Re: [PSES] Standard or practical guide to grounding electrical products which are not permanently installed

2012-12-18 Thread Brian Oconnell
The particular design manual that would apply is typically specified on the
CSA C of C and/or in the respective construction file. The DM is analogous
to a super-duper Section Gen + FUS + FIIS of an UL file. If CSA issued the
cert without that file - ask the assessment engr to send the respective DM
if you are not in the category cert program. Do not think that CSA writes a
DM for all safety standards.

Brian

-Original Message-
From: Brian Ceresney [mailto:bceres...@delta-q.com]
Sent: Monday, December 17, 2012 6:22 PM
To: oconne...@tamuracorp.com; 'EMC-PSTC'
Subject: RE: Standard or practical guide to grounding electrical
products which are not permanently installed

Thanks for your help, Brian. 
Unfortunately my two equipment standards are not very detailed, this product
has no  UL file yet, and my(out of date)copy of CSA 0.4 doesn't add much.
Time to buy more standards!

Could you explain the "CSA design manual" to me? I have never heard of a
design manual before, and didn't see it on the CSA site. Is it available
only for specific standards?  

Best Regards, 
Brian C.

Brian Ceresney, CTech.
Regulatory Team Lead,
Delta-Q Technologies Corp.
3755 Willingdon Ave.,
Burnaby, BC  Canada  V5G 3H3
Tel: 604-566-8827
www.delta-q.com
bceres...@delta-q.com

-Original Message-
From: Brian Oconnell [mailto:oconne...@tamuracorp.com] 
Sent: Monday, December 17, 2012 4:31 PM
To: Brian Ceresney; 'EMC-PSTC'
Subject: RE: Standard or practical guide to grounding electrical products
which are not permanently installed

Do not know why bonding materials/construction would not be in the scoped
safety standard. My typical refs for reliable bonding construction
requirements/suggestions are:
1. scoped safety standard for the equipment and/or end-use installation.
2. CSA design manual for the scoped standard(s).
3. Section General and/or Inspection Procedures of the affected UL file.
4. CSA No. 0.4
5. NEC article 250 (mostly wiring, but other hardware discussed)

There has to be 10E3 references for this stuff.

Brian

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of Brian
Ceresney
Sent: Monday, December 17, 2012 3:59 PM
To: 'EMC-PSTC'
Subject: Standard or practical guide to grounding electrical products which
are not permanently installed

Dear Regulatory Experts, 
I'm searching for a standard or guideline which will provide detailed
information about the internal grounding and bonding of products, and I've
had limited luck in finding anything suiting my purpose. Reviewing a few CSA
and UL standards hasn't been helpful.  
 
Specifically, I am interested in Class I plug and cord connected products,
which require the internal grounding wire to be secured to a metal,
non-current carrying enclosure. I need to know what kinds of
screw/nut/washer combinations are acceptable, mainly from a North American
viewpoint, but not excluding Europe.(As usual, I'm working with small
industrial-type battery chargers drawing less than 12A at 120V, 6A at 240V).

  
I'm particularly interested in requirements/acceptability of thread-cutting
or -forming screws, with or without locking washers. I'm wondering about
their securement performance over time.
 
The standards I've reviewed so far seem to be very non-specific about
requirements, while specifying some testing. Are there any documents out
there that are more detailed? 
 
Thanks in Advance,  
Brian C. 
 
Brian Ceresney, CTech.
Regulatory Team Lead,
Delta-Q Technologies Corp.
3755 Willingdon Ave.,
Burnaby, BC  Canada  V5G 3H3
Tel: 604-566-8827
www.delta-q.com
bceres...@delta-q.com


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] Standard or practical guide to grounding electrical products which are not permanently installed

2012-12-17 Thread Brian Ceresney
Thanks for your help, Brian. 
Unfortunately my two equipment standards are not very detailed, this product 
has no  UL file yet, and my(out of date)copy of CSA 0.4 doesn't add much. Time 
to buy more standards!

Could you explain the "CSA design manual" to me? I have never heard of a design 
manual before, and didn't see it on the CSA site. Is it available only for 
specific standards?  

Best Regards, 
Brian C.

Brian Ceresney, CTech.
Regulatory Team Lead,
Delta-Q Technologies Corp.
3755 Willingdon Ave.,
Burnaby, BC  Canada  V5G 3H3
Tel: 604-566-8827
www.delta-q.com
bceres...@delta-q.com


Confidentiality Notice: This email message, including any attachments, is for 
the sole use of the intended recipient(s) and may contain confidential and 
privileged information. Any unauthorized review, use, disclosure or 
distribution is prohibited. If you are not the intended recipient, please 
contact the sender by reply e-mail and destroy all copies of the original 
message.







