Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread David Milholen

Depending if you are using solid or stranded.
I prefer #2 stranded. A little easier to work with.
You should have a MGB at the tower. If tower has 3 legs run the #2 to 
all 3 do not make a ring.
The MGB should have a #6 bonded or lug to MGB and bonded or lug to tower 
steel.
Ground for equipment should return to #2 leading to Main earth and coax 
or cable ground leaving tower should be grounded to MGB.
That should be sufficient for a ground at tower site.  In order to make 
it more compliant you may want a ring around the tower and
pad with proper spacing of bonded ground rods. If this is done then the 
tower legs would bound to the ring along with MGB and equipment.

The Return to Main earth electrical would bond in one place on the ring.



On 4/15/2015 2:58 PM, Mike Hammett wrote:
Your ground should be at least 4 gauge, maybe even larger than that. 
One of the 0/x gauges is in my mind for some reason. That should bond 
the electrical ground with all tower and equipment grounds.




-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com

https://www.facebook.com/ICSILhttps://plus.google.com/+IntelligentComputingSolutionsDeKalbhttps://www.linkedin.com/company/intelligent-computing-solutionshttps://twitter.com/ICSIL


*From: *Paul McCall pa...@pdmnet.net
*To: *af@afmug.com
*Sent: *Wednesday, April 15, 2015 2:41:15 PM
*Subject: *[AFMUG] Electrical - Grounding question - long run

In my continued disposition of acknowledging that I am not a 
electrical grounding expert, I lay out this scenario for review, a new 
tower we just built.


We installed a new tower, approximately 200ft. from the service panel 
that feeds it.  We will be on our own breaker (kinda irrelevant here).


In the past, we had run 10 gauge wire (x3) out to the tower with 
110vac.  Voltage drop is relatively negligible, certainly within the 
bounds of working properly to drive our 24v charger for the battery array.


I was told, by a grounding “expert” that all my equipment electrical 
grounds need to homerun to a bus bar that ride the ground back to the 
service panel directly, that nothing else is acceptable.


AND, and this is the big part…  that I needed to seriously upgrade the 
200ft. ground wire only that rides back to the panel to something 
significantly bigger.  How much bigger I am not sure.


So, I figured I would ask the crowd for an answer J

Thanks!

Paul McCall, Pres.

PDMNet / Florida Broadband

658 Old Dixie Highway

Vero Beach, FL 32962

772-564-6800 office

772-473-0352 cell

www.pdmnet.com http://www.pdmnet.com/

pa...@pdmnet.net mailto:pa...@pdmnet.net




--


Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Josh Baird
We recently had a site where an electrician installed a panel and his own
ground (rod) for the electrical/AC ground.  We then installed our equipment
at the bottom of the tower and bonded everything in the cabinet to the
tower ground.  This site took a pretty bad strike and it was my
understanding that this may have happened because the surge traveled
through our equipment and out of the AC/electrical ground since it was the
path of least resistance.

I am admittedly stupid when it comes to grounding, so, was this actually
the proper way to ground this site?

Josh

On Wed, Apr 15, 2015 at 9:44 PM, Mark Radabaugh m...@amplex.net wrote:

 For electrical service purposes the ground wire you have is fine.  The
 tower itself obviously needs to be well grounded.

 Where is your equipment?  I'm assuming it's at the tower since you talk
 about driving the battery charger.  All of the equipment at the tower needs
 to be bonded together with the tower ground and the electrical ground.

 A good 120V surge suppressor at the tower, grounded to the tower ground,
 will help avoid damage from coming in over the power lines.

 You are not trying to protect equipment back at the breaker panel.   The
 ground wire size back to the panel is pretty irrelevant as long as it can
 carry enough current to trip the breaker in a short circuit condition.
 Other than that it doesn't serve much purpose.


 Mark

 On Apr 15, 2015, at 3:41 PM, Paul McCall pa...@pdmnet.net wrote:

  In my continued disposition of acknowledging that I am not a electrical
 grounding expert, I lay out this scenario for review, a new tower we just
 built.



 We installed a new tower, approximately 200ft. from the service panel that
 feeds it.  We will be on our own breaker (kinda irrelevant here).



 In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.
 Voltage drop is relatively negligible, certainly within the bounds of
 working properly to drive our 24v charger for the battery array.



 I was told, by a grounding “expert” that all my equipment electrical
 grounds need to homerun to a bus bar that ride the ground back to the
 service panel directly, that nothing else is acceptable.



 AND, and this is the big part…  that I needed to seriously upgrade the
 200ft. ground wire only that rides back to the panel to something
 significantly bigger.  How much bigger I am not sure.



 So, I figured I would ask the crowd for an answer J



 Thanks!







 Paul McCall, Pres.

 PDMNet / Florida Broadband

 658 Old Dixie Highway

 Vero Beach, FL 32962

 772-564-6800 office

 772-473-0352 cell

 www.pdmnet.com

 pa...@pdmnet.net






Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Paul McCall
That’s a great answer in theory, but both buildings that we had to be 
disconnected from were thoroughly checked out by a reputable and thorough 
electrician.

If the tower gets physically hit, the concept is… why induce that surge into 
your electrical ground as well for it to have to deal with?




From: Af [mailto:af-boun...@afmug.com] On Behalf Of Mike Hammett
Sent: Thursday, April 16, 2015 8:09 AM
To: af@afmug.com
Subject: Re: [AFMUG] Electrical - Grounding question - long run

If your grounding is failing, it is because some piece somewhere isn't big 
enough or connected properly.


-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com

[http://www.ics-il.com/images/fbicon.png]https://www.facebook.com/ICSIL[http://www.ics-il.com/images/googleicon.png]https://plus.google.com/+IntelligentComputingSolutionsDeKalb[http://www.ics-il.com/images/linkedinicon.png]https://www.linkedin.com/company/intelligent-computing-solutions[http://www.ics-il.com/images/twittericon.png]https://twitter.com/ICSIL


From: Paul McCall pa...@pdmnet.netmailto:pa...@pdmnet.net
To: af@afmug.commailto:af@afmug.com
Sent: Thursday, April 16, 2015 6:49:24 AM
Subject: Re: [AFMUG] Electrical - Grounding question - long run
Mark,

Proposing to bond electrical ground with tower ground at the tower is the 
opposite of what they are saying to do.  I know, I know … we have done that 
pretty regularly in the past.  We had a coupe towers that got total equipment 
losses a several different times… sometimes multiple times in one lightning 
season.   All the potentials were within a couple ohms of each other … 
everywhere.  We double, triple checked everything. Still got pounded.

At the expert’s sugg4estion of not bonding everything together at those 2  
towers, we separated the grounds, and guess what… no more damages (almost 2 
years now)  And I understand the concept, but the grey area for me is…  What 
about shielded Ethernet cables going up the tower…   I mean your APs are 
grounded (450s, ePMPs, sectors to the tower, yet they would plug into your 
electronics at the bottom of the tower…seemingly linking the two systems 
together regardless of intent.

I have lots of thoughts on that.. from shield kits on each Cat5 wire …to 
isolating antennas with rubber from the tower…. Which we have tried too, LOL.

It all starts to get a bit cloudy in understanding… over the years we have had 
both paid and unpaid “experts” say…absolutely THIS is the way to do it, yet the 
next guy contradicts the former guy more frequently than makes me feel 
comfortable.

Forrest, I hadn’t thought about backing the breaker size down to 15A…. that 
makes sense.   I will definitely try that  the bigger ground cable to see if 
that helps at this site.


From: Af [mailto:af-boun...@afmug.com] On Behalf Of Mark Radabaugh
Sent: Wednesday, April 15, 2015 9:44 PM
To: af@afmug.commailto:af@afmug.com
Subject: Re: [AFMUG] Electrical - Grounding question - long run

For electrical service purposes the ground wire you have is fine.  The tower 
itself obviously needs to be well grounded.

Where is your equipment?  I'm assuming it's at the tower since you talk about 
driving the battery charger.  All of the equipment at the tower needs to be 
bonded together with the tower ground and the electrical ground.

A good 120V surge suppressor at the tower, grounded to the tower ground, will 
help avoid damage from coming in over the power lines.

You are not trying to protect equipment back at the breaker panel.   The ground 
wire size back to the panel is pretty irrelevant as long as it can carry enough 
current to trip the breaker in a short circuit condition.  Other than that it 
doesn't serve much purpose.


Mark

On Apr 15, 2015, at 3:41 PM, Paul McCall 
pa...@pdmnet.netmailto:pa...@pdmnet.net wrote:
In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just built.

We installed a new tower, approximately 200ft. from the service panel that 
feeds it.  We will be on our own breaker (kinda irrelevant here).

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array.

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable.

AND, and this is the big part…  that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger.  How much bigger I am not sure.

So, I figured I would ask the crowd for an answer ☺

Thanks!



Paul McCall, Pres.
PDMNet / Florida Broadband
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800 office
772-473-0352 cell
www.pdmnet.comhttp://www.pdmnet.com/
pa

Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Mike Hammett
Tower ground wasn't sufficient? 

Also, fiber would help keep the surge out of your data path, if only the 
equipment vendors supported it. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Paul McCall pa...@pdmnet.net 
To: af@afmug.com 
Sent: Thursday, April 16, 2015 7:26:29 AM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 



That’s a great answer in theory, but both buildings that we had to be 
disconnected from were thoroughly checked out by a reputable and thorough 
electrician. 

If the tower gets physically hit, the concept is… why induce that surge into 
your electrical ground as well for it to have to deal with? 






From: Af [mailto:af-boun...@afmug.com] On Behalf Of Mike Hammett 
Sent: Thursday, April 16, 2015 8:09 AM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


If your grounding is failing, it is because some piece somewhere isn't big 
enough or connected properly. 



- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 




- Original Message -


From: Paul McCall  pa...@pdmnet.net  
To: af@afmug.com 
Sent: Thursday, April 16, 2015 6:49:24 AM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 
Mark, 

Proposing to bond electrical ground with tower ground at the tower is the 
opposite of what they are saying to do. I know, I know … we have done that 
pretty regularly in the past. We had a coupe towers that got total equipment 
losses a several different times… sometimes multiple times in one lightning 
season. All the potentials were within a couple ohms of each other … 
everywhere. We double, triple checked everything. Still got pounded. 

At the expert’s sugg4estion of not bonding everything together at those 2 
towers, we separated the grounds, and guess what… no more damages (almost 2 
years now) And I understand the concept, but the grey area for me is… What 
about shielded Ethernet cables going up the tower… I mean your APs are grounded 
(450s, ePMPs, sectors to the tower, yet they would plug into your electronics 
at the bottom of the tower…seemingly linking the two systems together 
regardless of intent. 

I have lots of thoughts on that.. from shield kits on each Cat5 wire …to 
isolating antennas with rubber from the tower…. Which we have tried too, LOL. 

It all starts to get a bit cloudy in understanding… over the years we have had 
both paid and unpaid “experts” say…absolutely THIS is the way to do it, yet the 
next guy contradicts the former guy more frequently than makes me feel 
comfortable. 

Forrest, I hadn’t thought about backing the breaker size down to 15A…. that 
makes sense. I will definitely try that  the bigger ground cable to see if 
that helps at this site. 




From: Af [ mailto:af-boun...@afmug.com ] On Behalf Of Mark Radabaugh 
Sent: Wednesday, April 15, 2015 9:44 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


For electrical service purposes the ground wire you have is fine. The tower 
itself obviously needs to be well grounded. 



Where is your equipment? I'm assuming it's at the tower since you talk about 
driving the battery charger. All of the equipment at the tower needs to be 
bonded together with the tower ground and the electrical ground. 



A good 120V surge suppressor at the tower, grounded to the tower ground, will 
help avoid damage from coming in over the power lines. 



You are not trying to protect equipment back at the breaker panel. The ground 
wire size back to the panel is pretty irrelevant as long as it can carry enough 
current to trip the breaker in a short circuit condition. Other than that it 
doesn't serve much purpose. 





Mark 


On Apr 15, 2015, at 3:41 PM, Paul McCall  pa...@pdmnet.net  wrote: 



In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just 
built. 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it. We will be on our own breaker (kinda irrelevant here). 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array. 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable. 

AND, and this is the big part… that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger. How much bigger I am not sure. 

So, I figured I would ask the crowd for an answer J 

Thanks! 



Paul McCall, Pres. 
PDMNet / Florida Broadband 
658 Old Dixie Highway 
Vero Beach, FL 32962 
772-564-6800 office 
772-473-0352 cell 
www.pdmnet.com 
pa...@pdmnet.net 






Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Mike Hammett
You should have had a large copper (I forget the exact size. I thought 4 or 
larger, but someone suggested 0/2.) among tower, equipment and electrical 
ground. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Josh Baird joshba...@gmail.com 
To: af@afmug.com 
Sent: Thursday, April 16, 2015 7:16:55 AM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


We recently had a site where an electrician installed a panel and his own 
ground (rod) for the electrical/AC ground. We then installed our equipment at 
the bottom of the tower and bonded everything in the cabinet to the tower 
ground. This site took a pretty bad strike and it was my understanding that 
this may have happened because the surge traveled through our equipment and out 
of the AC/electrical ground since it was the path of least resistance. 


I am admittedly stupid when it comes to grounding, so, was this actually the 
proper way to ground this site? 


Josh 




On Wed, Apr 15, 2015 at 9:44 PM, Mark Radabaugh  m...@amplex.net  wrote: 




For electrical service purposes the ground wire you have is fine. The tower 
itself obviously needs to be well grounded. 


Where is your equipment? I'm assuming it's at the tower since you talk about 
driving the battery charger. All of the equipment at the tower needs to be 
bonded together with the tower ground and the electrical ground. 


A good 120V surge suppressor at the tower, grounded to the tower ground, will 
help avoid damage from coming in over the power lines. 


You are not trying to protect equipment back at the breaker panel. The ground 
wire size back to the panel is pretty irrelevant as long as it can carry enough 
current to trip the breaker in a short circuit condition. Other than that it 
doesn't serve much purpose. 




Mark 

On Apr 15, 2015, at 3:41 PM, Paul McCall  pa...@pdmnet.net  wrote: 


blockquote



In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just 
built. 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it. We will be on our own breaker (kinda irrelevant here). 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array. 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable. 

AND, and this is the big part… that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger. How much bigger I am not sure. 

So, I figured I would ask the crowd for an answer J 

Thanks! 



Paul McCall, Pres. 
PDMNet / Florida Broadband 
658 Old Dixie Highway 
Vero Beach, FL 32962 
772-564-6800 office 
772-473-0352 cell 
www.pdmnet.com 
pa...@pdmnet.net 



/blockquote




Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Paul McCall
Mark,

Proposing to bond electrical ground with tower ground at the tower is the 
opposite of what they are saying to do.  I know, I know … we have done that 
pretty regularly in the past.  We had a coupe towers that got total equipment 
losses a several different times… sometimes multiple times in one lightning 
season.   All the potentials were within a couple ohms of each other … 
everywhere.  We double, triple checked everything. Still got pounded.

At the expert’s sugg4estion of not bonding everything together at those 2  
towers, we separated the grounds, and guess what… no more damages (almost 2 
years now)  And I understand the concept, but the grey area for me is…  What 
about shielded Ethernet cables going up the tower…   I mean your APs are 
grounded (450s, ePMPs, sectors to the tower, yet they would plug into your 
electronics at the bottom of the tower…seemingly linking the two systems 
together regardless of intent.

I have lots of thoughts on that.. from shield kits on each Cat5 wire …to 
isolating antennas with rubber from the tower…. Which we have tried too, LOL.

It all starts to get a bit cloudy in understanding… over the years we have had 
both paid and unpaid “experts” say…absolutely THIS is the way to do it, yet the 
next guy contradicts the former guy more frequently than makes me feel 
comfortable.

Forrest, I hadn’t thought about backing the breaker size down to 15A…. that 
makes sense.   I will definitely try that  the bigger ground cable to see if 
that helps at this site.


From: Af [mailto:af-boun...@afmug.com] On Behalf Of Mark Radabaugh
Sent: Wednesday, April 15, 2015 9:44 PM
To: af@afmug.com
Subject: Re: [AFMUG] Electrical - Grounding question - long run

For electrical service purposes the ground wire you have is fine.  The tower 
itself obviously needs to be well grounded.

Where is your equipment?  I'm assuming it's at the tower since you talk about 
driving the battery charger.  All of the equipment at the tower needs to be 
bonded together with the tower ground and the electrical ground.

A good 120V surge suppressor at the tower, grounded to the tower ground, will 
help avoid damage from coming in over the power lines.

You are not trying to protect equipment back at the breaker panel.   The ground 
wire size back to the panel is pretty irrelevant as long as it can carry enough 
current to trip the breaker in a short circuit condition.  Other than that it 
doesn't serve much purpose.


Mark

On Apr 15, 2015, at 3:41 PM, Paul McCall 
pa...@pdmnet.netmailto:pa...@pdmnet.net wrote:
In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just built.

We installed a new tower, approximately 200ft. from the service panel that 
feeds it.  We will be on our own breaker (kinda irrelevant here).

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array.

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable.

AND, and this is the big part…  that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger.  How much bigger I am not sure.

So, I figured I would ask the crowd for an answer ☺

Thanks!



Paul McCall, Pres.
PDMNet / Florida Broadband
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800 office
772-473-0352 cell
www.pdmnet.comhttp://www.pdmnet.com/
pa...@pdmnet.netmailto:pa...@pdmnet.net



Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Mike Hammett
If your grounding is failing, it is because some piece somewhere isn't big 
enough or connected properly. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Paul McCall pa...@pdmnet.net 
To: af@afmug.com 
Sent: Thursday, April 16, 2015 6:49:24 AM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 



Mark, 

Proposing to bond electrical ground with tower ground at the tower is the 
opposite of what they are saying to do. I know, I know … we have done that 
pretty regularly in the past. We had a coupe towers that got total equipment 
losses a several different times… sometimes multiple times in one lightning 
season. All the potentials were within a couple ohms of each other … 
everywhere. We double, triple checked everything. Still got pounded. 

At the expert’s sugg4estion of not bonding everything together at those 2 
towers, we separated the grounds, and guess what… no more damages (almost 2 
years now) And I understand the concept, but the grey area for me is… What 
about shielded Ethernet cables going up the tower… I mean your APs are grounded 
(450s, ePMPs, sectors to the tower, yet they would plug into your electronics 
at the bottom of the tower…seemingly linking the two systems together 
regardless of intent. 

I have lots of thoughts on that.. from shield kits on each Cat5 wire …to 
isolating antennas with rubber from the tower…. Which we have tried too, LOL. 

It all starts to get a bit cloudy in understanding… over the years we have had 
both paid and unpaid “experts” say…absolutely THIS is the way to do it, yet the 
next guy contradicts the former guy more frequently than makes me feel 
comfortable. 

Forrest, I hadn’t thought about backing the breaker size down to 15A…. that 
makes sense. I will definitely try that  the bigger ground cable to see if 
that helps at this site. 




From: Af [mailto:af-boun...@afmug.com] On Behalf Of Mark Radabaugh 
Sent: Wednesday, April 15, 2015 9:44 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


For electrical service purposes the ground wire you have is fine. The tower 
itself obviously needs to be well grounded. 



Where is your equipment? I'm assuming it's at the tower since you talk about 
driving the battery charger. All of the equipment at the tower needs to be 
bonded together with the tower ground and the electrical ground. 



A good 120V surge suppressor at the tower, grounded to the tower ground, will 
help avoid damage from coming in over the power lines. 



You are not trying to protect equipment back at the breaker panel. The ground 
wire size back to the panel is pretty irrelevant as long as it can carry enough 
current to trip the breaker in a short circuit condition. Other than that it 
doesn't serve much purpose. 





Mark 


On Apr 15, 2015, at 3:41 PM, Paul McCall  pa...@pdmnet.net  wrote: 



In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just 
built. 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it. We will be on our own breaker (kinda irrelevant here). 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array. 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable. 

AND, and this is the big part… that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger. How much bigger I am not sure. 

So, I figured I would ask the crowd for an answer J 

Thanks! 



Paul McCall, Pres. 
PDMNet / Florida Broadband 
658 Old Dixie Highway 
Vero Beach, FL 32962 
772-564-6800 office 
772-473-0352 cell 
www.pdmnet.com 
pa...@pdmnet.net 





Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Josh Luthman
Yes!!!

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373
On Apr 16, 2015 9:45 AM, Mark Radabaugh m...@amplex.net wrote:

  On 4/16/15 8:29 AM, Mike Hammett wrote:

 Tower ground wasn't sufficient?

 Also, fiber would help keep the surge out of your data path, if only the
 equipment vendors supported it.

  Mike Hammett

 In the spirit of Godwin's law (http://en.wikipedia.org/wiki/Godwin's_law),
 I propose we now have Hammett's law

 As an online discussion grows longer, the probability of the discussion
 invoking SFP's approaches 1

 Mark




Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Mark Radabaugh

On 4/16/15 7:49 AM, Paul McCall wrote:


Mark,

Proposing to bond electrical ground with tower ground at the tower is 
the opposite of what they are saying to do.  I know, I know … we have 
done that pretty regularly in the past.  We had a coupe towers that 
got total equipment losses a several different times… sometimes 
multiple times in one lightning season.  All the potentials were 
within a couple ohms of each other … everywhere.  We double, triple 
checked everything. Still got pounded.


You can leave the electrical ground separate at the tower site if it 
works for you.   I'm pretty convinced that a lot of the damage we see to 
electronics at the base is coming in on the power lines and grounding 
out through the tower (and our equipment) when the tower ground is 
significantly better than the electrical ground.


At the expert’s sugg4estion of not bonding everything together at 
those 2  towers, we separated the grounds, and guess what… no more 
damages (almost 2 years now)  And I understand the concept, but the 
grey area for me is…  What about shielded Ethernet cables going up the 
tower…   I mean your APs are grounded (450s, ePMPs, sectors to the 
tower, yet they would plug into your electronics at the bottom of the 
tower…seemingly linking the two systems together regardless of intent.


I usually do shielded cable with the shield open (not connected to 
anything) at the top and  grounded to the tower ground at the base.   It 
seems to work pretty well for us.


I have lots of thoughts on that.. from shield kits on each Cat5 wire 
…to isolating antennas with rubber from the tower…. Which we have 
tried too, LOL.


