Re: IEC 364 - Definition of SELV

1999-10-27 Thread Rich Nute



Hi Kevin:


   Is IEC 536 the base document for the definition of SELV?  

   (where it says that SELV means Safety Extra-Low Voltage)?  

Yes.

IEC 536, Definitions, Sub-clause 2.6:

Safety extra-low voltage (SELV)


HISTORY LESSON
==

Prior to IEC 536, I believe SELV was not defined as such, but
the concept of SELV, i.e., low voltage protected from higher 
voltages did indeed exist.

CEE Publication 10, Electric Motor-Operated Appliances, October,
1964, has the following definition:

Extra-low voltage denotes a nominal voltage not exceeding
42 V between conductors and between conductors and earth, 
the no-load voltage not exceeding 50 V.

When extra-low voltage is obtained from the supply mains,
it must be through a safety isolating transformer or a 
converter with separate windings.

Due to its similarity with the definition from IEC 536, it 
appears this CEE 10 ELV definition evolved to SELV.

CEE:   International Commission on Rules for the Approval of
   Electrical Equipment.

(I believe the CEE was absorbed by CEN and CENELEC.)

CEE Members:  Austria, Belgium, Czechoslovakia, Denmark, 
   Germany (FR), Finalnd, France, Greece, Hungary, Italy,
   Netherlands, Norway, Poland, Spain, Sweden, Switzerland,
   United Kingdom, Yugoslavia.


Best regards,
Rich




   From owner-emc-p...@majordomo.ieee.org Tue Oct 26 23:44:11 PDT 1999
   Received: from hpsdlo.sdd.hp.com (hpsdlo-sw.sdd.hp.com [15.80.36.40]) by 
 hpsdlfsg.sdd.hp.com with ESMTP (8.7.6/8.7.3 TIS 5.0/sdd epg) id XAA23435 for 
 ri...@hpsdlfsg.sdd.hp.com; Tue, 26 Oct 1999 23:44:11 -0700 (PDT)
   Received: from ruebert.ieee.org (ruebert.ieee.org [199.172.136.3])
   by hpsdlo.sdd.hp.com (8.8.6 (PHNE_14041)/8.8.5btis+epg) with ESMTP id 
 XAA04752
   for ri...@sdd.hp.com; Tue, 26 Oct 1999 23:44:09 -0700 (PDT)
   Received:  by ruebert.ieee.org (8.8.8+Sun/8.8.8)
   id CAA20446; Wed, 27 Oct 1999 02:19:26 -0400 (EDT)
   Date: Wed, 27 Oct 1999 02:18:15 -0400
   From: Kevin Richardson k...@compuserve.com
   Subject: Re: IEC 364 - Definition of SELV
   To: Rich Nute ri...@sdd.hp.com
   Cc: [unknown] emc-p...@ieee.org
   Message-ID: 199910270218_mc2-8a97-1...@compuserve.com
   MIME-Version: 1.0
   Content-Type: text/plain;
charset=ISO-8859-1
   Content-Disposition: inline
   Content-Transfer-Encoding: 8bit
   X-MIME-Autoconverted: from quoted-printable to 8bit by ruebert.ieee.org id 
 CAA20443
   Sender: owner-emc-p...@majordomo.ieee.org
   Precedence: bulk
   Reply-To: Kevin Richardson k...@compuserve.com
   X-Resent-To: Multiple Recipients emc-p...@majordomo.ieee.org
   X-Listname: emc-pstc
   X-Info: Help requests to  emc-pstc-requ...@majordomo.ieee.org
   X-Info: [Un]Subscribe requests to  majord...@majordomo.ieee.org
   X-Moderator-Address: emc-pstc-appro...@majordomo.ieee.org
   
   
   Hi Rich,
   
   Thank you for devoting so much time to reply.  This is just what I needed. 
   I am familiar with IEC 60950 and I wanted to be able to compare the
   definitions.  Thank you.
   
   One other question to Rich or anyone else that can help.
   
   Is IEC 536 the base document for the definition of SELV?  In addition to
   how SELV is expressed in IEC 364 I am also trying to confirm the base
   standard in the IEC responsible for the SELV definition.  Is it IEC 536 or
   some other document?  In which standard or guide is the term SELV spelt out
   (where it says that SELV means Safety Extra-Low Voltage)?  There must
   be a base IEC document somewhere that defines the term.
   
