Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-06 Thread peter merguerian
Dear Friends,

Thanks very much to the input regarding CB Tripping During Fault Testing.
There were many thoughts on the subject and I am sure that next time the wall
CB trips during fault tests at your third part certification laboratory, you
have something to talk about - make sure they do not charge you for the
discussion time!

Peter




  _  

Do you Yahoo!?
Yahoo! Mail Plus http://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com
 - Powerful. Affordable. Sign up now h
tp://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com 



Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-06 Thread Rich Nute




Hi Peter:


My comments were based on the proposed requirement to
test the PE path with the circuit prospective current
transient, e.g. 200 amps from a 10,000-amp source for 
the period of time required to operate the overcurrent 
device  -- say less than a second or so.

(The 200 amps is a function of the contact resistances 
and the wire resistances, independent of the fault; 
the duration is a function of the overcurrent device.
200 amps is a reasonable number for plug-and-socket
cord-connected products.)

In order to get this maximum current, the fault must
be near zero ohms for the duration of the current
transient.  

To achieve near-zero ohms, the fault must be a large-
area fault.  A small-area fault is likely to fuse
open due to the current density and resistance at the
contact.

(I had the unfortunate experience that such a test by
a cert house used a small-area contact at a point where
no basic insulation fault could occur; the PWB PE path
was destroyed.  We repeated the test at a large-area
contact where basic insulation could fault, and the
PWB PE path passed.)

   What if the over current device operates, the earthing path
   is compromised by the fault, but not destroyed?  

I believe this is the objective of the proposal -- to
test the PE path with the circuit prospective current.
I would expect the compliance criterion to be no damage 
to the PE path.

   What if the fault is of nonnear-zero impedance, the earthing
   path is damaged, but not opened, and resetting of the
   breaker does occur, but at some point the breaker holds due
   to the relatively high impedance?

This scenario moves from withstanding the circuit 
prospective current to withstanding the steady-state
current just below the operating point of the over-
current device.  

I suggest that this is the objective of the existing 
requirement to test at twice the overcurrent device
rating or 25 amps, whichever is less.

   a relatively complex earthing path, I have prepared a
   separate e-mail that includes some construction details and
   empirical data for a product in my lab.  To be sent soon.

I appreciate you sharing this data.


Best regards,
Rich






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-05 Thread Peter L. Tarver

This thread has been largely theoretical.  Let's look at
some empirical test results for a product I just completed
testing.

The product has a redundant power configuration and nearly
identical current paths for each of two power supplies,
though one has about 2 in. longer traces on one side of one
of the boards involved.  There is no supplementary
overcurrent protection between the appliance inlets and the
input connections of the power supplies.

The earthing path involves the following:

filtered appliance inlet --
quick-disconnect on filter --
~1.5 in. No. 18 AWG terminated in a ring lug --
earthing stackup on a PEM stud of ring lug (from filter),
KEPS nut, ring lug for downstream earthing, KEPS nut --
~15 in. No. 18 AWG to a header style, soldered through-hole
interconnect --
traces --
soldered through-hole interconnect (for hot swappable power
supply) --
soldered through-hole interconnect --
traces --
soldered through-hole to a header style, interconnect --
~9 in. No. 18 AWG --
soldered through-hole to a header style, interconnect on the
power supply --
internal power supply magic --
large, open-frame heatsink on power supply

This testing was first performed in situ and as intended in
normal use.  I believe this test configuration should be
used for the purposes of safety certification.

In each of the following cases, the earthing impedance test
current was maintained for 2 minutes.  These tests were
performed precompliance.

I first tested the shortest path.

before faulting test current: 20.0 A
after faulting test current: 20.4 A

before faulting: 0.008 Ohm (a 0.016 V drop across the path)
after faulting: 0.006 Ohm (a 0.012 V drop across the path)

Surprising to have a lower impedance final result.  So much
so, I assumed I must have done something incorrectly,
reflowed a bad solder joint, initiated metal migration ...
something, either during the fault test, the earthing
impedance test or both.

Based on the product's construction, I knew that some
incidental current paths contributed to the very low
earthing impedance.  I then removed the assemblies of
interest from the main chassis and retested on the other of
the two circuits, so that only the current path of specific
interest was involved.  I left the main protective earthing
connection intact on the chassis.  Testing the longest path,

before faulting test current: 20.5 A
after faulting test current: 20.4 A

before faulting: 0.038 Ohm (a 0.77 V drop across the path)
after faulting: 0.037 Ohm (a 0.75 V drop across the path)

Still compliant at a ~20 A current value and still an
apparent *reduction* in the impedance of the earthing path.
This is not coincidence and double checking my test methods
along the way told me there were no errors.

I performed a third test on the same sample, longest path,
still outside the enclosure.

before faulting test current: 20.4 A
after faulting test current: 30.2 A

before faulting: 0.036 Ohm (a 0.74 V drop across the path)
after faulting: 0.041 Ohm (a 1.24 V drop across the path)


The above testing was repeated in situ on a new test sample.
The earthing impedance test, before and after, was set to 40
A.  The results were very similar to those for the first in
situ test, with almost identical calculated impedances, and
the earthing path withstood the 40 A current very nicely.

It should be noted that I performed the fault on a 120V, 20
A branch circuit.  The product will be rated for 240 V and
CSA 22.2 No. 0.4 requires the test be performed on a circuit
with the voltage at the highest rating marked on the
product, but I only have 20 A circuits on 120V circuits; my
208 V circuits, which I can boost to 240V, are all 30 A.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-05 Thread Peter L. Tarver


 From: Rich Nute
 Sent: Wednesday, February 05, 2003 12:20 PM

 Hi Peter:

Hi, Rich.

 This test implies a near 0-ohm fault to the
 PE, where the PE circuit includes a PE trace
 on the PWB.

That's a reasonable assumption and is convenient for the
purposes of testing.  It is unlikely to be the only fault
case, but that's irrelevant to compliance with the standard
and should be considered internally, to the level of pain
tolerable by any particular company.

 If there is a zero-ohm fault, an over-current
 device, somewhere, will operate.  (Indeed, this
 is the function of the PE circuit!)  A zero-ohm
 fault implies a large-area contact with a fair
 amount of contact pressure for at least the
 period of time to operate the overcurrent device.

 Consequently, the product must be removed from
 service and repaired before being returned to
 service.

What if the over current device operates, the earthing path
is compromised by the fault, but not destroyed?  Let us not
forget that there are many who will reset a circuit breaker
ad infinitum, to failure, reimposing a fault repeatedly.  (I
spoke this afternoon to a coworker who is also landlord.
One tenant consistently overloaded a branch circuit and
reset the circuit breaker repeatedly, until it failed to
close.)

Each resetting of the circuit imposes a similar fault, with
a progressively weaker earthing circuit.  Let us assume that
at some point short of circuit breaker failure, the earthing
path becomes compromised enough that the branch circuit does
not open the circuit.

What if the fault is of nonnear-zero impedance, the earthing
path is damaged, but not opened, and resetting of the
breaker does occur, but at some point the breaker holds due
to the relatively high impedance?

We can let our imaginations wander from there and each
believe as we will that thus and such will or will not,
could or could not happen and debate the probabilities until
the ruminants return hither.  Bad stuff happens: dead-front
switchboards explode, fires are started by minor appliances
with safety certification house marks or questionable wiring
practices, trains jump the tracks...


 If the 0-ohm fault is on the PWB, then the PWB
 will need to be replaced.  It is difficult to
 imagine a fault of 0-ohm proportions that could
 be repaired without replacing the PWB assembly.
 Indeed, if the PWB PE circuit carries the high
 transient current, it may very well be that the
 supply conductors on the PWB may be blown off
 the PWB.  So, I question whether the compliance
 criteria need be applied.

If.  The fault might occur anywhere in the earthing path.
To give an idea of how a relatively simple idea can lead to
a relatively complex earthing path, I have prepared a
separate e-mail that includes some construction details and
empirical data for a product in my lab.  To be sent soon.


There is also the much more variable solder
 in the earthing
path.  While manufacturing techniques have
 come a long way
in terms of consistency, the amount of solder
 in a joint and
the quality of the joint itself can play a
 significant role.
It should be expected that a lower melting
 point solder will
perform less well than a higher melting point solder.
Appropriate process controls will have a
 positive effect.

 An ideal solder joint involves an amalgam at
 the joint with the conductors.  The properties
 of the amalgam are typically greater than
 the property of either material alone.  As in
 copper plumbing joints, an idea joint has very
 little solder between the two components being
 joined.

And yet, mass production of electrical and electronic
products, while generally yielding consistent-quality
products when produced in a conscientious environment, can
still have variability and initially undetectable problems
that even HALT testing can't predict and HASS testing can't
weed out.  There will be very few companies with zero field
returns where cracks develop in a laminate, solder joints
fail or are imperfect to the point of eventually some flaw
eventually rears its head.

The goal is to at least offer the impression that a
construction will not yield an insidious hazard at some
point in the future.  My recent experience has led me to
believe that, aside from a few head scratching results, the
test is *very* simple to perform and requires almost *no*
additional test equipment, over and above an earthing
impedance test setup and a modicum of ingenuity inherent in
any engineer.

 My guess would be that the current path will be
 that of least resistance, which will minimize
 the current through the solder around the joint.
 So, I would doubt that the solder (of a good
 joint) would be much affected by the current
 pulse.


 Best regards,
 Rich

There's no question that incidental currents can have a
positive effect, even if not considered reliable.  There's
no denying that it is possible to comply with the test, even
for a seemingly complex earthing path.  There is every

Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-05 Thread Rich Nute




Hi Peter:


   Not quite.  I^2·t will tell you the let through current of
   the copper trace, but will not necessarily tell you if the
   construction will be compliant.  The compliance criteria for
   this test include:
   
   * no damage to the trace (no lifting, probably no
   discoloration)
   * no damage to the PWB (no delamination, burning; I don't
   know if this includes burning off of solder mask)
   * before and after earthing impedance must comply with the
   0.1 Ohm maximum impedance
   * no change in earthing impedance greater than 10% of the
   before and after earthing impedance results

This test implies a near 0-ohm fault to the
PE, where the PE circuit includes a PE trace 
on the PWB.

If there is a zero-ohm fault, an over-current
device, somewhere, will operate.  (Indeed, this
is the function of the PE circuit!)  A zero-ohm
fault implies a large-area contact with a fair
amount of contact pressure for at least the 
period of time to operate the overcurrent device.

(A point-contact fault would blow a hole in the
copper trace due to very high current density
at the point of contact.)

Consequently, the product must be removed from
service and repaired before being returned to
service.

If the 0-ohm fault is on the PWB, then the PWB
will need to be replaced.  It is difficult to
imagine a fault of 0-ohm proportions that could
be repaired without replacing the PWB assembly.
Indeed, if the PWB PE circuit carries the high
transient current, it may very well be that the
supply conductors on the PWB may be blown off
the PWB.  So, I question whether the compliance 
criteria need be applied.

   There is also the much more variable solder in the earthing
   path.  While manufacturing techniques have come a long way
   in terms of consistency, the amount of solder in a joint and
   the quality of the joint itself can play a significant role.
   It should be expected that a lower melting point solder will
   perform less well than a higher melting point solder.
   Appropriate process controls will have a positive effect.

An ideal solder joint involves an amalgam at 
the joint with the conductors.  The properties
of the amalgam are typically greater than 
the property of either material alone.  As in
copper plumbing joints, an idea joint has very
little solder between the two components being
joined.

My guess would be that the current path will be
that of least resistance, which will minimize
the current through the solder around the joint.
So, I would doubt that the solder (of a good
joint) would be much affected by the current
pulse.


Best regards,
Rich





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-05 Thread Rich Nute




Hi Chris:


   It seems funny to me that most equipment has been historically made with
18AWG protective ground pigtail wires; and 25A ground fault tests have been
used for years.  
   
   Now that PC  traces are being used for protective ground; we want to test
with 200A or greater impulse currents?  I'm curious about what would happen to
your typical 18AWG line cord during this test.  I'm wondering if the line cord
would fuse open? 

The 18 AWG readily passes the circuit prospective
current test.  This is because the current is
transient, and is cut off before the wire in the 
cord can reach fusing temperature.

   One is at www.kepcopower.com/nomovax2.htm this is a nomograph of maximum
operating current, AWG and IR drop in the conductor.  The point A is
generally considered the point of maximum IR drop.  If you draw a line from
point A, through a wire gauge size; you'll get a max current.  Of course
this is steady state current; and the nomograph assumes a single wire.  Wire
bundles would be a worse case.  It's too bad that this chart doesn't contain
the fuse values for the wires as well (the  I squared * T values).

Fusing currents for wires are published in:

Reference Data for Radio Engineers
International Telephone and Telegraph Corporation
67 Broad Street
New York 4, New York

This reference says Courtesy of Automatic 
Electric Company, Chicago, Illinois.

The approximate fusing current for 18 AWG copper 
is 82.9 amperes.

The approximate fusing current of wires can be 
calculated from:

I  =  (K) * (d**3/2)

where d is the diameter of the wire, in inches
  K is a constant that depends on the metal

Here are some values for K:

copper:10,244
aluminum:   7,585
silver: 5,230
iron:   3,148
tin:1,642

The Standard Handbook for Electrical Engineers
by Fink and Beatty has some additional data,
including curves of current and time for each
AWG.  A couple of points for 18 AWG:

   0.1 second:~720 amps
   1.0 second:~220 amps
  10.0 second:~ 82 amps
   
   3.  The third problem is mechanical.  Once Earth ground brought to a pad
on the circuitboard; then there is still the issue of getting a good
mechanical mate to the chassis with a wide surface area.  If the connection is
made through a couple of teeth on a star washer; then there is a potential for
localized heating.   I'm just going to maximize surface contact area for this
one.  I'm also considering using multiple board to chassis connection
locations.  Every screw that connects the board to chassis is a potential
Earth ground connection.

The problem with mechanical connections to PWBs 
by means of screws is that the PWB base material 
is a plastic and is subject to cold-flow under 
compressive conditions.  In the long-term, the
connection can loosen.  

Not everyone pays attention to this, and, in 
practice, it is rarely a problem.

One way around this is to use a wire from the 
board to the chassis.


Best regards,
Rich






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-04 Thread Gary McInturff

Lou,
I'm not proposing anything mind you, but you could save some space if 
you had
a PWB mounted appliance inlet and you would still have to get the PEC to the
chassis. 
Gary


From: Lou Aiken [mailto:ai...@gulftel.com]
Sent: Tuesday, February 04, 2003 8:36 AM
To: Peter L. Tarver; emc-p...@majordomo.ieee.org
Subject: Re: EN60950 protective conductor test (was Re: Circuit Breaker
Tripping Dring Fault Tests)



Why not provide a fuse to prevent deterioration of the PE trace on a PCB?

Joking of course, but now that I have your attention, I would like to see
this thread move away from the physics and discuss what practical reasons
there are for using PC traces to provide earth fault circuits.


Lou Aiken, LaMer LLC
27109 Palmetto Drive
Orange Beach, AL
36561 USA

tel ++ 1 251 981 6786
fax ++ 1 251 981 3054
Cell ++ 1 251 979 4648

From: Peter L. Tarver peter.tar...@sanmina-sci.com
To: emc-p...@majordomo.ieee.org
Sent: Tuesday, February 04, 2003 9:53 AM
Subject: RE: EN60950 protective conductor test (was Re: Circuit Breaker
Tripping Dring Fault Tests)



Not quite.  I^2·t will tell you the let through current of
the copper trace, but will not necessarily tell you if the
construction will be compliant.  The compliance criteria for
this test include:

* no damage to the trace (no lifting, probably no
discoloration)
* no damage to the PWB (no delamination, burning; I don't
know if this includes burning off of solder mask)
* before and after earthing impedance must comply with the
0.1 Ohm maximum impedance
* no change in earthing impedance greater than 10% of the
before and after earthing impedance results

There is also the much more variable solder in the earthing
path.  While manufacturing techniques have come a long way
in terms of consistency, the amount of solder in a joint and
the quality of the joint itself can play a significant role.
It should be expected that a lower melting point solder will
perform less well than a higher melting point solder.
Appropriate process controls will have a positive effect.

These are some of the reasons some form of safety agency
factory auditing of this type of construction is normal.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com


 -Original Message-
 From: Chris Maxwell
 Sent: Tuesday, February 04, 2003 5:32 AM


 Exactly!

 Chris Maxwell


  -Original Message-
  From: drcuthbert [SMTP:drcuthb...@micron.com]
  Sent: Monday, February 03, 2003 7:50 PM
 
  What is needed is the I squared t rating of the
 breaker. Then the (I^2)(t)
  rating of the PCB. Then you know if the PCB can
 take it.
 
 Dave Cuthbert



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-04 Thread Chris Maxwell

PC traces are easier to assemble and the assembly can be done in a tighter
space.  I think (just an opinion)  that proper design could make this type of
system more reliable as well with less chances of wires coming loose...

 -Original Message-
 From: Lou Aiken [SMTP:ai...@gulftel.com]
 Sent: Tuesday, February 04, 2003 11:36 AM
 To:   Peter L. Tarver; emc-p...@majordomo.ieee.org
 Subject:  Re: EN60950 protective conductor test (was Re: Circuit Breaker
Tripping Dring Fault Tests)
 
 
 Why not provide a fuse to prevent deterioration of the PE trace on a PCB?
 
 Joking of course, but now that I have your attention, I would like to see
 this thread move away from the physics and discuss what practical reasons
 there are for using PC traces to provide earth fault circuits.
 
 
 Lou Aiken, LaMer LLC
 27109 Palmetto Drive
 Orange Beach, AL
 36561 USA
 
 tel ++ 1 251 981 6786
 fax ++ 1 251 981 3054
 Cell ++ 1 251 979 4648
 - Original Message -
 From: Peter L. Tarver peter.tar...@sanmina-sci.com
 To: emc-p...@majordomo.ieee.org
 Sent: Tuesday, February 04, 2003 9:53 AM
 Subject: RE: EN60950 protective conductor test (was Re: Circuit Breaker
 Tripping Dring Fault Tests)
 
 
 
 Not quite.  I^2·t will tell you the let through current of
 the copper trace, but will not necessarily tell you if the
 construction will be compliant.  The compliance criteria for
 this test include:
 
 * no damage to the trace (no lifting, probably no
 discoloration)
 * no damage to the PWB (no delamination, burning; I don't
 know if this includes burning off of solder mask)
 * before and after earthing impedance must comply with the
 0.1 Ohm maximum impedance
 * no change in earthing impedance greater than 10% of the
 before and after earthing impedance results
 
 There is also the much more variable solder in the earthing
 path.  While manufacturing techniques have come a long way
 in terms of consistency, the amount of solder in a joint and
 the quality of the joint itself can play a significant role.
 It should be expected that a lower melting point solder will
 perform less well than a higher melting point solder.
 Appropriate process controls will have a positive effect.
 
 These are some of the reasons some form of safety agency
 factory auditing of this type of construction is normal.
 
 
 Regards,
 
 Peter L. Tarver, PE
 Product Safety Manager
 Sanmina-SCI Homologation Services
 San Jose, CA
 peter.tar...@sanmina-sci.com
 
 
  -Original Message-
  From: Chris Maxwell
  Sent: Tuesday, February 04, 2003 5:32 AM
 
 
  Exactly!
 
  Chris Maxwell
 
 
   -Original Message-
   From: drcuthbert [SMTP:drcuthb...@micron.com]
   Sent: Monday, February 03, 2003 7:50 PM
  
   What is needed is the I squared t rating of the
  breaker. Then the (I^2)(t)
   rating of the PCB. Then you know if the PCB can
  take it.
  
  Dave Cuthbert
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list. 
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard

Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-04 Thread John Barnes

Chris,
Douglas Brooks wrote an article about Preese's and Onderdonk's equations
for fusing currents of wires, which was published in Printed Circuit
Magazine.  It can be downloaded from UltraCAD's web site at
http://www.ultracad.com/fusing.pdf

Appendix F of the book that I am writing for Kluwer, Robust Electronic
Design Reference, will cover the ampacity (current-carrying capacity) of
wires, printed circuit board traces, busbars, etc.  The manuscript is
due August 1st, so I had better get back to my writing...

John Barnes KS4GL, PE, NCE, ESDC Eng, SM IEEE
dBi Corporation
http://www.dbicorporation.com/


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-04 Thread John Woodgate

I read in !emc-pstc that Chris Maxwell chris.maxw...@nettest.com wrote
(in 83d652574e7af740873674f9fc12dbaaf7e...@utexh1w2.gnnettest.com)
about 'EN60950 protective conductor test (was Re: Circuit Breaker
Tripping Dring Fault Tests)' on Tue, 4 Feb 2003:

This would make heat dissipation different; and I would assume that it would 
make the fusing characteristics (I^2)(t) slightly different as well.

Or even a lot different. The reason why I personally would not use a
printed board trace as a PEC is that boards can develop cracks and thin
copper patches, so I couldn't guarantee that every board would stand the
test that the test sample passed. In this case, I don't think
potentially destructive sample testing is adequate, either. The PEC
needs to be 'four nines' reliable.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-04 Thread Lou Aiken

Why not provide a fuse to prevent deterioration of the PE trace on a PCB?

Joking of course, but now that I have your attention, I would like to see
this thread move away from the physics and discuss what practical reasons
there are for using PC traces to provide earth fault circuits.


Lou Aiken, LaMer LLC
27109 Palmetto Drive
Orange Beach, AL
36561 USA

tel ++ 1 251 981 6786
fax ++ 1 251 981 3054
Cell ++ 1 251 979 4648

From: Peter L. Tarver peter.tar...@sanmina-sci.com
To: emc-p...@majordomo.ieee.org
Sent: Tuesday, February 04, 2003 9:53 AM
Subject: RE: EN60950 protective conductor test (was Re: Circuit Breaker
Tripping Dring Fault Tests)



Not quite.  I^2·t will tell you the let through current of
the copper trace, but will not necessarily tell you if the
construction will be compliant.  The compliance criteria for
this test include:

* no damage to the trace (no lifting, probably no
discoloration)
* no damage to the PWB (no delamination, burning; I don't
know if this includes burning off of solder mask)
* before and after earthing impedance must comply with the
0.1 Ohm maximum impedance
* no change in earthing impedance greater than 10% of the
before and after earthing impedance results

There is also the much more variable solder in the earthing
path.  While manufacturing techniques have come a long way
in terms of consistency, the amount of solder in a joint and
the quality of the joint itself can play a significant role.
It should be expected that a lower melting point solder will
perform less well than a higher melting point solder.
Appropriate process controls will have a positive effect.

These are some of the reasons some form of safety agency
factory auditing of this type of construction is normal.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com


 -Original Message-
 From: Chris Maxwell
 Sent: Tuesday, February 04, 2003 5:32 AM


 Exactly!

 Chris Maxwell


  -Original Message-
  From: drcuthbert [SMTP:drcuthb...@micron.com]
  Sent: Monday, February 03, 2003 7:50 PM
 
  What is needed is the I squared t rating of the
 breaker. Then the (I^2)(t)
  rating of the PCB. Then you know if the PCB can
 take it.
 
 Dave Cuthbert



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-04 Thread Peter L. Tarver

Not quite.  I^2·t will tell you the let through current of
the copper trace, but will not necessarily tell you if the
construction will be compliant.  The compliance criteria for
this test include:

* no damage to the trace (no lifting, probably no
discoloration)
* no damage to the PWB (no delamination, burning; I don't
know if this includes burning off of solder mask)
* before and after earthing impedance must comply with the
0.1 Ohm maximum impedance
* no change in earthing impedance greater than 10% of the
before and after earthing impedance results

There is also the much more variable solder in the earthing
path.  While manufacturing techniques have come a long way
in terms of consistency, the amount of solder in a joint and
the quality of the joint itself can play a significant role.
It should be expected that a lower melting point solder will
perform less well than a higher melting point solder.
Appropriate process controls will have a positive effect.

These are some of the reasons some form of safety agency
factory auditing of this type of construction is normal.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com


 -Original Message-
 From: Chris Maxwell
 Sent: Tuesday, February 04, 2003 5:32 AM


 Exactly!

 Chris Maxwell


  -Original Message-
  From:   drcuthbert [SMTP:drcuthb...@micron.com]
  Sent:   Monday, February 03, 2003 7:50 PM
 
  What is needed is the I squared t rating of the
 breaker. Then the (I^2)(t)
  rating of the PCB. Then you know if the PCB can
 take it.
 
 Dave Cuthbert



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-04 Thread Chris Maxwell

Exactly!  There is lots of data and tables available on the web for steady
state current; but I haven't found any sources that would give the (I^2)(t)
values for wires or PCB traces.   Such tables would take a great deal of
mystery out of this subject.  Right now, the best guess is to go by steady
state current rating; but there must be faults in this.  A PCB trace that can
handle 10 Amps of steady state current has a totally different geometry than a
wire that can handle 10 Amps of steady state current.  This would make heat
dissipation different; and I would assume that it would make the fusing
characteristics (I^2)(t) slightly different as well.

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 




 -Original Message-
 From: drcuthbert [SMTP:drcuthb...@micron.com]
 Sent: Monday, February 03, 2003 7:50 PM
 To:   'John Woodgate'; emc-p...@majordomo.ieee.org
 Subject:  RE: EN60950 protective conductor test (was Re: Circuit Breaker
Tripping Dring Fault Tests)
 
 
 What is needed is the I squared t rating of the breaker. Then the (I^2)(t)
 rating of the PCB. Then you know if the PCB can take it. 
 
Dave Cuthbert
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-03 Thread John Woodgate

I read in !emc-pstc that cnew...@xycom.com wrote (in 85256CC2.005F2DA4.
0...@notes.fw.xycom.com) about 'EN60950 protective conductor test (was
Re: Circuit Breaker  Tripping Dring Fault Tests)' on Mon, 3 Feb
2003:

My UL guy tells me that I should expect the typical service type CB to be
rated
up to  + 10%.  So it appears that  I need to concern myself with a burst of
current
up to approximately 22 amps for the 20 amp AC circuit that my product is being
evaluated for.

Until it trips, your CB lets through the **whole 200 A**. The trip
current is practically irrelevant in this test; what matters is the trip
TIME. The board trace may stand 200 A for 50 ms but not for 100 ms.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-03 Thread Peter L. Tarver

I've had extensive discussion with UL regarding the
performance of this test.  Below are my comments, taken from
these discussions.

 -Original Message-
 From: Carl Newton
 Sent: Monday, February 03, 2003 9:20 AM


 1.  Three samples are tested;

Intended to demonstrate repeatability of the test results.

 2.  Trace resistance is measured before and after
 test.  Resistance cannot
   exceed 0.1 ohms, and cannot change more
 than 10% after test;

The test datasheets I have from UL state the impedance
before and after applying the fault is measured using an
ohmmeter.  I intend to use a lower current version of the
earthing impedance test for this purpose (say, 20A, rather
than 40A).

 3.  AC source is 240 Vac, 200 amps (20A circuit
 breaker X 10), power factor
   is 75 - 80% through shorted bus bars with a
 20/30 A (20 in my case)
 service
   entrance type circuit breaker in series
 with the testing terminals.  The
 circuit
   breaker is connected to the bus bars by
 1.22 m (4 ft.) of #12 AWG wire.

Some of this information is for the UL lab technician, in
order to increase the reproducibility of the results and
protect their equipment.  For instance:

*no power factor is specified in CSA 22.2 No. 0.4
*bus bars are what exist in UL's lab and are not a
requirement to perform this test
*UL's power panels this test is derived from will likely be
capable of very large fault currents, so they will add
resistance to limit the current
*a service entrance circuit breaker is not necessary; this
was chosen for it's larger interrupting rating, so as to not
degrade the breaker too quickly under repeated fault
conditions; you can use a plain old branch circuit breaker.


 4.  The test circuit is connected to the DUT via
 the grounding lead of the
   1.82 m (6 ft) power supply cord.  If cord
 is not provided, then #16 AWG
   wire is used.

It's anyone's guess why a No. 16

 5.  Test continues until ultimate results occur;
 e.g. CB trips, trace opens,
 etc.

 Carl

The preliminary testing I've performed in my lab indicates
that the fault portion of the test can be over very quickly
(probably ms, but I haven't tried to measure it), even with
No. 18 AWG conductors and four connectorized interfaces
involved.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-03 Thread cnew...@xycom.com



Lou,

It's my impression that the typical switching power supply, such as
that  used for ITE type equipment, will apply basic insulation between
the primary circuits and earthed conductive parts on the primary side.
They do this in order to minimize the creepage/clearance requirements
and subsequently reduce the size of the supply.  I'm referring specifically
to Tables 2G and 2F of 60950.

Thanks,
 Carl




From: Lou Aiken ai...@gulftel.com on 02/03/2003 01:46 PM

To:   Carl Newton/XYCOM@XYCOM, emc-p...@majordomo.ieee.org
cc:

Subject:  Re: EN60950 protective conductor test (was Re: Circuit Breaker
  Tripping Dring Fault Tests)



Carl, If the primary supply circuitry and components provide double or
reinforced insulation, nothing can become live in the event of a single
fault, the test becomes unnecessary, and I would argue that fact.

If the design does not provide double or reinforced insulation, the test
sounds applicable from points that could become live in case of a basic
insulation fault.

Regards,
Lou Aiken, LaMer LLC
27109 Palmetto Drive
Orange Beach, AL
36561 USA

tel ++ 1 251 981 6786
fax ++ 1 251 981 3054
Cell ++ 1 251 979 4648

From: cnew...@xycom.com
To: emc-p...@majordomo.ieee.org
Sent: Monday, February 03, 2003 11:19 AM
Subject: RE: EN60950 protective conductor test (was Re: Circuit Breaker
Tripping Dring Fault Tests)





 A slight divergence from the EN specifically, but I thought that the
 following would be helpful to this thread:

 I am presently working this issue with a UL engineer in accordance with
 UL 60950, 3rd Edition.   I also have the UL 60950 3rd Ed. Test Data
Sheets.
 Their Protective Earthing Trace Earth Fault Current Test, UL Doc.
190.eng,
 per Section 2.6.3.3 requires the following in my case:

 1.  Three samples are tested;

 2.  Trace resistance is measured before and after test.  Resistance cannot
   exceed 0.1 ohms, and cannot change more than 10% after test;

 3.  AC source is 240 Vac, 200 amps (20A circuit breaker X 10), power
factor
   is 75 - 80% through shorted bus bars with a 20/30 A (20 in my case)
 service
   entrance type circuit breaker in series with the testing terminals.
The
 circuit
   breaker is connected to the bus bars by 1.22 m (4 ft.) of #12 AWG
wire.

 4.  The test circuit is connected to the DUT via the grounding lead of the
   1.82 m (6 ft) power supply cord.  If cord is not provided, then #16
AWG
   wire is used.

 5.  Test continues until ultimate results occur; e.g. CB trips, trace
opens,
 etc.

 My UL guy tells me that I should expect the typical service type CB to be
rated
 up to  + 10%.  So it appears that  I need to concern myself with a burst
of
 current
 up to approximately 22 amps for the 20 amp AC circuit that my product is
being
 evaluated for.

 Carl





 From: Chris Maxwell chris.maxw...@nettest.com on 02/03/2003 09:29 AM

 Please respond to Chris Maxwell chris.maxw...@nettest.com

 To:   emc-p...@majordomo.ieee.org
 cc:(bcc: Carl Newton/XYCOM)

 Subject:  RE: EN60950 protective conductor test (was Re: Circuit Breaker
   Tripping Dring Fault Tests)




 This thread has been interesting.  I am, at this moment, considering a
design
 where I am almost forced to use a PC (printed circuit) trace for Earth
ground.

 It seems funny to me that most equipment has been historically made with
18AWG
 protective ground pigtail wires; and 25A ground fault tests have been used
for
 years.

 Now that PC  traces are being used for protective ground; we want to test
with
 200A or greater impulse currents?  I'm curious about what would happen to
your
 typical 18AWG line cord during this test.  I'm wondering if the line cord
would
 fuse open?

 There are a couple of handy charts on the web.

 One is at www.kepcopower.com/nomovax2.htm this is a nomograph of maximum
 operating current, AWG and IR drop in the conductor.  The point A is
generally
 considered the point of maximum IR drop.  If you draw a line from point
A,
 through a wire gauge size; you'll get a max current.  Of course this is
steady
 state current; and the nomograph assumes a single wire.  Wire bundles
would be a
 worse case.  It's too bad that this chart doesn't contain the fuse
values for
 the wires as well (the  I squared * T values).

 Another is at www.circuitboards.com/capacity.php3.   This is a chart of
max
 current for PC traces.  Remember that this is for TRACES and planes only;
it
 doesn't say anything about vias and other potential problems.

 At first pass, it seems that a trace size to handle twice the power cord's
max
 current, (from the nomograph) with a 10degC trace temperature rise (from
the PC
 trace chart), would be a good rule of thumb for the trace size.  If I have
room,
 I'll just make it bigger.  Once we pay for the PC board fabrication, the
copper
 is free!

 Even with an  adequately sized trace; I can think of a few potential
problems
 with the trace to chassis connection:

 1.  Many layout people open up PC traces

Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-03 Thread Lou Aiken

Carl, If the primary supply circuitry and components provide double or
reinforced insulation, nothing can become live in the event of a single
fault, the test becomes unnecessary, and I would argue that fact.

If the design does not provide double or reinforced insulation, the test
sounds applicable from points that could become live in case of a basic
insulation fault.

Regards,
Lou Aiken, LaMer LLC
27109 Palmetto Drive
Orange Beach, AL
36561 USA

tel ++ 1 251 981 6786
fax ++ 1 251 981 3054
Cell ++ 1 251 979 4648

From: cnew...@xycom.com
To: emc-p...@majordomo.ieee.org
Sent: Monday, February 03, 2003 11:19 AM
Subject: RE: EN60950 protective conductor test (was Re: Circuit Breaker
Tripping Dring Fault Tests)





 A slight divergence from the EN specifically, but I thought that the
 following would be helpful to this thread:

 I am presently working this issue with a UL engineer in accordance with
 UL 60950, 3rd Edition.   I also have the UL 60950 3rd Ed. Test Data
Sheets.
 Their Protective Earthing Trace Earth Fault Current Test, UL Doc.
190.eng,
 per Section 2.6.3.3 requires the following in my case:

 1.  Three samples are tested;

 2.  Trace resistance is measured before and after test.  Resistance cannot
   exceed 0.1 ohms, and cannot change more than 10% after test;

 3.  AC source is 240 Vac, 200 amps (20A circuit breaker X 10), power
factor
   is 75 - 80% through shorted bus bars with a 20/30 A (20 in my case)
 service
   entrance type circuit breaker in series with the testing terminals.
The
 circuit
   breaker is connected to the bus bars by 1.22 m (4 ft.) of #12 AWG
wire.

 4.  The test circuit is connected to the DUT via the grounding lead of the
   1.82 m (6 ft) power supply cord.  If cord is not provided, then #16
AWG
   wire is used.

 5.  Test continues until ultimate results occur; e.g. CB trips, trace
opens,
 etc.

 My UL guy tells me that I should expect the typical service type CB to be
rated
 up to  + 10%.  So it appears that  I need to concern myself with a burst
of
 current
 up to approximately 22 amps for the 20 amp AC circuit that my product is
being
 evaluated for.

 Carl





 From: Chris Maxwell chris.maxw...@nettest.com on 02/03/2003 09:29 AM

 Please respond to Chris Maxwell chris.maxw...@nettest.com

 To:   emc-p...@majordomo.ieee.org
 cc:(bcc: Carl Newton/XYCOM)

 Subject:  RE: EN60950 protective conductor test (was Re: Circuit Breaker
   Tripping Dring Fault Tests)




 This thread has been interesting.  I am, at this moment, considering a
design
 where I am almost forced to use a PC (printed circuit) trace for Earth
ground.

 It seems funny to me that most equipment has been historically made with
18AWG
 protective ground pigtail wires; and 25A ground fault tests have been used
for
 years.

 Now that PC  traces are being used for protective ground; we want to test
with
 200A or greater impulse currents?  I'm curious about what would happen to
your
 typical 18AWG line cord during this test.  I'm wondering if the line cord
would
 fuse open?

 There are a couple of handy charts on the web.

 One is at www.kepcopower.com/nomovax2.htm this is a nomograph of maximum
 operating current, AWG and IR drop in the conductor.  The point A is
generally
 considered the point of maximum IR drop.  If you draw a line from point
A,
 through a wire gauge size; you'll get a max current.  Of course this is
steady
 state current; and the nomograph assumes a single wire.  Wire bundles
would be a
 worse case.  It's too bad that this chart doesn't contain the fuse
values for
 the wires as well (the  I squared * T values).

 Another is at www.circuitboards.com/capacity.php3.   This is a chart of
max
 current for PC traces.  Remember that this is for TRACES and planes only;
it
 doesn't say anything about vias and other potential problems.

 At first pass, it seems that a trace size to handle twice the power cord's
max
 current, (from the nomograph) with a 10degC trace temperature rise (from
the PC
 trace chart), would be a good rule of thumb for the trace size.  If I have
room,
 I'll just make it bigger.  Once we pay for the PC board fabrication, the
copper
 is free!

 Even with an  adequately sized trace; I can think of a few potential
problems
 with the trace to chassis connection:

 1.  Many layout people open up PC traces or planes around vias so that
only four
 little 20 mil wide bridges carry the current to the via.  This is great
for
 soldering heat relief; but BAD for current carrying capacity.  These
little
 bridges can fuse open in high current conditions.  I am considering
solving this
 by not putting any thermal reliefs around your Earth ground vias and using
 multiple vias.

 2.  Another problem with these traces is using plated through vias with
screws
 through them.It has been found that plated through vias can crack when
they
 are put under pressure from screws.Some power supply manufacturers
solve
 this by bringing the Earth ground trace

RE: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-03 Thread Chris Maxwell

This thread has been interesting.  I am, at this moment, considering a design
where I am almost forced to use a PC (printed circuit) trace for Earth ground.

It seems funny to me that most equipment has been historically made with 18AWG
protective ground pigtail wires; and 25A ground fault tests have been used for
years.  

Now that PC  traces are being used for protective ground; we want to test with
200A or greater impulse currents?  I'm curious about what would happen to your
typical 18AWG line cord during this test.  I'm wondering if the line cord
would fuse open? 

There are a couple of handy charts on the web.

One is at www.kepcopower.com/nomovax2.htm this is a nomograph of maximum
operating current, AWG and IR drop in the conductor.  The point A is
generally considered the point of maximum IR drop.  If you draw a line from
point A, through a wire gauge size; you'll get a max current.  Of course
this is steady state current; and the nomograph assumes a single wire.  Wire
bundles would be a worse case.  It's too bad that this chart doesn't contain
the fuse values for the wires as well (the  I squared * T values).

Another is at www.circuitboards.com/capacity.php3.   This is a chart of max
current for PC traces.  Remember that this is for TRACES and planes only; it
doesn't say anything about vias and other potential problems.  

At first pass, it seems that a trace size to handle twice the power cord's max
current, (from the nomograph) with a 10degC trace temperature rise (from the
PC trace chart), would be a good rule of thumb for the trace size.  If I have
room, I'll just make it bigger.  Once we pay for the PC board fabrication, the
copper is free!

Even with an  adequately sized trace; I can think of a few potential problems
with the trace to chassis connection:

1.  Many layout people open up PC traces or planes around vias so that only
four little 20 mil wide bridges carry the current to the via.  This is great
for soldering heat relief; but BAD for current carrying capacity.  These
little bridges can fuse open in high current conditions.  I am considering
solving this by not putting any thermal reliefs around your Earth ground vias
and using multiple vias.

2.  Another problem with these traces is using plated through vias with screws
through them.It has been found that plated through vias can crack when
they are put under pressure from screws.Some power supply manufacturers
solve this by bringing the Earth ground trace to the surface with vias near
the chassis connection point; then route this to a solid plated pad on the
surface layer for chassis connection.  I am considering this same solution as
well.

3.  The third problem is mechanical.  Once Earth ground brought to a pad on
the circuitboard; then there is still the issue of getting a good mechanical
mate to the chassis with a wide surface area.  If the connection is made
through a couple of teeth on a star washer; then there is a potential for
localized heating.   I'm just going to maximize surface contact area for this
one.  I'm also considering using multiple board to chassis connection
locations.  Every screw that connects the board to chassis is a potential
Earth ground connection.

The last fuse in any power system is the cord connected to the product.  It
seems to me, (just an opinion now) that a Earth ground system made to handle
the worst case current of your worst case power input cable (along with some
design margin) would stand a good chance of passing any regulatory test.  

Can any of the gurus see a problem with this?

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 







This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-02-01 Thread John Woodgate

I read in !emc-pstc that Nick Williams nick.willi...@conformance.co.uk
wrote (in p05200f03ba60957364e4@[192.168.1.28]) about 'EN60950
protective conductor test (was Re: Circuit Breaker Tripping Dring Fault
Tests)' on Fri, 31 Jan 2003:

At 12:22 + 31/1/03, John Woodgate wrote:

There is a proposed amendment to IEC/EN 60950-1 requiring a test of the
protective conductor network at *prospective short-circuit current* for
the time it takes for the mains circuit protective device to operate.
The details are controversial at present, because the test currents
appear not to have taken into account the differences between
prospective short-circuit currents in different wiring systems and
supply voltages. Given that reservation, the lowest test current is 200
A.

The amendment is aimed at protective conductors which are surface or
internal traces of multi-layer printed boards. It is said that such
traces have failed in the field under high-current fault conditions.
--

Is the proposal to replace the existing test in the standard or to 
add an additional  test only for certain special circumstances?

It's additional.

Is there any evidence that this test would actually result in a 
significant number of poorly designed products which currently pass 
the requirements of the standard being rejected?

This is the claimed justification for the introduction. Field problems
have occurred where printed board conductors have failed in high-current
short-circuit conditions. The printed-board mounting versions of the IEC
60320 appliance connector encourage the use of board traces to carry the
PEC; something that I would not be happy about, in principle. 

The existing test has its faults but it is easy to do with some very 
cheap apparatus. It strikes me that the cost of doing a test at 200+A 
is potentially very substantial. 

I don't think 200 A is too much of a problem, but testing at higher
currents is proposed for some equipment. I don't want to be too
explicit, because the figures in the draft are highly suspect (of
applying to 120 V supplies!).

If the result of an amendment to the 
standard is that significant numbers of self-certified products which 
have not been properly tested in this aspect of their design reach 
the market, then the net result will actually be a significant 
reduction in the safety of end users.

I don't understand that. You mean that if people cheat, safety will be
compromised? That's always the case. But in fact, the presence of the
test may well concentrate attention on the need to make such traces
substantial, whether they are tested or not.

A cynic's view might also be that an amendment of this nature would 
suit the test labs and larger manufacturers fine, since they will be 
able to justify the cost of the apparatus required, whereas smaller 
manufacturers (and yes, small consultancy companies like mine) will 
not.
Remember you don't necessarily need 200 A at 230 V. I can get 200 A at a
bit over 1 V from a single turn on a big toroidal transformer.

OK, I admit I'm putting two and two together and getting about seven 
but I believe one should get one's retaliation in first in these 
circumstances! Any amendment along the lines suggested should be 
prepared to sacrifice a fair degree of technical accuracy against the 
need for the test to be cheap, quick and easy to perform.

It doesn't call for technical accuracy. You zap the equipment with the
200 A current for the operating time of the protective device and the
PEC either remains intact or doesn't.

Nowadays, standards writing should not just about getting accuracy 
and repeatability in testing but should also take into account the 
need to ensure that the requirements (and hence the tests) are 
actually possible to apply in the real world, and not just by people 
at specialist test houses.

I quite agree, but as you indicate above, there isn't too much *active*
support for that view. When I talk in the committees about low-cost
testing, people tend to remain silent. In any case, at present it's
difficult enough coping with the problems of the costly test equipment
not measuring correctly or not being feasible (low-distortion, high-
current mains supplies for IEC 61000-3-12, as a case in point).

If you want a copy of the draft, to make comments to the BSI committee,
please e-mail. Note that this offer can only be made to people in UK.
Others should approach their national standards body.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list

EN60950 protective conductor test (was Re: Circuit Breaker Tripping Dring Fault Tests)

2003-01-31 Thread Nick Williams

At 12:22 + 31/1/03, John Woodgate wrote:

There is a proposed amendment to IEC/EN 60950-1 requiring a test of the
protective conductor network at *prospective short-circuit current* for
the time it takes for the mains circuit protective device to operate.
The details are controversial at present, because the test currents
appear not to have taken into account the differences between
prospective short-circuit currents in different wiring systems and
supply voltages. Given that reservation, the lowest test current is 200
A.

The amendment is aimed at protective conductors which are surface or
internal traces of multi-layer printed boards. It is said that such
traces have failed in the field under high-current fault conditions.
--

Is the proposal to replace the existing test in the standard or to 
add an additional  test only for certain special circumstances?

Is there any evidence that this test would actually result in a 
significant number of poorly designed products which currently pass 
the requirements of the standard being rejected?

The existing test has its faults but it is easy to do with some very 
cheap apparatus. It strikes me that the cost of doing a test at 200+A 
is potentially very substantial. If the result of an amendment to the 
standard is that significant numbers of self-certified products which 
have not been properly tested in this aspect of their design reach 
the market, then the net result will actually be a significant 
reduction in the safety of end users.

A cynic's view might also be that an amendment of this nature would 
suit the test labs and larger manufacturers fine, since they will be 
able to justify the cost of the apparatus required, whereas smaller 
manufacturers (and yes, small consultancy companies like mine) will 
not.

OK, I admit I'm putting two and two together and getting about seven 
but I believe one should get one's retaliation in first in these 
circumstances! Any amendment along the lines suggested should be 
prepared to sacrifice a fair degree of technical accuracy against the 
need for the test to be cheap, quick and easy to perform.

Nowadays, standards writing should not just about getting accuracy 
and repeatability in testing but should also take into account the 
need to ensure that the requirements (and hence the tests) are 
actually possible to apply in the real world, and not just by people 
at specialist test houses.

Regards

Nick.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc