RE: Motor Drive Grounding Scheme

2001-10-19 Thread Stone, Richard A (Richard)

In typical testing of DC units,
the two inputs are floating
when doing for example: current checks
and hipot to chassis ground.

Yet, in a CO, the return lead is grounded,
so you have a test lab condition ( return floating )
and a real condition, return tied to CO earth ground
in service.

The only thing unusual might be the delta in the ground
connections, causing an impedance change, thus a voltage
swing.

In this case its 74vdc, so its hazardous,
I would think doing appropriate fault testing
@ UL would be sufficient.
Just saying its unsafe and NO is not reasonable.
Richard,

-Original Message-
From: Peter Merguerian [mailto:pmerguer...@itl.co.il]
Sent: Friday, October 19, 2001 3:45 AM
To: 'Mark Haynes'; IEEE EMC-PSTC Discussion List (E-mail)
Cc: Peter Deneault (E-mail); Tom Brenner; Doug Harris
Subject: RE: Motor Drive Grounding Scheme



Mark,

If you think your product is safe, you must be able to prove it. For
starters, I suggest you read UL60950. Somewhere in the Appendix, it allows
one side of the input supply to telecommunication equipment intended for
central office applications to be earthed. However, special markings andf
instructions are required. 

Regret I do not have the time to commit for a full reasearch at this time.
But, once you read the UL60950 standard, I am sure you will have a better
case to explain to UL. Also, I recommend that you talk to an expert at UL
rather than a low level engineer - you may try calling Jimmy Wong at UL
Melville.


This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.






PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175






-Original Message-
From: Mark Haynes [mailto:mhay...@dlsemc.com]
Sent: Thursday, October 18, 2001 6:44 PM
To: IEEE EMC-PSTC Discussion List (E-mail)
Cc: Peter Deneault (E-mail); Tom Brenner; Doug Harris
Subject: Motor Drive Grounding Scheme



Greetings All,

I work for a product safety consulting firm/test lab/agent.  I am currently
having some difficulties with UL relating to one of our customer's products.
The grounding scheme of the products has become a barrier which has halted
the planned testing.  In our opinion, the engineering rationale behind this
position is not very strong or clear.

The products are small open-type stepper and servo motor drives (rated up to
6 A) which are intended to be used within another enclosure.  They are
powered by an 18 - 74 V dc external source which is supplied by the user.
The drive output is a DC pulse width modulated waveform.  UL 508C and UL 840
are the standards being used.  The main issue is the fact that the DC -
(common) input supply lead is connected internally to the input ground (PE)
lead.  UL has referenced UL 508C requirements (not really applicable to
these particular products since we have agreed to use UL 840 for spacings)
that indicate that spacings are required within the product between these
two leads.  This implies that this grounding scheme cannot be used.  The
manufacturer has indicated that the drives will not operate properly without
this grounding connection.  The product designers made this connection
internally to prevent the common from floating above/below ground potential
and for EMI purposes.

The customer and my company do not agree with UL's position.  One possible
hazard UL stated was that the heatsink was connected to the grounded DC -
(common) internal bus and could be electrically "live".  Since the heatsink
is referenced to ground potential, it is not "live" during normal operation.
If an internal fault does occur, the circuitry is designed such that the
fault current will flow through the ground, as intended.  In addition, a
"hint" of possibly increasing the risk of shock was also mentioned.  No one
involved has been able to identify any real safety issues resulting from
this grounding scheme.  In order to address all potential safety hazards, we
have recommended that testing be conducted to confirm compliance with the
intent of the standards.  This would hopefully show that the products are
"safe" and that all foreseeable safety hazards (during normal and fault
conditions) have been identified and minimized/eliminated.  After weeks of
research and discussions, we have not been able to convince UL that this
grounding scheme should be allowed and that we should proceed with the
testing.

Does anyone know of any similar UL certified motor drives (or other similar
DC powered products) that employ this grounding scheme?  The closest
examples we could find 

RE: Motor Drive Grounding Scheme

2001-10-19 Thread Peter Merguerian

Mark,

If you think your product is safe, you must be able to prove it. For
starters, I suggest you read UL60950. Somewhere in the Appendix, it allows
one side of the input supply to telecommunication equipment intended for
central office applications to be earthed. However, special markings andf
instructions are required. 

Regret I do not have the time to commit for a full reasearch at this time.
But, once you read the UL60950 standard, I am sure you will have a better
case to explain to UL. Also, I recommend that you talk to an expert at UL
rather than a low level engineer - you may try calling Jimmy Wong at UL
Melville.


This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.






