RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation

2003-11-05 Thread POWELL, DOUG
John  Dave,
 
Thank you for your replies.  I was hoping someone else had independently found
these issues with the document.  My only other choices were, I am somehow
going senile or worse, insane.
 
I am concerned becuase this lack of attention to detail on the part of the
committee, brings the rest of the document into question.  I have a fair
background in high voltage technology and in addition have carefully checked
into IEC 60664 for help.  Suffice it to say, there are other things in the IEC
61010-1 that bother me when it comes to safety spacings requirements.
 
Is there anyone in this discussion group who was part of the committee and can
answer some of these concerns?
 
Regards,
 
 
-doug


Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80525 USA 


From: John Allen [mailto:john.al...@era.co.uk]
Sent: Wednesday, November 05, 2003 2:46 AM
To: 'drcuthb...@micron.com'; POWELL, DOUG
Cc: emc-p...@ieee.org
Subject: RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


Doug, Dave
 
This is not the first time the formulae and examples in 6.7 have been called
into question.
 
One of my customers raised a query about a year ago, and I forwarded the query
to the Chairman of the IEC TC for 61010, as well as the (BSI) Secretary
thereof, as attached - I received an acknowlegement from Mr Chapman but I
never received an answer!
 
There might well be misprints in this case as I found quite a few elsewhere on
an earlier occasion, as per a previous message to Mr Chapman, also attached!
 
Therefore I think you need to view the text of this edition of 61010-1 with
the proverbial pinch of salt :- if it doesnt look right then it probably
isn't!!
 
Regards
John Allen, 
Technical Consultant
EMC and Safety Engineering
ERA Technology Ltd.
Cleeve Road
Leatherhead 
Surrey KT22 7SA
UK
Tel: +44-1372-367025 (Direct)
+44-1372-367000 (Switchboard)
Fax: +44-1372-367102

 
 


From: drcuthb...@micron.com [mailto:drcuthb...@micron.com]
Sent: 04 November 2003 16:46
To: doug.pow...@aei.com; emc-p...@ieee.org
Subject: RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


Doug,
 
I find it confusing. Good thing there are examples.
 
example b) gives the correct answer. 
 
example a) does not look correct.
 
Reasoning:
 
1) F is solved incorrectly. It should be 0.297
2) The remainder looks correct. I get 20.5 mm (without interpolation)
 
With interpolation I get 18.4 mm.
 
 Dave Cuthbert
 Micron Technology
 
 
 

From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of POWELL, DOUG
Sent: Monday, November 03, 2003 2:48 PM
To: EMC-PSTC (E-mail)
Subject: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


 
Has anyone tried to work through the two examples given in this section?  In
trying to understand how to use the CLEARANCE = D1 + F(D2-D1) equation, I was
hoping to check my work with the examples that were given.  Either I'm missing
something or these examples have some really fundamental errors.
 
In my application, I am attempting to calculate the basic clearance for a
working voltage of 1500 VDC with transients that peak to 1800V and ride on the
VDC. The final peak voltage is 300 Volts higher than the steady-state 1500VDC,
which apparently meets the 6.7.3.1 b) 2) criteria.
 
 
 
Please help!
 
-doug
 
 
 

end



Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80525 USA 

 
___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com




*
Copyright ERA Technology Ltd. 2003. (www.era.co.uk). All rights reserved. 
The information supplied in this Commercial Communication should be treated
in confidence.
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com




RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation

2003-11-05 Thread John Allen
This is a multi-part message in MIME format.
Doug, Dave
 
This is not the first time the formulae and examples in 6.7 have been called
into question.
 
One of my customers raised a query about a year ago, and I forwarded the query
to the Chairman of the IEC TC for 61010, as well as the (BSI) Secretary
thereof, as attached - I received an acknowlegement from Mr Chapman but I
never received an answer!
 
There might well be misprints in this case as I found quite a few elsewhere on
an earlier occasion, as per a previous message to Mr Chapman, also attached!
 
Therefore I think you need to view the text of this edition of 61010-1 with
the proverbial pinch of salt :- if it doesnt look right then it probably
isn't!!
 
Regards
John Allen, 
Technical Consultant
EMC and Safety Engineering
ERA Technology Ltd.
Cleeve Road
Leatherhead 
Surrey KT22 7SA
UK
Tel: +44-1372-367025 (Direct)
+44-1372-367000 (Switchboard)
Fax: +44-1372-367102

 
 


From: drcuthb...@micron.com [mailto:drcuthb...@micron.com]
Sent: 04 November 2003 16:46
To: doug.pow...@aei.com; emc-p...@ieee.org
Subject: RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


Doug,
 
I find it confusing. Good thing there are examples.
 
example b) gives the correct answer. 
 
example a) does not look correct.
 
Reasoning:
 
1) F is solved incorrectly. It should be 0.297
2) The remainder looks correct. I get 20.5 mm (without interpolation)
 
With interpolation I get 18.4 mm.
 
 Dave Cuthbert
 Micron Technology
 
 
 

From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of POWELL, DOUG
Sent: Monday, November 03, 2003 2:48 PM
To: EMC-PSTC (E-mail)
Subject: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


 
Has anyone tried to work through the two examples given in this section?  In
trying to understand how to use the CLEARANCE = D1 + F(D2-D1) equation, I was
hoping to check my work with the examples that were given.  Either I'm missing
something or these examples have some really fundamental errors.
 
In my application, I am attempting to calculate the basic clearance for a
working voltage of 1500 VDC with transients that peak to 1800V and ride on the
VDC. The final peak voltage is 300 Volts higher than the steady-state 1500VDC,
which apparently meets the 6.7.3.1 b) 2) criteria.
 
 
 
Please help!
 
-doug
 
 
 

end



Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80525 USA 

 
___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com




*
Copyright ERA Technology Ltd. 2003. (www.era.co.uk). All rights reserved. 
The information supplied in this Commercial Communication should be treated
in confidence.
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com


---BeginMessage---
This attachment, originally named Message Text,
was removed because it is zero length.
---End Message---
---BeginMessage---
For the attention of the following Officers of IEC TC66 

 

Chairman:  Mr. Cecil CHAPMAN

Grant Instruments (Cambridge) Ltd.

Mill Barn

Bassingbourn, SG8 5PP, UK



 



Secretary: Mr. N.A.R. BRADFIELD

British Electrotechnical Committee

Electrical Department - Floor 11-6

British Standards Institution

389 Chiswick High Road

London W4 4AL, UK



Dear Sirs

 

It has been suggested that we draw to your attention the following technical 
and/or printing errors which appear in copies of BS EN 61010-1:2001 - and thus 
presumably in EN 61010-1:2001 and IEC 61010-1:2001

 

1) Clause 6.8.4 Voltage tests  Table 9 Test voltages for BASIC INSULATION 
(Page 52).



We are reasonably sure that there is a misprint in Column 1 Clearance of 
Table 9 , as follows: The line entry between 1.0 and 2.0 is 1.4 but it 
should be 1.5 (mm).



We believe that this is obvious from Table 8 Clearance for measurement 
categories II, III and IV where 1.5 (mm) is mentioned in numerous places but 
1.4 is not mentioned at all.



Apart from anything else, 1.5mm is the category II minimum value for nominal 
line voltages of 150V=300V - which

RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation

2003-11-04 Thread drcuthb...@micron.com
Doug,
 
I find it confusing. Good thing there are examples.
 
example b) gives the correct answer. 
 
example a) does not look correct.
 
Reasoning:
 
1) F is solved incorrectly. It should be 0.297
2) The remainder looks correct. I get 20.5 mm (without interpolation)
 
With interpolation I get 18.4 mm.
 
 Dave Cuthbert
 Micron Technology
 
 
 

From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of POWELL, DOUG
Sent: Monday, November 03, 2003 2:48 PM
To: EMC-PSTC (E-mail)
Subject: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


 
Has anyone tried to work through the two examples given in this section?  In
trying to understand how to use the CLEARANCE = D1 + F(D2-D1) equation, I was
hoping to check my work with the examples that were given.  Either I'm missing
something or these examples have some really fundamental errors.
 
In my application, I am attempting to calculate the basic clearance for a
working voltage of 1500 VDC with transients that peak to 1800V and ride on the
VDC. The final peak voltage is 300 Volts higher than the steady-state 1500VDC,
which apparently meets the 6.7.3.1 b) 2) criteria.
 
 
 
Please help!
 
-doug
 
 
 

end



Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80525 USA 

 
___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 