Hello Robert,

you could check into:  IEC 60926:1995 + A1:1999 Auxiliaries for lamps ?
Starting devices (other than glow starters) ? General and safety
requirements.
There is currently a proposal under development to refer to this standard
in IEC 60950 to address safety requirements for high pressure lamps and
their circuitry to generate starting pulses.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-642-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany


Loop, Robert rl...@hnt.wylelabs.com on 02.10.2000 20:36:42

Please respond to Loop, Robert rl...@hnt.wylelabs.com

To:   emc-p...@majordomo.ieee.org
cc:(bcc: Volker Gasse/Germany/IBM)
Subject:  IEC/EN Standard for Independent Lamp Control Gear





Group:

I need information on what standard covers an independent lamp control
device.  This product is used in a commercial environment, has a data
interface to a computer and is used to turn fluorescent light fixtures on
and off (not dim).  It is self-contained in its own enclosure and uses
electro-mechanical relays to provide mains power to a series of lights.

It was suggested by another forum subscriber that we look at EN60598-1
Luminaries. Unfortunately, in order to look at an EN standard, one
generally has to purchase them and they are not inexpensive.

To make a long story short, EN60598 only covers the light fixture itself,
not the device that is used to turn it on and off.  After reviewing all of
the standards covered under the LVD in the OJEC, nothing jumps out and says
here I am.

The only standard I could find that might be applicable:

EN60669-2-2:1997 - Switches for household and similar fixed installations.
Section 2: Electromagnetic remote-control switches.

Can anyone say yes, you're right, or no, you're out in left field?

Any help is greatly appreciated.
Sincerely,
Robert Loop
Engineering Supervisor
Wyle Laboratories
Product Safety
ph - (256) 837-4411 x313
fax- (256) 721-0144
e-mail: rl...@hnt.wylelabs.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org





Re: Paint

2000-07-27 Thread volker . gasse



Hello Bill,

RAL is a private German organisation
(RAL, Deutsches Institut für Gütesicherung und Kennzeichnung e.V. ),
which would translate into 'German Institute for Quality Assurance and
Marking'.
In their web-site (which is also available in English)
http://www.ral-colours.de/
you will find information regarding the coding system.
The 4-digit RAL Colours have been the standard for choosing
colours for more than 70 years now.
At the beginning the colour collection included 40 different colours.
Its number has risen to more than 200 today.
They also contain safety- and signalling colours.

Hope that helps,

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-642-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany


Bill Somerfield  bi...@eliz.com on 27.07.2000 13:43:18

Please respond to Bill   Somerfield  bi...@eliz.com

To:   emc-p...@ieee.org
cc:(bcc: Volker Gasse/Germany/IBM)
Subject:  Paint





Group,

Is there an international standard for paint color? I've seen RAL , but
can't really find what ist stands for?

Thank you for your help,
Bill Somerfield

Bill Somerfield
QA/Compliance Manager
Elizabeth-Hata International
bi...@eliz.com
412-829-7700
FAX 412-829-7330


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org





Re: EN60950, 3rd Edition . . .

2000-05-16 Thread volker . gasse



Hello Carla,

EN 60950 has already been ratified by CENELEC BT, dated January 1, 2000.
The following related dates have been set:

doa (date of announcement, publication in the EU Official Journal): July 1,
2000
dop (date of publication in at least one European member country): January
1, 2001
dow ( date of withdrawal of conflicting standards, which is EN 60950 2nd
edition A11:1998): January 1, 2005. This date will also be the date of
cessation (doc), by which the superseded standard looses its presumption of
conformity with the essential requirements of the Low Voltage Directive.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-642-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany


Carla Robinson carla_robin...@mw.3com.com on 15.05.2000 17:46:10

Please respond to Carla Robinson carla_robin...@mw.3com.com

To:   emc-p...@ieee.org
cc:(bcc: Volker Gasse/Germany/IBM)
Subject:  EN60950, 3rd Edition . . .







Greetings!

I am seeking information on when will the 3rd Edition of the EN60950, L.V.
Directive, go into effect?  When will it be ratified for the European
Community?