I have had isolated antennas pick up huge static charges and blow out 
equipment - but only on one specific tower.  It was weird. Grounded that 
setup to the tower and the problem went away - but we have plenty of 
other LMG Cyclone equipment where the case is ungrounded due to the 
plastic blocks that are part of the mount that have no issues.


It all starts to get a bit cloudy in understanding… over the years we 
have had both paid and unpaid “experts” say…absolutely THIS is the way 
to do it, yet the next guy contradicts the former guy more frequently 
than makes me feel comfortable.


Yup.   I tried researching all of this and bought a bunch of books on 
lightning, grounding, etc..  They all seem to agree on grounding 
everything together at a single point, yet as we have all found what 
works at one site doesn't seem to work at the next site.


Mark


Forrest, I hadn’t thought about backing the breaker size down to 15A…. 
that makes sense.   I will definitely try that  the bigger ground 
cable to see if that helps at this site.







Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Mark Radabaugh

On 4/16/15 8:16 AM, Josh Baird wrote:
We recently had a site where an electrician installed a panel and his 
own ground (rod) for the electrical/AC ground.  We then installed our 
equipment at the bottom of the tower and bonded everything in the 
cabinet to the tower ground. This site took a pretty bad strike and it 
was my understanding that this may have happened because the surge 
traveled through our equipment and out of the AC/electrical ground 
since it was the path of least resistance.


What equipment did you lose?  AP's at the top or equipment at the base?

The ground the electricians put in is usually crap.   Code tells them 
they have to run a ground rod - so they do.  If your lucky they might 
even tighten the acorn nut on the ground rod.   They are not required to 
check that the ground rod actually works or anything.


I would tie that ground rod back to your central ground point.

Mark


I am admittedly stupid when it comes to grounding, so, was this 
actually the proper way to ground this site?


Josh





Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Jaime Solorza
We install a separate grounding system for our SCADA masts and towers.
Ground rods and wire.  We do Not bond to the halo or triangle grid which
protects the RTU stuff.  We used cable grounding kit on Heliax .   We
insert a polyphaser in between cable and pigtail.  The radio power is
protected by terminal block fuses. Then surge protection on LAN ports
so far it has worked well
Jaime Solorza
On Apr 16, 2015 7:26 AM, Paul McCall pa...@pdmnet.net wrote:

  That’s a great answer in theory, but both buildings that we had to be
 disconnected from were thoroughly checked out by a reputable and thorough
 electrician.



 If the tower gets physically hit, the concept is… why induce that surge
 into your electrical ground as well for it to have to deal with?









 *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Mike Hammett
 *Sent:* Thursday, April 16, 2015 8:09 AM
 *To:* af@afmug.com
 *Subject:* Re: [AFMUG] Electrical - Grounding question - long run



 If your grounding is failing, it is because some piece somewhere isn't big
 enough or connected properly.



 -
 Mike Hammett
 Intelligent Computing Solutions
 http://www.ics-il.com

  https://www.facebook.com/ICSIL
 https://plus.google.com/+IntelligentComputingSolutionsDeKalb
 https://www.linkedin.com/company/intelligent-computing-solutions
 https://twitter.com/ICSIL

   --

 *From: *Paul McCall pa...@pdmnet.net
 *To: *af@afmug.com
 *Sent: *Thursday, April 16, 2015 6:49:24 AM
 *Subject: *Re: [AFMUG] Electrical - Grounding question - long run

 Mark,



 Proposing to bond electrical ground with tower ground at the tower is the
 opposite of what they are saying to do.  I know, I know … we have done that
 pretty regularly in the past.  We had a coupe towers that got total
 equipment losses a several different times… sometimes multiple times in one
 lightning season.   All the potentials were within a couple ohms of each
 other … everywhere.  We double, triple checked everything. Still got
 pounded.



 At the expert’s sugg4estion of not bonding everything together at those 2
  towers, we separated the grounds, and guess what… no more damages (almost
 2 years now)  And I understand the concept, but the grey area for me is…
 What about shielded Ethernet cables going up the tower…   I mean your APs
 are grounded (450s, ePMPs, sectors to the tower, yet they would plug into
 your electronics at the bottom of the tower…seemingly linking the two
 systems together regardless of intent.



 I have lots of thoughts on that.. from shield kits on each Cat5 wire …to
 isolating antennas with rubber from the tower…. Which we have tried too,
 LOL.



 It all starts to get a bit cloudy in understanding… over the years we have
 had both paid and unpaid “experts” say…absolutely THIS is the way to do it,
 yet the next guy contradicts the former guy more frequently than makes me
 feel comfortable.



 Forrest, I hadn’t thought about backing the breaker size down to 15A….
 that makes sense.   I will definitely try that  the bigger ground cable to
 see if that helps at this site.





 *From:* Af [mailto:af-boun...@afmug.com af-boun...@afmug.com] *On
 Behalf Of *Mark Radabaugh
 *Sent:* Wednesday, April 15, 2015 9:44 PM
 *To:* af@afmug.com
 *Subject:* Re: [AFMUG] Electrical - Grounding question - long run



 For electrical service purposes the ground wire you have is fine.  The
 tower itself obviously needs to be well grounded.



 Where is your equipment?  I'm assuming it's at the tower since you talk
 about driving the battery charger.  All of the equipment at the tower needs
 to be bonded together with the tower ground and the electrical ground.



 A good 120V surge suppressor at the tower, grounded to the tower ground,
 will help avoid damage from coming in over the power lines.



 You are not trying to protect equipment back at the breaker panel.   The
 ground wire size back to the panel is pretty irrelevant as long as it can
 carry enough current to trip the breaker in a short circuit condition.
  Other than that it doesn't serve much purpose.





 Mark


 On Apr 15, 2015, at 3:41 PM, Paul McCall pa...@pdmnet.net wrote:

  In my continued disposition of acknowledging that I am not a electrical
 grounding expert, I lay out this scenario for review, a new tower we just
 built.



 We installed a new tower, approximately 200ft. from the service panel that
 feeds it.  We will be on our own breaker (kinda irrelevant here).



 In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.
 Voltage drop is relatively negligible, certainly within the bounds of
 working properly to drive our 24v charger for the battery array.



 I was told, by a grounding “expert” that all my equipment electrical
 grounds need to homerun to a bus bar that ride the ground back to the
 service panel directly, that nothing else is acceptable.



 AND, and this is the big part…  that I needed to seriously upgrade the
 200ft. ground wire only

Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Mark Radabaugh

On 4/16/15 8:29 AM, Mike Hammett wrote:

Tower ground wasn't sufficient?

Also, fiber would help keep the surge out of your data path, if only 
the equipment vendors supported it.

Mike Hammett
In the spirit of Godwin's law 
(http://en.wikipedia.org/wiki/Godwin's_law), I propose we now have 
Hammett's law


As an online discussion grows longer, the probability of the discussion 
invoking SFP's approaches 1


Mark



Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Josh Baird
We lost a few AP's (450s, ugh) at the top, and a few SyncInjectors at the
base.  The AP's were going through WB SP's at the base in our cabinet
before they went into the SyncInjectors.

Ok - so really, EVERYTHING should be tied together.  It would seem that in
our scenario, the electrical ground was grounded to our central grounding
point (thus the tower and our equipment) only through our equipment, not
directly.  So, running a large-ish ground directly from the electrical
ground to our central grounding point seems appropriate here.

On Thu, Apr 16, 2015 at 9:41 AM, Mark Radabaugh m...@amplex.net wrote:

 On 4/16/15 8:16 AM, Josh Baird wrote:

 We recently had a site where an electrician installed a panel and his own
 ground (rod) for the electrical/AC ground.  We then installed our equipment
 at the bottom of the tower and bonded everything in the cabinet to the
 tower ground. This site took a pretty bad strike and it was my
 understanding that this may have happened because the surge traveled
 through our equipment and out of the AC/electrical ground since it was the
 path of least resistance.


 What equipment did you lose?  AP's at the top or equipment at the base?

 The ground the electricians put in is usually crap.   Code tells them they
 have to run a ground rod - so they do.  If your lucky they might even
 tighten the acorn nut on the ground rod.   They are not required to check
 that the ground rod actually works or anything.

 I would tie that ground rod back to your central ground point.

 Mark


 I am admittedly stupid when it comes to grounding, so, was this actually
 the proper way to ground this site?

 Josh





Re: [AFMUG] Electrical - Grounding question - long run

2015-04-16 Thread Mike Hammett
Nazi... 

;-) 






- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Mark Radabaugh m...@amplex.net 
To: af@afmug.com 
Sent: Thursday, April 16, 2015 8:45:52 AM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


On 4/16/15 8:29 AM, Mike Hammett wrote: 



Tower ground wasn't sufficient? 

Also, fiber would help keep the surge out of your data path, if only the 
equipment vendors supported it. 



blockquote


Mike Hammett 

/blockquote
In the spirit of Godwin's law ( http://en.wikipedia.org/wiki/Godwin's_law ), 
I propose we now have Hammett's law 

As an online discussion grows longer, the probability of the discussion 
invoking SFP's approaches 1 

Mark 




Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Mike Hammett
Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Paul McCall pa...@pdmnet.net 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 2:41:15 PM 
Subject: [AFMUG] Electrical - Grounding question - long run 



In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just 
built. 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it. We will be on our own breaker (kinda irrelevant here). 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array. 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable. 

AND, and this is the big part… that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger. How much bigger I am not sure. 

So, I figured I would ask the crowd for an answer J 

Thanks! 



Paul McCall, Pres. 
PDMNet / Florida Broadband 
658 Old Dixie Highway 
Vero Beach, FL 32962 
772-564-6800 office 
772-473-0352 cell 
www.pdmnet.com 
pa...@pdmnet.net 



Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Chuck McCown
The purpose of a ground wire is to ensure the breaker trips during a fault.  
Common/single point grounding is always highly recommended.  
I don’t have my NEC book handy, but they don’t need to be larger than a #6 and 
probably no larger than your #10 based on the circuit you are protecting.  
Perhaps smaller.Of course this has nothing to do with lightening or surge 
suppression.  

From: Paul McCall 
Sent: Wednesday, April 15, 2015 1:41 PM
To: af@afmug.com 
Subject: [AFMUG] Electrical - Grounding question - long run

In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just built.

 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it.  We will be on our own breaker (kinda irrelevant here).

 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array.

 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable.

 

AND, and this is the big part…  that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger.  How much bigger I am not sure.

 

So, I figured I would ask the crowd for an answer J

 

Thanks!

 

 

 

Paul McCall, Pres.

PDMNet / Florida Broadband 

658 Old Dixie Highway

Vero Beach, FL 32962

772-564-6800 office

772-473-0352 cell

www.pdmnet.com

pa...@pdmnet.net

 


Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Chuck McCown
For a 30 amp circuit?

From: Mike Hammett 
Sent: Wednesday, April 15, 2015 1:58 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds.




-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com







From: Paul McCall pa...@pdmnet.net
To: af@afmug.com
Sent: Wednesday, April 15, 2015 2:41:15 PM
Subject: [AFMUG] Electrical - Grounding question - long run


In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just built.



We installed a new tower, approximately 200ft. from the service panel that 
feeds it.  We will be on our own breaker (kinda irrelevant here).



In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array.



I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable.



AND, and this is the big part…  that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger.  How much bigger I am not sure.



So, I figured I would ask the crowd for an answer J



Thanks!







Paul McCall, Pres.

PDMNet / Florida Broadband 

658 Old Dixie Highway

Vero Beach, FL 32962

772-564-6800 office

772-473-0352 cell

www.pdmnet.com

pa...@pdmnet.net





Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Mike Hammett
Amperage is irrelevant, well, unless it's larger than the gauge I recommended. 
It's not an inside-home outlet, but bonding the ground between the electrical 
service and the equipment\tower. You don't want your tower ground to be better 
than your electrical service ground and have a surge decide the best path is 
through the electric (+ or neutral) and thus your equipment. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Chuck McCown ch...@wbmfg.com 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 3:01:06 PM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 




For a 30 amp circuit? 




From: Mike Hammett 
Sent: Wednesday, April 15, 2015 1:58 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Paul McCall pa...@pdmnet.net 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 2:41:15 PM 
Subject: [AFMUG] Electrical - Grounding question - long run 



In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just 
built. 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it. We will be on our own breaker (kinda irrelevant here). 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array. 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable. 

AND, and this is the big part… that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger. How much bigger I am not sure. 

So, I figured I would ask the crowd for an answer J 

Thanks! 



Paul McCall, Pres. 
PDMNet / Florida Broadband 
658 Old Dixie Highway 
Vero Beach, FL 32962 
772-564-6800 office 
772-473-0352 cell 
www.pdmnet.com 
pa...@pdmnet.net 




Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Jeremy
We usually put a breaker at the tower and then put in our own ground at the
tower and bond it to electrical ground.  No idea if this is the right way
to do it but you definitely don't want your only ground to be 200' away,
right?

On Wed, Apr 15, 2015 at 2:03 PM, Mike Hammett af...@ics-il.net wrote:

 Amperage is irrelevant, well, unless it's larger than the gauge I
 recommended. It's not an inside-home outlet, but bonding the ground between
 the electrical service and the equipment\tower. You don't want your tower
 ground to be better than your electrical service ground and have a surge
 decide the best path is through the electric (+ or neutral) and thus your
 equipment.



 -
 Mike Hammett
 Intelligent Computing Solutions
 http://www.ics-il.com

 https://www.facebook.com/ICSIL
 https://plus.google.com/+IntelligentComputingSolutionsDeKalb
 https://www.linkedin.com/company/intelligent-computing-solutions
 https://twitter.com/ICSIL

 --
 *From: *Chuck McCown ch...@wbmfg.com
 *To: *af@afmug.com
 *Sent: *Wednesday, April 15, 2015 3:01:06 PM

 *Subject: *Re: [AFMUG] Electrical - Grounding question - long run

  For a 30 amp circuit?

  *From:* Mike Hammett af...@ics-il.net
 *Sent:* Wednesday, April 15, 2015 1:58 PM
 *To:* af@afmug.com
 *Subject:* Re: [AFMUG] Electrical - Grounding question - long run

  Your ground should be at least 4 gauge, maybe even larger than that. One
 of the 0/x gauges is in my mind for some reason. That should bond the
 electrical ground with all tower and equipment grounds.



 -
 Mike Hammett
 Intelligent Computing Solutions
 http://www.ics-il.com

 https://www.facebook.com/ICSIL
 https://plus.google.com/+IntelligentComputingSolutionsDeKalb
 https://www.linkedin.com/company/intelligent-computing-solutions
 https://twitter.com/ICSIL

 --
 *From: *Paul McCall pa...@pdmnet.net
 *To: *af@afmug.com
 *Sent: *Wednesday, April 15, 2015 2:41:15 PM
 *Subject: *[AFMUG] Electrical - Grounding question - long run

  In my continued disposition of acknowledging that I am not a electrical
 grounding expert, I lay out this scenario for review, a new tower we just
 built.



