FCC part 15 section 109

2002-03-25 Thread Kristiaan . Carpentier
Hello group,

Part 15, section 109, states that as an alternative to the radiated emission 
limits shown in 
paragraphs (a) and (b) of this section, digital devices may be shown to 
comply with CISPR22 3rd ed. Further-on is stated that the testmethods of 
part 15 (referring to ANSI C63.4) apply.
Question:
If a lab performs Part 15 measurements for Class B devices below 1000MHz 
according to CISPR22:1997 with
- the limits of CISPR22
- the procedures of CISPR22
- at a 10 meter distance as per CISPR22,
Are these measurements performed in an correct way?
Regards,
Kris Carpentier

Australian compliance to ARE: creepage v breakdown voltage

2002-03-15 Thread Kristiaan . Carpentier
Hello,

According to the latest version of the Telecommunication Labelling Notice 
2001, products in the Category A50 are deemed to comply with ACA 
TS-001-1997 and AS/ACIF S043-2001. No problem for TS-001, but S043 needs 
Compliance level 3 only since January 1rst 2002.
The general approach is that testing for S043 must be done by a Recognised 
Testing Authority.
After verifying the latest list of RTA´s 
http://www.nata.asn.au/downloads/rtalist.pdf of March 7th, only 1 lab seems to 
be listed as RTA and it is not even 
located in Australia, but in the US.
From my reading of the Labelling Notice, Schedule 3 seems to give however 
other possibilities to comply, like a Certification or Competent body.
Any-one can shed some light on this issue? 

Regards,
Kris Carpentier

Re: New Generic ENs

2002-02-19 Thread Kristiaan . Carpentier

Richard,

EN 61000-6-1 has common deviations in clause 2, 3.5, Table 1 and Table 5.
EN 61000-6-3 has common deviations in clause 2, 4, 9, Table 1 and Annex A.
Both standards have an Annex ZA showing comparison between international
and EN/HD standards.
Hope this helps.
Regards,
Kris Carpentier





richwo...@tycoint.com on 19.02.2002 15:59:49

Please respond to richwo...@tycoint.com
  
  
  
 To:  emc-p...@majordomo.ieee.org 
  
 cc:  (bcc: Kristiaan CARPENTIER/BE/ALCATEL)  
  
  
  
 Subject: New Generic ENs 
  






Are EN 61000-6-1 and -3 identical to the IEC generic standards, or did
CENELEC introduce modifications?

Richard Woods
Sensormatic Electronics
Tyco International


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


noise immunity on mains powered equipment

2002-01-23 Thread Kristiaan . Carpentier

Hello,

Has any-one ever heard about a standard (non-military) that describes noise
immunity of mains powered equipment.
Testing seems to be done by the current bulk injection method. the standard
is not IEC 61000-4-6.
Regards,
Kris Carpentier


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: TNV-2 to Earth requirement

2002-01-17 Thread Kristiaan . Carpentier
Ed,

I do not know your specific application.
Therefore - if your TNV-2 circuit is connected to a telecom network -
EN60950, 2nd ed/A4 andNorway/Sweden requires SI for the mains. (see
EN60950:1992/A4:1997, AnnexZB)
SI means clearance, creepage, DTI and dielectric strength for 230V mains.

Why don's you use EN60950, 3rd edition?
SubClause 6.2.1.2 asks for an insulation between earth and a telecom
network, tested only with 1.5kV insulation test.
As I read the standard, additional requirements exist - for Norway  Sweden
- but only for DTI (ref. EN60950:2000, Annex ZB).

Regards,
Kris Carpentier


All,

I have a DC to DC filter which is rated 32 - 72 VDC input and output which I 
am considering to be TNV-2 according to EN60950/IEC60950 2nd edition.

This filter has a metal chassis which is earthed, and it will be installed in a 
service access area only by qualified service personnel. It is not
permanently connected or
pluggable type B, and does not have a provision for a permanently connected 
earthing conductor. With all this considered, it seems that Norway and
Sweden are the
only Countries that require Supplemental insulation for a primary circuit 
between this TNV-2 circuit and earth.
Is there any way around this requirement due to this filter operating at 72VDC 
and not being directly connected to mains?

Any help would be appreciated.

Ed





Ed Eszlari bosesaf...@hotmail.com on 17.01.2002 16:43:49

Please respond to Ed Eszlari bosesaf...@hotmail.com
  
  
  
 To:  t...@world.std.com, emc-p...@ieee.org   
  
 cc:  (bcc: Kristiaan CARPENTIER/BE/ALCATEL)  
  
  
  
 Subject: TNV-2 to Earth requirement  
  




(See attached file: att1.htm)


All,

I have a DC to DC "filter" which is rated 32 - 72 VDC input and output which I amconsidering to beTNV-2 according to EN60950/IEC60950 2nd edition. 

This filter has a metal chassis which is earthed, and it will be installed in a service access area only by qualified service personnel. It is not permanently connected or pluggable type B, and does not have a provision for a permanently connected earthing conductor. With all this considered, it seems that Norway and Sweden are the only Countries that require Supplemental insulation for a primary circuit between this TNV-2 circuit and earth. 
Is there any way around this requirement due to this filter operating at 72VDC andnot being directlyconnected to mains? 

Any help would be appreciated.

EdMSN Photos is the easiest way to share and print your photos: Click Here

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old messages are imported into the new server.


Standards applicable to crane equipment

2001-10-24 Thread Kristiaan . Carpentier



Dear all,

The product concerned is a metal box located on the (metal) roller bridge of a 
crane and controls the movement of that bridge.
It is powered by min. 48Vac and receives commands from an operator with a 
battery powered hand-held radio transmitter command box.
The 48V ac power supply is connected to the metal frame of the roller bridge.
The crane nor roller bridge are connected to ground by means of a fixed 
connection.
All additional metal parts are connected to the fixed or moving part of the 
crane.

Questions:
1.- What standards and regulations are applicable to both products for EMC, 
Safety and Radio,  for US and EU market?
2.- Can the metal frame be considered as reliably connected to PE?

Regards,
Kris Carpentier



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



high temperature circuitbreaker

2001-10-19 Thread Kristiaan . Carpentier



Hello group,

Circuit breakers and residual current operated circuitbreakers for house-hold 
applications are typically cetified at 40 degree Celcius.
If these types are built into other products, they do not comply with their 
temperature rating as specified in the safety certificate.
Does any-one know about references to circuit-breakers(230V ac, 10A) that can 
work safely at higher temperatures (70...90 degrees)
Regards,
Kris Carpentier



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



Question on FCC part 15

2001-10-02 Thread Kristiaan . Carpentier



Hello group,

A data acquisition board for building into a PC has been tested to the European 
standard EN 55022, class B by an accredited testlab in Europe.
This configuration is not meant for a residential market and I suppose FCC part 
15 is applicable.

Which procedure should be followed for part 15, DoC or verification?
Compliance required to Class A or Class B?
If the board can be built in different kind of PC's, how is testing performed?
To determine the max. frequency to test for, do I need the max. internal PC 
frequency or the max. internal freq. of the board?
Will the EN 55022 results be accepted by an FCC lab?, can a European CAB do the 
testing?

Any help is appreciated.
Regards,
Kris Carpentier



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



Safety requirements for mounting rails for lamps

2001-02-16 Thread Kristiaan . Carpentier



Dear all,

Who knows what product European safety requirements/ standards are valid for 
mounting-rails into which lamps at low voltage are mounted?
The rail is powered by 12 or 24 volt ac, the supply current can be approx. 16A.
Thanks in advance,

Kris Carpentier



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org