Carla Robinson
3Com Corp.
847-262-2494
carla_robin...@mw.3com.com



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Fwd:Isolations on inner layers

2000-03-17 Thread volker . gasse



Hello Jim and Mihai,

According to IEC 60950 3rd. edition, Clause 2.10.5.3, the distance between
two adjacent tracks on the same inner layer of a printed circuit board is
treated as distance through insulation, and therefore 0,4 mm apply for
supplementary or reinforced insulation.
Your question regarding air bubbles or other defects is should be covered
by the applied electric strength test.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-642-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany


jim_bac...@mail.monarch.com (Jim Bacher) on 17.03.2000 13:50:53

Please respond to jim_bac...@mail.monarch.com (Jim Bacher)

To:   emc-p...@ieee.org
cc:   mih...@trenew.pcnet.ro (bcc: Volker Gasse/Germany/IBM)
Subject:  Fwd:Isolations on inner layers





forwarding for mih...@trenew.pcnet.ro  ...  Jim

Forward Header_
Subject:Isolations on inner layers
Author: Mihai Vintila mih...@trenew.pcnet.ro
List-Post: emc-pstc@listserv.ieee.org
Date:   3/16/00 7:34 PM

Hello,

I have a question concerning isolations for hazardous voltages on
inner
layers of a multilayer PCB.
The material is standard FR4.
I have read the EN60950 spec and it seems like for copper on
different
inner layers an isolation of 0.4mm would be good enough. Now what I could
not
figure is about traces on the same inner layer. In this case an isolation
of 0.4
mm is as good as it is between different layers, or should I take into
consideration the manufacturing errors (impurities, air bubbles, a.s.o.)
and
make a bigger isolation, but how much bigger?
The voltages I am working with are some of them TNV1 and others
220VAC
(mains).

Many thanks,

Mihai


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: standard for lead shot dielectric testing

2000-03-17 Thread volker . gasse



Hello Barry,

you might check IEC 60851-5 (Test methods for winding wires) where Clause
4, (Test 13) uses the metal shot when determining breakdown voltages of a
twisted winding wire.
This test is also referenced in IEC 60950 Annex U.2.1.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-642-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany


barrym bar...@spaceship.com on 16.03.2000 22:26:37

Please respond to barrym bar...@spaceship.com





I'm looking for reference to any standard which may provide specifics for
using lead shot for dielectric strength testing.  I know this done for
insulation system qualifications, just have not identified a standard for
the test set up.

Thanks,
Barry Marks






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Frequency of temporary overvoltages on the mains supply/no data

1999-10-12 Thread volker . gasse



Dear Peter,

yesterday I received a very interesting document which includes a lot of
information and data on sources of overvoltages on the mains supply. It also
contains a large bibliography.
The document is a preliminary version of a technical report IEC 62066 (General
basic information regarding surge overvoltages and surge protection in
low-voltage a.c. power systems). The document is called 64/1034/CD and can be
obtained through your national standards committee.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-16-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany


P Lewis qsl_dir...@compuserve.com on 10.10.99 23:04:42

Please respond to P Lewis qsl_dir...@compuserve.com

To:   Volker Gasse/Germany/IBM@IBMDE
cc:
Subject:  Re: Frequency of temporary overvoltages on the mains  supply/no data




Dear Volker

Many thanks for the reply.  I understand you have not yet received any
statistical information on the frequency of voltage transients yet.  If you
are successful in the future, perhaps you would be so kind as to send me
some details.
With kind regards
Peter Lewis


Message text written by INTERNET:volker.ga...@de.ibm.com
Dear Peter,

it is rather difficult to obtain statistical material. So far I was not
successful, but I have had some dicussions with people dealing with
installation
of buildings. They gave me some hints whom to talk to. I assume it will
take a
while before I really get the required data.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49-7031-16-6796, Fax: -6916, e-mail: volker.ga...@de.ibm.com
Mail:  D3114/7103-91, D-70548 Stuttgart, Germany





-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



RE: Varistors to ground

1998-12-16 Thread Volker Gasse

You have raised an interesting question, especially in light of CE marking.
Once a CE marked product is placed on the EU market, there are no further
restrictions to limit its distribution or use in other member states. I do not
think it is possible to restrict usage in one specific country based on an
information in the users guide, especially if safety is involved.

