RE: Are NTCs Safe to Use in Electrical Equipment

2000-07-20 Thread John Juhasz
Personally . . . my take on this specific issue is to find the cause NOT
treat the symptom . . . there is (obviously) something wrong there. I
wouldn't put my family (or myself) at risk doing something like adding NTCs
in my house wiring when that's not a normal thing to do . . . 
 
That's my personal opinion . . . 
 
John Juhasz
Fiber Options
Bohemia, NY

-Original Message-
From: Peter Tarver [mailto:ptar...@nortelnetworks.com]
Sent: Thursday, July 20, 2000 11:01 AM
To: Jim Eichner; emc-p...@majordomo.ieee.org
Subject: RE: Are NTCs Safe to Use in Electrical Equipment



I really don't have a clear idea of whether or not your solution will work.
Let us know. 

NTCs, as with most thermistors, get very hot when in their switched state.
For the NTC, that's it's steady-state condition.  I wouldn't put this in a
junction box with other wiring, unless you're absolutely certain all the
wiring can take the temperatures they'll encounter (for normal household
wiring, likely not).

Rather, for the sake of your experiment, put the NTC in a separate (probably
should be metal) box that's in-line with the receptacle, with appropriate
goesintas and goesouttas.  Be certain to use your best safety engineer's hat
for this activity.

Regards, 

Peter L. Tarver, PE 
Homologation Engineering 
Nortel Networks 
ptar...@nortelnetworks.com 


-Original Message- 
From: Jim Eichner [ mailto:jim.eich...@xantrex.com
<mailto:jim.eich...@xantrex.com> ] 
Sent: Monday, July 10, 2000 11:35 AM 
To: emc-p...@majordomo.ieee.org 
Subject: RE: Are NTCs Safe to Use in Electrical Equipment 



On the subject of NTC's, please allow me a slight detour from the compliance

world to the real world. 

I have a circuit in my house that blows light bulbs far more often than any 
other.  I can't determine any reason for this - the voltage seems normal and

there aren't any transient-producers on that same circuit (that I'm aware 
of).  Long life and rural-duty bulbs make little or no difference. 

Instead of figuring out the root cause, I'm considering resorting to trying 
to deal with the symptom (blown bulbs) by putting an NTC in series with the 
light fixture somewhere.  My thinking is that the mechanism that blows an 
incandescent bulb filament is related to the high inrush current into the 
cold (and therefore low R) filament, and the physical and thermal stresses 
that that inrush causes. 

Any comments on how likely this is to help, and whether or not I can safely 
put an NTC in an junction box full of wires?  I'd check the NTC's 
temperature under load (they get hot) and compare that the the temp. rating 
of the wires in the box.  I'd also insulate the bare legs of the NTC and try

to make sure it isn't touching anything else.  Anyone familiar with the 
failure modes of these things? 

Thanks, 

Jim 

-Original Message- 
From: Peter Merguerian [ mailto:pmerguer...@itl.co.il
<mailto:pmerguer...@itl.co.il> ] 
Sent: Monday, July 10, 2000 7:58 AM 
To: emc-p...@majordomo.ieee.org 
Subject: Are NTCs Safe to Use in Electrical Equipment 



Dear All, 

I have seen some design where NTCs are used to limit inrush currents in 
motion controllers. 

Q. Are NTCs safe and reliable as means to limit inrush currents? 

Q. Are there safety considerations to consider for circuits employing NTCs? 

Q. Are there any Approved (previously evaluated) NTC components out there? 


I appreciate all of your comments and/or links regarding the use of NTCs in 
electrical equipment. 

Thanks 

Peter Merguerian 
Managing Director 
Product Testing Division 
I.T.L. (Product Testing) Ltd. 
Hacharoshet 26, POB 211 
Or Yehuda 60251, Israel 

Tel: 972-3-5339022 Fax: 972-3-5339019 
e-mail: pmerguer...@itl.co.il 
website: http://www.itl.co.il <http://www.itl.co.il>  






--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Jim Bacher:  jim_bac...@mail.monarch.com 
 Michael Garretson:pstc_ad...@garretson.org 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 


--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Jim Bacher:  jim_bac...@mail.monarch.com 
 Michael Garretson:pstc_ad...@garretson.org 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 




RE: Are NTCs Safe to Use in Electrical Equipment

2000-07-20 Thread Peter Tarver
Peter -

Thermistors are in common usage and my limited experience with them
indicates they are reliable for their intended function.

The thermal issues have been discussed, and the usual regimen for high
temperature components applies.  I'm not aware of any other particular
safety concerns.

There are some NTC is UL's RCD, under Thermistor Type Devices (XGPU2).  I
don't know about certifications with other agencies or for other countries.

Regards,

Peter L. Tarver, PE
Homologation Engineering
Nortel Networks
ptar...@nortelnetworks.com


-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: Monday, July 10, 2000 7:58 AM
To: emc-pstc
Subject: Are NTCs Safe to Use in Electrical Equipment



Dear All,

I have seen some design where NTCs are used to limit inrush currents in
motion controllers. 

Q. Are NTCs safe and reliable as means to limit inrush currents?

Q. Are there safety considerations to consider for circuits employing NTCs?

Q. Are there any Approved (previously evaluated) NTC components out there?


I appreciate all of your comments and/or links regarding the use of NTCs in
electrical equipment.

Thanks 

Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org




RE: Are NTCs Safe to Use in Electrical Equipment

2000-07-20 Thread Peter Tarver
I really don't have a clear idea of whether or not your solution will work.
Let us know.

NTCs, as with most thermistors, get very hot when in their switched state.
For the NTC, that's it's steady-state condition.  I wouldn't put this in a
junction box with other wiring, unless you're absolutely certain all the
wiring can take the temperatures they'll encounter (for normal household
wiring, likely not).

Rather, for the sake of your experiment, put the NTC in a separate (probably
should be metal) box that's in-line with the receptacle, with appropriate
goesintas and goesouttas.  Be certain to use your best safety engineer's hat
for this activity.

Regards,

Peter L. Tarver, PE
Homologation Engineering
Nortel Networks
ptar...@nortelnetworks.com


-Original Message-
From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: Monday, July 10, 2000 11:35 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: Are NTCs Safe to Use in Electrical Equipment



On the subject of NTC's, please allow me a slight detour from the compliance
world to the real world.

I have a circuit in my house that blows light bulbs far more often than any
other.  I can't determine any reason for this - the voltage seems normal and
there aren't any transient-producers on that same circuit (that I'm aware
of).  Long life and rural-duty bulbs make little or no difference.

Instead of figuring out the root cause, I'm considering resorting to trying
to deal with the symptom (blown bulbs) by putting an NTC in series with the
light fixture somewhere.  My thinking is that the mechanism that blows an
incandescent bulb filament is related to the high inrush current into the
cold (and therefore low R) filament, and the physical and thermal stresses
that that inrush causes.

Any comments on how likely this is to help, and whether or not I can safely
put an NTC in an junction box full of wires?  I'd check the NTC's
temperature under load (they get hot) and compare that the the temp. rating
of the wires in the box.  I'd also insulate the bare legs of the NTC and try
to make sure it isn't touching anything else.  Anyone familiar with the
failure modes of these things?

Thanks,

Jim 

-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: Monday, July 10, 2000 7:58 AM
To: emc-p...@majordomo.ieee.org
Subject: Are NTCs Safe to Use in Electrical Equipment



Dear All,

I have seen some design where NTCs are used to limit inrush currents in
motion controllers. 

Q. Are NTCs safe and reliable as means to limit inrush currents?

Q. Are there safety considerations to consider for circuits employing NTCs?

Q. Are there any Approved (previously evaluated) NTC components out there?


I appreciate all of your comments and/or links regarding the use of NTCs in
electrical equipment.

Thanks 

Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org




RE: Are NTCs Safe to Use in Electrical Equipment

2000-07-10 Thread Scott Lacey

Jim,
Replacing the switch with a toggle type dimmer will greatly lengthen the
service life of bulbs. I have them in bedrooms and the bathroom. The main
intent was to prevent being jolted awake by bright lights if it were
necessary to get up at night. Because they look like ordinary light
switches, visitors have no trouble operating them.

As to using NTC thermistors, I would recommend that you NOT use them inside
of an electrical box. They do get quite hot, and even if they did not damage
wire insulation, you might be risking your insurance coverage in the event
of a fire. I have used them in the past to reduce inrush currents in power
supplies, but these were forced air cooled. Without forced cooling, they
provide almost no protection if power is re-applied almost immediately after
shutoff.

By the way, mechanical vibration may be the real culprit. I used to work in
a place where the bulbs failed with alarming frequency in our old shield
room. Leaving the ventilation blower off reduced the failure rate. Fragile
filaments hate to be shaken.

Scott Lacey

-Original Message-
From: owner-emc-p...@ieee.org [mailto:owner-emc-p...@ieee.org]On Behalf
Of Jim Eichner
Sent: Monday, July 10, 2000 2:35 PM
To: emc-p...@majordomo.ieee.org
Subject: RE: Are NTCs Safe to Use in Electrical Equipment



On the subject of NTC's, please allow me a slight detour from the compliance
world to the real world.

I have a circuit in my house that blows light bulbs far more often than any
other.  I can't determine any reason for this - the voltage seems normal and
there aren't any transient-producers on that same circuit (that I'm aware
of).  Long life and rural-duty bulbs make little or no difference.

Instead of figuring out the root cause, I'm considering resorting to trying
to deal with the symptom (blown bulbs) by putting an NTC in series with the
light fixture somewhere.  My thinking is that the mechanism that blows an
incandescent bulb filament is related to the high inrush current into the
cold (and therefore low R) filament, and the physical and thermal stresses
that that inrush causes.

Any comments on how likely this is to help, and whether or not I can safely
put an NTC in an junction box full of wires?  I'd check the NTC's
temperature under load (they get hot) and compare that the the temp. rating
of the wires in the box.  I'd also insulate the bare legs of the NTC and try
to make sure it isn't touching anything else.  Anyone familiar with the
failure modes of these things?

Thanks,

Jim

-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: Monday, July 10, 2000 7:58 AM
To: emc-p...@majordomo.ieee.org
Subject: Are NTCs Safe to Use in Electrical Equipment



Dear All,

I have seen some design where NTCs are used to limit inrush currents in
motion controllers.

Q. Are NTCs safe and reliable as means to limit inrush currents?

Q. Are there safety considerations to consider for circuits employing NTCs?

Q. Are there any Approved (previously evaluated) NTC components out there?


I appreciate all of your comments and/or links regarding the use of NTCs in
electrical equipment.

Thanks

Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Are NTCs Safe to Use in Electrical Equipment-short life of li ght bulbs

2000-07-10 Thread Jim Eichner

In the spirit of trying the simplest thing first, I'll swap the light switch
out for a new one and see what happens.

Thanks for the tip,

Jim 

-Original Message-
From: Robert Macy [mailto:m...@california.com]
Sent: Monday, July 10, 2000 12:49 PM
To: Jim Eichner; emc-p...@majordomo.ieee.org
Subject: Re: Are NTCs Safe to Use in Electrical Equipment-short life of
light bulbs


The subject of short life of light bulbs appears often on the
alt.home.repairnewsgroup.

People come up with potential sources of problems like "on the same branch
with the sump pump(or well pump)", and "long lines to the light bulb".
Their solutions were to put in those dimmer switches that cause the light
bulb to only get power at crossover "gently" turning them on.  And "lower
the voltage", and ... but the consensus of the true source of short
lived light bulbs is "either a poor neutral termination or the light switch
needs to be replaced!"

I thought this a suspect answer until after this experience.  My bathroom
fixture took out light bulbs at the rate of about 1 per month, but that made
sense with the concentration of heat inside its housing and with the ON/OFF
cycling it is subjected to.

Then one day the switch jammed up and had to be replaced.  After that
replacement, the fixture will keep bulbs for almost a year.

Evidently, the "bouncing" contacts really do a trip on the cold filaments.
You might be right in that an NTC (Negative Temperature Coefficient
Resistor) will make up for it.  But it hardly seems worth the effort.  (Plus
if it's not the switch, a potential of a poor neutral could really mean a
major problem in your system. )

  - Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112

-Original Message-
From: Jim Eichner 
To: emc-p...@majordomo.ieee.org 
List-Post: emc-pstc@listserv.ieee.org
Date: Monday, July 10, 2000 12:22 PM
Subject: RE: Are NTCs Safe to Use in Electrical Equipment


>
>On the subject of NTC's, please allow me a slight detour from the
compliance
>world to the real world.
>
>I have a circuit in my house that blows light bulbs far more often than any
>other.  I can't determine any reason for this - the voltage seems normal
and
>there aren't any transient-producers on that same circuit (that I'm aware
>of).  Long life and rural-duty bulbs make little or no difference.
>
>Instead of figuring out the root cause, I'm considering resorting to trying
>to deal with the symptom (blown bulbs) by putting an NTC in series with the
>light fixture somewhere.  My thinking is that the mechanism that blows an
>incandescent bulb filament is related to the high inrush current into the
>cold (and therefore low R) filament, and the physical and thermal stresses
>that that inrush causes.
>
>Any comments on how likely this is to help, and whether or not I can safely
>put an NTC in an junction box full of wires?  I'd check the NTC's
>temperature under load (they get hot) and compare that the the temp. rating
>of the wires in the box.  I'd also insulate the bare legs of the NTC and
try
>to make sure it isn't touching anything else.  Anyone familiar with the
>failure modes of these things?
>
>Thanks,
>
>Jim
>
>-Original Message-
>From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
>Sent: Monday, July 10, 2000 7:58 AM
>To: emc-p...@majordomo.ieee.org
>Subject: Are NTCs Safe to Use in Electrical Equipment
>
>
>
>Dear All,
>
>I have seen some design where NTCs are used to limit inrush currents in
>motion controllers.
>
>Q. Are NTCs safe and reliable as means to limit inrush currents?
>
>Q. Are there safety considerations to consider for circuits employing NTCs?
>
>Q. Are there any Approved (previously evaluated) NTC components out there?
>
>
>I appreciate all of your comments and/or links regarding the use of NTCs in
>electrical equipment.
>
>Thanks
>
>Peter Merguerian
>Managing Director
>Product Testing Division
>I.T.L. (Product Testing) Ltd.
>Hacharoshet 26, POB 211
>Or Yehuda 60251, Israel
>
>Tel: 972-3-5339022 Fax: 972-3-5339019
>e-mail: pmerguer...@itl.co.il
>website: http://www.itl.co.il
>
>
>
>
>
>
>---
>This message is from the IEEE EMC Society Product Safety
>Technical Committee emc-pstc discussion list.
>
>To cancel your subscription, send mail to:
> majord...@ieee.org
>with the single line:
> unsubscribe emc-pstc
>
>For help, send mail to the list administrators:
> Jim Bacher:  jim_bac...@mail

Re: Are NTCs Safe to Use in Electrical Equipment-short life of light bulbs

2000-07-10 Thread Robert Macy

The subject of short life of light bulbs appears often on the
alt.home.repairnewsgroup.

People come up with potential sources of problems like "on the same branch
with the sump pump(or well pump)", and "long lines to the light bulb".
Their solutions were to put in those dimmer switches that cause the light
bulb to only get power at crossover "gently" turning them on.  And "lower
the voltage", and ... but the consensus of the true source of short
lived light bulbs is "either a poor neutral termination or the light switch
needs to be replaced!"

I thought this a suspect answer until after this experience.  My bathroom
fixture took out light bulbs at the rate of about 1 per month, but that made
sense with the concentration of heat inside its housing and with the ON/OFF
cycling it is subjected to.

Then one day the switch jammed up and had to be replaced.  After that
replacement, the fixture will keep bulbs for almost a year.

Evidently, the "bouncing" contacts really do a trip on the cold filaments.
You might be right in that an NTC (Negative Temperature Coefficient
Resistor) will make up for it.  But it hardly seems worth the effort.  (Plus
if it's not the switch, a potential of a poor neutral could really mean a
major problem in your system. )

  - Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112

-Original Message-
From: Jim Eichner 
To: emc-p...@majordomo.ieee.org 
List-Post: emc-pstc@listserv.ieee.org
Date: Monday, July 10, 2000 12:22 PM
Subject: RE: Are NTCs Safe to Use in Electrical Equipment


>
>On the subject of NTC's, please allow me a slight detour from the
compliance
>world to the real world.
>
>I have a circuit in my house that blows light bulbs far more often than any
>other.  I can't determine any reason for this - the voltage seems normal
and
>there aren't any transient-producers on that same circuit (that I'm aware
>of).  Long life and rural-duty bulbs make little or no difference.
>
>Instead of figuring out the root cause, I'm considering resorting to trying
>to deal with the symptom (blown bulbs) by putting an NTC in series with the
>light fixture somewhere.  My thinking is that the mechanism that blows an
>incandescent bulb filament is related to the high inrush current into the
>cold (and therefore low R) filament, and the physical and thermal stresses
>that that inrush causes.
>
>Any comments on how likely this is to help, and whether or not I can safely
>put an NTC in an junction box full of wires?  I'd check the NTC's
>temperature under load (they get hot) and compare that the the temp. rating
>of the wires in the box.  I'd also insulate the bare legs of the NTC and
try
>to make sure it isn't touching anything else.  Anyone familiar with the
>failure modes of these things?
>
>Thanks,
>
>Jim
>
>-----Original Message-
>From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
>Sent: Monday, July 10, 2000 7:58 AM
>To: emc-p...@majordomo.ieee.org
>Subject: Are NTCs Safe to Use in Electrical Equipment
>
>
>
>Dear All,
>
>I have seen some design where NTCs are used to limit inrush currents in
>motion controllers.
>
>Q. Are NTCs safe and reliable as means to limit inrush currents?
>
>Q. Are there safety considerations to consider for circuits employing NTCs?
>
>Q. Are there any Approved (previously evaluated) NTC components out there?
>
>
>I appreciate all of your comments and/or links regarding the use of NTCs in
>electrical equipment.
>
>Thanks
>
>Peter Merguerian
>Managing Director
>Product Testing Division
>I.T.L. (Product Testing) Ltd.
>Hacharoshet 26, POB 211
>Or Yehuda 60251, Israel
>
>Tel: 972-3-5339022 Fax: 972-3-5339019
>e-mail: pmerguer...@itl.co.il
>website: http://www.itl.co.il
>
>
>
>
>
>
>---
>This message is from the IEEE EMC Society Product Safety
>Technical Committee emc-pstc discussion list.
>
>To cancel your subscription, send mail to:
> majord...@ieee.org
>with the single line:
> unsubscribe emc-pstc
>
>For help, send mail to the list administrators:
> Jim Bacher:  jim_bac...@mail.monarch.com
> Michael Garretson:pstc_ad...@garretson.org
>
>For policy questions, send mail to:
> Richard Nute:   ri...@ieee.org
>
>
>---
>This message is from the IEEE EMC Society Product Safety
>Technical Committee emc-pstc discussion list.
>
>To cancel your subscription, send mail to:
> ma

RE: Are NTCs Safe to Use in Electrical Equipment

2000-07-10 Thread Jim Eichner

On the subject of NTC's, please allow me a slight detour from the compliance
world to the real world.

I have a circuit in my house that blows light bulbs far more often than any
other.  I can't determine any reason for this - the voltage seems normal and
there aren't any transient-producers on that same circuit (that I'm aware
of).  Long life and rural-duty bulbs make little or no difference.

Instead of figuring out the root cause, I'm considering resorting to trying
to deal with the symptom (blown bulbs) by putting an NTC in series with the
light fixture somewhere.  My thinking is that the mechanism that blows an
incandescent bulb filament is related to the high inrush current into the
cold (and therefore low R) filament, and the physical and thermal stresses
that that inrush causes.

Any comments on how likely this is to help, and whether or not I can safely
put an NTC in an junction box full of wires?  I'd check the NTC's
temperature under load (they get hot) and compare that the the temp. rating
of the wires in the box.  I'd also insulate the bare legs of the NTC and try
to make sure it isn't touching anything else.  Anyone familiar with the
failure modes of these things?

Thanks,

Jim 

-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: Monday, July 10, 2000 7:58 AM
To: emc-p...@majordomo.ieee.org
Subject: Are NTCs Safe to Use in Electrical Equipment



Dear All,

I have seen some design where NTCs are used to limit inrush currents in
motion controllers. 

Q. Are NTCs safe and reliable as means to limit inrush currents?

Q. Are there safety considerations to consider for circuits employing NTCs?

Q. Are there any Approved (previously evaluated) NTC components out there?


I appreciate all of your comments and/or links regarding the use of NTCs in
electrical equipment.

Thanks 

Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Are NTCs Safe to Use in Electrical Equipment

2000-07-10 Thread Dick Grobner

Raychem (www.raychem.com)is one manufacturer that have PTC's that are UL
Recognized. I'm not sure if they have NTC's. We use their PTC's as
resettable overload devices (in transformers mainly) in our UL Certified
product line (medical). We have never had a problem with UL evaluating the
devices with PTC's. We have been using them successfully for 5 years. No
experience with NTC's but do know they can be used as a limiter for in-rush
currents.
List of companies that Mfg NTC's (UL recognized?)
Western Electronic Corp 805-482-8002
Sensor Scientific 800-524-1610 (www.sensorsci.com)
Ketema 714-630-0081 

FYI: Sensor Scientific has a planning guide for NTC's

Good Luck!

-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: Monday, July 10, 2000 9:58 AM
To: emc-p...@majordomo.ieee.org
Subject: Are NTCs Safe to Use in Electrical Equipment



Dear All,

I have seen some design where NTCs are used to limit inrush currents in
motion controllers. 

Q. Are NTCs safe and reliable as means to limit inrush currents?

Q. Are there safety considerations to consider for circuits employing NTCs?

Q. Are there any Approved (previously evaluated) NTC components out there?


I appreciate all of your comments and/or links regarding the use of NTCs in
electrical equipment.

Thanks 

Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Are NTCs Safe to Use in Electrical Equipment

2000-07-10 Thread Peter Merguerian

Dear All,

I have seen some design where NTCs are used to limit inrush currents in
motion controllers. 

Q. Are NTCs safe and reliable as means to limit inrush currents?

Q. Are there safety considerations to consider for circuits employing NTCs?

Q. Are there any Approved (previously evaluated) NTC components out there?


I appreciate all of your comments and/or links regarding the use of NTCs in
electrical equipment.

Thanks 

Peter Merguerian
Managing Director
Product Testing Division
I.T.L. (Product Testing) Ltd.
Hacharoshet 26, POB 211
Or Yehuda 60251, Israel

Tel: 972-3-5339022 Fax: 972-3-5339019
e-mail: pmerguer...@itl.co.il
website: http://www.itl.co.il 






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org