Re: [Declude.Virus] OT - Server Room Temperature

2005-08-12 Thread Doug Traylor



We just looked at the operating spec of our servers 
from the Manufacturer's (Dell) website. The max is listed as 95* F and we 
run around 80* F during the day on weekdays and up to 92* F on the weekends when 
they turn off the AC in the plant. We have our own AC which runs 24/7 in 
the computer room/closet. So far we have not had any noticeable system 
problems in the five years we have been operating this way. 

When we had a large IBM mainframe with all the 
dressing, we kept it in a large computer room that was kept at a chilly 66* 
F. I was a computer operator then and worked in there for 8-12 hours a 
day. I would wear two shirts and longs sleeves to work,even when it 
was 110* F outside - Texas.

Doug


  - Original Message - 
  From: 
  Jeff 
  
  To: Declude.Virus@declude.com 
  Sent: Thursday, August 11, 2005 8:58 
  AM
  Subject: [Declude.Virus] OT - Server Room 
  Temperature
  
  Can someone point me to a source of information 
  regarding what temperaturea server room should be at ?
  
  Thank you.
  
  


Re: [Declude.Virus] OT - Server Room Temperature

2005-08-12 Thread Jim Matuska



We keep our server rooms (and our office) around 
65-70degrees. I am usually wearing a sweatshirt and a heavy coat 
year round. 

Jim Matuska Jr.Computer Tech2, CCNANez 
Perce TribeInformation Systems[EMAIL PROTECTED]

  - Original Message - 
  From: 
  Doug 
  Traylor 
  To: Declude.Virus@declude.com 
  Sent: Friday, August 12, 2005 9:01 
  AM
  Subject: Re: [Declude.Virus] OT - Server 
  Room Temperature
  
  We just looked at the operating spec of our 
  servers from the Manufacturer's (Dell) website. The max is listed as 95* 
  F and we run around 80* F during the day on weekdays and up to 92* F on the 
  weekends when they turn off the AC in the plant. We have our own AC 
  which runs 24/7 in the computer room/closet. So far we have not had any 
  noticeable system problems in the five years we have been operating this 
  way. 
  
  When we had a large IBM mainframe with all the 
  dressing, we kept it in a large computer room that was kept at a chilly 66* 
  F. I was a computer operator then and worked in there for 8-12 hours a 
  day. I would wear two shirts and longs sleeves to work,even when 
  it was 110* F outside - Texas.
  
  Doug
  
  
- Original Message - 
From: 
Jeff 

To: Declude.Virus@declude.com 
Sent: Thursday, August 11, 2005 8:58 
AM
Subject: [Declude.Virus] OT - Server 
Room Temperature

Can someone point me to a source of information 
regarding what temperaturea server room should be at ?

Thank you.




Re: [Declude.Virus] OT - Server Room Temperature

2005-08-12 Thread Matt




Doug,

Hard drives are probably the most sensitive components that you have in
your servers, and I am not aware of any hard drives that should be run
above 50C/122F. My server runs about 35F hotter for the system temp
than the environment and about 40F hotter for the CPU's than the
environment. Note that these readings are under normal load, but when
the server redlines, the CPU's increase by about 15F and the system by
about 5F. Considering that the hard drives create heat themselves and
their much lower tolerance for heat in comparison to solid state
components, it would seem that going over 30C/85F for the ambient
temperature would be very dangerous as far as the hard drives go in an
active server. Hard drives will likely go over their operating
temperature long before the system or the processors unless you have a
broken fan or bad connection with a heat sync. My system is spec'd at
15C/27F over the hard drive's tolerance, and my CPU's at 27C/50F over.

IMO, 66F is the proper server room temperature, and it gives some
leeway for adding more equipment and other issues that can crop up such
as A/C failures. 72F would be the high end normal temp that I would
want to see. If my colo was over 75F, I would definitely complain.
The guy next to me with 25 TB's of 15,000 RPM SCSI drives would
probably complain louder :)

Matt



Doug Traylor wrote:

  
  
  
  We just looked at the operating spec
of our servers from the Manufacturer's (Dell) website. The max is
listed as 95* F and we run around 80* F during the day on weekdays and
up to 92* F on the weekends when they turn off the AC in the plant. We
have our own AC which runs 24/7 in the computer room/closet. So far we
have not had any noticeable system problems in the five years we have
been operating this way. 
  