 We installed a new tower, approximately 200ft. from the service panel that
 feeds it.  We will be on our own breaker (kinda irrelevant here).



 In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.
 Voltage drop is relatively negligible, certainly within the bounds of
 working properly to drive our 24v charger for the battery array.



 I was told, by a grounding “expert” that all my equipment electrical
 grounds need to homerun to a bus bar that ride the ground back to the
 service panel directly, that nothing else is acceptable.



 AND, and this is the big part…  that I needed to seriously upgrade the
 200ft. ground wire only that rides back to the panel to something
 significantly bigger.  How much bigger I am not sure.



 So, I figured I would ask the crowd for an answer J



 Thanks!







 Paul McCall, Pres.

 PDMNet / Florida Broadband

 658 Old Dixie Highway

 Vero Beach, FL 32962

 772-564-6800 office

 772-473-0352 cell

 www.pdmnet.com

 pa...@pdmnet.net







Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Chuck McCown
So, you are hanging a receptacle on a tower.  30 amp  10 gauge.  
You want a 4 gauge ground?  I understanding bonding the tower to a common bond 
point with a large gauge wire.  But the three wires run in some liquidtite or 
conduit can be smaller.  How about only hot and neutral inside EMT.  If the 
only goal is to get a safe receptacle at the top of the tower I would thing 
that would suffice as long as the tower itself is bonded properly.  No?

From: Mike Hammett 
Sent: Wednesday, April 15, 2015 2:03 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Amperage is irrelevant, well, unless it's larger than the gauge I recommended. 
It's not an inside-home outlet, but bonding the ground between the electrical 
service and the equipment\tower. You don't want your tower ground to be better 
than your electrical service ground and have a surge decide the best path is 
through the electric (+ or neutral) and thus your equipment.




-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com







From: Chuck McCown ch...@wbmfg.com
To: af@afmug.com
Sent: Wednesday, April 15, 2015 3:01:06 PM
Subject: Re: [AFMUG] Electrical - Grounding question - long run


For a 30 amp circuit?

From: Mike Hammett 
Sent: Wednesday, April 15, 2015 1:58 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds.




-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com







From: Paul McCall pa...@pdmnet.net
To: af@afmug.com
Sent: Wednesday, April 15, 2015 2:41:15 PM
Subject: [AFMUG] Electrical - Grounding question - long run


In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just built.



We installed a new tower, approximately 200ft. from the service panel that 
feeds it.  We will be on our own breaker (kinda irrelevant here).



In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array.



I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable.



AND, and this is the big part…  that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger.  How much bigger I am not sure.



So, I figured I would ask the crowd for an answer J



Thanks!







Paul McCall, Pres.

PDMNet / Florida Broadband 

658 Old Dixie Highway

Vero Beach, FL 32962

772-564-6800 office

772-473-0352 cell

www.pdmnet.com

pa...@pdmnet.net






Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Mike Hammett
I'm referring to 200' between the tower and your service. Those need to be 
large. UP the tower? Whatever that requirement would be. 10 gauge may be fine. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Chuck McCown ch...@wbmfg.com 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 3:07:47 PM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 




So, you are hanging a receptacle on a tower. 30 amp 10 gauge. 
You want a 4 gauge ground? I understanding bonding the tower to a common bond 
point with a large gauge wire. But the three wires run in some liquidtite or 
conduit can be smaller. How about only hot and neutral inside EMT. If the only 
goal is to get a safe receptacle at the top of the tower I would thing that 
would suffice as long as the tower itself is bonded properly. No? 




From: Mike Hammett 
Sent: Wednesday, April 15, 2015 2:03 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


Amperage is irrelevant, well, unless it's larger than the gauge I recommended. 
It's not an inside-home outlet, but bonding the ground between the electrical 
service and the equipment\tower. You don't want your tower ground to be better 
than your electrical service ground and have a surge decide the best path is 
through the electric (+ or neutral) and thus your equipment. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Chuck McCown ch...@wbmfg.com 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 3:01:06 PM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 




For a 30 amp circuit? 




From: Mike Hammett 
Sent: Wednesday, April 15, 2015 1:58 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Paul McCall pa...@pdmnet.net 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 2:41:15 PM 
Subject: [AFMUG] Electrical - Grounding question - long run 



In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just 
built. 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it. We will be on our own breaker (kinda irrelevant here). 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array. 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable. 

AND, and this is the big part… that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger. How much bigger I am not sure. 

So, I figured I would ask the crowd for an answer J 

Thanks! 



Paul McCall, Pres. 
PDMNet / Florida Broadband 
658 Old Dixie Highway 
Vero Beach, FL 32962 
772-564-6800 office 
772-473-0352 cell 
www.pdmnet.com 
pa...@pdmnet.net 





Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Chuck McCown
Ahhh, didn’t catch that the tower was 200’ from the service.  I see...

From: Mike Hammett 
Sent: Wednesday, April 15, 2015 2:14 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run

I'm referring to 200' between the tower and your service. Those need to be 
large. UP the tower? Whatever that requirement would be. 10 gauge may be fine.




-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com







From: Chuck McCown ch...@wbmfg.com
To: af@afmug.com
Sent: Wednesday, April 15, 2015 3:07:47 PM
Subject: Re: [AFMUG] Electrical - Grounding question - long run


So, you are hanging a receptacle on a tower.  30 amp  10 gauge.  
You want a 4 gauge ground?  I understanding bonding the tower to a common bond 
point with a large gauge wire.  But the three wires run in some liquidtite or 
conduit can be smaller.  How about only hot and neutral inside EMT.  If the 
only goal is to get a safe receptacle at the top of the tower I would thing 
that would suffice as long as the tower itself is bonded properly.  No?

From: Mike Hammett 
Sent: Wednesday, April 15, 2015 2:03 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Amperage is irrelevant, well, unless it's larger than the gauge I recommended. 
It's not an inside-home outlet, but bonding the ground between the electrical 
service and the equipment\tower. You don't want your tower ground to be better 
than your electrical service ground and have a surge decide the best path is 
through the electric (+ or neutral) and thus your equipment.




-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com







From: Chuck McCown ch...@wbmfg.com
To: af@afmug.com
Sent: Wednesday, April 15, 2015 3:01:06 PM
Subject: Re: [AFMUG] Electrical - Grounding question - long run


For a 30 amp circuit?

From: Mike Hammett 
Sent: Wednesday, April 15, 2015 1:58 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds.




-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com







From: Paul McCall pa...@pdmnet.net
To: af@afmug.com
Sent: Wednesday, April 15, 2015 2:41:15 PM
Subject: [AFMUG] Electrical - Grounding question - long run


In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just built.



We installed a new tower, approximately 200ft. from the service panel that 
feeds it.  We will be on our own breaker (kinda irrelevant here).



In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array.



I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable.



AND, and this is the big part…  that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger.  How much bigger I am not sure.



So, I figured I would ask the crowd for an answer J



Thanks!







Paul McCall, Pres.

PDMNet / Florida Broadband 

658 Old Dixie Highway

Vero Beach, FL 32962

772-564-6800 office

772-473-0352 cell

www.pdmnet.com

pa...@pdmnet.net







Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Mike Hammett
I didn't think you'd be wrong. Just missed a piece of info in the original 
post. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Chuck McCown ch...@wbmfg.com 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 3:15:29 PM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 




Ahhh, didn’t catch that the tower was 200’ from the service. I see... 




From: Mike Hammett 
Sent: Wednesday, April 15, 2015 2:14 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


I'm referring to 200' between the tower and your service. Those need to be 
large. UP the tower? Whatever that requirement would be. 10 gauge may be fine. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Chuck McCown ch...@wbmfg.com 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 3:07:47 PM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 




So, you are hanging a receptacle on a tower. 30 amp 10 gauge. 
You want a 4 gauge ground? I understanding bonding the tower to a common bond 
point with a large gauge wire. But the three wires run in some liquidtite or 
conduit can be smaller. How about only hot and neutral inside EMT. If the only 
goal is to get a safe receptacle at the top of the tower I would thing that 
would suffice as long as the tower itself is bonded properly. No? 




From: Mike Hammett 
Sent: Wednesday, April 15, 2015 2:03 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


Amperage is irrelevant, well, unless it's larger than the gauge I recommended. 
It's not an inside-home outlet, but bonding the ground between the electrical 
service and the equipment\tower. You don't want your tower ground to be better 
than your electrical service ground and have a surge decide the best path is 
through the electric (+ or neutral) and thus your equipment. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Chuck McCown ch...@wbmfg.com 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 3:01:06 PM 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 




For a 30 amp circuit? 




From: Mike Hammett 
Sent: Wednesday, April 15, 2015 1:58 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] Electrical - Grounding question - long run 


Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds. 




- 
Mike Hammett 
Intelligent Computing Solutions 
http://www.ics-il.com 



- Original Message -

From: Paul McCall pa...@pdmnet.net 
To: af@afmug.com 
Sent: Wednesday, April 15, 2015 2:41:15 PM 
Subject: [AFMUG] Electrical - Grounding question - long run 



In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just 
built. 

We installed a new tower, approximately 200ft. from the service panel that 
feeds it. We will be on our own breaker (kinda irrelevant here). 

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array. 

I was told, by a grounding “expert” that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable. 

AND, and this is the big part… that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger. How much bigger I am not sure. 

So, I figured I would ask the crowd for an answer J 

Thanks! 



Paul McCall, Pres. 
PDMNet / Florida Broadband 
658 Old Dixie Highway 
Vero Beach, FL 32962 
772-564-6800 office 
772-473-0352 cell 
www.pdmnet.com 
pa...@pdmnet.net 






Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Larry Smith
Hmmm, not an electrical person either, but quick search online
says #6 gauge highly recommended for 200' run vice the #10 you 
mention.

-- 
Larry Smith
lesm...@ecsis.net

On Wed April 15 2015 14:41, Paul McCall wrote:
 In my continued disposition of acknowledging that I am not a electrical
 grounding expert, I lay out this scenario for review, a new tower we just
 built.

 We installed a new tower, approximately 200ft. from the service panel that
 feeds it.  We will be on our own breaker (kinda irrelevant here).

 In the past, we had run 10 gauge wire (x3) out to the tower with 110vac. 
 Voltage drop is relatively negligible, certainly within the bounds of
 working properly to drive our 24v charger for the battery array.

 I was told, by a grounding expert that all my equipment electrical
 grounds need to homerun to a bus bar that ride the ground back to the
 service panel directly, that nothing else is acceptable.

 AND, and this is the big part...  that I needed to seriously upgrade the
 200ft. ground wire only that rides back to the panel to something
 significantly bigger.  How much bigger I am not sure.

 So, I figured I would ask the crowd for an answer :)

 Thanks!



 Paul McCall, Pres.
 PDMNet / Florida Broadband
 658 Old Dixie Highway
 Vero Beach, FL 32962
 772-564-6800 office
 772-473-0352 cell
 www.pdmnet.comhttp://www.pdmnet.com/
 pa...@pdmnet.netmailto:pa...@pdmnet.net


[AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Paul McCall
In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario for review, a new tower we just built.

We installed a new tower, approximately 200ft. from the service panel that 
feeds it.  We will be on our own breaker (kinda irrelevant here).

In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
Voltage drop is relatively negligible, certainly within the bounds of working 
properly to drive our 24v charger for the battery array.

I was told, by a grounding expert that all my equipment electrical grounds 
need to homerun to a bus bar that ride the ground back to the service panel 
directly, that nothing else is acceptable.

AND, and this is the big part...  that I needed to seriously upgrade the 200ft. 
ground wire only that rides back to the panel to something significantly 
bigger.  How much bigger I am not sure.

So, I figured I would ask the crowd for an answer :)

Thanks!



Paul McCall, Pres.
PDMNet / Florida Broadband
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800 office
772-473-0352 cell
www.pdmnet.comhttp://www.pdmnet.com/
pa...@pdmnet.netmailto:pa...@pdmnet.net



Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Paul McCall
4 gauge was what I was considering.  We run a polyphaser on the AC at the tower 
box as well, as our “receptacle”


From: Af [mailto:af-boun...@afmug.com] On Behalf Of Mike Hammett
Sent: Wednesday, April 15, 2015 4:20 PM
To: af@afmug.com
Subject: Re: [AFMUG] Electrical - Grounding question - long run

I didn't think you'd be wrong. Just missed a piece of info in the original post.


-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com

[http://www.ics-il.com/images/fbicon.png]https://www.facebook.com/ICSIL[http://www.ics-il.com/images/googleicon.png]https://plus.google.com/+IntelligentComputingSolutionsDeKalb[http://www.ics-il.com/images/linkedinicon.png]https://www.linkedin.com/company/intelligent-computing-solutions[http://www.ics-il.com/images/twittericon.png]https://twitter.com/ICSIL


From: Chuck McCown ch...@wbmfg.commailto:ch...@wbmfg.com
To: af@afmug.commailto:af@afmug.com
Sent: Wednesday, April 15, 2015 3:15:29 PM
Subject: Re: [AFMUG] Electrical - Grounding question - long run
Ahhh, didn’t catch that the tower was 200’ from the service.  I see...

From: Mike Hammettmailto:af...@ics-il.net
Sent: Wednesday, April 15, 2015 2:14 PM
To: af@afmug.commailto:af@afmug.com
Subject: Re: [AFMUG] Electrical - Grounding question - long run

I'm referring to 200' between the tower and your service. Those need to be 
large. UP the tower? Whatever that requirement would be. 10 gauge may be fine.


-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com

[http://www.ics-il.com/images/fbicon.png]https://www.facebook.com/ICSIL[http://www.ics-il.com/images/googleicon.png]https://plus.google.com/+IntelligentComputingSolutionsDeKalb[http://www.ics-il.com/images/linkedinicon.png]https://www.linkedin.com/company/intelligent-computing-solutions[http://www.ics-il.com/images/twittericon.png]https://twitter.com/ICSIL

From: Chuck McCown ch...@wbmfg.commailto:ch...@wbmfg.com
To: af@afmug.commailto:af@afmug.com
Sent: Wednesday, April 15, 2015 3:07:47 PM
Subject: Re: [AFMUG] Electrical - Grounding question - long run
So, you are hanging a receptacle on a tower.  30 amp  10 gauge.
You want a 4 gauge ground?  I understanding bonding the tower to a common bond 
point with a large gauge wire.  But the three wires run in some liquidtite or 
conduit can be smaller.  How about only hot and neutral inside EMT.  If the 
only goal is to get a safe receptacle at the top of the tower I would thing 
that would suffice as long as the tower itself is bonded properly.  No?

From: Mike Hammettmailto:af...@ics-il.net
Sent: Wednesday, April 15, 2015 2:03 PM
To: af@afmug.commailto:af@afmug.com
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Amperage is irrelevant, well, unless it's larger than the gauge I recommended. 
It's not an inside-home outlet, but bonding the ground between the electrical 
service and the equipment\tower. You don't want your tower ground to be better 
than your electrical service ground and have a surge decide the best path is 
through the electric (+ or neutral) and thus your equipment.


-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com

[http://www.ics-il.com/images/fbicon.png]https://www.facebook.com/ICSIL[http://www.ics-il.com/images/googleicon.png]https://plus.google.com/+IntelligentComputingSolutionsDeKalb[http://www.ics-il.com/images/linkedinicon.png]https://www.linkedin.com/company/intelligent-computing-solutions[http://www.ics-il.com/images/twittericon.png]https://twitter.com/ICSIL

From: Chuck McCown ch...@wbmfg.commailto:ch...@wbmfg.com
To: af@afmug.commailto:af@afmug.com
Sent: Wednesday, April 15, 2015 3:01:06 PM
Subject: Re: [AFMUG] Electrical - Grounding question - long run
For a 30 amp circuit?

From: Mike Hammettmailto:af...@ics-il.net
Sent: Wednesday, April 15, 2015 1:58 PM
To: af@afmug.commailto:af@afmug.com
Subject: Re: [AFMUG] Electrical - Grounding question - long run

Your ground should be at least 4 gauge, maybe even larger than that. One of the 
0/x gauges is in my mind for some reason. That should bond the electrical 
ground with all tower and equipment grounds.


-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com

[http://www.ics-il.com/images/fbicon.png]https://www.facebook.com/ICSIL[http://www.ics-il.com/images/googleicon.png]https://plus.google.com/+IntelligentComputingSolutionsDeKalb[http://www.ics-il.com/images/linkedinicon.png]https://www.linkedin.com/company/intelligent-computing-solutions[http://www.ics-il.com/images/twittericon.png]https://twitter.com/ICSIL

From: Paul McCall pa...@pdmnet.netmailto:pa...@pdmnet.net
To: af@afmug.commailto:af@afmug.com
Sent: Wednesday, April 15, 2015 2:41:15 PM
Subject: [AFMUG] Electrical - Grounding question - long run
In my continued disposition of acknowledging that I am not a electrical 
grounding expert, I lay out this scenario

Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Mark Radabaugh
For electrical service purposes the ground wire you have is fine.  The tower 
itself obviously needs to be well grounded.

Where is your equipment?  I'm assuming it's at the tower since you talk about 
driving the battery charger.  All of the equipment at the tower needs to be 
bonded together with the tower ground and the electrical ground.

A good 120V surge suppressor at the tower, grounded to the tower ground, will 
help avoid damage from coming in over the power lines.

You are not trying to protect equipment back at the breaker panel.   The ground 
wire size back to the panel is pretty irrelevant as long as it can carry enough 
current to trip the breaker in a short circuit condition.  Other than that it 
doesn't serve much purpose. 


Mark

 On Apr 15, 2015, at 3:41 PM, Paul McCall pa...@pdmnet.net wrote:
 
 In my continued disposition of acknowledging that I am not a electrical 
 grounding expert, I lay out this scenario for review, a new tower we just 
 built.
  
 We installed a new tower, approximately 200ft. from the service panel that 
 feeds it.  We will be on our own breaker (kinda irrelevant here).
  
 In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.  
 Voltage drop is relatively negligible, certainly within the bounds of working 
 properly to drive our 24v charger for the battery array.
  
 I was told, by a grounding “expert” that all my equipment electrical grounds 
 need to homerun to a bus bar that ride the ground back to the service panel 
 directly, that nothing else is acceptable.
  
 AND, and this is the big part…  that I needed to seriously upgrade the 200ft. 
 ground wire only that rides back to the panel to something significantly 
 bigger.  How much bigger I am not sure.
  
 So, I figured I would ask the crowd for an answer  J
  
 Thanks!
  
  
  
 Paul McCall, Pres.
 PDMNet / Florida Broadband
 658 Old Dixie Highway
 Vero Beach, FL 32962
 772-564-6800 office
 772-473-0352 cell
 www.pdmnet.com
 pa...@pdmnet.net
  


Re: [AFMUG] Electrical - Grounding question - long run

2015-04-15 Thread Forrest Christian (List Account)
Mark's answer matches what my recommendation would be.

I'd just use the same sized conductor for ground that you used for the
circuit itself, and make sure that the breaker is sized correctly (meaning
not too large) for the wire run.   I would probably put a 15A breaker in
back at the panel, even with a 10GA run, unless you needed 15A for some
reason, at which point I'd run 230V and step it down at the tower.The
purpose of sizing the breaker down is to better match the actual capacity
of the circuit at that distance.

It sounds like the expert in this case has somehow gotten the idea that the
only acceptable solution is to have a single low-impedance ground system
which encompasses the entire system, including the panel.  To do this
effectively, you *would* have to have a large conductor so that effectively
all grounding points are electrically identical.  However, in this case,
it's probably better to treat it as two separate grounding systems, with a
higher-impedance (resistance) grounding path between them which will serve
the purpose of allowing the circuit breaker to clear a phase-to-ground
fault by tripping, but not encourage surges to travel between the two
systems - you want tower system surges to go into the tower ground, and the
electrical system surges to go into the electrical ground.   Alternatively
you could include a transformer at the tower end to separate the grounds
completely - See separately dervived ground in the code.   You'd have to
take care to ensure the ground is truly isolated, but I think this is
excessive.

-forrest


For longer

On Wed, Apr 15, 2015 at 7:44 PM, Mark Radabaugh m...@amplex.net wrote:

 For electrical service purposes the ground wire you have is fine.  The
 tower itself obviously needs to be well grounded.

 Where is your equipment?  I'm assuming it's at the tower since you talk
 about driving the battery charger.  All of the equipment at the tower needs
 to be bonded together with the tower ground and the electrical ground.

 A good 120V surge suppressor at the tower, grounded to the tower ground,
 will help avoid damage from coming in over the power lines.

 You are not trying to protect equipment back at the breaker panel.   The
 ground wire size back to the panel is pretty irrelevant as long as it can
 carry enough current to trip the breaker in a short circuit condition.
 Other than that it doesn't serve much purpose.


 Mark

 On Apr 15, 2015, at 3:41 PM, Paul McCall pa...@pdmnet.net wrote:

  In my continued disposition of acknowledging that I am not a electrical
 grounding expert, I lay out this scenario for review, a new tower we just
 built.



 We installed a new tower, approximately 200ft. from the service panel that
 feeds it.  We will be on our own breaker (kinda irrelevant here).



 In the past, we had run 10 gauge wire (x3) out to the tower with 110vac.
 Voltage drop is relatively negligible, certainly within the bounds of
 working properly to drive our 24v charger for the battery array.



 I was told, by a grounding “expert” that all my equipment electrical
 grounds need to homerun to a bus bar that ride the ground back to the
 service panel directly, that nothing else is acceptable.



 AND, and this is the big part…  that I needed to seriously upgrade the
 200ft. ground wire only that rides back to the panel to something
 significantly bigger.  How much bigger I am not sure.



 So, I figured I would ask the crowd for an answer J



 Thanks!







 Paul McCall, Pres.

 PDMNet / Florida Broadband

 658 Old Dixie Highway

 Vero Beach, FL 32962

 772-564-6800 office

 772-473-0352 cell

 www.pdmnet.com

 pa...@pdmnet.net






-- 
*Forrest Christian* *CEO**, PacketFlux Technologies, Inc.*
Tel: 406-449-3345 | Address: 3577 Countryside Road, Helena, MT 59602
forre...@imach.com | http://www.packetflux.com
http://www.linkedin.com/in/fwchristian  http://facebook.com/packetflux
http://twitter.com/@packetflux