Re: Info on EMI Filters

1998-08-27 Thread reheller
Robert, what do you mean by "...Use a y cap, not two caps..."?

Aren't two y caps used, one from line to ground and one from neutral to
ground?




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


RE: ESD test levels for medical equipment

1998-08-27 Thread Gary McInturff
Many companies have internal standards that are much higher than
the CE requirements. Sometimes they are historical accidents. Before
general ESD requirements out on the production floor 25Kv testing for
product survivability was a good idea. I still have some larger
customers that require 20 to 25 Kv end product survivability. I
personally require our equipment to meet 16 Kv air discharge, and 8 Kv
direct contact discharges because of the mission criticality of large
LAN systems.
In short I would take into account not only the minimum
requirements (Europe may like to think they have all the answers) but
how often people (no people to touch or shove things into the equipment
no ESD event), and the results of an ESD failure, either operationally
or functionally and then make a determination of the levels you want. 
Gary McInturff

-Original Message-
From:   plaw...@west.net [SMTP:plaw...@west.net]
Sent:   Wednesday, August 26, 1998 11:47 AM
To: emc-p...@majordomo.ieee.org; me...@world.std.com
Subject:ESD test levels for medical equipment

My company has been testing our standard power supply products
to the ESD test
voltages in IEC601-1-2:1993 (Medical EMC requirements).  The
levels are 3kV
contact & 8kV air.

Recently, one of our customers started testing to IEC601-2-24
(Safety of
Infusion Pumps and Controllers).  They said the levels in that
spec are 8kV
contact & 15kV air - much higher than our test levels.

Is this a trend for ESD test levels in product-specific
standards, of
significantly higher test levels?  Or are other medical
product-specific
standards comparable to IEC601-1-2 (ie, with a few kV)?
I realize that the next version of IEC601-1-2 raises the contact
discharge
voltage to 6kV.  This doesn't seem like a big change.

If the trend is toward higher voltages in these other standards,
I'd like to
find out so we can plan accordingly.

--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


RE: FDA Requirements

1998-08-27 Thread Darrell Locke (MSMail)
Mike,

I posed this question to the group a few weeks back.  See the archive
postings for July 28 and 29 for responses.   I also did research and
could not come up with any written requirements for stainless steel.  It
seems to just be a commonly accepted practice.

Darrell Locke
Advanced Input Devices
 --
From: Mike Morrow
To: IEEE EMC Board
Subject: FDA Requirements
List-Post: emc-pstc@listserv.ieee.org
Date: Thursday, August 27, 1998 6:03AM

I've always been told that any piece of equipment being used in a
"sanitary" application (i.e. food processing, etc) must be constructed
of
stainless steel.  I'm after the actual standard that has this
requirement.  Can aluminum be used??

Any help is appreciated.

Mike Morrow
Product Standards Engineer
Data Instruments
mike_mor...@datainstruments.com
mmor...@compuserve.com
Phone 978-264-9550 xt-201
Fax 978-263-0630


 -
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


FDA Requirements

1998-08-27 Thread Mike Morrow
I've always been told that any piece of equipment being used in a 
"sanitary" application (i.e. food processing, etc) must be constructed of 
stainless steel.  I'm after the actual standard that has this 
requirement.  Can aluminum be used??

Any help is appreciated.

Mike Morrow
Product Standards Engineer
Data Instruments
mike_mor...@datainstruments.com
mmor...@compuserve.com
Phone 978-264-9550 xt-201
Fax 978-263-0630


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


Southeast Asia's Regulation for Transmitter.

1998-08-27 Thread Tetsuya Hashimoto
Hello,

I want to know about Southeast Asia's Regulation for Transmitter.
We have a plan to export our client transmitter which provides 800MHz,10mW
output to Indonesia,Singarpore,Philippines and Malaysia.
Is there any regulation to regulate this kind of equipment in their
countries.
If there are , please advice about the regulation and then how we  can
conform to the regulation.

〒516-1106
108 Yokowa-cho Ise-city Mie-ken
A-pex International Co.,Ltd.
2nd Division EMC Yokowa Lab.
Tetsuya Hashimoto
TEL 0596-39-1485  FAX 0596-39-0232
E-mail: has...@a-pex.co.jp 


IEC1000-4-12

1998-08-27 Thread rogerhsu

 Hi all,
 
 Can anyone tell me to which EMC standard does it call for the 
 IEC1000-4-12 tests?
 
 Thanks & Regards,
 
 Roger Hsu

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


Interpretation of Australian Standard TS001

1998-08-27 Thread Kevin Richardson
John,

This clause means that IF a detachable plug is used it should not be of a
type which is normally used to connect to the network.  In other words, if
you disconnect the cable from the CE to the LIU, at the LIU, you should not
be able to then plug that cable (coming directly from the CE) into a
standard network line connection socket.

Hope this clears it up a little.

Best regards,
Kevin

> Sender: owner-emc-p...@majordomo.ieee.org
> Received: from ruebert.ieee.org (ruebert.ieee.org [199.172.136.3])
>   by arl-img-9.compuserve.com (8.8.6/8.8.6/2.12) with ESMTP id
LAA07709;
>   Wed, 26 Aug 1998 11:35:21 -0400 (EDT)
> Received:  by ruebert.ieee.org (8.8.8/8.8.8)
>   id KAA21826 for emc-pstc-resent; Wed, 26 Aug 1998 10:07:29 -0400
(EDT)
> From: f...@netc.ie
> Date: Wed, 26 Aug 98 14:56:55 
> Message-Id: <9807269041.aa904168...@netc.netc.ie>
> To: emc-p...@ieee.org, emc-p...@majordomo.ieee.org
> Subject: Interpretation of  Australian Standard TS001 
> Sender: owner-emc-p...@majordomo.ieee.org
> Precedence: bulk
> Reply-To: f...@netc.ie
> X-Resent-To: Multiple Recipients 
> X-Listname: emc-pstc
> X-Info: Help requests to  emc-pstc-requ...@majordomo.ieee.org
> X-Info: [Un]Subscribe requests to  majord...@majordomo.ieee.org
> X-Moderator-Address: emc-pstc-appro...@majordomo.ieee.org
> 
> 
>  Hi all,
>  
>  I have a question regarding TS001 - 1997 which is an Australian 
>  Standard for safety of telecoms equipment for customer use.
>  
>  Clause 5.3 permits the use of a separate Line Isolation Unit which
is 
>  connected between the telecoms device, typically a modem, and the 
>  network. The purpose of this LIU is to provide electrical separation

>  from the network to SELV, in the case where the device itself does
not 
>  provide that separation.
>  
>  Clause 5.3.2 allows three methods to prevent the possibility of the 
>  LIU being bypassed, resulting in the device being directly connected

>  to the network. The first method is the "Use of detachable cabling 
>  that will not allow direct connection of CE to a telecommunications 
>  network"
>  
>  My question is should the above sentence read "non-detachable"
istead 
>  of "detachable"? Otherwise can anybody shed some light on the
intent?
>  
>  All comments appreciated.
>  
>  John Fee
>  
>  f...@netc.ie
> 
> -
> This message is coming from the emc-pstc discu

Best regards,
Kevin RichardsonPh:   
02-43-29-4070
Stanimore Pty Limited   Fax:   02-43-28-5639
"The Technology Requirements Specialists"   Int'l:
+61-2-43-2x-
Email:  Internet:  k...@compuserve.com  Compuserve: 100356,374

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


THANK YOU: Frank Goto

1998-08-27 Thread Rich Nute




To:   All subscribers to the IEEE emc-pstc listserver.

From: Roger Volgstadt, Ed Price, Richard Nute

Subject:  THANK YOU, Frank Goto


We do our best not to post non-technical, administrative
messages.  But, occasionally we must make some announcements
as to the status of our operation, problems, policies, and
such.  Today, we are posting a different kind of 
administrative message:  We are recognizing one of our 
subscribers.

Frank Goto, is not only a subscriber, but one of our two 
listserver administrators.  Frank is moving on to other 
things.  

The listserver admin job is to maintain a 100% valid e-mail
address list.  As many of you know, each new address is
tested by our admins before we add it to our list.  But, 
this is not the only job.  Many subscribers move without
notifying us.  Often, servers go down which make addresses
look invalid.  IT departments change your default address 
without telling you!  For these and other reasons, our 
listserver, majordomo, bounces these undeliverable messages 
back to our admins.  We get up to 100 such bounce messages 
a day from our 730 subscribers!  Some bounces are valid,
some are not.  Each message must be read, and a decision 
must be made as to what must be done.  (We reduce the load 
by splitting it between two admins.)

Despite what appears to be an overwhelming job, each 
admin, including Frank, that has served has said it was a 
personally rewarding activity.  Through it, we get to meet 
our subscribers, who are a marvelous bunch of professionals!

Our subscribers are in many, many countries.  E-mail has
no special traits to show you the country location of 
whoever posts a message.  Administering our listserver can
be done from anywhere in the world.  And so it is with
Frank.  Frank has done his job from Japan!

I have been very fortunate in having the opportunity to 
meet Frank face-to-face in Japan earlier this spring.  (I've
not yet met Ed Price who is right here in San Diego!)

So, for all the good work for the past year or so, a big
THANK YOU! to Frank!  And we wish you the best!


With best personal regards,
Rich


ps:   Our replacement admin is Jim Bacher.

pps:  go...@a-pex.co.jp 
  go...@mint.or.jp 



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).


Re: Interpretation of Australian Standard TS001

1998-08-27 Thread Barry Esmore
Hello John,

There is no mistake with the spec's wording. The intent of the clause is to
have cabling that will prevent the LIU from being easily bypassed. With the
method that you have mentioned this could be achieved by the CE having a
non-standard connector that will prevent direct connection to the network.
In this case the user is encouraged to connect the CE to the LIU via the
non-standard connector and then make the network connection to the LIU
using a standard connector (RJ11 etc).

If the LIU and CE were joined with a "non-detachable" cable this would also
meet the intention of this clause as the user would need to make some
serious changes to bypass the LIU.

Regards
Barry Esmore


--
> From: f...@netc.ie
> To: emc-p...@ieee.org; emc-p...@majordomo.ieee.org
> Subject: Interpretation of  Australian Standard TS001 
> Date: Thursday, 27 August 1998 0:56
> 
> 
>  Hi all,
>  
>  I have a question regarding TS001 - 1997 which is an Australian 
>  Standard for safety of telecoms equipment for customer use.
>  
>  Clause 5.3 permits the use of a separate Line Isolation Unit which
is 
>  connected between the telecoms device, typically a modem, and the 
>  network. The purpose of this LIU is to provide electrical separation

>  from the network to SELV, in the case where the device itself does
not 
>  provide that separation.
>  
>  Clause 5.3.2 allows three methods to prevent the possibility of the 
>  LIU being bypassed, resulting in the device being directly connected

>  to the network. The first method is the "Use of detachable cabling 
>  that will not allow direct connection of CE to a telecommunications 
>  network"
>  
>  My question is should the above sentence read "non-detachable"
istead 
>  of "detachable"? Otherwise can anybody shed some light on the
intent?
>  
>  All comments appreciated.
>  
>  John Fee
>  
>  f...@netc.ie


-
This message is coming from the emc-pstc discussion list.