  When we had a large IBM mainframe
with all the dressing, we kept it in a large computer room that was
kept at a chilly 66* F. I was a computer operator then and worked in
there for 8-12 hours a day. I would wear two shirts and longs sleeves
to work,even when it was 110* F outside - Texas.
  
  Doug
  
  
-
Original Message - 
From:
Jeff

To:
Declude.Virus@declude.com 
Sent:
Thursday, August 11, 2005 8:58 AM
Subject:
[Declude.Virus] OT - Server Room Temperature


Can someone point me to a source
of information regarding what temperaturea server room should be at ?

Thank you.


  





Re: [Declude.Virus] OT - Server Room Temperature

2005-08-12 Thread Doug Traylor



I agree that the room should be much cooler, I 
hatecoming in on the weekends here,but the management has an "if it 
ain't broke don't fix it" attitude and point out that we have had no significant 
problems over 5 years so why change things now. We have had a few drives 
(4 out of 20)fail over the years, some internal, some in a 
Powervault,but nothing that seems out of the ordinary for 5 year old 10k 
rpm drives that are always on. Since they are all raided, it has not 
caused us any trouble yet and we simply replace the drive under our sevice 
contract. I always look at it as an opportunity to get more drive space as 
they don't make drives that small anymore. 
Upgrading our drives one at a time. 
:o)

4 failures out of 20 drives over 5 years. 
Does that seem too high a failure rate or about average?

If it could be proven that the high temps are 
causing drive failures the management might be a bit more interested in 
upgrading the AC system in the computer room.

Doug


  - Original Message - 
  From: 
  Matt 
  To: Declude.Virus@declude.com 
  Sent: Friday, August 12, 2005 11:30 
  AM
  Subject: Re: [Declude.Virus] OT - Server 
  Room Temperature
  Doug,Hard drives are probably the most sensitive 
  components that you have in your servers, and I am not aware of any hard 
  drives that should be run above 50C/122F. My server runs about 35F 
  hotter for the system temp than the environment and about 40F hotter for the 
  CPU's than the environment. Note that these readings are under normal 
  load, but when the server redlines, the CPU's increase by about 15F and the 
  system by about 5F. Considering that the hard drives create heat 
  themselves and their much lower tolerance for heat in comparison to solid 
  state components, it would seem that going over 30C/85F for the ambient 
  temperature would be very dangerous as far as the hard drives go in an active 
  server. Hard drives will likely go over their operating temperature long 
  before the system or the processors unless you have a broken fan or bad 
  connection with a heat sync. My system is spec'd at 15C/27F over the 
  hard drive's tolerance, and my CPU's at 27C/50F over.IMO, 66F is the 
  proper server room temperature, and it gives some leeway for adding more 
  equipment and other issues that can crop up such as A/C failures. 72F 
  would be the high end normal temp that I would want to see. If my colo 
  was over 75F, I would definitely complain. The guy next to me with 25 
  TB's of 15,000 RPM SCSI drives would probably complain louder 
  :)MattDoug Traylor wrote: 
  



We just looked at the operating spec of our 
servers from the Manufacturer's (Dell) website. The max is listed as 
95* F and we run around 80* F during the day on weekdays and up to 92* F on 
the weekends when they turn off the AC in the plant. We have our own 
AC which runs 24/7 in the computer room/closet. So far we have not had 
any noticeable system problems in the five years we have been operating this 
way. 

When we had a large IBM mainframe with all the 
dressing, we kept it in a large computer room that was kept at a chilly 66* 
F. I was a computer operator then and worked in there for 8-12 hours a 
day. I would wear two shirts and longs sleeves to work,even when 
it was 110* F outside - Texas.

Doug


  - 
  Original Message - 
  From: 
  Jeff 
  
  To: 
  Declude.Virus@declude.com 
  
  Sent: 
  Thursday, August 11, 2005 8:58 AM
  Subject: 
  [Declude.Virus] OT - Server Room Temperature
  
  Can someone point me to a source of 
  information regarding what temperaturea server room should be at 
  ?
  
  Thank you.
  
  


RE: [Declude.Virus] OT - Server Room Temperature

2005-08-12 Thread Dave Marchette
Title: Message



Interesting observation I have made over the last few years, specifically 
on Dell servers is that the hotswap backplanesdo not tolerate rapid and 
frequent temperature changes.We have observedserverrooms 
thatremain at a constant temperature over a few degrees, and even if the 
temp is always 93 F, no backplane issues. However, in smaller rooms 
with less thermal mass and withnot enough thermostat hesteresis(too wide 
of a trigger range), the temperaturecan vary by 10 degrees over 10 
minutes. This can causeodd random backplane connectivity issues, 
where drivesseem to 'shake' off of the array. 


  
  -Original Message-From: 
  [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On 
  Behalf Of Doug TraylorSent: Friday, August 12, 2005 12:03 
  PMTo: Declude.Virus@declude.comSubject: Re: 
  [Declude.Virus] OT - Server Room Temperature
  I agree that the room should be much cooler, I 
  hatecoming in on the weekends here,but the management has an "if 
  it ain't broke don't fix it" attitude and point out that we have had no 
  significant problems over 5 years so why change things now. We have had 
  a few drives (4 out of 20)fail over the years, some internal, some in a 
  Powervault,but nothing that seems out of the ordinary for 5 year old 10k 
  rpm drives that are always on. Since they are all raided, it has not 
  caused us any trouble yet and we simply replace the drive under our sevice 
  contract. I always look at it as an opportunity to get more drive space 
  as they don't make drives that small anymore. 
  Upgrading our drives one at a time. 
  :o)
  
  4 failures out of 20 drives over 5 years. 
  Does that seem too high a failure rate or about average?
  
  If it could be proven that the high temps are 
  causing drive failures the management might be a bit more interested in 
  upgrading the AC system in the computer room.
  
  Doug
  
  
- Original Message - 
From: 
Matt 

To: Declude.Virus@declude.com 
Sent: Friday, August 12, 2005 11:30 
AM
Subject: Re: [Declude.Virus] OT - 
    Server Room Temperature
Doug,Hard drives are probably the most sensitive 
components that you have in your servers, and I am not aware of any hard 
drives that should be run above 50C/122F. My server runs about 35F 
hotter for the system temp than the environment and about 40F hotter for the 
CPU's than the environment. Note that these readings are under normal 
load, but when the server redlines, the CPU's increase by about 15F and the 
system by about 5F. Considering that the hard drives create heat 
themselves and their much lower tolerance for heat in comparison to solid 
state components, it would seem that going over 30C/85F for the ambient 
temperature would be very dangerous as far as the hard drives go in an 
active server. Hard drives will likely go over their operating 
temperature long before the system or the processors unless you have a 
broken fan or bad connection with a heat sync. My system is spec'd at 
15C/27F over the hard drive's tolerance, and my CPU's at 27C/50F 
over.IMO, 66F is the proper server room temperature, and it gives 
some leeway for adding more equipment and other issues that can crop up such 
as A/C failures. 72F would be the high end normal temp that I would 
want to see. If my colo was over 75F, I would definitely 
complain. The guy next to me with 25 TB's of 15,000 RPM SCSI drives 
would probably complain louder :)MattDoug Traylor 
wrote: 

  
  

  We just looked at the operating spec of our 
  servers from the Manufacturer's (Dell) website. The max is listed as 
  95* F and we run around 80* F during the day on weekdays and up to 92* F 
  on the weekends when they turn off the AC in the plant. We have our 
  own AC which runs 24/7 in the computer room/closet. So far we have 
  not had any noticeable system problems in the five years we have been 
  operating this way. 
  
  When we had a large IBM mainframe with all 
  the dressing, we kept it in a large computer room that was kept at a 
  chilly 66* F. I was a computer operator then and worked in there for 
  8-12 hours a day. I would wear two shirts and longs sleeves to 
  work,even when it was 110* F outside - Texas.
  
  Doug
  
  
- 
Original Message - 
From: 
Jeff 
To: 
Declude.Virus@declude.com 

Sent: 
Thursday, August 11, 2005 8:58 AM
Subject: 
[Declude.Virus] OT - Server Room Temperature

Can someone point me to a source of 
information regarding what temperaturea server room should be at 
?

Thank you.




Re: [Declude.Virus] OT - Server Room Temperature

2005-08-12 Thread Matt




Doug,

It seems to be within normal conditions that you have a 20%/5 year
failure rate, but the sample is way too small to make any sort of
scientific determination. Certain types of drives are of course better
than others, and drives can degrade substantially without actually
failing. It's also hard to tell how long they might have lasted if it
averaged 20F lower than it is now, or what affect raising the
temperature on the weekends only might cause.

