Sam -

Your post was no doubt sent before I replied to John Allen.
FWIW, I'll try to add some clarity on the power cross
testing.

The power lines that are collocated with telecommunication
lines are typically medium voltage.  There are both induced
voltages into and metallic power cross to the
telecommunication lines.  The primary protector at a
building entrance limits the voltages available to do harm
to 600Vrms (assumed sinusoidal).  There might also be
secondary protection on telecommunication lines that include
supplemental overvoltage protection that limits the voltage
downstream to even lesser levels.

The 120V and 240V power cross tests are to simulate someone
digging and tearing through both a branch circuit and a
telecommunication line in a stroke.

While much of the telecommunications infrastructure is
buried, I hesitate to say most is.  In most new
construction since ~1970, perhaps earlier, it is.  It
certainly isn't in my parents' neighborhood; or probably
most older neighborhoods and business districts, especially
those that are less wealthy than others.

Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com



 From: Sam Davis
 Sent: Thursday, December 12, 2002 7:56 AM

 In the US, aren't overhead power lines in the 10
 kV range?

 Anyway, my point here is that the power line
 cross at the overhead poles
 won't just put 120V on the phone lines, but 10kV,
 likely incinerating the
 line.   I'm not sure where the power line cross
 test is simulating, but it's
 not at the overhead poles.

 Besides that, most telephone wiring is buried.

 Just my 2C,
 Sam



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: TNV Test Generator

2002-12-13 Thread Peter L. Tarver

You're welcome, John.

Yes, the test seems brutal.  In North America, ringing is
maximum 105Vrms, possibly riding on up to a -56.5Vdc wetted
line (but not necessarily) and is limited to a few tens of
mA.  120V/1200Ohms is still only 100mA, but that doesn't
mean it won't cause grief at 3-5 times the US ringing
current.

However, the specification is for that source, IF there
isn't one available to simulate the actual network.  Sort of
a poor man's networks simulator.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
2000 Ringwood Ave.
San Jose, CA 95131-1749
V: 408-904-2081
F: 408-904-2095
M: 408-234-3529
peter.tar...@sanmina-sci.com

 From: John Allen
 Sent: Thursday, December 12, 2002 8:18 AM

 Peter

 Thanks for that - quite a different background to
 how it seemed to read to
 me!

 But in that case it does seem a bit of a brutal
 test to apply to guard
 against a hazard caused solely by a
 telecomms-circuit source - surely a
 relatively low power source would be appropriate?

 Any idea why they did not more closely specify
 the equipment to be used?

 Regards

 Johh Allen



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: TNV Test Generator

2002-12-12 Thread John Allen

Peter

Thanks for that - quite a different background to how it seemed to read to
me!

But in that case it does seem a bit of a brutal test to apply to guard
against a hazard caused solely by a telecomms-circuit source - surely a
relatively low power source would be appropriate?

Any idea why they did not more closely specify the equipment to be used?

Regards

Johh Allen


-Original Message-
From: Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: 12 December 2002 16:04
To: John Allen; emc-p...@majordomo.ieee.org
Subject: RE: TNV Test Generator


John, et al -

No this is not the power cross test, which is described in
Annex NAC of CSA/UL60950, third ed.  This test is intended
to simulate continuous ringing from the network, is akin the
an SELV reliability test and, IIRC, was added to the base
IEC 60950 standard at the behest of the French, due to
limitations in their ability to guarantee cadenced ringing
at all locations in their networks.

Don Boroski is correct about test setup, though I'd use a
variable autotransformer after an isolation transformer to
set the voltage, rather than just taking it off of the line.

As to real world power cross, on 15NON2000 I forwarded an
unedited copy of a usenet posting containing a link to the
Orange County on 15NOV2000, where power cross caused some
small fires and fire fighters evacuated several homes.
Because my post is not in the mindcruiser archive and the
link in it to the newspaper article is now broken, I've
placed a copy in the Info Pieces in the telecom general
topics category on the mindcruiser site.  The poster's
remarks are also very interesting.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com


_
This e-mail has been scanned for viruses by the WorldCom Internet Managed
Scanning Service - powered by MessageLabs. For further information visit
http://www.worldcom.com


*
Copyright ERA Technology Ltd. 2002. (www.era.co.uk). All rights reserved. 
The information supplied in this Commercial Communication should be treated
in confidence.
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.

_
This e-mail has been scanned for viruses by the WorldCom Internet Managed 
Scanning Service - powered by MessageLabs. For further information visit 
http://www.worldcom.com

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: TNV Test Generator

2002-12-12 Thread Peter L. Tarver

John, et al -

No this is not the power cross test, which is described in
Annex NAC of CSA/UL60950, third ed.  This test is intended
to simulate continuous ringing from the network, is akin the
an SELV reliability test and, IIRC, was added to the base
IEC 60950 standard at the behest of the French, due to
limitations in their ability to guarantee cadenced ringing
at all locations in their networks.

Don Boroski is correct about test setup, though I'd use a
variable autotransformer after an isolation transformer to
set the voltage, rather than just taking it off of the line.

As to real world power cross, on 15NON2000 I forwarded an
unedited copy of a usenet posting containing a link to the
Orange County on 15NOV2000, where power cross caused some
small fires and fire fighters evacuated several homes.
Because my post is not in the mindcruiser archive and the
link in it to the newspaper article is now broken, I've
placed a copy in the Info Pieces in the telecom general
topics category on the mindcruiser site.  The poster's
remarks are also very interesting.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: TNV Test Generator

2002-12-12 Thread Sam Davis

In the US, aren't overhead power lines in the 10 kV range?  The power
companies send power down the lines in kV (with relatively low current), and
in the neighborhood of the customer, they have a large transformer which
brings the voltage down to the 120 V range, with 100s of amps for that short
run.  The reason for this transmission scheme is that power (and power loss)
is equal to I^2 R, so the higher the voltage, the lower the current
necessary, and thus lower power loss over miles of resistance.

Anyway, my point here is that the power line cross at the overhead poles
won't just put 120V on the phone lines, but 10kV, likely incinerating the
line.   I'm not sure where the power line cross test is simulating, but it's
not at the overhead poles.

Besides that, most telephone wiring is buried.  It is becoming increasingly
rare to have telephone poles holding telephone wires.  I'm not saying this
is a reason to remove this requirement, because as long as the condition may
exist in a normal or single fault (storm), there is a need to evaluate
and/or test for it.

Just my 2C,
Sam

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of John Allen
Sent: Thursday, December 12, 2002 2:43 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: TNV Test Generator



Hi Folks

Is this not just the old UL/CSA (UL 1457/1950 etc) test to simulate a 120V
power line falling onto the external POTS (etc)cable?

In which case the test generator would be as per the relevant UL/CSA specs,
and from memory that is similar to what has been suggested by Ken Javor or
Don Borowski.

This test was carried out because in North Americal most telephone cables
and power cables are strung on poles - and the lines contact each other when
the poles get knocked down by the awful weather (and/or awful drivers in
some cases!) they often get in many states (Thank goodness I live in the UK
- we don't get as much weather like that!)

BTW, IMHO:
a) Instead of a default of 120V, the test should specify the default to be
application of the maximum nominal supply voltage of the equipment being
tested, since that is likely to represent more closely the supply voltage on
the power poles where the equipment is to be installed. [i.e. it would be
120V for N. America, but it would be 230V for Europe - and so on].

b) Even the latter does not address the problem that many overhead power
distribution cables are 3-phase - so the test voltage should be the maximum
phase-to-phase voltage in question.

However, it has to said that the above changes would not go down well with
suppliers of existing certified equipment - and I have no history to prove
that the existing test is anything but adequate.

Does anyone else know of real world problems that this test does not
cover?

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel:+44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax:+44 (0) 1372-367102 (Fax)


-Original Message-
From: don_borow...@selinc.com [mailto:don_borow...@selinc.com]
Sent: 11 December 2002 22:19
To: emc-p...@majordomo.ieee.org
Subject: Re: TNV Test Generator




Am I missing something, or can you not just take a low impedance source of
120 VAC and simply add an external 1200 resistor in series with its output?

Don Borowski
Schweitzer Engineer Labs
Pullman, WA





FastWave bi...@fastwave.com@majordomo.ieee.org on 12/11/2002 12:55:45 PM

Please respond to FastWave bi...@fastwave.com

Sent by:owner-emc-p...@majordomo.ieee.org


To:'emc-p...@majordomo.ieee.org' emc-p...@majordomo.ieee.org
cc:
Subject:TNV Test Generator



Telecom - Product Safety Question:

I am looking for a test generator per clause 2.3.5 of IEC60950 = a test
generator is used that provides 120 V +/- 2 VAC at 50 or 60 Hz and has an
internal impedance of 1200 ohms +/- 2%. Anybody have any input on a source
to buy or a method to build such a device. It's the internal impedance
aspect that's throwing me for a loop.

Thanks for your time and input,

Bill Bisenius
EDD
bi...@productsafet.com mailto:bi...@productsafet.com
North Carolina - the natural disaster capital of the U.S. - last week's ice
storm left us all without power, heat, or phones for several days (during
30
degree weather). Come to North Carolina and have your house smashed by
falling ice covered trees (or hurricanes in the summer).



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy

RE: TNV Test Generator

2002-12-12 Thread John Allen

Hi Folks

Is this not just the old UL/CSA (UL 1457/1950 etc) test to simulate a 120V
power line falling onto the external POTS (etc)cable? 

In which case the test generator would be as per the relevant UL/CSA specs,
and from memory that is similar to what has been suggested by Ken Javor or
Don Borowski.

This test was carried out because in North Americal most telephone cables
and power cables are strung on poles - and the lines contact each other when
the poles get knocked down by the awful weather (and/or awful drivers in
some cases!) they often get in many states (Thank goodness I live in the UK
- we don't get as much weather like that!)

BTW, IMHO: 
a) Instead of a default of 120V, the test should specify the default to be
application of the maximum nominal supply voltage of the equipment being
tested, since that is likely to represent more closely the supply voltage on
the power poles where the equipment is to be installed. [i.e. it would be
120V for N. America, but it would be 230V for Europe - and so on].

b) Even the latter does not address the problem that many overhead power
distribution cables are 3-phase - so the test voltage should be the maximum
phase-to-phase voltage in question.

However, it has to said that the above changes would not go down well with
suppliers of existing certified equipment - and I have no history to prove
that the existing test is anything but adequate.

Does anyone else know of real world problems that this test does not
cover?

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel:+44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax:+44 (0) 1372-367102 (Fax)


-Original Message-
From: don_borow...@selinc.com [mailto:don_borow...@selinc.com]
Sent: 11 December 2002 22:19
To: emc-p...@majordomo.ieee.org
Subject: Re: TNV Test Generator




Am I missing something, or can you not just take a low impedance source of
120 VAC and simply add an external 1200 resistor in series with its output?

Don Borowski
Schweitzer Engineer Labs
Pullman, WA





FastWave bi...@fastwave.com@majordomo.ieee.org on 12/11/2002 12:55:45 PM

Please respond to FastWave bi...@fastwave.com

Sent by:owner-emc-p...@majordomo.ieee.org


To:'emc-p...@majordomo.ieee.org' emc-p...@majordomo.ieee.org
cc:
Subject:TNV Test Generator



Telecom - Product Safety Question:

I am looking for a test generator per clause 2.3.5 of IEC60950 = a test
generator is used that provides 120 V +/- 2 VAC at 50 or 60 Hz and has an
internal impedance of 1200 ohms +/- 2%. Anybody have any input on a source
to buy or a method to build such a device. It's the internal impedance
aspect that's throwing me for a loop.

Thanks for your time and input,

Bill Bisenius
EDD
bi...@productsafet.com mailto:bi...@productsafet.com
North Carolina - the natural disaster capital of the U.S. - last week's ice
storm left us all without power, heat, or phones for several days (during
30
degree weather). Come to North Carolina and have your house smashed by
falling ice covered trees (or hurricanes in the summer).



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

_
This e-mail has been scanned for viruses by the WorldCom Internet Managed
Scanning Service - powered by MessageLabs. For further information visit
http://www.worldcom.com

Re: TNV Test Generator

2002-12-12 Thread Don_Borowski


Am I missing something, or can you not just take a low impedance source of
120 VAC and simply add an external 1200 resistor in series with its output?

Don Borowski
Schweitzer Engineer Labs
Pullman, WA





FastWave bi...@fastwave.com@majordomo.ieee.org on 12/11/2002 12:55:45 PM

Please respond to FastWave bi...@fastwave.com

Sent by:owner-emc-p...@majordomo.ieee.org


To:'emc-p...@majordomo.ieee.org' emc-p...@majordomo.ieee.org
cc:
Subject:TNV Test Generator



Telecom - Product Safety Question:

I am looking for a test generator per clause 2.3.5 of IEC60950 = a test
generator is used that provides 120 V +/- 2 VAC at 50 or 60 Hz and has an
internal impedance of 1200 ohms +/- 2%. Anybody have any input on a source
to buy or a method to build such a device. It's the internal impedance
aspect that's throwing me for a loop.

Thanks for your time and input,

Bill Bisenius
EDD
bi...@productsafet.com mailto:bi...@productsafet.com
North Carolina - the natural disaster capital of the U.S. - last week's ice
storm left us all without power, heat, or phones for several days (during
30
degree weather). Come to North Carolina and have your house smashed by
falling ice covered trees (or hurricanes in the summer).



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: TNV Test Generator

2002-12-11 Thread Ken Javor

It's bad form to answer a question with a question, but I will ask a very 
simple-minded question: Is the specified test generator anything different
than the ac line (possibly through an isolation transformer) in series with
1200 Ohms?

--
From: FastWave bi...@fastwave.com
To: 'emc-p...@majordomo.ieee.org' emc-p...@majordomo.ieee.org
Subject: TNV Test Generator
Date: Wed, Dec 11, 2002, 2:55 PM



 Telecom - Product Safety Question:

 I am looking for a test generator per clause 2.3.5 of IEC60950 = a test
 generator is used that provides 120 V +/- 2 VAC at 50 or 60 Hz and has an
 internal impedance of 1200 ohms +/- 2%. Anybody have any input on a source
 to buy or a method to build such a device. It's the internal impedance
 aspect that's throwing me for a loop.

 Thanks for your time and input,

 Bill Bisenius
 EDD
 bi...@productsafet.com mailto:bi...@productsafet.com
 North Carolina - the natural disaster capital of the U.S. - last week's ice
 storm left us all without power, heat, or phones for several days (during 30
 degree weather). Come to North Carolina and have your house smashed by
 falling ice covered trees (or hurricanes in the summer).



 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


TNV Test Generator

2002-12-11 Thread FastWave

Telecom - Product Safety Question:

I am looking for a test generator per clause 2.3.5 of IEC60950 = a test
generator is used that provides 120 V +/- 2 VAC at 50 or 60 Hz and has an
internal impedance of 1200 ohms +/- 2%. Anybody have any input on a source
to buy or a method to build such a device. It's the internal impedance
aspect that's throwing me for a loop.

Thanks for your time and input,

Bill Bisenius
EDD
bi...@productsafet.com mailto:bi...@productsafet.com 
North Carolina - the natural disaster capital of the U.S. - last week's ice
storm left us all without power, heat, or phones for several days (during 30
degree weather). Come to North Carolina and have your house smashed by
falling ice covered trees (or hurricanes in the summer).



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list