   Best regards,
   Kevin


Hi Kevin:


   Can anyone please provide the SELV definition from IEC 364?

I'm working from some old documents, but...

SELV is not expressly defined in IEC 364-4-41.  Instead,
it specifies Protection by safety extra-low voltage.

It says:

Protection against electric shock in normal service
and in case of a fault is deemed to be ensured when:

- the nominal voltage cannot exceed the upper limit
  of Voltage Band I*,

- the supply is from one of the safety sources listed
  in Sub-clause 411.1.2, and

- the conditions of Sub-clause 411.1.3 are fulfilled.

*See IEC Publication 449: Voltage Bands for Electrical
  Installations of Buildings.

The safety sources are:

- a safety isolating transformer,

- a source of current providing a degree of safety 
  equivalent to that of the safety isolating transformer
  (e.g., motor generators with windings providing 
  equivalent isolation),

- an electrochemical source (e.g., a battery) or another
  source independent of a higher-voltage circuit (e.g., a
  diesel-driven generator,

- certain electronic devices complying with appropriate
  standards where measure have been taken to ensure

Re: IEC 364 - Definition of SELV

1999-10-27 Thread Kevin Richardson

Hi Rich,

Thank you for devoting so much time to reply.  This is just what I needed. 
I am familiar with IEC 60950 and I wanted to be able to compare the
definitions.  Thank you.

One other question to Rich or anyone else that can help.

Is IEC 536 the base document for the definition of SELV?  In addition to
how SELV is expressed in IEC 364 I am also trying to confirm the base
standard in the IEC responsible for the SELV definition.  Is it IEC 536 or
some other document?  In which standard or guide is the term SELV spelt out
(where it says that SELV means Safety Extra-Low Voltage)?  There must
be a base IEC document somewhere that defines the term.

Best regards,
Kevin
 
 
 Hi Kevin:
 
 
Can anyone please provide the SELV definition from IEC 364?
 
 I'm working from some old documents, but...
 
 SELV is not expressly defined in IEC 364-4-41.  Instead,
 it specifies Protection by safety extra-low voltage.
 
 It says:
 
 Protection against electric shock in normal service
 and in case of a fault is deemed to be ensured when:
 
 - the nominal voltage cannot exceed the upper limit
   of Voltage Band I*,
 
 - the supply is from one of the safety sources listed
   in Sub-clause 411.1.2, and
 
 - the conditions of Sub-clause 411.1.3 are fulfilled.
 
 *See IEC Publication 449: Voltage Bands for Electrical
   Installations of Buildings.
 
 The safety sources are:
 
 - a safety isolating transformer,
 
 - a source of current providing a degree of safety 
   equivalent to that of the safety isolating transformer
   (e.g., motor generators with windings providing 
   equivalent isolation),
 
 - an electrochemical source (e.g., a battery) or another
   source independent of a higher-voltage circuit (e.g., a
   diesel-driven generator,
 
 - certain electronic devices complying with appropriate
   standards where measure have been taken to ensure that, 
   even in the case of aninternal fault, the voltage at the
   outgoing termainals cannot exceed the values specified in
   Sub-clause 411.1.1.
 
 The definition of SELV appears in IEC 536:
 
 A voltage which does not exceed 50 V ac rms between
 conductors, or between any conductor and earth, in a 
 circuit which is isolated from the supply mains by means
 such as a safety isolating transformer or converter with
 separate windings.
 
 IEC 950 defines SELV CIRCUIT:
 
 A secondary circuit which is so designed and protected 
 that under normal and single fault conditions, its 
 voltages do not exceed a safe value.
 
 
 SELV is a special case of ELV, Extra Low Voltage.  ELV is
 defined (or implied) as a maximum voltage value deemed not to 
 cause an electric shock.  SELV applies to an ELV where, in
 the absence of specific protective mechanisms, the ELV would
 exceed ELV under fault conditions.  So, SELV implies ELV with
 some means to prevent the voltage from exceeding ELV limits
 in the event of a fault.
 
 A single-insulated transformer ELV secondary is ELV.
 
 A double-insulated transformer ELV secondary is SELV.
 
 An ELV battery is ELV.  It may or may not be SELV, depending
 on your point of view.  
 
 1:  Since the battery itself cannot exceed ELV under single-
 fault conditions, then it cannot be SELV.  Or, 
 
 2:  Since the battery itself cannot exceed ELV cannot exceed 
 ELV under single-fault conditions, then it must be SELV.  
 
 However, as defined, SELV implies an included protective
 mechanism to limit the voltage in the event of a fault.  SELV
 also implies that the ELV is derived from a higher, non-ELV
 source.
 
 If you accept that a battery is ELV, then the safety standards 
 require that the battery voltages cannot be touched!
 
 
 Best regards,
 Rich
 
 
 
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 
 
 
 
 
 
 --- Internet Header 
 Sender: owner-emc-p...@majordomo.ieee.org
 Received: from ruebert.ieee.org (ruebert.ieee.org [199.172.136.3])
   by spdmgaaf.compuserve.com (8.9.3/8.9.3/SUN-1.7) with ESMTP id
UAA01279;
   Tue, 26 Oct 1999 20:08:23 -0400 (EDT)
 Received:  by ruebert.ieee.org (8.8.8+Sun/8.8.8)
   id UAA19661; Tue, 26 Oct 1999 20:07:41 -0400 (EDT)
 Date: Tue, 26 Oct 1999 17:06:45 -0700 (PDT)
 From: Rich Nute ri...@sdd.hp.com
 Message-Id: 199910270006.raa26...@epgc478.sdd.hp.com
 To: k...@compuserve.com
 Subject: Re: IEC 364 - Definition of SELV
 Cc: emc-p...@ieee.org
 In-Reply-To: 199910252120_mc2-8a6c-2...@compuserve.com from Kevin
Richardson at Oct 25, 99 09:20:44 pm
 MIME-Version: 1.0
 Content-Type: text/plain; charset=US-ASCII
 Content-Transfer

Re: IEC 364 - Definition of SELV

1999-10-27 Thread Rich Nute



Hi Kevin:


   Can anyone please provide the SELV definition from IEC 364?

I'm working from some old documents, but...

SELV is not expressly defined in IEC 364-4-41.  Instead,
it specifies Protection by safety extra-low voltage.

It says:

Protection against electric shock in normal service
and in case of a fault is deemed to be ensured when:

- the nominal voltage cannot exceed the upper limit
  of Voltage Band I*,

- the supply is from one of the safety sources listed
  in Sub-clause 411.1.2, and

- the conditions of Sub-clause 411.1.3 are fulfilled.

*See IEC Publication 449: Voltage Bands for Electrical
  Installations of Buildings.

The safety sources are:

- a safety isolating transformer,

- a source of current providing a degree of safety 
  equivalent to that of the safety isolating transformer
  (e.g., motor generators with windings providing 
  equivalent isolation),

- an electrochemical source (e.g., a battery) or another
  source independent of a higher-voltage circuit (e.g., a
  diesel-driven generator,

- certain electronic devices complying with appropriate
  standards where measure have been taken to ensure that, 
  even in the case of aninternal fault, the voltage at the
  outgoing termainals cannot exceed the values specified in
  Sub-clause 411.1.1.

The definition of SELV appears in IEC 536:

A voltage which does not exceed 50 V ac rms between
conductors, or between any conductor and earth, in a 
circuit which is isolated from the supply mains by means
such as a safety isolating transformer or converter with
separate windings.

IEC 950 defines SELV CIRCUIT:

A secondary circuit which is so designed and protected 
that under normal and single fault conditions, its 
voltages do not exceed a safe value.


SELV is a special case of ELV, Extra Low Voltage.  ELV is
defined (or implied) as a maximum voltage value deemed not to 
cause an electric shock.  SELV applies to an ELV where, in
the absence of specific protective mechanisms, the ELV would
exceed ELV under fault conditions.  So, SELV implies ELV with
some means to prevent the voltage from exceeding ELV limits
in the event of a fault.

A single-insulated transformer ELV secondary is ELV.

A double-insulated transformer ELV secondary is SELV.

An ELV battery is ELV.  It may or may not be SELV, depending
on your point of view.  

1:  Since the battery itself cannot exceed ELV under single-
fault conditions, then it cannot be SELV.  Or, 

2:  Since the battery itself cannot exceed ELV cannot exceed 
ELV under single-fault conditions, then it must be SELV.  

However, as defined, SELV implies an included protective
mechanism to limit the voltage in the event of a fault.  SELV
also implies that the ELV is derived from a higher, non-ELV
source.

If you accept that a battery is ELV, then the safety standards 
require that the battery voltages cannot be touched!


Best regards,
Rich




-