In other cases of country specific restrictions, like 'Special National
Conditions' in European Norms, the design has to cover all of them to be able
to state compliance to this standard and to apply CE marking.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49 7031-16-6796, Fax: -6916, e-mail: ga...@de.ibm.com
Mail:  3114/7103-91, D-70548 Stuttgart, Germany



owner-emc-p...@majordomo.ieee.org on 15.12.98 22:52:54
Please respond to wo...@sensormatic.com
To: emc-p...@majordomo.ieee.org
cc:
Subject: RE: Varistors to ground


 Volker, thank you for this useful information. You indicated that
the decisions are to be followed by all of the test houses, yet many of the
decisions appear to be accepted in only some countries. If all of the test
houses are expected to follow the decision, why are country exceptions
allowed and what does it mean to us designers?


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Varistors to ground

1998-12-16 Thread Volker Gasse

Hello Jim,

there is currently work ongoing in IEC TC74 to include requirements for
varistors into IEC 60950. However, until those proposals have reached a level
to be included into an amendment of the 3rd edition may take a while.
I understand that varistors without fuses and sparc gaps in series are only
allowed if separately approved as mentioned, and with the indicated country
limitations.

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49 7031-16-6796, Fax: -6916, e-mail: ga...@de.ibm.com
Mail:  3114/7103-91, D-70548 Stuttgart, Germany



owner-emc-p...@majordomo.ieee.org on 16.12.98 02:55:01
Please respond to jeich...@statpower.com
To: emc-p...@majordomo.ieee.org
cc:
Subject: RE: Varistors to ground


Volker:  Thanks for the explanation.

I am left with 2 questions:

1. You wrote The new decision is not part of the upcoming safety
standard for IT products, IEC 60950 3rd edition, which is likely to be
available beginning of next year.  What does that omission tell us?  If
the 3rd edition has been written by people aware of the OSM/EE
decisions, who consciously did not include the decisions in the new
edition, then do they mean that varistors to ground are acceptable and
not subject to the requirements in the 2 decisions you quoted?

2. It isn't clear whether the recent decision allows a varistor approved
to IEC 601051-1 without a spark gap and fuse or whether the new decision
overrules the old decision in this respect.

Thanks again for any clarification anyone can offer.

Regards,

Jim Eichner
Statpower Technologies Corporation
jeich...@statpower.com
http://www.statpower.com
Any opinions expressed are those of my invisible friend, who really
exists.  Honest.

 -Original Message-
 From: Volker Gasse [SMTP:ga...@de.ibm.com]
 Sent: Tuesday, December 15, 1998 2:34 AM
 To: emc-p...@majordomo.ieee.org
 Subject: RE: Varistors to ground


 The mentioned Cenelec decision is taken from the 'List of decisions
 from
 CENELEC Operational Staff Meeting for Electronic Equipment (OSM/EE)'.
 Here representatives from EU Testhouses meet to discuss
 interpretations of
 clauses in safety
 standards such as EN 60950 for IT products. These decisions are to be
 followed
 by all European
 testhouses. However, those decisions should be
 interpretations/clarifications
 to the existing
 standards, but not addition of new requirements.

 For EN 60950, Clause 1.5.1, Decision 98/2 states:

 'A combination  of a varistor in series with a spark gap (Gas-Tube)
 [between the mains and the protective earth]
 complying with Basic Insulation, and with a fuse will be accepted for

 a. Pluggable equipment Type B and permanently connected equipment:  by
 all
 countries
 b. Pluggable equipment Type A: by all countries except DK, UK and SE.
 For pluggable equipment Type A two fuses are required.'
 (To be sure that even by non-polarized plugs a fuse is provided)

 This interpretation is an extension to a decision which was already
 issued in
 1/94:

