Here is how I see the argument
If you pipe the sprinkler with a smaller diameter line then that sprinkler
has to be part of your hydraulic calculation (arguably you could just
switch to the sprinkler below the obstruction and remove the sprinkler
above the obstruction, as you are not required to ca
What I have is an ESFR system where i need to add a single sprinkler in 2
locations under ducts. 23.4.4.7.3.1 states that sprinklers under obstructions
do not need to be included in hydraulic calculations. 23.4.4.7.3.2 states that
if the sprinklers are under obstructions are piped w
NPFA 13 2016 23.4.4.7.3.2
From: Fpdcdesign
Sent: Tuesday, August 23, 2022 9:30 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Sizing of pipe below obstructions
Brett, any specific reference for that?
On Aug 23, 2022 at 12:21 PM, mailto:
Brett, any specific reference for that?
>
> On Aug 23, 2022 at 12:21 PM, mailto:br...@proudline.ca)>
> wrote:
>
>
>
> Typically non storage sprinkler supplied with 1"
> Storage type sprinkler supplied with same size as branch line (typical for
> ESFR sprink
Typically non storage sprinkler supplied with 1"
Storage type sprinkler supplied with same size as branch line (typical for
ESFR sprinklers)
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 760
Nothing showing up?
Same as branch above?
R/
Matt
Matthew J. Willis, CWBSP
Rapid Fire Protection, Inc.
600 E. Carlson St. Suite AB | Cheyenne, WY. 82009
Office (307) 426-4077 ext. 404
Direct (307) 316-6630
Cell (605) 391-2733
[cid:image001.png@01D8B6D8.8DF7AD40]
From: Fpdcdesign
Sent: Tuesd
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (tel:860-535-2080) (ofc)
860-554-7054 (tel:860-554-7054) (fax)
860-608-4559 (tel:860-608-4559) (cell)
_
Sprinkl