The bottom line is would seem to be what the potential cost to the
business is when a server completely goes down, either to be rebuilt,
restored, due to multiple drive failures, or failure of some other
component due to heat. You clearly aren't a banking institution,
though depending on circumstances, your servers might be just as vital
and therefore worth the extra ~$20/month that it costs to keep them
cooler...or maybe not. Ever wonder why good backup software costs more
than the OS?

Matt




Doug Traylor wrote:

  
  
  I agree that the room should be much
cooler, I hatecoming in on the weekends here,but the management has
an "if it ain't broke don't fix it" attitude and point out that we have
had no significant problems over 5 years so why change things now. We
have had a few drives (4 out of 20)fail over the years, some internal,
some in a Powervault,but nothing that seems out of the ordinary for 5
year old 10k rpm drives that are always on. Since they are all raided,
it has not caused us any trouble yet and we simply replace the drive
under our sevice contract. I always look at it as an opportunity to
get more drive space as they don't make drives that small anymore. 
  Upgrading our drives one at a time.
:o)
  
  4 failures out of 20 drives over 5
years. Does that seem too high a failure rate or about average?
  
  If it could be proven that the high
temps are causing drive failures the management might be a bit more
interested in upgrading the AC system in the computer room.
  
  Doug
  
  
-
Original Message - 
From:
Matt

To:
Declude.Virus@declude.com 
Sent:
Friday, August 12, 2005 11:30 AM
Subject:
Re: [Declude.Virus] OT - Server Room Temperature


Doug,

Hard drives are probably the most sensitive components that you have in
your servers, and I am not aware of any hard drives that should be run
above 50C/122F. My server runs about 35F hotter for the system temp
than the environment and about 40F hotter for the CPU's than the
environment. Note that these readings are under normal load, but when
the server redlines, the CPU's increase by about 15F and the system by
about 5F. Considering that the hard drives create heat themselves and
their much lower tolerance for heat in comparison to solid state
components, it would seem that going over 30C/85F for the ambient
temperature would be very dangerous as far as the hard drives go in an
active server. Hard drives will likely go over their operating
temperature long before the system or the processors unless you have a
broken fan or bad connection with a heat sync. My system is spec'd at
15C/27F over the hard drive's tolerance, and my CPU's at 27C/50F over.

IMO, 66F is the proper server room temperature, and it gives some
leeway for adding more equipment and other issues that can crop up such
as A/C failures. 72F would be the high end normal temp that I would
want to see. If my colo was over 75F, I would definitely complain.
The guy next to me with 25 TB's of 15,000 RPM SCSI drives would
probably complain louder :)

Matt



Doug Traylor wrote:

  
  
  We just looked at the operating
spec of our servers from the Manufacturer's (Dell) website. The max is
listed as 95* F and we run around 80* F during the day on weekdays and
up to 92* F on the weekends when they turn off the AC in the plant. We
have our own AC which runs 24/7 in the computer room/closet. So far we
have not had any noticeable system problems in the five years we have
been operating this way. 
  
  When we had a large IBM
mainframe with all the dressing, we kept it in a large computer room
that was kept at a chilly 66* F. I was a computer operator then and
worked in there for 8-12 hours a day. I would wear two shirts and
longs sleeves to work,even when it was 110* F outside - Texas.
  
  Doug
  
  
-
Original Message - 
From:
Jeff 
To:
Declude.Virus@declude.com 
Sent:
Thursday, August 11, 2005 8:58 AM
Subject:
[Declude.Virus] OT - Server Room Temperature


Can someone point me to a
source of information regarding what temperaturea server room should
be at ?

Thank you.


  

  





[Declude.Virus] OT - Server Room Temperature

2005-08-11 Thread Jeff



Can someone point me to a source of information 
regarding what temperaturea server room should be at ?

Thank you.




RE: [Declude.Virus] OT - Server Room Temperature

2005-08-11 Thread Fox, Thomas



http://www.google.com/search?hl=enq=recommended+server+room+temperature

  
  
  From: [EMAIL PROTECTED] 
  [mailto:[EMAIL PROTECTED] On Behalf Of 
  JeffSent: Thursday, August 11, 2005 9:58 AMTo: 
  Declude.Virus@declude.comSubject: [Declude.Virus] OT - Server Room 
  Temperature
  
  Can someone point me to a source of information 
  regarding what temperaturea server room should be at ?
  
  Thank you.