PETER S. MERGUERIAN
Technical Director
I.T.L. (Product Testing) Ltd.
26 Hacharoshet St., POB 211
Or Yehuda 60251, Israel
Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019
Mobile: + 972-(0)54-838175






-Original Message-
From: Mark Haynes [mailto:mhay...@dlsemc.com]
Sent: Thursday, October 18, 2001 6:44 PM
To: IEEE EMC-PSTC Discussion List (E-mail)
Cc: Peter Deneault (E-mail); Tom Brenner; Doug Harris
Subject: Motor Drive Grounding Scheme



Greetings All,

I work for a product safety consulting firm/test lab/agent.  I am currently
having some difficulties with UL relating to one of our customer's products.
The grounding scheme of the products has become a barrier which has halted
the planned testing.  In our opinion, the engineering rationale behind this
position is not very strong or clear.

The products are small open-type stepper and servo motor drives (rated up to
6 A) which are intended to be used within another enclosure.  They are
powered by an 18 - 74 V dc external source which is supplied by the user.
The drive output is a DC pulse width modulated waveform.  UL 508C and UL 840
are the standards being used.  The main issue is the fact that the DC -
(common) input supply lead is connected internally to the input ground (PE)
lead.  UL has referenced UL 508C requirements (not really applicable to
these particular products since we have agreed to use UL 840 for spacings)
that indicate that spacings are required within the product between these
two leads.  This implies that this grounding scheme cannot be used.  The
manufacturer has indicated that the drives will not operate properly without
this grounding connection.  The product designers made this connection
internally to prevent the common from floating above/below ground potential
and for EMI purposes.

The customer and my company do not agree with UL's position.  One possible
hazard UL stated was that the heatsink was connected to the grounded DC -
(common) internal bus and could be electrically "live".  Since the heatsink
is referenced to ground potential, it is not "live" during normal operation.
If an internal fault does occur, the circuitry is designed such that the
fault current will flow through the ground, as intended.  In addition, a
"hint" of possibly increasing the risk of shock was also mentioned.  No one
involved has been able to identify any real safety issues resulting from
this grounding scheme.  In order to address all potential safety hazards, we
have recommended that testing be conducted to confirm compliance with the
intent of the standards.  This would hopefully show that the products are
"safe" and that all foreseeable safety hazards (during normal and fault
conditions) have been identified and minimized/eliminated.  After weeks of
research and discussions, we have not been able to convince UL that this
grounding scheme should be allowed and that we should proceed with the
testing.

Does anyone know of any similar UL certified motor drives (or other similar
DC powered products) that employ this grounding scheme?  The closest
examples we could find were AC powered products with DC ground referenced
secondary circuits.  However, this is not the same since a transformer
usually provides the required isolation.

Does anyone have any comments/information on this grounding scheme that
might be helpful in building a stronger case either way?  The closest thing
we could reference was a grounded DC distribution system in the 1999
National Electrical Code (NEC - NFPA 70).

Please respond at your earliest convenience.

Thanks in advance for your assistance,

Mark A. Haynes
Senior Product Safety Engineer
D.L.S. Conformity Assessment, Inc.
1250 Peterson Drive
Wheeling, IL 60090-6454
(847) 537-6400 (Ext. 157)
Fax (847) 537-6488
mhay...@dlsemc.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at: 

RE: Motor Drive Grounding Scheme

2001-10-19 Thread Scott Lacey

Mark.
As described, the situation to me sounds no worse than any other earthed
connection. The only hazard would seem to be as a return for hazardous
voltages - exactly the same situation as the sheet metal enclosure that
surrounds it. In my experience sometimes the "approver's" representative
makes a snap judgement when confronted with something unfamiliar. It then
becomes difficult for them to back down without losing face. I would suggest
gently trying to convince the representative of the logic of your position.

Scott Lacey

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Mark Haynes
Sent: Thursday, October 18, 2001 12:44 PM
To: IEEE EMC-PSTC Discussion List (E-mail)
Cc: Peter Deneault (E-mail); Tom Brenner; Doug Harris
Subject: Motor Drive Grounding Scheme



Greetings All,

I work for a product safety consulting firm/test lab/agent.  I am currently
having some difficulties with UL relating to one of our customer's products.
The grounding scheme of the products has become a barrier which has halted
the planned testing.  In our opinion, the engineering rationale behind this
position is not very strong or clear.

The products are small open-type stepper and servo motor drives (rated up to
6 A) which are intended to be used within another enclosure.  They are
powered by an 18 - 74 V dc external source which is supplied by the user.
The drive output is a DC pulse width modulated waveform.  UL 508C and UL 840
are the standards being used.  The main issue is the fact that the DC -
(common) input supply lead is connected internally to the input ground (PE)
lead.  UL has referenced UL 508C requirements (not really applicable to
these particular products since we have agreed to use UL 840 for spacings)
that indicate that spacings are required within the product between these
two leads.  This implies that this grounding scheme cannot be used.  The
manufacturer has indicated that the drives will not operate properly without
this grounding connection.  The product designers made this connection
internally to prevent the common from floating above/below ground potential
and for EMI purposes.

The customer and my company do not agree with UL's position.  One possible
hazard UL stated was that the heatsink was connected to the grounded DC -
(common) internal bus and could be electrically "live".  Since the heatsink
is referenced to ground potential, it is not "live" during normal operation.
If an internal fault does occur, the circuitry is designed such that the
fault current will flow through the ground, as intended.  In addition, a
"hint" of possibly increasing the risk of shock was also mentioned.  No one
involved has been able to identify any real safety issues resulting from
this grounding scheme.  In order to address all potential safety hazards, we
have recommended that testing be conducted to confirm compliance with the
intent of the standards.  This would hopefully show that the products are
"safe" and that all foreseeable safety hazards (during normal and fault
conditions) have been identified and minimized/eliminated.  After weeks of
research and discussions, we have not been able to convince UL that this
grounding scheme should be allowed and that we should proceed with the
testing.

Does anyone know of any similar UL certified motor drives (or other similar
DC powered products) that employ this grounding scheme?  The closest
examples we could find were AC powered products with DC ground referenced
secondary circuits.  However, this is not the same since a transformer
usually provides the required isolation.

Does anyone have any comments/information on this grounding scheme that
might be helpful in building a stronger case either way?  The closest thing
we could reference was a grounded DC distribution system in the 1999
National Electrical Code (NEC - NFPA 70).

Please respond at your earliest convenience.

Thanks in advance for your assistance,

Mark A. Haynes
Senior Product Safety Engineer
D.L.S. Conformity Assessment, Inc.
1250 Peterson Drive
Wheeling, IL 60090-6454
(847) 537-6400 (Ext. 157)
Fax (847) 537-6488
mhay...@dlsemc.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is bro

Motor Drive Grounding Scheme

2001-10-18 Thread Mark Haynes

Greetings All,

I work for a product safety consulting firm/test lab/agent.  I am currently
having some difficulties with UL relating to one of our customer's products.
The grounding scheme of the products has become a barrier which has halted
the planned testing.  In our opinion, the engineering rationale behind this
position is not very strong or clear.

The products are small open-type stepper and servo motor drives (rated up to
6 A) which are intended to be used within another enclosure.  They are
powered by an 18 - 74 V dc external source which is supplied by the user.
The drive output is a DC pulse width modulated waveform.  UL 508C and UL 840
are the standards being used.  The main issue is the fact that the DC -
(common) input supply lead is connected internally to the input ground (PE)
lead.  UL has referenced UL 508C requirements (not really applicable to
these particular products since we have agreed to use UL 840 for spacings)
that indicate that spacings are required within the product between these
two leads.  This implies that this grounding scheme cannot be used.  The
manufacturer has indicated that the drives will not operate properly without
this grounding connection.  The product designers made this connection
internally to prevent the common from floating above/below ground potential
and for EMI purposes.

The customer and my company do not agree with UL's position.  One possible
hazard UL stated was that the heatsink was connected to the grounded DC -
(common) internal bus and could be electrically "live".  Since the heatsink
is referenced to ground potential, it is not "live" during normal operation.
If an internal fault does occur, the circuitry is designed such that the
fault current will flow through the ground, as intended.  In addition, a
"hint" of possibly increasing the risk of shock was also mentioned.  No one
involved has been able to identify any real safety issues resulting from
this grounding scheme.  In order to address all potential safety hazards, we
have recommended that testing be conducted to confirm compliance with the
intent of the standards.  This would hopefully show that the products are
"safe" and that all foreseeable safety hazards (during normal and fault
conditions) have been identified and minimized/eliminated.  After weeks of
research and discussions, we have not been able to convince UL that this
grounding scheme should be allowed and that we should proceed with the
testing.

Does anyone know of any similar UL certified motor drives (or other similar
DC powered products) that employ this grounding scheme?  The closest
examples we could find were AC powered products with DC ground referenced
secondary circuits.  However, this is not the same since a transformer
usually provides the required isolation.

Does anyone have any comments/information on this grounding scheme that
might be helpful in building a stronger case either way?  The closest thing
we could reference was a grounded DC distribution system in the 1999
National Electrical Code (NEC - NFPA 70).

Please respond at your earliest convenience.

Thanks in advance for your assistance,

Mark A. Haynes
Senior Product Safety Engineer
D.L.S. Conformity Assessment, Inc.
1250 Peterson Drive
Wheeling, IL 60090-6454
(847) 537-6400 (Ext. 157)
Fax (847) 537-6488
mhay...@dlsemc.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.