 'If a Varistor  is separately approved according to Publications IEC
 601051-1
 and IEC 601051-2, it can be accepted without a protective device. If a
 Varistor  is not separately approved, a protective device against the
 short-circuit is required.
 Varistors tested according to CECC 42200 are considered as acceptable
 in the
 same way as tested to IEC 601051.
 Varistors between the mains and the protective earth cannot be
 accepted by the
 following countries:
 Pluggable equipment, type A:
 Austria, Belgium, Denmark, Finland, Norway, Sweden, United Kingdom.'
 The new decision is not part of the upcoming safety standard for
 IT products, IEC 60950 3rd edition, which is likely to be available
 beginning
 of next year.
 One of the reasons for requiring the spark gap in series with the
 varistor is a
 possible increase
 in leakage current if the varistor has been exposed to several mains
 transients.

 It should be noted, that IEC/EN 60950 does not require the use of
 transient
 suppressing
 components.

 Concerning the

 mit freundlichen Gruessen/ best regards
 Volker Gasse

 IBM Germany, Technical Relations/Product Safety,
 Tel: +49 7031-16-6796, Fax: -6916, e-mail: ga...@de.ibm.com
 Mail:  3114/7103-91, D-70548 Stuttgart, Germany

 -- Forwarded by Volker Gasse/Germany/IBM on
 15.12.98 11:20
 ---


 owner-emc-p...@majordomo.ieee.org on 15.12.98 02:11:00
 Please respond to jeich...@statpower.com
 To: j...@bighorn.dr.lucent.com
 cc: emc-p...@majordomo.ieee.org
 Subject: RE: Varistors to ground


 John:  Sorry I can't help, but I am interested in what replies you
 get.


 I also wonder what force the Decision carries.  Is it a mandatory part
 of the Low Voltage Directive?  How does it relate to the LVD or to the
 various EN's in force under the LVD?

 Thanks in advance for any light you can shed on these murky waters!

 Regards,

 Jim Eichner
 Statpower Technologies Corporation
 jeich

RE: Varistors to ground

1998-12-15 Thread Volker Gasse

The mentioned Cenelec decision is taken from the 'List of decisions from
CENELEC Operational Staff Meeting for Electronic Equipment (OSM/EE)'.
Here representatives from EU Testhouses meet to discuss interpretations of
clauses in safety
standards such as EN 60950 for IT products. These decisions are to be followed
by all European
testhouses. However, those decisions should be interpretations/clarifications
to the existing
standards, but not addition of new requirements.

For EN 60950, Clause 1.5.1, Decision 98/2 states:

'A combination  of a varistor in series with a spark gap (Gas-Tube)
[between the mains and the protective earth]
complying with Basic Insulation, and with a fuse will be accepted for

a. Pluggable equipment Type B and permanently connected equipment:  by all
countries
b. Pluggable equipment Type A: by all countries except DK, UK and SE.
For pluggable equipment Type A two fuses are required.'
(To be sure that even by non-polarized plugs a fuse is provided)

This interpretation is an extension to a decision which was already issued in
1/94:

'If a Varistor  is separately approved according to Publications IEC 601051-1
and IEC 601051-2, it can be accepted without a protective device. If a
Varistor  is not separately approved, a protective device against the
short-circuit is required.
Varistors tested according to CECC 42200 are considered as acceptable in the
same way as tested to IEC 601051.
Varistors between the mains and the protective earth cannot be accepted by the
following countries:
Pluggable equipment, type A:
Austria, Belgium, Denmark, Finland, Norway, Sweden, United Kingdom.'
The new decision is not part of the upcoming safety standard for
IT products, IEC 60950 3rd edition, which is likely to be available beginning
of next year.
One of the reasons for requiring the spark gap in series with the varistor is a
possible increase
in leakage current if the varistor has been exposed to several mains
transients.

It should be noted, that IEC/EN 60950 does not require the use of transient
suppressing
components.

Concerning the

mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49 7031-16-6796, Fax: -6916, e-mail: ga...@de.ibm.com
Mail:  3114/7103-91, D-70548 Stuttgart, Germany

-- Forwarded by Volker Gasse/Germany/IBM on 15.12.98 11:20
---


owner-emc-p...@majordomo.ieee.org on 15.12.98 02:11:00
Please respond to jeich...@statpower.com
To: j...@bighorn.dr.lucent.com
cc: emc-p...@majordomo.ieee.org
Subject: RE: Varistors to ground


John:  Sorry I can't help, but I am interested in what replies you get.


I also wonder what force the Decision carries.  Is it a mandatory part
of the Low Voltage Directive?  How does it relate to the LVD or to the
various EN's in force under the LVD?

Thanks in advance for any light you can shed on these murky waters!

Regards,

Jim Eichner
Statpower Technologies Corporation
jeich...@statpower.com
http://www.statpower.com
Any opinions expressed are those of my invisible friend, who really
exists.  Honest.



 -Original Message-
 From: Boucher, John [SMTP:j...@bighorn.dr.lucent.com]
 Sent: Monday, December 14, 1998 9:07 AM
 To: 'emc-p...@ieee.org'
 Subject: Varistors to ground

 All:

 I have received a copy of a CENELEC Decision (dated 6/98) regarding
 the use
 of varistors between mains conductors and ground. This particular
 Decision
 is written in a rather unclear fashion (at least its unclear to me...I
 tend
 to be rather literal in my interpretations of written requirements),
 and I
 am struggling with defining the actual requirements.

 If anyone out there has received this Decision, and believes they are
 clear
 about what the actual bottom line requirements are, please let me
 know. I
 have muddled through some of the issues, but need some confirmation on
 a
 couple of points (see the questions below). It may seem to some that
 the
 answers to these questions are straight-forward in the Decision, but I
 have
 studied this Decision (maybe too much) and find these points unclear.

 1) Is this Decision only for pluggable equipment type A, or is the
 spark-gap
 / fuse requirement in effect for pluggable equipment type B as well?

 2) Will  Denmark, UK, and Sweden accept varistors to ground if the
 circuit
 contains a spark-gap and two fuses?

 3) The installation instructions for our PABX systems include the
 requirement for a permanently connected ground wire between the
 equipment
 ground and an approved building ground (this ground wire is in
 addition to
 the green wire lead in the AC mains). This wire is required for all
 our
 PABX systems (AC and DC powered systems, pluggable type A, type B, and
 permanently connected systems). Does this permanent ground connection
 provide an exemption to this Decision?

 If this Decision means DK, UK, SE will simply not accept varistors to
 ground, then a lot of small pluggable type A equipment intended

LVD Standards

1998-11-10 Thread Volker Gasse

Hello Peter,

the following Internet Address points to lists of standards for most of the EU
Directives.

http://www2.echo.lu/nasd/index.html

But you have to be careful as this may not always contain the latest level of
applicable standards.



mit freundlichen Gruessen/ best regards
Volker Gasse

IBM Germany, Technical Relations/Product Safety,
Tel: +49 7031-16-6796, Fax: -6916, e-mail: ga...@de.ibm.com
Mail:  3114/7103-91, D-70548 Stuttgart, Germany
Home Page: http://www.de.ibm.com/kn/tu/tu_tu.html

-- Forwarded by Volker Gasse/Germany/IBM on 10.11.98 09:17
---


owner-emc-p...@majordomo.ieee.org on 10.11.98 06:44:57
Please respond to peterh...@aol.com
To: emc-p...@majordomo.ieee.org
cc:
Subject: LVD Standards


Hello All,

Can someone let me know if I can get the list of LVD standards published in
the OJ on the WWW?

Many thanks
Peter Hays
prterh...@aol.com




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: VDE 0565

1998-01-30 Thread Volker Gasse
Massimo,

VDE 0565 contains 8 parts, the one dealing with chokes
is part 2, part 2-1 and 2-2 which correspond to
EN 138000, EN 138100 and EN 138101. (all dated march 1997)
I could not find a corresponding IEC standard.

Mit freundlichen Gruessen/ Best regards, Volker Gasse

IBM Germany, Technical Relations/Product Safety, D3114/7103-91,
Tel: +49 7031-16-6796, Fax: -6916, e-mail: ga...@de.ibm.com



owner-emc-p...@majordomo.ieee.org on 30.01.98 16:03:15
Please respond to regr...@esaote.com @ internet
To: emc-p...@majordomo.ieee.org @ internet
cc:
Subject: VDE 0565






Hello!
Within the technical data of a power line choke I read: compliance with
VDE 0565. I guess it's a large German standard about safety (?) and
performances (?) of passive components used in power line filters.
Does anybody know the corresponding IEC or CENELEC standards (if any)?
The manufacturer claims a CE conformity. Is the compliance with this
national standard enough?
Thanks
Massimo

---
ESAOTE S.p.A. Massimo Polignano
Research  Product Development   Regulatory Affairs
Via di Caciolle,15   tel:+39.55.4229402
I- 50127 Florencefax:+39.55.4223305
   e-mail: regr...@esaote.com





ERGONOMICS/Color Red Restrictions

1997-01-23 Thread Volker Gasse
From: V. Gasse, Product Safety Authority.TEL 49-(0)7031-16-6796
  IBM Germany, Technical Relations...FAX 49-(0)7031-16-6916
  e-mail: ga...@de.ibm.com

What has been said about the use of red indicators in
Standards like IEC 73 and IEC 950 is correct.
Here Red Indicators are allowed, if it is clear that safety
is not involved.
However, some testhouses in Germany have restricted the
use of the color red only to be used as safety indicator, because
only if used exclusively in this sense, red is meaningful as
a safety relevant indication.
This interpretation is based on a German Safety Directive VBG 125.
Attempts to achieve harmonisation within other EU countries have been
made and are ongoing.


 Does anyone know if there are any formal restrictions to using  red
 colored lights for front panel displays and indicators?
 
 Is there a harmonized European standard or regulation or a specific
 national regulation that requires the restriction of the color red for
 warning, danger, etc.
 
 It seems it may have been a German ergonomic requirement before various
 standards were harmonized.  Can anyone shed some light on this issue?
 
 Don Umbdenstock
 Sensormatic
 
  End of mail text
 
 Additional SMTP headers from original mail item follow:
 Received: from ruebert.ieee.org by E-MAIL.COM (IBM VM SMTP V2R3) with TCP;
Wed, 22 Jan 97 16:49:09 EST
 Received: (from daemon¹localhost) by ruebert.ieee.org (8.7.5/8.7.3) id
OAA1032
  for emc-pstc-list; Wed, 22 Jan 1997 14:39:53 -0500 (EST)
 Message-ID:
c=US%a=_%p=Sensormatic%l=SENSORMATI/SFLAEXCHAN/00018084¹flgwyex1.
 ensormatic.com
 X-Mailer:  Microsoft Exchange Server Internet Mail Connector Version
4.0.837.3
 MIME-Version: 1.0
 Content-Type: text/plain; charset=us-ascii
 Content-Transfer-Encoding: 7bit
 Sender: owner-emc-pstc¹majordomo.ieee.org
 Precedence: bulk
 Reply-To: UMBDENSTOCK, DON UMBDENSTOC¹Sensormatic.com
 X-Resent-To: Multiple Recipients emc-pstc¹majordomo.ieee.org
 X-Listname: emc-pstc
 X-List-Description: Product Safety Tech. Committee, EMC Society
 X-Info: Help requests to  emc-pstc-request¹majordomo.ieee.org
 X-Info: ÜUnðSubscribe requests to  majordomo¹majordomo.ieee.org
 X-Moderator-Address: emc-pstc-approval¹majordomo.ieee.org

Mit freundlichen Gruessen/Best regards, V. Gasse


Re: Magnet wire

1996-08-30 Thread Volker Gasse
From: V. Gasse, Product Safety Authority.TEL 49-(0)7031-16-6796
  IBM, Technical Relations Germany,..FAX 49-(0)7031-16-6916

Egon,

being a member of the mentioned TC74 workgroup I would like to
point out, that Amd.4 of IEC 950 still only allows polyimid or FEP
wires to be used in Scl. 2.9.4.4 together with the Annex U tests.
The proposed widening of the scope to 'equivalent material'
could not be implemented into this amendment, and will happen
in IEC 950 3rd edition.

However there is an optional path to qualify the wire according
to 2.9.4.2 (Thin film insulation) with an electric strength test.

There is a common modification for EN 60950 Amd.4 in process
that would allow the use of other materials under Scl. 2.9.4.4.
This Common Modification is currently out for vote in the
National Committees.

I can backup your observation about the proactive role of Furukawa.
They are instrumental in improving the current standard especially
the Annex U, which in it's present form gives manufacturers and
testhouses a hard time.

Mit freundlichen Gruessen/Best regards, V. Gasse
INTERNET:  ga...@de.ibm.com
*** Forwarding note from I1467402--IBMMAIL  08/30/96 04:57 ***
=
List-Post: emc-pstc@listserv.ieee.org
Date: 29 Aug 96 21:18:45 EDT
From: Egon H. Varju 73132.¹CompuServe.COM
To: IEEE emc-pstc¹ieee.org
Cc: Shigeo Yamaguchi /c=JP/a=NIFTY/p=SVC/s=QWL01633/¹X400.compuserve.com
Subject: Re: Magnet wire

On 29/8/96  Peter Tarver wrote:

On the other side of the coin, Annex U only allows winding wire that is =
spirally wrapped in polyimide film, which the subject wire is not.  =
Properly used, I'm confident that TEX-E will make it through most any UL =
evaluation, particulalry for ITE, since that was my goal in doing the =
work.  The same probably applies to CSA (Egon?).  However, you will =
probably have more difficulty with the application elsewhere than in the =
northern bits of  North America.

There are several manufacturers of such extruded triple-insulated wire, many of
which, including Furukawa Electric, have received CSA certification and UL
recognition.  Of course I can not recommend or endorse any particular
manufacturer, and I'm sure that they are all equally suitable for the
application.  But purely by coincidence, I've also had occasion to meet with
Furukawa.

Both CSA and UL have accepted this kind of wire for use in ITE products.
Before
the inception of Annex U, this was accepted based on the requirements of thin
film insulation.  Test were done to special productions of the subject wire
that
were made especially for CSA/UL, with only 2 layers of insulation (both inner
and both outer ones).  There were no test failures.

Annex U has complicated things however, by specifying the specific materials
that can be used; namely polyimide.  The subject wire uses polyamide.  Not
being
a chemical or materials engineer, I really don't know what the difference is,
but needless to say, this is now no longer officially acceptable.  Of course,
since it was accepted before, I'm sure CSA and UL will continue to accept it
for
the time being.

The same policy appears to apply to most European agencies, since they had also
accepted this wire in the past.  However, there is one European agency that is
currently flatly refusing to accept this kind of wire.  They are being strictly
correct in rejecting this, since it doesn't comply with the wording in IEC950.
This situation is not expected to change until the publication of Ammendment 4

By the way, it is my PRIVATE opinion that IEC950 should not specify specific
materials at the exclusion of enything else.  I'm certainly not a materials
expert and neither are most agency product safety professionals, so I'd rather
see a test that can be performed.  If Annex U is suitable for certain types of
wire, then it should apply to all types.

At the time I was performing the evaluation on the subject winding wire, =
the proposal for Annex U had been made, but was not yet voted on in TC74 =
or in some similar state of being.  It was my understanding then that =
there was either one or a small core of magnet wire manufacturers in =
Europe (German, meguesses) that pushed for Annex U.  I urged Furukawa to =
take the issue up with TC 74, but haven't heard or read anything on topic =
since.

As it happens, I also urged them to lobby TC74.  In fact we managed to get them
a one hour presentation at the TC-74 meeting in Copenhagen last September, and
again at the Paris meeting in April.  To give credit where credit is due, UL
was
also instrumental in helping to secure these hearings (thanks Al and Lal|)

We also helped them prepare the technical arguments, test data and presentation
materials, which were received very well by the members of TC74.  They gave an
excellent presentation and, as a result, it is my understanding that the
wording
in IEC950 will change to allow for polyimide ... OR EQUIVALENT in compliance