to indicate the
presence of a ground fault. The latter requires that faulted circuits
be isolated either by disconnecting the ungrounded conductors of the
faulted circuit or by shutting down power to the output power circuits
of the inverter or charge controller.
  
A final GFPD requirement is found in Article 960.5(C), which calls for
a visible warning in the proximity of the ground-fault indicator. The
warning could be an LED, an LCD or both. In general, the manufacturer
provides this electric shock hazard warning as part of the listed
grid-tied inverter or charge controller. However, where a PV system
includes batteries, the installer must apply a duplicate warning label
near the batteries, stating:
  
  WARNING 
ELECTRIC SHOCK HAZARD 
IF A GROUND FAULT IS INDICATED, NORMALLY 
GROUNDED CONDUCTORS MAY BE UNGROUNDED 
AND ENERGIZED
  
  
One change in the GFPD requirements introduced in 1987 is that it is no
longer necessary to short-circuit, or “crowbar,” the PV array in the
event of a ground fault. This added step had the effect of reducing the
PV array voltage to zero, minimizing shock hazard. The requirement was
dropped in a subsequent Code cycle, as leaving the array in a
short-circuited condition created several other issues.”
  
  
  If you’re a Home Power subscriber, you can
access the original article in the HP archives. If not, it is
summarized above.
  
Best,
  
  David Brearley, Senior Technical Editor
  SolarPro magazine 
NABCEP Certified PV Installer ™
  david.brear...@solarprofessional.com
Direct: 541.261.6545
  
  
On 7/19/11 2:19 PM, "Hans Frederickson" <h...@fredelectric.com> wrote:
  
  
  Kent,
I'm not a geezer yet, but thanks to my dad I do have a copy of the 1987
NEC. 690-5 (Ground Fault Detection and Interruption) was added in the
1990 NEC. There is no 690-5 or mention of ground fault
detection/interruption in the 1987 NEC.
 
In the 1990 NEC,
section 690-5 is very small compared to 690.5 in the 2011 NEC. Here's
the complete text from 1990:
 
"690-5. Ground
Fault Detection and Interruption.  Roof-mounted photovoltaic arrays
located on dwellings shall be provided with ground-fault protection to
reduce fire hazard. The ground-fault protection circuit shall be
capable of detecting a ground fault, interrupting the fault path, and
disabling the array."
 
The handbook for
1990 goes on to say that the gfp device must:
1) detect the ground fault
2) open the grounded conductor to interrupt the ground fault
3) open the ungrounded conductors and short the photoltaic array source
to disable it
 
For some reason,
I've never heard of item #3, specifically the part about shorting the
array. Can anyone shed light on this?
 
Regards,
-Hans

From: re-wrenches-boun...@lists.re-wren

Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread Hans Frederickson
David,
Thanks for the interesting history on GFPDs. My copy of the 1987 NEC does
not have 690-5, and it's not missing any pages. Either my code book is an
incomplete printing or perhaps John Wiles was referring to a 1987 proposal
that didn't make it into the code until the 1990 NEC. 
 
Regards,
-Hans 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Brearley
Sent: Tuesday, July 19, 2011 12:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 1987 NEC


Hans,

John Wiles described the evolution of this standard for a Home Power article
that we referenced later in a SolarPro on PV System Ground Faults:

http://solarprofessional.com/article/?file=SP2_5_pg60_Mync

"As described by John Wiles, program manager for the Institute for the
Energy and the Environment, in the February/ March 2008 Home Power article
"Ground-Fault Protection Is Expanding," Article 690.5 was added to the NEC
in 1987. One of Wiles' first projects in the PV industry was to develop
"prototype hardware" to meet the new Code requirement. "The basic concept
(of the original GFPD prototype)," writes Wiles, "was to insert a 0.5- or
1-amp circuit breaker in the dc system-bonding conductor." This small
circuit breaker senses any current between the grounded current-carrying
conductor and the grounding system, tripping if current exceeds the 0.5 A or
1 A rating. By mechanically linking this smaller breaker to larger capacity
breakers that are installed inline with the ungrounded current-carrying
array conductors, it is possible to detect, interrupt and indicate that a
ground fault has occurred, and to disconnect the fault.

These early GFPDs were manufactured for 48 V or lower PV systems. According
to Wiles, "As higher voltage, utility-interactive PV inverters became
available in the late 1990s, using a 0.5- or 1-amp fuse as the sensing
element and the inverter's control electronics to monitor the fuse was more
cost effective." While the sensing equipment may have changed, in general
the role of the modern GFPD remains the same as it was in 1987:

1. Detect ground faults in PV arrays. 
2. Interrupt the fault current. 
3. Indicate that a ground fault has occurred. 
4. Disconnect the faulted part of the array.

These four GFPD requirements for grounded PV arrays are spelled out in NEC
690.5(A) and 690.5(B). The former requires ground-fault detection and
interruption (GFDI), which includes the provision to indicate the presence
of a ground fault. The latter requires that faulted circuits be isolated
either by disconnecting the ungrounded conductors of the faulted circuit or
by shutting down power to the output power circuits of the inverter or
charge controller.

A final GFPD requirement is found in Article 960.5(C), which calls for a
visible warning in the proximity of the ground-fault indicator. The warning
could be an LED, an LCD or both. In general, the manufacturer provides this
electric shock hazard warning as part of the listed grid-tied inverter or
charge controller. However, where a PV system includes batteries, the
installer must apply a duplicate warning label near the batteries, stating:


WARNING 
ELECTRIC SHOCK HAZARD 
IF A GROUND FAULT IS INDICATED, NORMALLY 
GROUNDED CONDUCTORS MAY BE UNGROUNDED 
AND ENERGIZED 



One change in the GFPD requirements introduced in 1987 is that it is no
longer necessary to short-circuit, or "crowbar," the PV array in the event
of a ground fault. This added step had the effect of reducing the PV array
voltage to zero, minimizing shock hazard. The requirement was dropped in a
subsequent Code cycle, as leaving the array in a short-circuited condition
created several other issues."


If you're a Home Power subscriber, you can access the original article in
the HP archives. If not, it is summarized above.

Best,

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer T
david.brear...@solarprofessional.com
Direct: 541.261.6545


On 7/19/11 2:19 PM, "Hans Frederickson"  wrote:




Kent,
I'm not a geezer yet, but thanks to my dad I do have a copy of the 1987 NEC.
690-5 (Ground Fault Detection and Interruption) was added in the 1990 NEC.
There is no 690-5 or mention of ground fault detection/interruption in the
1987 NEC.

In the 1990 NEC, section 690-5 is very small compared to 690.5 in the 2011
NEC. Here's the complete text from 1990:

"690-5. Ground Fault Detection and Interruption.  Roof-mounted photovoltaic
arrays located on dwellings shall be provided with ground-fault protection
to reduce fire hazard. The ground-fault protection circuit shall be capable
of detecting a ground fault, interrupting the fault path, and disabling the
array."

The handbook for 1990 goes on to say that the gfp device must:
1) detect the ground fault
2) open the grounded conductor to interrupt the gr

Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread David Brearley
Hans,

John Wiles described the evolution of this standard for a Home Power article
that we referenced later in a SolarPro on PV System Ground Faults:

http://solarprofessional.com/article/?file=SP2_5_pg60_Mync

³As described by John Wiles, program manager for the Institute for the
Energy and the Environment, in the February/ March 2008 Home Power article
"Ground-Fault Protection Is Expanding," Article 690.5 was added to
the NEC in 1987. One of Wiles¹ first projects in the PV industry was to
develop ³prototype hardware² to meet the new Code requirement. "The basic
concept (of the original GFPD prototype)," writes Wiles, "was to insert a
0.5- or 1-amp circuit breaker in the dc system-bonding conductor." This
small circuit breaker senses any current between the grounded
current-carrying conductor and the grounding system, tripping if current
exceeds the 0.5 A or 1 A rating. By mechanically linking this smaller
breaker to larger capacity breakers that are installed inline with the
ungrounded current-carrying array conductors, it is possible to detect,
interrupt and indicate that a ground fault has occurred, and to disconnect
the fault.

These early GFPDs were manufactured for 48 V or lower PV systems. According
to Wiles, ³As higher voltage, utility-interactive PV inverters became
available in the late 1990s, using a 0.5- or 1-amp fuse as the sensing
element and the inverter¹s control electronics to monitor the fuse was more
cost effective.² While the sensing equipment may have changed, in general
the role of the modern GFPD remains the same as it was in 1987:

1. Detect ground faults in PV arrays. 
2. Interrupt the fault current. 
3. Indicate that a ground fault has occurred. 
4. Disconnect the faulted part of the array.

These four GFPD requirements for grounded PV arrays are spelled out
in NEC 690.5(A) and 690.5(B). The former requires ground-fault detection and
interruption (GFDI), which includes the provision to indicate the presence
of a ground fault. The latter requires that faulted circuits be isolated
either by disconnecting the ungrounded conductors of the faulted circuit or
by shutting down power to the output power circuits of the inverter or
charge controller.

A final GFPD requirement is found in Article 960.5(C), which calls for a
visible warning in the proximity of the ground-fault indicator. The warning
could be an LED, an LCD or both. In general, the manufacturer provides this
electric shock hazard warning as part of the listed grid-tied inverter or
charge controller. However, where a PV system includes batteries, the
installer must apply a duplicate warning label near the batteries, stating:

WARNING 
ELECTRIC SHOCK HAZARD 
IF A GROUND FAULT IS INDICATED, NORMALLY 
GROUNDED CONDUCTORS MAY BE UNGROUNDED 
AND ENERGIZED 

One change in the GFPD requirements introduced in 1987 is that it is no
longer necessary to short-circuit, or ³crowbar,² the PV array in the event
of a ground fault. This added step had the effect of reducing the PV array
voltage to zero, minimizing shock hazard. The requirement was dropped in a
subsequent Code cycle, as leaving the array in a short-circuited condition
created several other issues.²


If you¹re a Home Power subscriber, you can access the original article in
the HP archives. If not, it is summarized above.

Best,

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com
Direct: 541.261.6545


On 7/19/11 2:19 PM, "Hans Frederickson"  wrote:

> Kent,
> I'm not a geezer yet, but thanks to my dad I do have a copy of the 1987 NEC.
> 690-5 (Ground Fault Detection and Interruption) was added in the 1990 NEC.
> There is no 690-5 or mention of ground fault detection/interruption in the
> 1987 NEC.
>  
> In the 1990 NEC, section 690-5 is very small compared to 690.5 in the 2011
> NEC. Here's the complete text from 1990:
>  
> "690-5. Ground Fault Detection and Interruption.  Roof-mounted photovoltaic
> arrays located on dwellings shall be provided with ground-fault protection to
> reduce fire hazard. The ground-fault protection circuit shall be capable of
> detecting a ground fault, interrupting the fault path, and disabling the
> array."
>  
> The handbook for 1990 goes on to say that the gfp device must:
> 1) detect the ground fault
> 2) open the grounded conductor to interrupt the ground fault
> 3) open the ungrounded conductors and short the photoltaic array source to
> disable it
>  
> For some reason, I've never heard of item #3, specifically the part about
> shorting the array. Can anyone shed light on this?
>  
> Regards,
> -Hans
> 
> 
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
> Sent: Monday, July 18, 2011 10:07 PM
> To: g...@icarussolarservices

Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread Hans Frederickson
Kent,
I'm not a geezer yet, but thanks to my dad I do have a copy of the 1987 NEC.
690-5 (Ground Fault Detection and Interruption) was added in the 1990 NEC.
There is no 690-5 or mention of ground fault detection/interruption in the
1987 NEC.
 
In the 1990 NEC, section 690-5 is very small compared to 690.5 in the 2011
NEC. Here's the complete text from 1990:
 
"690-5. Ground Fault Detection and Interruption.  Roof-mounted photovoltaic
arrays located on dwellings shall be provided with ground-fault protection
to reduce fire hazard. The ground-fault protection circuit shall be capable
of detecting a ground fault, interrupting the fault path, and disabling the
array."
 
The handbook for 1990 goes on to say that the gfp device must:
1) detect the ground fault
2) open the grounded conductor to interrupt the ground fault
3) open the ungrounded conductors and short the photoltaic array source to
disable it
 
For some reason, I've never heard of item #3, specifically the part about
shorting the array. Can anyone shed light on this?
 
Regards,
-Hans

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Monday, July 18, 2011 10:07 PM
To: g...@icarussolarservices.com; RE-wrenches
Subject: Re: [RE-wrenches] 1987 NEC


Gary,

No one else has come up with a 1987 NEC. If you can get a copy of 1987
section 690.5 (I think it was 690-5 back then), I'd appreciate it.

Kent Osterberg
Blue Mountain Solar



Gary Willett wrote: 

Kent:

I am a member of the International Association of Electrical Inspectors
(IAEI), and they're headquartered here in the Dallas area.

If you aren't successful getting the info from a Wrench with the 1987 code
book, let me know and I am sure I can request a FAXed copy of 1987 section
690.5.



Regards,

Gary Willett, PE
g...@icarussolarservices.com


On 7/15/2011 4:30 PM, Kent Osterberg wrote: 

I'm looking for the text of 1987 NEC 690.5 to compare with 2011 version. If
any of you geezers have kept copies that old, please contact me off list.
Thanks. 

Kent Osterberg 
Blue Mountain Solar 
___ 
List sponsored by Home Power magazine 

List Address: RE-wrenches@lists.re-wrenches.org 

Options & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 

List rules & etiquette: 
www.re-wrenches.org/etiquette.htm 

Check out participant bios: 
www.members.re-wrenches.org 






  _  


___

List sponsored by Home Power magazine



List Address: RE-wrenches@lists.re-wrenches.org



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out participant bios:

www.members.re-wrenches.org



  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1987 NEC

2011-07-18 Thread Kent Osterberg




Gary,

No one else has come up with a 1987 NEC. If you can get a copy of 1987
section 690.5 (I think it was 690-5 back then), I'd appreciate it.

Kent Osterberg
Blue Mountain Solar



Gary Willett wrote:

  
  
  Kent:
  
I am a member of the International Association of Electrical Inspectors
(IAEI), and they're headquartered here in the Dallas area.
  
If you aren't successful getting the info from a Wrench with the 1987
code book, let me know and I am sure I can request a FAXed copy of 1987
section 690.5.
  
  
  
  
  
  
  
  

  
  

  
  
  Regards,
  
Gary Willett, PE
  g...@icarussolarservices.com
  
  
  
On 7/15/2011 4:30 PM, Kent Osterberg wrote:
  I'm
looking for the text of 1987 NEC 690.5 to compare with 2011 version. If
any of you geezers have kept copies that old, please contact me off
list. Thanks. 

Kent Osterberg 
Blue Mountain Solar 
___ 
List sponsored by Home Power magazine 

List Address: RE-wrenches@lists.re-wrenches.org


Options & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette: 
www.re-wrenches.org/etiquette.htm


Check out participant bios: 
www.members.re-wrenches.org



  
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1987 NEC

2011-07-15 Thread Gary Willett

Kent:

I am a member of the International Association of Electrical Inspectors 
(IAEI), and they're headquartered here in the Dallas area.


If you aren't successful getting the info from a Wrench with the 1987 
code book, let me know and I am sure I can request a FAXed copy of 1987 
section 690.5.


Regards,

Gary Willett, PE
g...@icarussolarservices.com 


On 7/15/2011 4:30 PM, Kent Osterberg wrote:
I'm looking for the text of 1987 NEC 690.5 to compare with 2011 
version. If any of you geezers have kept copies that old, please 
contact me off list. Thanks.


Kent Osterberg
Blue Mountain Solar
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] 1987 NEC

2011-07-15 Thread Kent Osterberg
I'm looking for the text of 1987 NEC 690.5 to compare with 2011 version. 
If any of you geezers have kept copies that old, please contact me off 
list. Thanks.


Kent Osterberg
Blue Mountain Solar
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org