-Original Message-
From: Brian Oconnell [mailto:oconne...@tamuracorp.com] 
Sent: Monday, December 17, 2012 4:31 PM
To: Brian Ceresney; 'EMC-PSTC'
Subject: RE: Standard or practical guide to grounding electrical products which 
are not permanently installed

Do not know why bonding materials/construction would not be in the scoped 
safety standard. My typical refs for reliable bonding construction 
requirements/suggestions are:
1. scoped safety standard for the equipment and/or end-use installation.
2. CSA design manual for the scoped standard(s).
3. Section General and/or Inspection Procedures of the affected UL file.
4. CSA No. 0.4
5. NEC article 250 (mostly wiring, but other hardware discussed)

There has to be 10E3 references for this stuff.

Brian

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of Brian Ceresney
Sent: Monday, December 17, 2012 3:59 PM
To: 'EMC-PSTC'
Subject: Standard or practical guide to grounding electrical products which are 
not permanently installed

Dear Regulatory Experts, 
I'm searching for a standard or guideline which will provide detailed 
information about the internal grounding and bonding of products, and I've had 
limited luck in finding anything suiting my purpose. Reviewing a few CSA and UL 
standards hasn't been helpful.  
 
Specifically, I am interested in Class I plug and cord connected products, 
which require the internal grounding wire to be secured to a metal, non-current 
carrying enclosure. I need to know what kinds of screw/nut/washer combinations 
are acceptable, mainly from a North American viewpoint, but not excluding 
Europe.(As usual, I'm working with small industrial-type battery chargers 
drawing less than 12A at 120V, 6A at 240V). 
  
I'm particularly interested in requirements/acceptability of thread-cutting or 
-forming screws, with or without locking washers. I'm wondering about their 
securement performance over time.
 
The standards I've reviewed so far seem to be very non-specific about 
requirements, while specifying some testing. Are there any documents out there 
that are more detailed? 
 
Thanks in Advance,  
Brian C. 
 
Brian Ceresney, CTech.
Regulatory Team Lead,
Delta-Q Technologies Corp.
3755 Willingdon Ave.,
Burnaby, BC  Canada  V5G 3H3
Tel: 604-566-8827
www.delta-q.com
bceres...@delta-q.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] Standard or practical guide to grounding electrical products which are not permanently installed

2012-12-17 Thread Brian Oconnell
Do not know why bonding materials/construction would not be in the scoped
safety standard. My typical refs for reliable bonding construction
requirements/suggestions are:
1. scoped safety standard for the equipment and/or end-use installation.
2. CSA design manual for the scoped standard(s).
3. Section General and/or Inspection Procedures of the affected UL file.
4. CSA No. 0.4
5. NEC article 250 (mostly wiring, but other hardware discussed)

There has to be 10E3 references for this stuff.

Brian

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of Brian
Ceresney
Sent: Monday, December 17, 2012 3:59 PM
To: 'EMC-PSTC'
Subject: Standard or practical guide to grounding electrical products which
are not permanently installed

Dear Regulatory Experts, 
I'm searching for a standard or guideline which will provide detailed
information about the internal grounding and bonding of products, and I've
had limited luck in finding anything suiting my purpose. Reviewing a few CSA
and UL standards hasn't been helpful.  
 
Specifically, I am interested in Class I plug and cord connected products,
which require the internal grounding wire to be secured to a metal,
non-current carrying enclosure. I need to know what kinds of
screw/nut/washer combinations are acceptable, mainly from a North American
viewpoint, but not excluding Europe.(As usual, I'm working with small
industrial-type battery chargers drawing less than 12A at 120V, 6A at 240V).

  
I'm particularly interested in requirements/acceptability of thread-cutting
or -forming screws, with or without locking washers. I'm wondering about
their securement performance over time.
 
The standards I've reviewed so far seem to be very non-specific about
requirements, while specifying some testing. Are there any documents out
there that are more detailed? 
 
Thanks in Advance,  
Brian C. 
 
Brian Ceresney, CTech.
Regulatory Team Lead,
Delta-Q Technologies Corp.
3755 Willingdon Ave.,
Burnaby, BC  Canada  V5G 3H3
Tel: 604-566-8827
www.delta-q.com
bceres...@delta-q.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: